Canada, by contrast, seems to regularly inspect new equipment installations for 
the presence of a listing mark.
 
Mike Sherman
Sherman PSC LLC

> On 01/07/2026 11:41 AM CST Jim Bacher, WB8VSU <[email protected]> wrote:
>  
>  
> It's mandatory, but not enforced by OSHA unless an issue arises. 
>  
> There are a few cities that do enforce it. Los Angeles being one of them. If 
> their inspectors find such a product they will require it's removal and that 
> includes trade show demos. 
>  
> One company I dealt with many years ago was paying for site inspections of 
> their products when installing their products, instead of certifying their 
> products. 
>  
> Once you have a CB Report, getting a NRTL cert isn't too difficult or 
> expensive. 
>  
>  
> Jim Bacher, WB8VSU
> [email protected]
> JBRC Consulting LLC 
> Product EMC & Regulatory Consultant
> https://www.trc.guru/ https://trc.guru/ email:[email protected]
> IEEE Life Senior Member
>  
> 
> On January 7, 2026 12:22:26 PM "[email protected]" 
> <[email protected]> wrote:
> 
> >  
> > John and James,
> >  
> > Thank you so much for your valuable feedback.
> >  
> > I see a lot of products that are used in the professional market that do 
> > not have any type of 3rd party certification and they are being sold on the 
> > market and they are from some big manufacturers. So would you agree that 
> > 3rd party certification is not mandatory but rather valuntary? 
> >  
> > Thanks
> > Peter
> >  
> > On Tuesday, January 6, 2026 at 05:48:11 AM PST, James Hulbert 
> > <[email protected]> wrote:
> >  
> >  
> > 
> > We all own a debit of gratitude to Leonard Frier.
> > 
> >  
> > 
> > Jim Hulbert
> > 
> >  
> > 
> > From: John Allen <[email protected]>
> > Sent: Monday, January 5, 2026 7:55 PM
> > To: [email protected]
> > Subject: [EXTERNAL] Re: [PSES] Mandatory NRTL certification
> > 
> >  
> > 
> > This message is from an EXTERNAL EMAIL system. Use caution and think before 
> > opening attachments, clicking links, or responding.
> > 
> > By the way, "NRTL" used to say "UL".  Leonard Frier (owner of MET labs), 
> > god bless that man, took OSHA to court and in 1988 the OSHA regulation 
> > changed from "UL" to "NRTL".
> > 
> >  
> > 
> > Here is a copy of the Federal Register back in 1988.............
> > 
> >  
> > 
> >  
> > 
> > Best Regards and Be Safe,
> > 
> >  
> > 
> > John
> > 
> >  
> > 
> > John Allen | President & CEO | Product Safety Consulting, Inc.
> > 
> > Your Outsourced Compliance Department®
> > 
> > 630-238-0188, Cell: 630-330-3145
> > 
> > [social_facebook_box_blue for signature] 
> > https://urldefense.com/v3/__http://www.facebook.com/pages/Product-Safety-Consulting-Inc/97306850917__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOm-hF-7s$[social_twitter_box_blue
> >  for signature] 
> > https://urldefense.com/v3/__http://twitter.com/SafetyTesting__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyO8Dodz5k$[social_linkedin_box_blue
> >  for signature] 
> > https://urldefense.com/v3/__http://www.linkedin.com/in/productsafetyconsultinginc__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyO2rUDbLw$
> >  https://www.youtube.com/channel/UCVSzENmSoWeNFSBQcOYN7-A 
> > https://urldefense.com/v3/__https://www.youtube.com/channel/UCVSzENmSoWeNFSBQcOYN7-A__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyO2WYnukI$
> > www.productsafetyinc.com 
> > https://urldefense.com/v3/__http://www.productsafetyinc.com/__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyO0cBSDwU$
> > 
> > https://search.anab.org/public/organization_files/Product-Safety-Consulting-Inc-Cert-and-Scope-File-11-07-2025_1762537985.pdf
> >  
> > https://urldefense.com/v3/__https://search.anab.org/public/organization_files/Product-Safety-Consulting-Inc-Cert-and-Scope-File-11-07-2025_1762537985.pdf__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOD5bcJ68$
> > 
> >  
> > 
> > Please be sure to fill out our PSC FEEDBACK FORM 
> > https://urldefense.com/v3/__https://forms.office.com/Pages/ResponsePage.aspx?id=8xxUCRKaqEeNkIEOiGsk7jTjZMN9C19NoFd7qKZd5Q5UNEQ3OEpBVUFFMFVZRFpRNTVPRFMzUVNWRS4u__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyO-0Anj5o$
> > 
> >  
> > 
> > +++++++++++++++++++++++++++++++++++++++++++
> > 
> > IEEE Product Safety Engineering Society
> > 
> > President 2024-2025
> > 
> > Compliance 101 Technical Committee Chairman
> > 
> > IEEE Senior Member
> > 
> >  
> > 
> > Keeping our members informed and educated on Product Safety and Compliance
> > 
> >  https://ewh.ieee.org/soc/pses/index.html 
> > https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/index.html__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOg7sNxik$
> > 
> >  
> > 
> >  
> > 
> >  
> > 
> >  
> > 
> > Although PSC maintains the highest level of virus protection, this e-mail 
> > and any attachments should be scanned by your virus protection software.  
