I wish to make two points:
1. Kirchoff’s Current Law states that the sum of currents entering a node
equals the sum of currents leaving the node. The Law applies to summation of
leakage (touch) currents (e.g., through a 2,000-ohm resistor) and to summation
of protective conductor currents (through 0 ohms). In a power strip protective
grounding conductor, I’m assuming 0 ohms to ground, so the current is slightly
higher (1 to 10 % depending on the leakage current limit and the voltage you
are using) in the protective grounding conductor than leakage (touch) current.
See IEC 60990 for touch (leakage) current and protective conductor current
measurement procedures.
2. A GFCI measures the current difference between line and neutral
conductors, not current in the protective conductor. It nominally operates at
5 mA. We assume (with a reasonable degree of accuracy) that leakage (touch)
current is 100% of the differential current measured by the GFCI. It is
possible, although unlikely, for some of the GFCI differential current to find
another return path than the protective grounding conductor.
Best regards,
Rich
From: Lfresearch Jose <000000734758d943-dmarc-requ...@listserv.ieee.org>
Sent: Wednesday, August 24, 2022 1:44 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] High Touch Current and GFCIs
I have wondered about something similar.
If I use a 6 way power strip, I’m assuming all the leakage currents for
anything plugged in sum. Is that correct? I recall getting a few trips when I
used a power strip and It’s only just twigged that might be why.
Cheers,
Derek.
Sent from my iPad
On Aug 24, 2022, at 3:27 PM, Brian Kunde <bkundew...@gmail.com
<mailto:bkundew...@gmail.com> > wrote:
If I have a rake of electrical equipment with a single power cord and a
combined touch current exceeding 6mA, and I plug the rake into a circuit with a
GFCI, will it trip?
Thanks.
The Other Brian
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org <mailto:emc-p...@ieee.org> >
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org> >
For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org <mailto:j.bac...@ieee.org> >
David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com> >
_____
To unsubscribe from the EMC-PSTC list, click the following link:
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org <mailto:emc-p...@ieee.org> >
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org> >
For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org <mailto:j.bac...@ieee.org> >
David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com> >
_____
To unsubscribe from the EMC-PSTC list, click the following link:
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Mike Cantwell <mcantw...@ieee.org>
For policy questions, send mail to:
Jim Bacher: <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link:
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1