The cancellation that Mr. Woodgate points out could occur with industrial 
equipment that was powered from North American  120/240 V ac, 3-wire single 
phase or 240 Vac, single phase circuits (where there are two line conductors 
separated in phase by 180 degrees on a center-tapped, single-phase distribution 
transformer) or from 208 Vac, single-phase equipment  (where the two line 
conductors are separated in phase by 120 degrees on a 3-phase distribution 
transformer).

If your market was strictly North America, you might use this to your 
advantage.  It is likely, though, that such equipment is sold on the global 
market, so you might test for touch current with a 230 V, single phase input 
(that is, 230V to earthed neutral).  Then, no such cancellation of touch 
current.

Best regards,

Don Gies




Internal
From: John Woodgate <j...@woodjohn.uk>
Sent: Thursday, August 25, 2022 3:32 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] High Touch Current and GFCIs


[External email: Use caution with links and attachments]

________________________________



There is also a question in my mind as to whether there can be partial 
cancellation of touch current. I suspect this is highly improbable in the US, 
due to the distribution system ensuring that the neutral has a very low voltage 
difference from the PEC. But in Europe, it's not inconceivable that the neutral 
could be, say, 4.6 V relative to PEC and the neutral-to-PEC capacitance 25 
times that of L to PEC, so that half the L-to-PEC leakage current is cancelled 
by the N to PEC current.
======================================================================================
Best wishes John Woodgate OOO-Own Opinions Only
www.woodjohn.uk<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.woodjohn.uk%2F&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527292966147%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=YTPpuf0fmAT3zFhO2daPXwkAknmm000tpUrSpv941i8%3D&reserved=0>
Rayleigh, Essex UK
It all depends

On 2022-08-25 19:12, Richard Nute wrote:


I wish to make two points:


  1.  Kirchoff’s Current Law states that the sum of currents entering a node 
equals the sum of currents leaving the node.  The Law applies to summation of 
leakage (touch) currents (e.g., through a 2,000-ohm resistor) and to summation 
of protective conductor currents (through 0 ohms).  In a power strip protective 
grounding conductor, I’m assuming 0 ohms to ground, so the current is slightly 
higher (1 to 10 % depending on the leakage current limit and the voltage you 
are using) in the protective grounding conductor than leakage (touch) current.

See IEC 60990 for touch (leakage) current and protective conductor current 
measurement procedures.



  1.  A GFCI measures the current difference between line and neutral 
conductors, not current in the protective conductor.  It nominally operates at 
5 mA.  We assume (with a reasonable degree of accuracy) that leakage (touch) 
current is 100% of the differential current measured by the GFCI.  It is 
possible, although unlikely, for some of the GFCI differential current to find 
another return path than the protective grounding conductor.
Best regards,
Rich


From: Lfresearch Jose 
<000000734758d943-dmarc-requ...@listserv.ieee.org><mailto:000000734758d943-dmarc-requ...@listserv.ieee.org>
Sent: Wednesday, August 24, 2022 1:44 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: Re: [PSES] High Touch Current and GFCIs

I have wondered about something similar.

If I use a 6 way power strip, I’m assuming all the leakage currents for 
anything plugged in sum. Is that correct? I recall getting a few trips when I 
used a power strip and It’s only just twigged that might be why.

Cheers,

Derek.
Sent from my iPad


On Aug 24, 2022, at 3:27 PM, Brian Kunde 
<bkundew...@gmail.com<mailto:bkundew...@gmail.com>> wrote:

If I have a rake of electrical equipment with a single power cord and a 
combined touch current exceeding 6mA, and I plug the rake into a circuit with a 
GFCI, will it trip?

Thanks.

The Other Brian
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527292966147%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=iOWJbGDVA2VIgouaMohdShgvwFzojuN1gl1ubfZXDkU%3D&reserved=0>

Website: 
http://www.ieee-pses.org/<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527292966147%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=RIbHyi3PQeLwNiamzN8WWRja%2BBH5pNct996d8%2FcGA9w%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527292966147%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=%2B3BXSDx%2FFW3ka%2F8qtYdWoB5ChfZpvCgtp8REaziAIOc%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527292966147%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=yQ8%2FCoTTn0eXilIec7VyzvvovpAVJ%2B7ikqg7J%2BFwaZk%3D&reserved=0>

For help, send mail to the list administrators:
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Flistserv.ieee.org%2Fcgi-bin%2Fwa%3FSUBED1%3DEMC-PSTC%26A%3D1&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527292966147%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=I%2Fxrsn%2FEs0mAoeuHkA%2B1rLs1KRiRvVFO%2Bni3IgEHF2M%3D&reserved=0>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527292966147%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=iOWJbGDVA2VIgouaMohdShgvwFzojuN1gl1ubfZXDkU%3D&reserved=0>

Website: 
http://www.ieee-pses.org/<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527292966147%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=RIbHyi3PQeLwNiamzN8WWRja%2BBH5pNct996d8%2FcGA9w%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527292966147%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=%2B3BXSDx%2FFW3ka%2F8qtYdWoB5ChfZpvCgtp8REaziAIOc%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527293122383%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=UBJ4qCk0JFeFZfKSnYEk8XzjhuIqlk0DO0Lah%2FCBUo4%3D&reserved=0>

For help, send mail to the list administrators:
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Flistserv.ieee.org%2Fcgi-bin%2Fwa%3FSUBED1%3DEMC-PSTC%26A%3D1&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527293122383%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=mpl2CMixwENfzPREtJeozqYvfa1pXs%2FbSwOElx5HON0%3D&reserved=0>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527293122383%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=kha%2FmXiYj0yq5oFrbkSu4Fbm4OrVMoob6C0iUefL0tE%3D&reserved=0>

Website: 
http://www.ieee-pses.org/<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527293122383%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=IU%2FvmV8DzsjXq6WH6QMluEfuRPuYWQGegJ0wwNzuzUE%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527293122383%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=2SeZoyGisCpLyh645tf75NhTUpzzheBZbWUqZO9X%2Fds%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527293122383%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=UBJ4qCk0JFeFZfKSnYEk8XzjhuIqlk0DO0Lah%2FCBUo4%3D&reserved=0>

For help, send mail to the list administrators:
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Flistserv.ieee.org%2Fcgi-bin%2Fwa%3FSUBED1%3DEMC-PSTC%26A%3D1&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527293122383%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=mpl2CMixwENfzPREtJeozqYvfa1pXs%2FbSwOElx5HON0%3D&reserved=0>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527293122383%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=kha%2FmXiYj0yq5oFrbkSu4Fbm4OrVMoob6C0iUefL0tE%3D&reserved=0>

Website: 
http://www.ieee-pses.org/<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527293278625%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=%2Bayzm53iKmezelUzjwz%2Baj5yphpHtR%2Bz5SOYpa60RIw%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527293278625%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=tQDSzIOZMDLnkSfJ%2Fq4AGLZTAGkgD9Vo%2FWTx%2F9632Kc%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=05%7C01%7Cdonald.gies%40se.com%7C7046b051e9cd42fd084908da86d07966%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637970527293278625%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=sA3K3I8AnBq1krARsYfiHH93Y2TO3jGZPb1tYizRZUs%3D&reserved=0>

For help, send mail to the list administrators:
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to