> > It is the responsibility of the recipient to check that it is virus free.  
> > PSC does not accept any responsibility for data loss or systems damage 
> > arising in any way from its use.  This message is confidential and intended 
> > only for the individual to whom or entity to which it is addressed.  If you 
> > are not the intended recipient or addressee, or an employee or agent 
> > responsible for delivering this message to the addressee, you are hereby 
> > notified that any dissemination, distribution, or copying, in whole or 
> > part, of this message is strictly prohibited.  If you believe that you have 
> > been sent this message in error, please do not read it.  Please immediately 
> > reply to sender that you have received this message in error.  Then 
> > permanently delete all copies of the message.
> > 
> > Thank you
> > 
> >  
> > 
> >  
> > 
> > 
> > ---------------------------------------------
> > 
> > From: John Allen <[email protected] 
> > mailto:[email protected]>
> > Sent: Monday, January 5, 2026 6:43 PM
> > To: [email protected] mailto:[email protected] 
> > <[email protected] mailto:[email protected]>
> > Subject: Re: [PSES] Mandatory NRTL certification
> > 
> >  
> > 
> > Hello and Happy New Year!!
> > 
> >  
> > 
> > I hope to simplify and clarify the vagueness - See OSHA's definition of 
> > acceptable installation below.  
> > 
> >  
> > 
> > OSHA requires NRTL if there is an applicable Standard (item 1).  If there 
> > is not an applicable Standard the AHJ can accept his own evaluation or 
> > another Federal agency's evaluation (item 2), or if the equipment is custom 
> > the AHJ can accept the manufacturers test data (item 3).
> > 
> >  
> > 
> > Our experience is Field Evaluation labeling satisfies most AHJs for items 2 
> > and 3.  I believe AHJs do not want the liability of accepting non-Certified 
> > installations and prefer an NRTL FE label at a minimum.
> > 
> >  
> > 
> > https://www.osha.gov/laws-regs/regulations/standardnumber/1910/1910.399 
> > https://urldefense.com/v3/__https://www.osha.gov/laws-regs/regulations/standardnumber/1910/1910.399__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOtfI9jjo$
> > 
> >  
> > 
> > Part Number:1910
> > 
> > * Part Number Title:Occupational Safety and Health Standards
> > * Subpart:1910 Subpart S
> > * Subpart Title:Electrical
> > * Standard Number: 
> > 
> > 1910.399 
> > https://urldefense.com/v3/__https://www.osha.gov/laws-regs/interlinking/standards/1910.399__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOHkM_MmA$
> > 
> > * Title: Definitions applicable to this subpart.
> > * GPO Source: e-CFR 
> > https://urldefense.com/v3/__https://www.ecfr.gov/cgi-bin/text-idx?SID=65b279ee2e7530009034c1f152d451e5&tpl=*ecfrbrowse*Title29*29tab_02.tpl__;Ly8v!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOC2qFMOY$
> > 
> > Acceptable. An installation or equipment is acceptable to the Assistant 
> > Secretary of Labor, and approved within the meaning of this subpart S:
> > 
> > (1) If it is accepted, or certified, or listed, or labeled, or otherwise 
> > determined to be safe by a nationally recognized testing laboratory 
> > recognized pursuant to § 1910.7; or
> > 
> > (2) With respect to an installation or equipment of a kind that no 
> > nationally recognized testing laboratory accepts, certifies, lists, labels, 
> > or determines to be safe, if it is inspected or tested by another Federal 
> > agency, or by a State, municipal, or other local authority responsible for 
> > enforcing occupational safety provisions of the National Electrical Code, 
> > and found in compliance with the provisions of the National Electrical Code 
> > as applied in this subpart; or
> > 
> > (3) With respect to custom-made equipment or related installations that are 
> > designed, fabricated for, and intended for use by a particular customer, if 
> > it is determined to be safe for its intended use by its manufacturer on the 
> > basis of test data which the employer keeps and makes available for 
> > inspection to the Assistant Secretary and his authorized representatives.
