I'm hoping that you can provide one of your straightforward "Rich Nute Explanations" for the apparent contradiction behind the rationale that allows a surge protection component to be placed across a required safety isolation barrier, and then removed for the purpose of performing the hipot test.
I have been involved with safety compliance for over 30 years, and this concept is one that has never made complete sense to me. On one level, I can just bump along and limit my attention to what the safety standard actually says, but I would like to understand what the thinking is behind that.
This allowance (removing surge protection components for the hipot test) appears in a variety of standards and clauses within those standards, such as EN 60950-1, clauses 5.2.2, 6.1.2, and 6.2.2.
If you could help clarify the thinking behind this allowance, I would greatly appreciate it.
Thanks,
Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
[email protected]
http://www.randolph-telecom.com
Hi Bill:
SPDs, regardless of configuration, are notorious for being
prone to failure, either short-circuit or open-circuit or
any value of resistance between those two extremes. (One
cannot predict the energy the SPD will be required to
dissipate.)
From a safety point of view, all such failures must be
accounted for such that the safety of the equipment is not
compromised by any failure of the SPD.
If the SPD should fail open-circuit, then expected
transients that are therefore not attenuated, must not
cause the insulation to fail. Hence, the insulation must
pass the hi-pot test without the SPD in place.
As for the requirement for the GDT to pass the hi-pot test...
??? I don't have any rationale for this.
Best regards,
Rich
On 5/10/2013 10:11 AM, Bill Owsley wrote:
I'm running into a dilemma. Not being a Safety Engineer myself, but rubbing elbows with them...
On a piece of ITE equipment, I need some surge suppression for worldwide markets with one annoying requirement for 4 kV, otherwise just 2 kV line to earth, and using either plugable cords or permanent connection, whichever is worse.
Now the Safety guys tell me that MOV's alone cannot bridge the insulation (Basic or Functional, I forget.) between primary and earth, when using one of power cable options mentioned above.
But a proper qualified (GDT) gas discharge tube can do the bridging. So we figured to use them in series.
On a quick and dirty bench test it works to 4 kV.
Then the Safety guys pull out the rest of the story and point out 5.2.2 which seems to indicate that the GDT is to meet the Hi-Pot test, 1500 vac.
Previously, section, 1.5.9.4 (?) indicates that the surge protection devices can be removed during the Hi-Pot test.
But now I have a Surge suppression circuit that has to withstand the same Hi-Pot as the rest of the board.
Question is how does a surge protection circuit protect the board when it has to meet the same Hi-Pot test?
In other words, when a surge comes along, which is going to break over first?
The surge protection or the board?
Is the purpose of surge suppression is to keep the clamped voltage below a problem level?
What am I missing in this?
Thanks...
- Bill
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <[email protected] <mailto:[email protected]>>
All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected] <mailto:[email protected]>>
Mike Cantwell <[email protected] <mailto:[email protected]>>
For policy questions, send mail to:
Jim Bacher <[email protected] <mailto:[email protected]>>
David Heald <[email protected] <mailto:[email protected]>>
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <[email protected]>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>
For policy questions, send mail to:
Jim Bacher: <[email protected]>
David Heald: <[email protected]>
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
[email protected]
http://www.randolph-telecom.com
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <[email protected]>
All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>
For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]>

