Hi Carlos,

 

Thank you.  That makes sense.  Based on that, I would expect to be able to set 
the bus voltage, Vm, and it stick, but it doesn’t.  If I set Vm=2 and run the 
load flow it solves properly with the resulting bus voltage being 1.154pu.

 

So, in essence, I am specifying the magnitude for the slack bus in the “mpc.gen 
Vg” setting, and then I am specifying the angle for the slack bus in the 
“mpc.bus Va” setting.  You would expect both mag and angle to be specified in 
the same place.

 

This is counterintuitive, which is why I ask if this level of detail about how 
input is used/overridden is documented anywhere – or if it will just be a 
learn-by-trying approach.

 

Either way, I’m very happy to have found this fantastic software.  Thank you 
for your help.

 

Best regards,

Russ

 

 

From: [email protected] 
[mailto:[email protected]] On Behalf Of Carlos E 
Murillo-Sanchez
Sent: Wednesday, December 9, 2020 4:11 PM
To: MATPOWER discussion forum
Subject: Re: infinite bus, 1 branch/1 gen

 

Carlos wrote:

Dear Russ:  Bus #1 is designated as the slack bus (and hence, also for angular 
reference).  Thus, for this particular bus alone, the angle is assumed known 
and taken from the respective column in the bus table.  This is a standard 
power flow assumption.