On Tue, Feb 14, 2012 at 8:51 PM, Charles Lepple <[email protected]> wrote:
> On Feb 14, 2012, at 12:56 PM, Matt Schulte wrote:
>
>> Why does it say "battery.test.status: Battery bad - replace?"
>
> Not to be too literal, but it comes from this block of code in 
> tripplite_usb.c, which may or may not be accurate for your specific model.
>
>        if(tl_model == TRIPP_LITE_SMARTPRO || tl_model == 
> TRIPP_LITE_OMNIVS_2001 || tl_model == TRIPP_LITE_SMART_0004) {
>                switch(s_value[2]) {
>                        case '0':
>                                dstate_setinfo("battery.test.status", "Battery 
> OK");
>                                break;
>                        case '1':
>                                dstate_setinfo("battery.test.status", "Battery 
> bad - replace");
>                                break;
>                        case '2':
>                                status_set("CAL");
>                                break;
>                        case '3':
>                                status_set("OVER");
>                                dstate_setinfo("battery.test.status", 
> "Overcurrent?");
>                                break;
>                        case '4':
>                                /* The following message is confusing, and may 
> not be accurate: */
>                                /* dstate_setinfo("battery.test.status", 
> "Battery state unknown"); */
>                                break;
>
> Usually, after you first plug in the UPS, the status bit says "4", which 
> apparently means that the battery charger hasn't seen much of the slope of 
> the charge or discharge curve yet. (If the battery is just being topped off, 
> you can't really tell its capacity by the instantaneous current or voltage.)
>
> After a deep discharge cycle, the charging circuit has seen both the rate of 
> discharge as well as the rate of charge, and it can guess as to whether the 
> battery is close to the end of its life. Lead-acid batteries are usually good 
> for 3-5 years.
>
Any idea why it would decide to throw the "bad" flag on a new battery?
 I recently (as in maybe two weeks ago) had to replace the battery in
the UPS.