My NRTL inspects to NFPA 79 only for field labeling of our machinery.

-Dave

From: Leber, Jody (Suwanee) [mailto:[email protected]]
Sent: Wednesday, October 08, 2014 9:23 AM
To: [email protected]
Subject: Re: [PSES] Scope of NFPA 79

Charlie,

As long as the product is certified to UL 61010-1 by a third party that is 
accepted by the AHJ, you should be fine.  You could also field label it at the 
installation site.  NFPA 79 would not be needed.  The AHJ's are typically 
looking for a third party mark.  Just make sure the third party is accepted by 
the AHJ.  OSHA NRTL does not necessarily mean local AHJ acceptance.  Many 
jurisdiction have their own rules and approval schemes for field labeling.

Best Regards,

Jody Leber
Consumer Testing Services
Global Battery and Accumulator Technical Manager
Battery, Energy Efficiency and Performance Laboratory Manager

Direct: 770.570.1838
Main: 770.570.1800
Mobile: 678.469.9835

From: Charlie Blackham [mailto:[email protected]]
Sent: Wednesday, October 08, 2014 9:01 AM
To: [email protected]
Subject: Re: [PSES] Scope of NFPA 79


Ron / Jody



Product is covered by Semi S2, and 3rd party report.

We apply 61010-1 standards as the equipment is "industrial process control" - 
and will be NRTL listed.



The equipment is going to be sold into more than one jurisdiction - is 
applicability, or not, of NFPA 79 going to come down to interpretation of local 
AHJ, or is there a way I can get a definitive in/out scope decision?



regards

Charlie



________________________________
From: Ronald Wellman <[email protected]>
Sent: 08 October 2014 13:51
To: Charlie Blackham; [email protected]
Subject: RE: [PSES] Scope of NFPA 79

You might want to ask your Customers what they require. Since your equipment 
processes semiconductor gases then SEMI S2 will most likely come into play. 
Also, depending on who your Customers are, they might require field labeling to 
comply with local OSHA requirements, and the standard mostly used in these 
cases is NFPA 79.

Best regards,
Ron Wellman

From: Charlie Blackham [mailto:[email protected]]
Sent: Wednesday, October 8, 2014 3:13 AM
To: [email protected]
Subject: [PSES] Scope of NFPA 79


All



I'm trying to determine whether a product falls within scope of NFPA79 for USA.



EU Machinery Directive determines whether a product is within scope by what it 
does, but my reading of NFPA79 is that the latter also considers "what it does 
it to".



Looking at the 2015 version, NFPA79, Chapter 3, section 3.3.54  defines 
'Industrial Machinery'  as:
" A power-driven machine (or group of machines working together in a 
coordinated manner),  not portable by hand while working, that is used to 
process material by cutting; forming;  pressure; electrical, thermal, or 
optical techniques; lamination; or a combination of these  processes. Machine 
can include associated equipment used to transfer material or tooling,  
including fixtures to assemble/disassemble, to inspect or test, or to package. 
[The associated  electrical equipment, including the logic controller(s) and 
associated software or logic together  with the machine actuators and sensors, 
are considered as part of the industrial machine.]"



The product in question processes gases (in silicon wafer and flat panel 
manufacturing plants) - so I don't think it processes "material".



If that is the case, it would be outside scope of NFPA79, and just within scope 
of NFPA70. Comments?



regards

Charlie


Charlie Blackham
Sulis Consultants Ltd
Tel: +44 (0)7946 624317
Web: 
www.sulisconsultants.com<https://outlook.hslive.net/owa/redir.aspx?C=02be3bf3e3a544d1bdf7b6c99fbd12f5&URL=http%3a%2f%2fwww.sulisconsultants.com%2f>
Registered in England and Wales, number 05466247
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
Information in this email and any attachments is confidential and intended 
solely for the use of the individual(s) to whom it is addressed or otherwise 
directed. Please note that any views or opinions presented in this email are 
solely those of the author and do not necessarily represent those of the 
Company. Finally, the recipient should check this email and any attachments for 
the presence of viruses. The Company accepts no liability for any damage caused 
by any virus transmitted by this email. All SGS services are rendered in 
accordance with the applicable SGS conditions of service available on request 
and accessible at http://www.sgs.com/en/Terms-and-Conditions.aspx
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to