I used halshow to temporarily change the sserial error-lim parameter. Then I 
set a watch on the error counter and I didn’t see it move.
It appears that I don’t get any SSerial errors. Is my test valid?

For confirmation on your assessment of the noise levels, here is a look at the 
voltage on the differential signals.



> On Aug 7, 2020, at 1:18 PM, Peter C. Wallace <p...@mesanet.com> wrote:
> 
> On Fri, 7 Aug 2020, Thaddeus Waldner wrote:
> 
>> Date: Fri, 7 Aug 2020 13:07:04 -0500
>> From: Thaddeus Waldner <thadw...@gmail.com>
>> Reply-To: "Enhanced Machine Controller (EMC)"
>>    <emc-users@lists.sourceforge.net>
>> To: "Enhanced Machine Controller (EMC)" <emc-users@lists.sourceforge.net>
>> Subject: Re: [Emc-users] 7i73 Lagging jog key
>> I finally got to do a little troubleshooting and hereџџs what I found:
> 
> Key response on the keypad is never as fast as the on-screen UI but it is 
> consistent. Iџџm guessing thereџџs about a 100-300 ms delay but thatџџs just 
> a guess. Could this delay be due to the fact that this is a scanning keypad? 
> What is the scan rate on
> 
> Once the inverter starts, I get a LOT of noise on the SmartSerial lines. The 
> noise voltage is around 4v  as measured from the 7i73 ground but it spikes to 
> higher than that. Frequency is about 40khz but itџџs not consistent.
> 
> The noise on the 5v power supply line to the 7i73 is minimal. The 7i73 and 
> all its connected switches are grounded only through the boardџџs connection 
> to the 7i96 board.
> 
> Would a shielded ethernet cable help?
> 
>> On Jul 31, 2020, at 9:17 AM, andy pugh <bodge...@gmail.com> wrote:
>> On Fri, 31 Jul 2020 at 15:15, Peter C. Wallace <p...@mesanet.com> wrote:
>>> Also even with default sserial error management you could only have
>>> 10 servo thread cycles (10 ms with a 1 ms servo thread) of delay
>>> due to failed transactions before a sserial error popup would occur.
>> Maybe noise on the keyboard itself? Is the keycode pin a single clean
>> transition?
>> -- 
>> atp
>> "A motorcycle is a bicycle with a pandemonium attachment and is
>> designed for the especial use of mechanical geniuses, daredevils and
>> lunatics."
>> џџ George Fitch, Atlanta Constitution Newspaper, 1912
>> _______________________________________________
>> Emc-users mailing list
>> Emc-users@lists.sourceforge.net
>> https://lists.sourceforge.net/lists/listinfo/emc-users
> 
> 
> 4V of noise should be OK (its within the common mode range of the 
> differential recievers which is -7 to +12V ) as long as you do not get 
> sserial errors I dont think this is the cause of your delays. You can see if 
> you get _any_ sserial errors by setting the error threshold to 1
> 
> 
> Peter Wallace
> Mesa Electronics
> _______________________________________________