Hi,
I have a simple problem as shown below. The upper bus is the infinite, slack bus. For the specified P & Q, I want to solve for VX. Per my hand calculations (iterations) the result will be VX=1.174pu @-3.3°. Now, I am trying to model this in a simple load flow as my first ever attempt to use MATPOWER (attached, which fails miserably). I have the manual and understand all of the bus, generator, and branch data. What I dont know is what can be left out in solving this simple problem? The machine is rated 16kV, 176MVA but Id prefer to leave that out and just work all in per unit (including data entry) if possible. Thanks, Russ _____ Russell W. Patterson, P.E. Chair IEEE PSRC (http://pes-psrc.org) Office: 423-702-9981
function mpc = example1 %Example 1 % Bus 1 is infinite and is 1.154 pu and zero degrees % Bus 2 has a 176MVA generator, P=0.85pu and Q=0.279pu both flowing into bus 2 % Impedance between bus 1 & 2 is j0.0921 pu % \%% MATPOWER Case Format : Version 2 mpc.version = '2'; \%%----- Power Flow Data -----\%% \%% system MVA base mpc.baseMVA = 176; \%% bus data % bus_i type Pd Qd Gs Bs area Vm Va baseKV zone Vmax Vmin mpc.bus = [ 1 3 0 0 0 0 1 1.154 0 16 1 1.154 1.154; 2 1 -.85 -.279 0 0 1 1 0 16 1 1.5 0.9; ]; \%% generator data % bus Pg Qg Qmax Qmin Vg mBase status Pmax Pmin Pc1 Pc2 Qc1min Qc1max Qc2min Qc2max ramp_agc ramp_10 ramp_30 ramp_q apf mpc.gen = [ 2 149.6 49.104 49.104 49.104 1 176 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0; ]; \%% branch data % fbus tbus r x b rateA rateB rateC ratio angle status angmin angmax mpc.branch = [ 1 2 0 .0921 0 0 0 0 0 0 1 0 0; ];