> > 
> >  
> > 
> >  
> > 
> > Best Regards and Be Safe,
> > 
> >  
> > 
> > John
> > 
> >  
> > 
> > John Allen | President & CEO | Product Safety Consulting, Inc.
> > 
> > Your Outsourced Compliance Department®
> > 
> > 630-238-0188, Cell: 630-330-3145
> > 
> > [social_facebook_box_blue for signature] 
> > https://urldefense.com/v3/__http://www.facebook.com/pages/Product-Safety-Consulting-Inc/97306850917__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOm-hF-7s$[social_twitter_box_blue
> >  for signature] 
> > https://urldefense.com/v3/__http://twitter.com/SafetyTesting__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyO8Dodz5k$[social_linkedin_box_blue
> >  for signature] 
> > https://urldefense.com/v3/__http://www.linkedin.com/in/productsafetyconsultinginc__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyO2rUDbLw$
> >  https://www.youtube.com/channel/UCVSzENmSoWeNFSBQcOYN7-A 
> > https://urldefense.com/v3/__https://www.youtube.com/channel/UCVSzENmSoWeNFSBQcOYN7-A__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyO2WYnukI$
> > www.productsafetyinc.com 
> > https://urldefense.com/v3/__http://www.productsafetyinc.com/__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyO0cBSDwU$
> > 
> > https://search.anab.org/public/organization_files/Product-Safety-Consulting-Inc-Cert-and-Scope-File-11-07-2025_1762537985.pdf
> >  
> > https://urldefense.com/v3/__https://search.anab.org/public/organization_files/Product-Safety-Consulting-Inc-Cert-and-Scope-File-11-07-2025_1762537985.pdf__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOD5bcJ68$
> > 
> >  
> > 
> > Please be sure to fill out our PSC FEEDBACK FORM 
> > https://urldefense.com/v3/__https://forms.office.com/Pages/ResponsePage.aspx?id=8xxUCRKaqEeNkIEOiGsk7jTjZMN9C19NoFd7qKZd5Q5UNEQ3OEpBVUFFMFVZRFpRNTVPRFMzUVNWRS4u__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyO-0Anj5o$
> > 
> >  
> > 
> > +++++++++++++++++++++++++++++++++++++++++++
> > 
> > IEEE Product Safety Engineering Society
> > 
> > President 2024-2025
> > 
> > Compliance 101 Technical Committee Chairman
> > 
> > IEEE Senior Member
> > 
> >  
> > 
> > Keeping our members informed and educated on Product Safety and Compliance
> > 
> >  https://ewh.ieee.org/soc/pses/index.html 
> > https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/index.html__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOg7sNxik$
> > 
> >  
> > 
> >  
> > 
> >  
> > 
> >  
> > 
> > Although PSC maintains the highest level of virus protection, this e-mail 
> > and any attachments should be scanned by your virus protection software.  
> > It is the responsibility of the recipient to check that it is virus free.  
> > PSC does not accept any responsibility for data loss or systems damage 
> > arising in any way from its use.  This message is confidential and intended 
> > only for the individual to whom or entity to which it is addressed.  If you 
> > are not the intended recipient or addressee, or an employee or agent 
> > responsible for delivering this message to the addressee, you are hereby 
> > notified that any dissemination, distribution, or copying, in whole or 
> > part, of this message is strictly prohibited.  If you believe that you have 
> > been sent this message in error, please do not read it.  Please immediately 
> > reply to sender that you have received this message in error.  Then 
> > permanently delete all copies of the message.
> > 
> > Thank you
> > 
> >  
> > 
> > 
> > ---------------------------------------------
> > 
> > From: Ralph McDiarmid <[email protected] mailto:[email protected]>
> > Sent: Monday, January 5, 2026 6:17 PM
> > To: [email protected] mailto:[email protected] 
> > <[email protected] mailto:[email protected]>
> > Subject: Re: [PSES] Mandatory NRTL certification
> > 
> >  
> > 
> > [EXTERNAL EMAIL] DO NOT CLICK links or attachments unless you recognize the 
> > sender and know the content is safe.
> > 
> > Happy New Year.
