John Kasunich wrote:
> Thomas Kaiser wrote:
> 
>  > Today I measured the time (with a stop watch) to move 200 mm in
>  > full speed (G00 Z-200.0) and got +8 seconds. Looks like the it
>  > does not move at 3000 mm / min.
> 
> 
>  > [EMCMOT]
>  > EMCMOT = motmod
>  > SHMEM_KEY = 111
>  > COMM_TIMEOUT = 1.0
>  > COMM_WAIT = 0.010
>  > BASE_PERIOD = 100000
>  > SERVO_PERIOD = 1000000
> 
> BASE_PERIOD = 100000 means you can never move faster than 100 
> microseconds between each step pulse.  That is 10000 step pulses per second.
> 
>  > [AXIS_0]
>  > SCALE = 400.0
> 
> Max step rate of 10000 steps/sec, divided by 400 steps/mm, means a 
> maximum speed of 25mm per second.  At 25mm/second, it will take 8 
> seconds to travel 200mm, exactly as you measured.

That looks right. I am familiar with PLC programming and there we have 
to check the cycle time of the PLC program. That means I got It. This 
configuration was done with stepconf. So, I just entered the value in 
stepconf and thought it is ok.
The 40000 step on time can not be achieved in the base_period and never 
in the servo_period cycle :-(

I use Linux since 1998, but its the first time I use a real time kernel, 
now.

> 
>  > MAX_VELOCITY = 50.0
> 
> But your configuration is asking for 50mm per second.  It is impossible 
> for the step generator to generate that speed.  It will fall behind the 
> commanded position and cause a following error - unless you set the 
> following error limit to a crazy value:

I don't know the correct velocity of these drives, so I just put 
something there.

> 
>  > MIN_FERROR = 10000.0

I add this to avoid the following error. I know I have to change after I 
could set up this machine right, but is this really needed? I don't have 
any feedback from the axis, So how can EMC2 detect a following error? 
EMC2 is only sending pulses to the axis and assumes that the axis moves 
this distance. I am wrong on this one?

> 
> The following error limit tells EMC "if you ever find yourself this far 
> away from the proper position, STOP!"
> 
> When you set following error to 10000mm, you are telling EMC "it is OK 
> if you cut 10 meters away from the proper location".  NOT GOOD!

See above

> 
> If you get following errors, you should NOT fix them by raising the 
> following error limit.  You should figure out the real reason for the 
> errors and fix it properly.

I know, but when you starting with this and you don't have the "big 
picture" it helps at the first try to move axis, doesn't it?

> 
> I think the reason that the jogs are running after you stop is that the 
> commanded position (moving at 50mm/sec) has gotten ahead of the motors 
> (moving at 25mm/sec).  After you release the button, the commanded 
> position stops, but the motors keep running until they catch up.

After reading your explanation, I think it is this.

> 
> Fix the speed problem and the crazy following error limit, and the jog 
> problem will fix itself.

Your right, too.

But I have to start somewhere. Only reading documentation does not help. 
When some other person move the light to an other direction helps 
sometimes more.

Thanks a lot.