Hi William,

is the problem the actual connection or the AGS?

if its the actual connection, have you tried putting a load ( say 1000 watt 
heater) on the generator directly  to stabilize the volt/hz from the genny?
if for a test if nothing else.

jay

peltz power

On Sep 8, 2011, at 9:40 PM, William Miller wrote:

> Friends:
> 
> Working yesterday on a newer XW system with a new Kohler RES15 generator.  
> This is the first time I have tested the inverter with this generator.  The 
> inverter would not maintain a transfer to the generator.  After about an hour 
> on the phone with tech support, the tech searched previous calls and 
> announced that there is a known incompatibility between the Kohler RES15 and 
> a certain version of the XW firmware.  I was advised to upgrade the firmware.
> 
> I wonder how this can be.  Voltage and frequency even in the moment the 
> inverter did try to connect are well within specifications. After some 
> thought, all I can guess is that there might be some noise on the AC signal 
> that the inverter might reject.
> 
> Has anyone else experienced this?  Any insight to be offered?
> 
> Thanks in advance.
> 
> William Miller
> 
> William Miller 
> Miller Solar
> Voice :805-438-5600
> email: [email protected]
> http://millersolar.com
> License No. C-10-773985
> 
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to