Hi Russ,

Attached is the file with some modifications. I obtained the same result
you got manually.

================================================================================
|     System Summary
    |
================================================================================

How many?                How much?              P (MW)            Q (MVAr)
---------------------    -------------------  -------------
 -----------------
Buses              2     Total Gen Capacity       0.0          49.1 to 49.1
Generators         2     On-line Capacity         0.0          49.1 to 49.1
Committed Gens     2     Generation (actual)     -0.0               9.4
Loads              0     Load                     0.0               0.0
  Fixed            0       Fixed                  0.0               0.0
  Dispatchable     0       Dispatchable          -0.0 of -0.0      -0.0
Shunts             0     Shunt (inj)             -0.0               0.0
Branches           1     Losses (I^2 * Z)         0.00              9.41
Transformers       0     Branch Charging (inj)     -                0.0
Inter-ties         0     Total Inter-tie Flow     0.0               0.0
Areas              1

                          Minimum                      Maximum
                 -------------------------  --------------------------------
Voltage Magnitude   1.154 p.u. @ bus 1          1.174 p.u. @ bus 2
Voltage Angle       0.00 deg   @ bus 1          3.31 deg   @ bus 2
P Losses (I^2*R)             -                  0.00 MW    @ line 1-2
Q Losses (I^2*X)             -                  9.41 MVAr  @ line 1-2

================================================================================
|     Bus Data
    |
================================================================================
 Bus      Voltage          Generation             Load
  #   Mag(pu) Ang(deg)   P (MW)   Q (MVAr)   P (MW)   Q (MVAr)
----- ------- --------  --------  --------  --------  --------
    1  1.154    0.000*  -149.60    -39.69       -         -
    2  1.174    3.313    149.60     49.10       -         -
                        --------  --------  --------  --------
               Total:     -0.00      9.41      0.00      0.00

================================================================================
|     Branch Data
   |
================================================================================
Brnch   From   To    From Bus Injection   To Bus Injection     Loss (I^2 *
Z)
  #     Bus    Bus    P (MW)   Q (MVAr)   P (MW)   Q (MVAr)   P (MW)   Q
(MVAr)
-----  -----  -----  --------  --------  --------  --------  --------
 --------
   1      1      2   -149.60    -39.69    149.60     49.10     0.000
 9.41
                                                             --------
 --------
                                                    Total:     0.000
 9.41

Best,

Uriel


El mar, 8 de dic. de 2020 a la(s) 19:59, Russ Patterson ([email protected])
escribió:

> Hi Uriel,
>
>
>
> I made the changes you suggested and I’m getting this “out of bound” error:
>
>
>
> >> runpf('example1')
>
> error: pv(1): out of bound 0 (dimensions are 0x1)
>
> error: called from
>
>     bustypes at line 43 column 13
>
>     runpf at line 114 column 19
>
>
>
> thank you,
>
> russ
>
>
>
>
>
> *From:* [email protected] [mailto:
> [email protected]] *On Behalf Of *Uriel Fernando
> Sandoval Pérez
> *Sent:* Tuesday, December 8, 2020 7:18 PM
> *To:* MATPOWER discussion forum
> *Subject:* Re: infinite bus, 1 branch/1 gen
>
>
>
> Hi,
>
>
>
>
>
> It seems you are modelling de active/reactive power injections as a
> negative load. But,
>
> then you also define a generator with P=149.6 and Q=49.104. You should
> delete de load ( set to zero Pd and Qd), fix the active power of the
> generator and set Qmax=Qmin=49.104
>
>
>
>
>
> Hope this helps.
>
>
>
> El mar., 8 de diciembre de 2020 16:02, Russ Patterson <[email protected]>
> escribió:
>
> Hi,
>
>
>
> I have a simple problem as shown below.  The upper bus is the infinite,
> slack bus.  For the specified P & Q, I want to solve for VX.  Per my hand
> calculations (iterations) the result will be VX=1.174pu @-3.3°.
>
>
>
> Now, I am trying to model this in a simple load flow as my *first ever*
> attempt to use MATPOWER (attached, which fails miserably).
>
>
>
>
>
> I have the manual and understand all of the bus, generator, and branch
> data.  What I don’t know is – what can be left out in solving this simple
> problem?   The machine is rated 16kV, 176MVA but I’d prefer to leave that
> out and just work all in per unit (including data entry) if possible.
>
>
>
> Thanks,
>
> Russ
>
>
> ------------------------------
>