Group,

This topic has resurrected a question I have always had about AC Mains Power in 
Europe.  I have always believed that 230Vac in Europe is derived from 3-phase.  
I could see where a home or small business might be powered only by a single 
phase, but wouldn't a large company or factory be powered by 3-phase and to 
which a single room or lab would most likely have receptacles powered by 
different circuits on different phases of the 380V?

Also, surge pulses can be cause by many sources that do not make the surge 
common mode to an entire building, so it is most possible that a "System" can 
see a surge on one power cord and not on all power cords.

Here is the States, our homes are generally powered by Split Phase AC where the 
receptacles within the same room are on different circuits and different 
phases.  In Canada, it is common to have two phases of 208 powering 115V 
receptacles within the same dual receptacle.

Here at work within our lab (in the States), our 230V high powered equipment is 
powered by its own dedicated 230V L-L circuit derived from a 230V 3-phase 
transformer. Each 230V receptacle has its own circuit and which could be on 
different L-L phases. Lower powered 230V equipment is powered off a different 
transformer and all of our 115V receptacles throughout the building is powered 
by one of 3-phases Line to Neutral circuits derived from 208V 3-phase.   It is 
common for adjacent 115V receptacles to be on different phases.   So a typical 
system setup in our work area is almost guaranteed to powered by different 
circuits, different phases, and  different transformers within our company's 
multiple source power system. BTW, we also have lighting powered by 277V 
derived from L-N on our 480V 3-phase power which comes right off the pole.  
This 480V 3-phase powers the entire building including all of our transformers.

Is this type of power distribution not common in larger facilities within 
Europe?

The Other Brian

From: Larry K. Stillings [mailto:[email protected]]
Sent: Wednesday, January 02, 2019 5:16 PM
To: [email protected]
Subject: [PSES] IEC 61000-4-5 Surge Testing Single plug vs. multiple plug system

All,

I received the following email from a customer today via their customer 
addressing our application of surge testing. We are testing laboratory 
equipment per IEC/EN 61326-1 and IEC/EN 61326-2-6 and specifically are having 
failures with respect to surge on a system that has multiple power cords. We 
are testing one power cord at a time. Here are their comments

we have never tested a system comprised of multiple instruments in this way 
before. i.e. applying surge to one unit at a time - we have always, with 
agreement from our customers, applied surge (and in fact all tests) to all of 
the units plugged into e.g. a mains distribution block all at the same time. 
Especially for surge, it seems unlikely that in the real world any real surge 
on the mains supply would not affect all things in a system as it is very 
likely they are all plugged into the same mains circuit in e.g a particular 
room. To further bolster this, we have made comment to customers in the past 
that it could be noted in the manual to ensure this is the case.

 By applying surge to all units at the same time, we maintain all of their 
supply voltages at the same level. I can see how, by applying a surge to a 
single part of the wider system, communications issues could occur as suddenly 
the points of reference (i.e. reference voltages) for different parts of the 
system could be pulled away from each other by the surge.

Testing a system by applying the tests to all at once, rather than a single 
item at a time, isn't necessarily an "easy way out" either. For other tests 
e.g. conducted emissions, where noise transmitted from the unit under test back 
onto the mains supply is measured, passing is made more difficult by measuring 
all units at once. Where in this case one at a time would be much more 
favourable. Our test house has always advised that we can choose, either all 
tests one at a time, or all tests applied to all through a mains block, but we 
cannot mix and match between different sections for the conducted EMC tests.

I know this brings up all sorts of questions, however I would like to focus on 
the surge testing at the moment. I am pretty sure at least one of the standards 
says conducted emissions shall be tested on each port individually, but we 
don't need to go there right now ;-)

Thoughts when you get responses like this?
Larry K. Stillings
Compliance Worldwide, Inc.
Test Locally, Sell Globally and Launch Your Products Around the World!
FCC - Wireless - Telecom - CE Marking - International Approvals - Product Safety
357 Main Street
Sandown, NH 03873
(603) 887 3903 Fax 887-6445
www.complianceworldwide.com<http://www.complianceworldwide.com>

Privileged/Confidential Information may be contained in this message. If you 
are not the addressee indicated in this message (or responsible for delivery of 
the message to such person), you may not copy or deliver this message to 
anyone. In such case, you should destroy this message and kindly notify the 
sender by reply email. Please advise immediately if you or your employer do not 
consent to Internet email for messages of this kind. Opinions, conclusions and 
other information in this message that do not relate to the official business 
of my firm shall be understood as neither given nor endorsed by it.


-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

________________________________
LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to