I appreciate the replies, but I am not getting the information I am
seeking.

Some machines have just the SCCR Rating, such as

*SCCR: 10kA*

but a few machines we have looked at include a reference to the "Max
Voltage", such as

*SCCR: 10kA RMS Symmetrical, 480V Maximum*

What is the source, code, standard, directive, etc. that calls out the Max
Voltage as a requirement in the SCCR rating that is printed on the
Nameplate label?  We cannot find such a source.

In our case, we have a machine that can operate at 230V, 380V, or 480V
depending on how the motor is wired. So on a machine rated 230V it has a
SCCR rating that includes the Max Voltage of 480V.  We are getting
push-back from the field saying that having the voltage on the SCCR rating
is confusing. To resolve this, we want to remove the reference to the Max
Voltage, but before we do that, we want to find out if it is mandated in
the code or some standard.

I can see where the max voltage might be required on some components. Maybe
it is an old requirement that is no longer required.  I am just guessing.

Thanks again for your help.
The Other Brian


On Tue, May 14, 2024 at 3:54 PM Scott Aldous <
00000220f70c299a-dmarc-requ...@listserv.ieee.org> wrote:

> Starting on page 7, the white paper that Rich linked to also references UL
> 508A, supplement SB, which is a method of determining SCCR for industrial
> control panels without test. The method at a high level involves carrying
> over the SCCR rating of the "weakest link in the chain" from a protective
> component standpoint to the overall panel. I wonder if that method may have
> been used for the machinery in question, with a component level voltage
> rating (improperly, in my opinion) shifted over to the end device. Note
> that UL 508A includes "at a nominal voltage" in its definition of SCCR.
>
> On Tue, May 14, 2024 at 12:33 PM Richard Nute <ri...@ieee.org> wrote:
>
>>
>>
>> Hi Brian:
>>
>>
>>
>> See the very last line of:
>>
>>
>>
>>
>> https://www.mouser.com/pdfDocs/littelfuse_industrial_whitepaper_increase_sccr.pdf
>>
>>
>>
>> Best regards,
>>
>> Rich
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> *From:* Ralph McDiarmid <rmm.priv...@gmail.com>
>> *Sent:* Tuesday, May 14, 2024 11:41 AM
>> *To:* EMC-PSTC@LISTSERV.IEEE.ORG
>> *Subject:* Re: [PSES] SCCR Rating Question
>>
>>
>>
>> Could this number to used to select a suitable circuit breaker and so the
>> interrupting voltage is an important parameter?
>>
>>
>>
>> The nameplate rating on the machine should be the information an
>> electrician needs during installation and selection of wire size and type.
>>
>>
>>
>> Ralph
>>
>>
>>
>> *From:* Brian Kunde <bkundew...@gmail.com>
>> *Sent:* Tuesday, May 14, 2024 11:29 AM
>> *To:* EMC-PSTC@LISTSERV.IEEE.ORG
>> *Subject:* [PSES] SCCR Rating Question
>>
>>
>>
>> Greetings to all.
>>
>>
>>
>> I am new to SCCR ratings on industrial machinery.  The ratings I have
>> seen sometimes has a "Maximum Voltage" included, such as;
>>
>>
>>
>> SCCR: 22kA, 600V Maximum
>>
>>
>>
>> Where does the voltage value come from?  In one case, the machine had a
>> line voltage rating of "120/208 Vac", but the SCCR rating had a voltage
>> rating of "Max 600V".
>>
>>
>>
>> Can this be confusing? Might something think the machine can operate at
>> 600Vac?
>>
>>
>>
>> Thanks for any replies.
>>
>> The Other Brian
>>
>>
>>
>>
>> ------------------------------
>>
>> This message is from the IEEE Product Safety Engineering Society emc-pstc
>> discussion list. To post a message to the list, send your e-mail to
>> EMC-PSTC@LISTSERV.IEEE.ORG
>>
>> All emc-pstc postings are archived and searchable on the web at:
>> https://www.mail-archive.com/emc-pstc@listserv.ieee.org/
>> <https://www.mail-archive.com/emc-pstc@listserv.ieee.org/%20>
>>
>> Website: https://ewh.ieee.org/soc/pses/
>> Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to
>> unsubscribe) <https://ewh.ieee.org/soc/pses/list.html>
>> List rules: https://ewh.ieee.org/soc/pses/listrules.html
>>
>> For help, send mail to the list administrators:
>> Mike Sherman at: msherma...@comcast.net
>> Rick Linford at: linf...@ieee.org
>>
>> For policy questions, send mail to:
>> Jim Bacher at: j.bac...@ieee.org
>> ------------------------------
>>
>> To unsubscribe from the EMC-PSTC list, click the following link:
>> https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
>> ------------------------------
>>
>> This message is from the IEEE Product Safety Engineering Society emc-pstc
>> discussion list. To post a message to the list, send your e-mail to
>> EMC-PSTC@LISTSERV.IEEE.ORG
>>
>> All emc-pstc postings are archived and searchable on the web at:
>> https://www.mail-archive.com/emc-pstc@listserv.ieee.org/
>> <https://www.mail-archive.com/emc-pstc@listserv.ieee.org/%20>
>>
>> Website: https://ewh.ieee.org/soc/pses/
>> Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to
>> unsubscribe) <https://ewh.ieee.org/soc/pses/list.html>
>> List rules: https://ewh.ieee.org/soc/pses/listrules.html
>>
>> For help, send mail to the list administrators:
>> Mike Sherman at: msherma...@comcast.net
>> Rick Linford at: linf...@ieee.org
>>
>> For policy questions, send mail to:
>> Jim Bacher at: j.bac...@ieee.org
>> ------------------------------
>>
>> To unsubscribe from the EMC-PSTC list, click the following link:
>> https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
>> ------------------------------
>>
>> This message is from the IEEE Product Safety Engineering Society emc-pstc
>> discussion list. To post a message to the list, send your e-mail to
>> EMC-PSTC@LISTSERV.IEEE.ORG
>> All emc-pstc postings are archived and searchable on the web at:
>> https://www.mail-archive.com/emc-pstc@listserv.ieee.org/
>>
>> Website: https://ewh.ieee.org/soc/pses/
>> Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to
>> unsubscribe) <https://ewh.ieee.org/soc/pses/list.html>
>> List rules: https://ewh.ieee.org/soc/pses/listrules.html
>>
>> For help, send mail to the list administrators:
>> Mike Sherman at: msherma...@comcast.net
>> Rick Linford at: linf...@ieee.org
>>
>> For policy questions, send mail to:
>> Jim Bacher at: j.bac...@ieee.org
>> ------------------------------
>>
>> To unsubscribe from the EMC-PSTC list, click the following link:
>> https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
>>
>
>
> --
> Scott Aldous | Regulatory Compliance Manager | scottald...@google.com |
> 650-253-1994 <(650)%20253-1994>
>
> ------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to
> EMC-PSTC@LISTSERV.IEEE.ORG
> All emc-pstc postings are archived and searchable on the web at:
> https://www.mail-archive.com/emc-pstc@listserv.ieee.org/
>
> Website: https://ewh.ieee.org/soc/pses/
> Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to
> unsubscribe) <https://ewh.ieee.org/soc/pses/list.html>
> List rules: https://ewh.ieee.org/soc/pses/listrules.html
>
> For help, send mail to the list administrators:
> Mike Sherman at: msherma...@comcast.net
> Rick Linford at: linf...@ieee.org
>
> For policy questions, send mail to:
> Jim Bacher at: j.bac...@ieee.org
> ------------------------------
>
> To unsubscribe from the EMC-PSTC list, click the following link:
> https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to