> > 
> >  
> > 
> > The US Dept of Labor has a mandate to enforce workplace safety regulations. 
> > One of its many agencies is the Occupational Safety and Health 
> > Administration which is tasked with ensuring a safe work environment by 
> > enforcing product compliance by the application of US standards and done by 
> > accredited laboratories. That means products that are within scope of at 
> > least one UL standard must be shown to be compliant to that standard by a 
> > Nationally Recognized Testing Laboratory.  (an accredited laboratory and 
> > OSHA runs the NRTL accreditation program)
> > 
> >  
> > 
> > Ralph
> > 
> >  
> > 
> > From: [email protected] mailto:[email protected] 
> > <[email protected] 
> > mailto:[email protected]>
> > Sent: January 5, 2026 3:40 PM
> > To: [email protected] mailto:[email protected]
> > Subject: [PSES] Mandatory NRTL certification
> > 
> >  
> > 
> > Happy New Year to all
> > 
> > I was asked by one of the engineers that I work with if getting safety 
> > certification for a product in the US is mandatory or not? i.e do 
> > manufacturer of electrical or electronics have to have certification from 
> > NRTL or other 3rd party labs? The products in question are 100% used in 
> > professional environment and are not intended for general consumer market. 
> > If this is a mandatory requirement, where can I see the requirements 
> > written?
> > 
> > Thanks
> > 
> > Pete
> > 
> >  
> > 
> > 
> > ---------------------------------------------
> > 
> > This message is from the IEEE Product Safety Engineering Society emc-pstc 
> > discussion list. To post a message to the list, send your e-mail to 
> > [email protected] mailto:[email protected]
> > 
> > All emc-pstc postings are archived and searchable on the web at:
> > https://www.mail-archive.com/[email protected]/ 
> > https://urldefense.com/v3/__https://www.mail-archive.com/[email protected]/*20__;JQ!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOfQ3e7Cw$
> > 
> > Website: https://ewh.ieee.org/soc/pses/ 
> > https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOtSY9_vA$
> > Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
> > unsubscribe) 
> > https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/list.html__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOXtBHmN4$
> > List rules: 
> > https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf 
> > https://urldefense.com/v3/__https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyO2WK_IC8$
> > 
> > For help, send mail to the list administrators:
> > Mike Sherman at: [email protected] mailto:[email protected]
> > Rick Linford at: [email protected] mailto:[email protected]
> > 
> > For policy questions, send mail to:
> > Jim Bacher at: [email protected] mailto:[email protected]
> > 
> > 
> > ---------------------------------------------
> > 
> > To unsubscribe from the EMC-PSTC list, click the following link: 
> > https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1 
> > https://urldefense.com/v3/__https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOPVk4SdA$
> > 
> > 
> > ---------------------------------------------
> > 
> > This message is from the IEEE Product Safety Engineering Society emc-pstc 
> > discussion list. To post a message to the list, send your e-mail to 
> > [email protected] mailto:[email protected]
> > 
> > All emc-pstc postings are archived and searchable on the web at:
> > https://www.mail-archive.com/[email protected]/ 
> > https://urldefense.com/v3/__https://www.mail-archive.com/[email protected]/__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOpd0TRn8$
> > 
> > Website: https://ewh.ieee.org/soc/pses/ 
> > https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOtSY9_vA$
> > Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
> > unsubscribe) 
> > https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/list.html__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOXtBHmN4$
> > List rules: 
> > https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf 
> > https://urldefense.com/v3/__https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyO2WK_IC8$
> > 
> > For help, send mail to the list administrators:
> > Mike Sherman at: [email protected] mailto:[email protected]
> > Rick Linford at: [email protected] mailto:[email protected]
> > 
> > For policy questions, send mail to:
> > Jim Bacher at: [email protected] mailto:[email protected]
> > 
> > 
> > ---------------------------------------------
> > 
> > To unsubscribe from the EMC-PSTC list, click the following link: 
> > https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1 
> > https://urldefense.com/v3/__https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOPVk4SdA$
> > 
> > 
> > ---------------------------------------------
> > 
> > This message is from the IEEE Product Safety Engineering Society emc-pstc 
> > discussion list. To post a message to the list, send your e-mail to 
> > [email protected] mailto:[email protected]
> > 
> > All emc-pstc postings are archived and searchable on the web at:
> > https://www.mail-archive.com/[email protected]/ 
> > https://urldefense.com/v3/__https://www.mail-archive.com/[email protected]/__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOpd0TRn8$
> > 
> > Website: https://ewh.ieee.org/soc/pses/ 
> > https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOtSY9_vA$
> > Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
> > unsubscribe) 
> > https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/list.html__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOXtBHmN4$
> > List rules: 
> > https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf 
> > https://urldefense.com/v3/__https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyO2WK_IC8$
> > 
> > For help, send mail to the list administrators:
> > Mike Sherman at: [email protected] mailto:[email protected]
> > Rick Linford at: [email protected] mailto:[email protected]
> > 
> > For policy questions, send mail to:
> > Jim Bacher at: [email protected] mailto:[email protected]
> > 
> > 
> > ---------------------------------------------
> > 
> > To unsubscribe from the EMC-PSTC list, click the following link: 
> > https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1 
> > https://urldefense.com/v3/__https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!GXa4NB5MBjHR!QWzoP4he-0GDBE_08PDsLCHh-IxQgC5p8T3Pf3mPb0d3oJGwITM0mNXq_cxaGlZ_d9W1jlLJbbXMTQhI_5Fp1FyOPVk4SdA$
> > 
> > This email message may contain confidential, proprietary and/or privileged 
> > information. It is intended only for the use of the intended recipient(s). 
