Thanks ! 
A very clear answer.   Not the one I wanted, but clear.




>________________________________
> From: Boštjan Glavič <bostjan.gla...@siq.si>
>To: Bill Owsley <wdows...@yahoo.com> 
>Cc: "EMC-PSTC@LISTSERV.IEEE.ORG" <EMC-PSTC@LISTSERV.IEEE.ORG> 
>Sent: Saturday, May 11, 2013 12:29 PM
>Subject: Re: [PSES] safety 60950 and surge suppression circuits
> 
>
>Hi Bill,
>
>You can use MOV (VDR) primary to PE as long as you have reliable earth. 
>Reliable earth is considered for pluggable equipment type B or permanently 
>connected equipment. For pluggable equipment type A, you would need additional 
>earthing point, what is usually not acceptable for clients.
>
>Unfortunately, if you use combination VDR + GDT, GDT needs to comply with 
>requirements for basic insulation (1500Vac) for any kind of equipment. I know 
>the requirement is strange but also new hazard based standard 62368-1 has the 
>same requirement.
>
>GDT alone cannot use bridge basic insulation primary to PE.
>
>But please note, this is valid for primary circuit only. For secondary 
>circuits no such requirements are applicable.
>
>Best regards,
>Bostjan
>
>
>
>On 11. maj 2013, at 18:09, "Bill Owsley" 
><wdows...@yahoo.com<mailto:wdows...@yahoo.com>> wrote:
>
>I'm running into a dilemma.   Not being a Safety Engineer myself, but rubbing 
>elbows with them...
>On a piece of ITE equipment, I need some surge suppression for worldwide 
>markets with one annoying requirement for 4 kV, otherwise just 2 kV line to 
>earth, and using either plugable cords or permanent connection, whichever is 
>worse.
>Now the Safety guys  tell me that MOV's alone cannot bridge the insulation 
>(Basic or Functional, I forget.)  between primary and earth, when using one of 
>power cable options mentioned above.
>But a proper qualified (GDT) gas discharge tube can do the bridging.  So we 
>figured to use them in series.
>On a quick and dirty bench test it works to 4 kV.
>Then the Safety guys pull out the rest of the story and point out 5.2.2 which 
>seems to indicate that the GDT is to meet the Hi-Pot test, 1500 vac.
>Previously, section, 1.5.9.4 (?)  indicates that the surge protection devices 
>can be removed during the Hi-Pot test.
>But now I have a Surge suppression circuit that has to withstand the same 
>Hi-Pot as the rest of the board.
>Question is how does a surge protection circuit protect the board when it has 
>to meet the same Hi-Pot test?
>In other words, when a surge comes along, which is going to break over first?
>The surge protection or the board?
>Is the purpose of surge suppression is to keep the clamped voltage below a 
>problem level?
>What am I missing in this?
>
>Thanks...
>- Bill
>
>-
>----------------------------------------------------------------
>
>This message is from the IEEE Product Safety Engineering Society emc-pstc 
>discussion list. To post a message to the list, send your e-mail to 
><emc-p...@ieee.org<mailto:emc-p...@ieee.org>>
>
>All emc-pstc postings are archived and searchable on the web at: 
>http://www.ieee-pses.org/emc-pstc.html
>
>Attachments are not permitted but the IEEE PSES Online Communities site at 
>http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
>formats), large files, etc.
>
>Website: http://www.ieee-pses.org/
>Instructions: http://listserv.ieee.org/request/user-guide.html
>List rules: http://www.ieee-pses.org/listrules.html
>
>For help, send mail to the list administrators:
>Scott Douglas <emcp...@radiusnorth.net<mailto:emcp...@radiusnorth.net>>
>Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>
>
>For policy questions, send mail to:
>Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
>David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>
>
>-
>----------------------------------------------------------------
>This message is from the IEEE Product Safety Engineering Society emc-pstc 
>discussion list. To post a message to the list, send your e-mail to 
><emc-p...@ieee.org>
>
>All emc-pstc postings are archived and searchable on the web at:
>http://www.ieee-pses.org/emc-pstc.html
>
>Attachments are not permitted but the IEEE PSES Online Communities site at 
>http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
>formats), large files, etc.
>
>Website:  http://www.ieee-pses.org/
>Instructions:  http://listserv.ieee.org/request/user-guide.html
>List rules: http://www.ieee-pses.org/listrules.html
>
>For help, send mail to the list administrators:
>Scott Douglas <emcp...@radiusnorth.net>
>Mike Cantwell <mcantw...@ieee.org>
>
>For policy questions, send mail to:
>Jim Bacher:  <j.bac...@ieee.org>
>David Heald: <dhe...@gmail.com>
>
>
>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <emcp...@radiusnorth.net>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to