On Tue, Feb 14, 2012 at 11:53 AM, Matt Schulte <[email protected]> wrote:
> On Tue, Feb 14, 2012 at 7:10 AM, Charles Lepple <[email protected]> wrote:
>> On Feb 14, 2012, at 3:42 AM, Arnaud Quette wrote:
>>
>>>> shutdown sequence testing results:
>>>> Not sure exactly what you would like to see here, but after
>>>> configuring everything and pulling the plug the system shut down
>>>> correctly when the UPS dropped below 20%.
>>>
>>> we just need a confirmation as you did, plus the fact that the UPS was
>>> powered off in the end.
>>
>> Not critical, but did the UPS power on automatically after you plugged it 
>> back in, or did you have to press the power button manually?
>
> I might have just powered back up if I had given it more time, but I
> was sort of anxious to get my server back up.  I plugged the UPS back
> in, then reached over and turned on the server.  It didn't like that
> and dropped power to the server.  Then I pressed the power button to
> turn it off and then on again, then was able to power up my server
> again.
>
>>
>>>> /etc/log/daemon.log:
>>>> Feb 13 10:11:47 backup upsmon[12058]: UPS tripplite@localhost battery is 
>>>> low
>>>> Feb 13 10:11:47 backup upsd[11649]: Client [email protected] set FSD on UPS 
>>>> [trip
>>>> plite]
>>>> Feb 13 10:11:47 backup upsmon[12058]: Executing automatic power-fail 
>>>> shutdown
>>>> Feb 13 10:11:47 backup upsmon[12058]: Auto logout and shutdown proceeding
>>>>
>>>> link:
>>>> http://www.tripplite.com/en/products/model.cfm?txtModelID=21
>>
>> Tripp Lite tends to reuse marketing names for products even when the inner 
>> workings have changed. That web page describes how the UPS works with the 
>> auto-shutdown code in Windows and OS X, but I don't think that applies to 
>> UPSes which work with the tripplite_usb driver (that would be more in line 
>> with usbhid-ups). Approximately when was this UPS manufactured?
>>
> It was purchased in 2004 so I would guess sometime around then.
>
>>> thanks for your report.
>>> I've just added an entry to the HCL.
>>> For the sake of completion, could you please also send upsrw and upscmd 
>>> outputs?
>>
>> Agreed, this would be good for verification.
>>
> Did the outputs that I sent just before this email have what you need?
>
>>> I leave up to Charles, the driver author, to ask more info for
>>> potential driver improvement.
>>
>> At this point, I am not actively working on this driver, so any improvements 
>> would be contingent on your availability to test new code (and tolerating 
>> the potential downtime that would go with that testing). Also, I don't have 
>> a system with PowerAlert.
>>
> I am game for testing if you have anything you want to do.  I just may
> take a day or two to wait for an off peak time.  I also do not have a
> system with PowerAlert.
>
> Matt Schulte

I have a question for you guys, today after the UPS has come back to a
full charge I get a red light on the front of the UPS and I get this
from upsc:

matt@backup:~$ upsc tripplite
battery.charge: 100
battery.test.status: Battery bad - replace
battery.voltage: 14.56
battery.voltage.nominal: 12
device.mfr: Tripp Lite
device.model: OMNISMART500
device.type: ups
driver.name: tripplite_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.internal: 0.20
input.voltage: 109.23
input.voltage.nominal: 120
output.voltage: 113.5
ups.debug.load_banks: 0
ups.debug.V: 31 30 32 30 58 58 0d '1020XX.'
ups.delay.shutdown: 64
ups.firmware: F0966.A
ups.firmware.aux: protocol 2001
ups.mfr: Tripp Lite
ups.model: OMNISMART500
ups.power.nominal: 500
ups.productid: 0001
ups.status: OL
ups.vendorid: 09ae

Why does it say "battery.test.status: Battery bad - replace?"

_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to