Of course in our office and in many commercial locations, the ground pin is 
neither on top nor on bottom:

[cid:[email protected]]

Jim Hulbert

From: Ron <[email protected]>
Sent: Friday, June 12, 2026 11:28 PM
To: [email protected]
Subject: Re: [PSES] [EXTERNAL] [PSES] Friday Question - in the USA, ground pin 
down or gorund pin up?


This message is from an EXTERNAL EMAIL system. Use caution and think before 
opening attachments, clicking links, or responding.
First, welcome from world of retirement. It's been a long while since I 
contributed.

For the subject at hand, my father was a licensed electrician & would install 
outlets with the ground pin facing up to signal that the receptacle (or half of 
a duplex receptacle) was controlled by a wall switch. I don't know how common 
practice that was,  but it seems to be.

From a safety perspective, I am not aware if either orientation is more or less 
safe also as confirmed below (especially since I've not been active in 
compliance for some years now).

Hope this answered your question.

Best regards,

Ron Pickard
Sent from my Smartphone

On June 12, 2026, at 19:32, Ted Eckert 
<[email protected]<mailto:[email protected]>>
 wrote:

The orientation of the ground pin likely doesn't matter if there is any 
flooding. The frame of the duplex outlet is ground, and the line and neutral 
screws on the sides are symmetrical, so there will be a line connection towards 
the bottom regardless of which orientation the outlet is installed in.

Nonmetallic sheathed cable, such as Romex, often has paper around the ground 
wire as a spacer. If there is any flooding, water wicks into the cable and rots 
it from the inside out. This cable would need to be stripped from a 
flood-damaged structure. In my opinion, this is a bigger issue in a flooded 
residential structure in the U.S. I think the outlet orientation would be a 
very low priority at that point.

UL_Flood_Electrical_Equipment_WP_V4.pdf<https://urldefense.com/v3/__https://code-authorities.ul.com/wp-content/uploads/sites/46/2019/12/UL_Flood_Electrical_Equipment_WP_V4.pdf__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObN86KQHg$>

Ted Eckert
The opinions expressed are my own and do not necessarily reflect those of my 
employers or UL.
________________________________
From: Larry Merchell <[email protected]<mailto:[email protected]>>
Sent: Friday, June 12, 2026 6:01 PM
To: [email protected]<mailto:[email protected]> 
<[email protected]<mailto:[email protected]>>
Subject: Re: [PSES] [EXTERNAL] [PSES] Friday Question - in the USA, ground pin 
down or gorund pin up?

You don't often get email from 
[email protected]<mailto:[email protected]>. Learn why this is 
important<https://urldefense.com/v3/__https://aka.ms/LearnAboutSenderIdentification__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsOaR3ADZsQ$>
Is the ground pin down safer in a single fault condition where there is a flood 
or if the fire sprinklers are activated?

Larry Merchell
________________________________
From: John Woodgate <[email protected]<mailto:[email protected]>>
Sent: Friday, June 12, 2026 4:12 PM
To: [email protected]<mailto:[email protected]> 
<[email protected]<mailto:[email protected]>>
Subject: Re: [PSES] [EXTERNAL] [PSES] Friday Question - in the USA, ground pin 
down or gorund pin up?


Agreed; losing the ground connection must not  create an unsafe condition, but 
leakage is inevitable, even if it is much less than 1 mA, so that when the 
ground connection is lost, accessible parts may be at 50 V or so to ground when 
touched, which can be felt as a mild shock.
On 2026-06-12 23:42, Ralph McDiarmid wrote:

A fundamental axiom across all modern product‑safety standards is that two 
independent levels of protection must exist so that no single failure can 
result in a hazard or in an unsafe condition.



From: John Woodgate <[email protected]><mailto:[email protected]>
Sent: June 12, 2026 8:58 AM
To: [email protected]<mailto:[email protected]>
Subject: Re: [PSES] [EXTERNAL] [PSES] Friday Question - in the USA, ground pin 
down or gorund pin up?



Yes, but that by itself should not create an unsafe condition. A second fault 
is needed (NOT!) to make accessible conducting parts live. There might be a 
mild shock due  to leakage current, though.

On 2026-06-12 16:24, Ted Eckert wrote:

However, if the plug is pulled at a severe angle, there is a risk that the 
ground connection breaks before line and neutral.

--
Best wishes John Woodgate RAYLEIGH Essex OOO-Own Opinions Only 
www.woodjohn.uk<https://urldefense.com/v3/__http://www.woodjohn.uk/__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObkJVRnug$>
 If something is true: * as far as we know - it's science *for certain - it's 
mathematics *unquestionably - it's religion



[https://s-install.avcdn.net/ipm/preview/icons/icon-envelope-tick-green-avg-v1.png]<https://urldefense.com/v3/__http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObfjBNG-Q$>

Virus-free.www.avg.com<https://urldefense.com/v3/__http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObfjBNG-Q$>

________________________________

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]<mailto:[email protected]>

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/<https://urldefense.com/v3/__https://www.mail-archive.com/[email protected]/*20__;JQ!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsOZ4pMs0aA$>

