I agree with Pete for the most part. Be careful in claiming compliance with EN 60204-1, however, as there are still some areas where the harmonization is less than perfect (pilot lights, and operator button colours, among others). Also be aware that EN 61439-1 plus EN 61439-X can also be applied to electrical assemblies under the Machinery directive, and are called out by EN 60204-1.
IMO, if the equipment is already being certified under UL 61010 for example, the only only reason to apply NFPA 79 would be where it is helpful and does not conflict with UL 61010. Doug Nix [email protected] On 8-Oct-14, at 14:19, Pete Perkins <[email protected]> wrote: > Charlie, et al, > > I have worked with manufacturers of semiconductor equipment > and have found that NFPA79 is quite useful. As has been mentioned, Semi-S2 > etc. applies to this equipment but this is not a certification standard > accepted by AHJ inspectors in the USA. > > For manufacturer's who don't want to go thru all the expense > of getting a custom designed product Listed to 61010-1 (but design the > product to be in compliance with the needed requirements) a Field Labeling to > NFPA79 is a straightforward way to demonstrate compliance to the AHJ > inspector for installation within the US. The inspection and Field Labeling > is usually done by a local contractor (perhaps a NRTL test house) at the > installation. The manufacturer may also ask for a plant inspection and a > NFPA79 Report to assure themselves that the machine complies, as part of the > S2 evaluation. > > Further, NFPA79 is harmonized with IEC/EN 60204, electrical > safety of machinery. Being able to show compliance with NFPA79 allows the > manufacturer to claim compliance to 60204 within their technical file as part > of the CE marking requirements. Marking as compliant to NFPA79(/60204) has > been used by manufacturers as part of their CE marking process. > Additionally, within the US, many manufacturers have their > electrical panels assembled in a UL Panel Shop. The electrical panel shop - > sometimes a contractor or sometimes a captive shop - can apply their UL Panel > Shop certification sticker to the unit. This is further proof that the key > electrical installation is in compliance with US NFPA70 rules - which are > followed in harmonizing with NFPA79/60204. This eases the NFPA79 inspection > and certification process when the product is assessed and certified on-site, > as required by most jurisdictions. > > You would have to work thru all of the logic steps to show > that Euro designed equipment fully complies with American NFPA79 > requirements. Common issues include adequate breaking capacity for > fusing/circuit breakers, etc. > > Whether or not the scopes are carefully aligned (a legal > question) should not interfere with adopting such a practical scheme by > manufacturers to cover the needed certifications for worldwide acceptance of > this equipment. > > :>) br, Pete > > Peter E Perkins, PE > Principal Product Safety Engineer > PO Box 23427 > Tigard, ORe 97281-3427 > > 503/452-1201 fone/fax > [email protected] > > _ _ _ _ _ _ > > All > > I'm trying to determine whether a product falls within scope of NFPA79 for > USA. > > EU Machinery Directive determines whether a product is within scope by what > it does, but my reading of NFPA79 is that the latter also considers "what it > does it to". > > Looking at the 2015 version, NFPA79, Chapter 3, section 3.3.54 defines > 'Industrial Machinery' as: > " A power-driven machine (or group of machines working together in a > coordinated manner), not portable by hand while working, that is used to > process material by cutting; forming; pressure; electrical, thermal, or > optical techniques; lamination; or a combination of these processes. Machine > can include associated equipment used to transfer material or tooling, > including fixtures to assemble/disassemble, to inspect or test, or to > package. [The associated electrical equipment, including the logic > controller(s) and associated software or logic together with the machine > actuators and sensors, are considered as part of the industrial machine.]" > > The product in question processes gases (in silicon wafer and flat panel > manufacturing plants) - so I don't think it processes "material". > > If that is the case, it would be outside scope of NFPA79, and just within > scope of NFPA70. Comments? > > regards > Charlie > > Charlie Blackham > Sulis Consultants Ltd > Tel: +44 (0)7946 624317 > Web: www.sulisconsultants.com > Registered in England and Wales, number 05466247 > - > ---------------------------------------------------------------- > This message is from the IEEE Product Safety Engineering Society emc-pstc > discussion list. To post a message to the list, send your e-mail to > <[email protected]> > All emc-pstc postings are archived and searchable on the web at: > http://www.ieee-pses.org/emc-pstc.html > Attachments are not permitted but the IEEE PSES Online Communities site at > http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used > formats), large files, etc. > Website: http://www.ieee-pses.org/ > Instructions: http://www.ieee-pses.org/list.html (including how to > unsubscribe) > List rules: http://www.ieee-pses.org/listrules.html > For help, send mail to the list administrators: > Scott Douglas <[email protected]> > Mike Cantwell <[email protected]> > For policy questions, send mail to: > Jim Bacher <[email protected]> > David Heald <[email protected]> > > - > ---------------------------------------------------------------- > This message is from the IEEE Product Safety Engineering Society emc-pstc > discussion list. To post a message to the list, send your e-mail to > <[email protected]> > All emc-pstc postings are archived and searchable on the web at: > http://www.ieee-pses.org/emc-pstc.html > Attachments are not permitted but the IEEE PSES Online Communities site at > http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used > formats), large files, etc. > Website: http://www.ieee-pses.org/ > Instructions: http://www.ieee-pses.org/list.html (including how to > unsubscribe) > List rules: http://www.ieee-pses.org/listrules.html > For help, send mail to the list administrators: > Scott Douglas <[email protected]> > Mike Cantwell <[email protected]> > For policy questions, send mail to: > Jim Bacher <[email protected]> > David Heald <[email protected]> - ---------------------------------------------------------------- This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <[email protected]> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <[email protected]> Mike Cantwell <[email protected]> For policy questions, send mail to: Jim Bacher: <[email protected]> David Heald: <[email protected]>