Is it not also true that you don't have to follow the derating if you are
using a single-outlet circuit (ie the breaker only supplies one single
outlet)?  I thought I remembered that being the case, but I can't quote
chapter and verse.

To add to the list of weird (yet NRTL marked) cables; what about a C13 to
C20 (or C14 to C19) jumper?  I can see cases where this is justifiable, but
it just feels wrong:

https://www.stayonline.com/power-iec-c20-c13-cords.aspx

https://www.stayonline.com/iec-c14-to-c19-15-amp.aspx

-Ken A

On Mon, Oct 9, 2017 at 12:24 PM, Ted Eckert <
[email protected]> wrote:

> Hello Brian,
>
>
>
> This falls under the issue of “continuous” vs. “non-continuous” loads.
> NFPA 70, section 210.19 is one of the clauses that sets the requirement for
> the 80% derating. However, it states: “Where a branch circuit supplies
> continuous loads or any combination of continuous and noncontinuous loads,
> the minimum branch-circuit conductor size shall have an allowable ampacity
> not less than the noncontinuous load plus 125 percent of the continuous
> load.”
>
>
>
> “Continuous” is a load intended to be used for 3 hours or more. A
> hairdryer or microwave are not “continuous”. (If they are, you either have
> too many dogs and need to stop walking them in the rain or you like cooking
> food until it tastes like charcoal.)
>
>
>
> The problem is that a detachable cord with an appliance coupler could be
> used with any product. Unless it has a built-in timer, you have no way of
> guaranteeing that it won’t be used with a product that draws current for
> less than 3 hours. There may be “non-continuous” loads with an appliance
> coupler and rated for 15 A. As such, I would expect such a detachable cord
> to need to be rated for at least 15 A.
>
>
>
> A cord with a NEMA 5-20P would then be prohibited from having a C13
> connector at the other end. It would need a C19 instead.
>
>
>
> That being said, for some specialty industries, you can find some strange
> combinations of plugs and receptacles.
>
> http://www.marinco.com/en/s15-504
>
>
>
> Ted Eckert
>
> Microsoft Corporation
>
>
>
> The opinions expressed are my own and do not necessarily reflect those of
> my employer.
>
>
>
> *From:* Kunde, Brian [mailto:[email protected]]
> *Sent:* Monday, October 9, 2017 8:31 AM
> *To:* [email protected]
> *Subject:* [PSES] NEMA 5-20P with IEC 60320 C13
>
>
>
> It is my understanding that according to the US National Electric Code, 15
> amp receptacle are derated to 12 amps max., and 20 amp receptacles are
> derated to 16 amps.
>
>
>
> IEC 60320 C13 connectors are rated 15 amps in North America. Do I derate
> them as well or can I draw 15 amps continuous from the C13 connector?
>
>
>
> So here is the big question:
>
>
>
> If I have a power cord with a NEMA-5-20P at one end, IEC 60320 C13 at the
> other end, and 14awg cordage (rated 18A), can I use/ship this power cord
> with a product rated 15 amps?
>
>
>
> Thanks to all.
>
> The Other Brian
> ------------------------------
> *LECO Corporation Notice:* This communication may contain confidential
> information intended for the named recipient(s) only. If you received this
> by mistake, please destroy it and notify us of the error. Thank you.
>
> -
> ----------------------------------------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to <
> [email protected]>
>
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
> <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Ccd07d70741384ef672a708d50f2ad7c1%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636431599042974081&sdata=KPn0zexfjGkIaute9FWGP4vvV00uCRcuq6GtjQwrsoc%3D&reserved=0>
>
> Attachments are not permitted but the IEEE PSES Online Communities site at
> http://product-compliance.oc.ieee.org/
> <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Ccd07d70741384ef672a708d50f2ad7c1%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636431599042974081&sdata=q%2FDeWz1bT6EE9ZzNJ6pCeXkgJ15OalJ9h%2FLcaw3NxwE%3D&reserved=0>
> can be used for graphics (in well-used formats), large files, etc.
>
> Website: http://www.ieee-pses.org/
> <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Ccd07d70741384ef672a708d50f2ad7c1%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636431599042974081&sdata=cqdYdOYIlOCxox3pWdNSzaHQ8h78bRZpog6wz48PYUU%3D&reserved=0>
> Instructions: http://www.ieee-pses.org/list.html (including how to
> unsubscribe)
> <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Ccd07d70741384ef672a708d50f2ad7c1%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636431599042974081&sdata=pTffGjqXHDDcluuvgpr4zQcuPEaUev8Wfdu%2BM13esH0%3D&reserved=0>
> List rules: http://www.ieee-pses.org/listrules.html
> <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Ccd07d70741384ef672a708d50f2ad7c1%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636431599042974081&sdata=zlByB75xMImmpqiaNEUPl6kS0%2Bqf%2B%2BcdBD%2BQqP6OjDs%3D&reserved=0>
>
> For help, send mail to the list administrators:
> Scott Douglas <[email protected]>
> Mike Cantwell <[email protected]>
>
> For policy questions, send mail to:
> Jim Bacher <[email protected]>
> David Heald <[email protected]>
> -
> ----------------------------------------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to &LT;
> [email protected]&GT;
>
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
>
> Attachments are not permitted but the IEEE PSES Online Communities site at
> http://product-compliance.oc.ieee.org/ can be used for graphics (in
> well-used formats), large files, etc.
>
> Website: http://www.ieee-pses.org/
> Instructions: http://www.ieee-pses.org/list.html (including how to
> unsubscribe) <http://www.ieee-pses.org/list.html>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
> Scott Douglas &LT;[email protected]&GT;
> Mike Cantwell &LT;[email protected]&GT;
>
> For policy questions, send mail to:
> Jim Bacher &LT;[email protected]&GT;
> David Heald &LT;[email protected]&GT;
>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to