Hi,

It seems you are modelling de active/reactive power injections as a
negative load. But,
then you also define a generator with P=149.6 and Q=49.104. You should
delete de load ( set to zero Pd and Qd), fix the active power of the
generator and set Qmax=Qmin=49.104


Hope this helps.