On Wed, Feb 15, 2012 at 5:47 PM, Charles Lepple <[email protected]> wrote:
> On Feb 15, 2012, at 12:58 PM, Matt Schulte wrote:
>
>> On Tue, Feb 14, 2012 at 8:51 PM, Charles Lepple <[email protected]> wrote:
>>> On Feb 14, 2012, at 12:56 PM, Matt Schulte wrote:
>>>
>>>> Why does it say "battery.test.status: Battery bad - replace?"
>>>
>>> Not to be too literal, but it comes from this block of code in 
>>> tripplite_usb.c, which may or may not be accurate for your specific model.
>>>
>>>        if(tl_model == TRIPP_LITE_SMARTPRO || tl_model == 
>>> TRIPP_LITE_OMNIVS_2001 || tl_model == TRIPP_LITE_SMART_0004) {
>>>                switch(s_value[2]) {
>>>                        case '0':
>>>                                dstate_setinfo("battery.test.status", 
>>> "Battery OK");
>>>                                break;
>>>                        case '1':
>>>                                dstate_setinfo("battery.test.status", 
>>> "Battery bad - replace");
>>>                                break;
>>>                        case '2':
>>>                                status_set("CAL");
>>>                                break;
>>>                        case '3':
>>>                                status_set("OVER");
>>>                                dstate_setinfo("battery.test.status", 
>>> "Overcurrent?");
>>>                                break;
>>>                        case '4':
>>>                                /* The following message is confusing, and 
>>> may not be accurate: */
>>>                                /* dstate_setinfo("battery.test.status", 
>>> "Battery state unknown"); */
>>>                                break;
>>>
>>> Usually, after you first plug in the UPS, the status bit says "4", which 
>>> apparently means that the battery charger hasn't seen much of the slope of 
>>> the charge or discharge curve yet. (If the battery is just being topped 
>>> off, you can't really tell its capacity by the instantaneous current or 
>>> voltage.)
>>>
>>> After a deep discharge cycle, the charging circuit has seen both the rate 
>>> of discharge as well as the rate of charge, and it can guess as to whether 
>>> the battery is close to the end of its life. Lead-acid batteries are 
>>> usually good for 3-5 years.
>>>
>> Any idea why it would decide to throw the "bad" flag on a new battery?
>> I recently (as in maybe two weeks ago) had to replace the battery in
>> the UPS.
>
>
> It's possible that the UPS needs to be recalibrated somehow - is there a 
> procedure in the manual?
>
> Unfortunately, we don't know the command necessary to initiate a deep 
> discharge test from the USB side, but maybe there is a front panel button 
> sequence.
>
> I don't think we've heard that this is necessary on Tripp Lite UPSes, but 
> some APC units apparently get confused if there is no ground connection while 
> discharging. (We'll need to replace all occurrences of "pull the plug" with 
> something like "turn off the power strip" or similar.)
>
FWIW: I made the bad battery message go away by running a "Self Test"
by holding down the Mute button for two seconds while the unit is
powered on and everything connected to it is running.