Hi Russ, Attached is the file with some modifications. I obtained the same result you got manually.
================================================================================
| System Summary
|
================================================================================
How many? How much? P (MW) Q (MVAr)
--------------------- ------------------- -------------
-----------------
Buses 2 Total Gen Capacity 0.0 49.1 to 49.1
Generators 2 On-line Capacity 0.0 49.1 to 49.1
Committed Gens 2 Generation (actual) -0.0 9.4
Loads 0 Load 0.0 0.0
Fixed 0 Fixed 0.0 0.0
Dispatchable 0 Dispatchable -0.0 of -0.0 -0.0
Shunts 0 Shunt (inj) -0.0 0.0
Branches 1 Losses (I^2 * Z) 0.00 9.41
Transformers 0 Branch Charging (inj) - 0.0
Inter-ties 0 Total Inter-tie Flow 0.0 0.0
Areas 1
Minimum Maximum
------------------------- --------------------------------
Voltage Magnitude 1.154 p.u. @ bus 1 1.174 p.u. @ bus 2
Voltage Angle 0.00 deg @ bus 1 3.31 deg @ bus 2
P Losses (I^2*R) - 0.00 MW @ line 1-2
Q Losses (I^2*X) - 9.41 MVAr @ line 1-2
================================================================================
| Bus Data
|
================================================================================
Bus Voltage Generation Load
# Mag(pu) Ang(deg) P (MW) Q (MVAr) P (MW) Q (MVAr)
----- ------- -------- -------- -------- -------- --------
1 1.154 0.000* -149.60 -39.69 - -
2 1.174 3.313 149.60 49.10 - -
-------- -------- -------- --------
Total: -0.00 9.41 0.00 0.00
================================================================================
| Branch Data
|
================================================================================
Brnch From To From Bus Injection To Bus Injection Loss (I^2 *
Z)
# Bus Bus P (MW) Q (MVAr) P (MW) Q (MVAr) P (MW) Q
(MVAr)
----- ----- ----- -------- -------- -------- -------- --------
--------
1 1 2 -149.60 -39.69 149.60 49.10 0.000
9.41
--------
--------
Total: 0.000
9.41
Best,
Uriel
El mar, 8 de dic. de 2020 a la(s) 19:59, Russ Patterson ([email protected])
escribió:
> Hi Uriel,
>
>
>
> I made the changes you suggested and I’m getting this “out of bound” error:
>
>
>
> >> runpf('example1')
>
> error: pv(1): out of bound 0 (dimensions are 0x1)
>
> error: called from
>
> bustypes at line 43 column 13
>
> runpf at line 114 column 19
>
>
>
> thank you,
>
> russ
>
>
>
>
>
> *From:* [email protected] [mailto:
> [email protected]] *On Behalf Of *Uriel Fernando
> Sandoval Pérez
> *Sent:* Tuesday, December 8, 2020 7:18 PM
> *To:* MATPOWER discussion forum
> *Subject:* Re: infinite bus, 1 branch/1 gen
>
>
>
> Hi,
>
>
>
>
>
> It seems you are modelling de active/reactive power injections as a
> negative load. But,
>
> then you also define a generator with P=149.6 and Q=49.104. You should
> delete de load ( set to zero Pd and Qd), fix the active power of the
> generator and set Qmax=Qmin=49.104
>
>
>
>
>
> Hope this helps.
>
>
>
> El mar., 8 de diciembre de 2020 16:02, Russ Patterson <[email protected]>
> escribió:
>
> Hi,
>
>
>
> I have a simple problem as shown below. The upper bus is the infinite,
> slack bus. For the specified P & Q, I want to solve for VX. Per my hand
> calculations (iterations) the result will be VX=1.174pu @-3.3°.
>
>
>
> Now, I am trying to model this in a simple load flow as my *first ever*
> attempt to use MATPOWER (attached, which fails miserably).
>
>
>
>
>
> I have the manual and understand all of the bus, generator, and branch
> data. What I don’t know is – what can be left out in solving this simple
> problem? The machine is rated 16kV, 176MVA but I’d prefer to leave that
> out and just work all in per unit (including data entry) if possible.
>
>
>
> Thanks,
>
> Russ
>
>
> ------------------------------
>