The various clauses of NFPA 70 are reviewed, challenged, debated, argued and 
rewritten. I don’t think the clause in question remains because nobody has 
challenged it. Part of the issue is that the electrical infrastructure in the 
U.S. has been developed around this rule. If affects circuit breaker trip 
curves, conduit fill, wire sizes and rating and many other aspects of a 
building’s electrical system. If the rule were changed, would there be problems 
switching over? Would you have overheating in older structures where circuit 
breakers were replaced without updating wiring? Wold there be other effects of 
mixing 80% and 100% rated components? How many U.S. national standards would 
need to be updated?

It is a poor analogy, but think about switching sides that you drive on the 
road. Sweden switched on September 3, 1967. Street signs, traffic signals and 
road markings all had to be changed. Headlights had to be adjusted or re-aimed. 
For quite a while, there was a mix of left-hand and right-hand drive cars. It 
was a massive undertaking for a country with fewer people than either London or 
New York City.

Changing the way branch circuits are rated in the U.S. could be done, but it 
would be an extremely complicated undertaking. The risks of a mismatch of 
circuits, circuit protection and loads would be significant for a long time. I 
suspect that by the time the technology evolved to the point where the 
requirement could be eliminated, it was too late and eliminating it would 
result in too much expense and rework.

Ted Eckert
Microsoft Corporation

The opinions expressed are my own and do not necessarily reflect those of my 
employer.

From: John Woodgate [mailto:[email protected]]
Sent: Tuesday, October 10, 2017 12:49 PM
To: [email protected]
Subject: Re: [PSES] NEMA 5-20P with IEC 60320 C13


Well, yes, because the IEC tends to believe that rated values are realistic and 
do not need to be adjusted downwards. I suspect that at some point in the 
distant past (maybe even nearly 100 years ago), some connectors in wide use 
were found to overheat at rated current, so the 'derating rule' was brought in, 
and no-one has challenged it since.

John Woodgate OOO-Own Opinions Only

J M Woodgate and Associates 
www.woodjohn.uk<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.woodjohn.uk&data=02%7C01%7Cted.eckert%40microsoft.com%7Cb9a5abba70d24e2f093e08d51018031b%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636432617679408094&sdata=jNpj%2FFhCHx9ir37o7Xf5GxovOe2h0nU9FIZnbo5mItE%3D&reserved=0>

Rayleigh, Essex UK
On 2017-10-10 20:12, Ralph McDiarmid wrote:

The NEC (NFPA 70) talks about “continuous currents” and when to apply the 
all-too-familiar 125% rule.  Canadian Electric Code (CSA part I) has same 
requirement.  The IEC seems to have avoided it.



Ralph McDiarmid

Product Compliance

Engineering

Solar Business

Schneider Electric

D  604-422-2622



From: Kunde, Brian [mailto:[email protected]]

Sent: Monday, October 09, 2017 8:31 AM

To: [email protected]<mailto:[email protected]>

Subject: [PSES] NEMA 5-20P with IEC 60320 C13



It is my understanding that according to the US National Electric Code, 15 amp 
receptacle are derated to 12 amps max., and 20 amp receptacles are derated to 
16 amps.



IEC 60320 C13 connectors are rated 15 amps in North America. Do I derate them 
as well or can I draw 15 amps continuous from the C13 connector?



So here is the big question:



If I have a power cord with a NEMA-5-20P at one end, IEC 60320 C13 at the other 
end, and 14awg cordage (rated 18A), can I use/ship this power cord with a 
product rated 15 amps?



Thanks to all.

The Other Brian

________________________________________

LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.



-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]><mailto:[email protected]>



All emc-pstc postings are archived and searchable on the web at:

http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cb9a5abba70d24e2f093e08d51018031b%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636432617679408094&sdata=zC0HNIXqIogkZMth1h1zUiqWn3Mc8rEi9eXz6xZ14kk%3D&reserved=0>



Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Cb9a5abba70d24e2f093e08d51018031b%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636432617679408094&sdata=raSduLOrqGxhkL4IdY%2FH6Gqga1qcTDFzuiFS9I4HNfo%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.



Website:  
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Cb9a5abba70d24e2f093e08d51018031b%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636432617679408094&sdata=f8tEK4esWBTlU8%2FUC9J0%2FKhPXX22DdtSZkfbujvkDsg%3D&reserved=0>

Instructions:  
http://www.ieee-pses.org/list.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cb9a5abba70d24e2f093e08d51018031b%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636432617679408094&sdata=9FinxY9DwUzyIHdXWFfu8XUVkuZYpBLt9BIBevGv80Q%3D&reserved=0>
 (including how to unsubscribe)

List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cb9a5abba70d24e2f093e08d51018031b%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636432617679408094&sdata=eFRhNHWPccXgpFJazny6Bcu9JPspAtW8QSOvT2GLxNo%3D&reserved=0>



For help, send mail to the list administrators:

Scott Douglas <[email protected]><mailto:[email protected]>

Mike Cantwell <[email protected]><mailto:[email protected]>



For policy questions, send mail to:

Jim Bacher:  <[email protected]><mailto:[email protected]>

David Heald: <[email protected]><mailto:[email protected]>

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cb9a5abba70d24e2f093e08d51018031b%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636432617679408094&sdata=zC0HNIXqIogkZMth1h1zUiqWn3Mc8rEi9eXz6xZ14kk%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Cb9a5abba70d24e2f093e08d51018031b%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636432617679408094&sdata=raSduLOrqGxhkL4IdY%2FH6Gqga1qcTDFzuiFS9I4HNfo%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7Cb9a5abba70d24e2f093e08d51018031b%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636432617679408094&sdata=f8tEK4esWBTlU8%2FUC9J0%2FKhPXX22DdtSZkfbujvkDsg%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cb9a5abba70d24e2f093e08d51018031b%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636432617679408094&sdata=9FinxY9DwUzyIHdXWFfu8XUVkuZYpBLt9BIBevGv80Q%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7Cb9a5abba70d24e2f093e08d51018031b%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636432617679408094&sdata=eFRhNHWPccXgpFJazny6Bcu9JPspAtW8QSOvT2GLxNo%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to