Website: https://ewh.ieee.org/soc/pses/ 
<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObshF1Skg$>
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/list.html__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObPnXFvhw$>
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf<https://urldefense.com/v3/__https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsOaqJPaISg$>

For help, send mail to the list administrators:
Mike Sherman at: [email protected]<mailto:[email protected]>
Rick Linford at: [email protected]<mailto:[email protected]>

For policy questions, send mail to:
Jim Bacher at: [email protected]<mailto:[email protected]>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://urldefense.com/v3/__https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObCnBIHUw$>

________________________________

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]<mailto:[email protected]>
All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/<https://urldefense.com/v3/__https://www.mail-archive.com/[email protected]/__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsOZeVer18A$>

Website: https://ewh.ieee.org/soc/pses/ 
<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObshF1Skg$>
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/list.html__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObPnXFvhw$>
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf<https://urldefense.com/v3/__https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsOaqJPaISg$>

For help, send mail to the list administrators:
Mike Sherman at: [email protected]<mailto:[email protected]>
Rick Linford at: [email protected]<mailto:[email protected]>

For policy questions, send mail to:
Jim Bacher at: [email protected]<mailto:[email protected]>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://urldefense.com/v3/__https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObCnBIHUw$>
--
Best wishes John Woodgate RAYLEIGH Essex OOO-Own Opinions Only 
www.woodjohn.uk<https://urldefense.com/v3/__http://www.woodjohn.uk/__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObkJVRnug$>
 If something is true: * as far as we know - it's science *for certain - it's 
mathematics *unquestionably - it's religion
________________________________

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]<mailto:[email protected]>
All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/<https://urldefense.com/v3/__https://www.mail-archive.com/[email protected]/__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsOZeVer18A$>

Website: https://ewh.ieee.org/soc/pses/ 
<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObshF1Skg$>
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/list.html__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObPnXFvhw$>
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf<https://urldefense.com/v3/__https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsOaqJPaISg$>

For help, send mail to the list administrators:
Mike Sherman at: [email protected]<mailto:[email protected]>
Rick Linford at: [email protected]<mailto:[email protected]>

For policy questions, send mail to:
Jim Bacher at: [email protected]<mailto:[email protected]>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://urldefense.com/v3/__https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObCnBIHUw$>

________________________________

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]<mailto:[email protected]>
All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/<https://urldefense.com/v3/__https://www.mail-archive.com/[email protected]/__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsOZeVer18A$>

Website: https://ewh.ieee.org/soc/pses/ 
<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObshF1Skg$>
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/list.html__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObPnXFvhw$>
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf<https://urldefense.com/v3/__https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsOaqJPaISg$>

For help, send mail to the list administrators:
Mike Sherman at: [email protected]<mailto:[email protected]>
Rick Linford at: [email protected]<mailto:[email protected]>

For policy questions, send mail to:
Jim Bacher at: [email protected]<mailto:[email protected]>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://urldefense.com/v3/__https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObCnBIHUw$>

________________________________

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]<mailto:[email protected]>
All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/<https://urldefense.com/v3/__https://www.mail-archive.com/[email protected]/__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsOZeVer18A$>

Website: https://ewh.ieee.org/soc/pses/ 
<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObshF1Skg$>
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/list.html__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObPnXFvhw$>
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf<https://urldefense.com/v3/__https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsOaqJPaISg$>

For help, send mail to the list administrators:
Mike Sherman at: [email protected]<mailto:[email protected]>
Rick Linford at: [email protected]<mailto:[email protected]>

For policy questions, send mail to:
Jim Bacher at: [email protected]<mailto:[email protected]>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://urldefense.com/v3/__https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObCnBIHUw$>

________________________________

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]<mailto:[email protected]>
All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/<https://urldefense.com/v3/__https://www.mail-archive.com/[email protected]/__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsOZeVer18A$>

Website: https://ewh.ieee.org/soc/pses/ 
<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObshF1Skg$>
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)<https://urldefense.com/v3/__https://ewh.ieee.org/soc/pses/list.html__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObPnXFvhw$>
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf<https://urldefense.com/v3/__https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsOaqJPaISg$>

For help, send mail to the list administrators:
Mike Sherman at: [email protected]<mailto:[email protected]>
Rick Linford at: [email protected]<mailto:[email protected]>

For policy questions, send mail to:
Jim Bacher at: [email protected]<mailto:[email protected]>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://urldefense.com/v3/__https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!GXa4NB5MBjHR!Rnz5BXBm3iADyJLxFuEusldl7cLkPSdLsaUQ-fNcB7wM_lpcPUH_uJvjUKBnLC_Iigde_PxcsYGBmi9vsObCnBIHUw$>

This email message may contain confidential, proprietary and/or privileged 
information. It is intended only for the use of the intended recipient(s). If 
you have received it in error, please immediately advise the sender by reply 
email and then delete this message. No one other than the intended recipient 
may disclose, copy, distribute or use the information contained in this message.


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf

For help, send mail to the list administrators:
Mike Sherman at: [email protected]
Rick Linford at: [email protected]

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to