> > If you have received it in error, please immediately advise the sender by 
> > reply email and then delete this message. No one other than the intended 
> > recipient may disclose, copy, distribute or use the information contained 
> > in this message.
> > 
> > ---------------------------------------------
> > 
> > This message is from the IEEE Product Safety Engineering Society emc-pstc 
> > discussion list. To post a message to the list, send your e-mail to 
> > [email protected]
> > 
> > All emc-pstc postings are archived and searchable on the web at:
> > https://www.mail-archive.com/[email protected]/
> > 
> > Website: https://ewh.ieee.org/soc/pses/ https://ewh.ieee.org/soc/pses/
> > Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
> > unsubscribe) https://ewh.ieee.org/soc/pses/list.html
> > List rules: 
> > https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf
> > 
> > For help, send mail to the list administrators:
> > Mike Sherman at: [email protected] mailto:[email protected]
> > Rick Linford at: [email protected] mailto:[email protected]
> > 
> > For policy questions, send mail to:
> > Jim Bacher at: [email protected] mailto:[email protected]
> > 
> > 
> > ---------------------------------------------
> > 
> > To unsubscribe from the EMC-PSTC list, click the following link: 
> > https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
> > 
> > 
> > ---------------------------------------------
> > 
> > This message is from the IEEE Product Safety Engineering Society emc-pstc 
> > discussion list. To post a message to the list, send your e-mail to 
> > [email protected]
> > 
> > All emc-pstc postings are archived and searchable on the web at:
> > https://www.mail-archive.com/[email protected]/
> > 
> >  
> > 
> > Website: https://ewh.ieee.org/soc/pses/ https://ewh.ieee.org/soc/pses/
> > Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
> > unsubscribe) https://ewh.ieee.org/soc/pses/list.html
> > List rules: 
> > https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf
> > 
> > For help, send mail to the list administrators:
> > Mike Sherman at: [email protected] mailto:[email protected]
> > Rick Linford at: [email protected] mailto:[email protected]
> > 
> > For policy questions, send mail to:
> > Jim Bacher at: [email protected] mailto:[email protected]
> > 
> > 
> > ---------------------------------------------
> > 
> > To unsubscribe from the EMC-PSTC list, click the following link: 
> > https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
> > 
>  
> 
> ---------------------------------------------
> 
> This message is from the IEEE Product Safety Engineering Society emc-pstc 
> discussion list. To post a message to the list, send your e-mail to 
> [email protected]
> 
> All emc-pstc postings are archived and searchable on the web at:
> https://www.mail-archive.com/[email protected]/
> 
>  
> 
> Website: https://ewh.ieee.org/soc/pses/ https://ewh.ieee.org/soc/pses/
> Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
> unsubscribe) https://ewh.ieee.org/soc/pses/list.html
> List rules: 
> https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf
> 
> For help, send mail to the list administrators:
> Mike Sherman at: [email protected] mailto:[email protected]
> Rick Linford at: [email protected] mailto:[email protected]
> 
> For policy questions, send mail to:
> Jim Bacher at: [email protected] mailto:[email protected]
> 
> 
> ---------------------------------------------
> 
> To unsubscribe from the EMC-PSTC list, click the following link: 
> https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
> 

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf

For help, send mail to the list administrators:
Mike Sherman at: [email protected]
Rick Linford at: [email protected]

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to