Hi Matt,

2012/2/13 Matt Schulte <[email protected]>:
> Device manufacturer and name:
> Tripp-Lite OmniSmart500
>
> upsc output:
> matt@backup:/etc$ sudo upsc tripplite
> battery.charge: 100
> battery.test.status: Battery OK
> battery.voltage: 14.56
> battery.voltage.nominal: 12
> device.mfr: Tripp Lite
> device.model: OMNISMART500
> device.type: ups
> driver.name: tripplite_usb
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.version: 2.4.3
> driver.version.internal: 0.20
> input.voltage: 108.60
> input.voltage.nominal: 120
> output.voltage: 113.0
> ups.debug.load_banks: 0
> ups.debug.V: 31 30 32 30 58 58 0d '1020XX.'
> ups.delay.shutdown: 64
> ups.firmware: F0966.A
> ups.firmware.aux: protocol 2001
> ups.mfr: Tripp Lite
> ups.model: OMNISMART500
> ups.power.nominal: 500
> ups.productid: 0001
> ups.status: OL
> ups.vendorid: 09ae
> matt@backup:/etc$
>
> shutdown sequence testing results:
> Not sure exactly what you would like to see here, but after
> configuring everything and pulling the plug the system shut down
> correctly when the UPS dropped below 20%.

we just need a confirmation as you did, plus the fact that the UPS was
powered off in the end.

> /etc/log/daemon.log:
> Feb 13 10:11:47 backup upsmon[12058]: UPS tripplite@localhost battery is low
> Feb 13 10:11:47 backup upsd[11649]: Client [email protected] set FSD on UPS 
> [trip
> plite]
> Feb 13 10:11:47 backup upsmon[12058]: Executing automatic power-fail shutdown
> Feb 13 10:11:47 backup upsmon[12058]: Auto logout and shutdown proceeding
>
> link:
> http://www.tripplite.com/en/products/model.cfm?txtModelID=21

thanks for your report.
I've just added an entry to the HCL.
For the sake of completion, could you please also send upsrw and upscmd outputs?

I leave up to Charles, the driver author, to ask more info for
potential driver improvement.

cheers,
Arnaud
-- 
Linux / Unix Expert R&D - Eaton - http://powerquality.eaton.com
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.free.fr/

_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to