Jay:

I disconnected the AGS and the problem persisted. Adding a load may help but I did not test this. This would require a permanent load and might not be desirable.

William



At 07:36 AM 9/9/2011, you wrote:
Hi William,

is the problem the actual connection or the AGS?

if its the actual connection, have you tried putting a load ( say 1000 watt heater) on the generator directly to stabilize the volt/hz from the genny?
if for a test if nothing else.

jay

peltz power

On Sep 8, 2011, at 9:40 PM, William Miller wrote:

Friends:

Working yesterday on a newer XW system with a new Kohler RES15 generator. This is the first time I have tested the inverter with this generator. The inverter would not maintain a transfer to the generator. After about an hour on the phone with tech support, the tech searched previous calls and announced that there is a known incompatibility between the Kohler RES15 and a certain version of the XW firmware. I was advised to upgrade the firmware.

I wonder how this can be. Voltage and frequency even in the moment the inverter did try to connect are well within specifications. After some thought, all I can guess is that there might be some noise on the AC signal that the inverter might reject.

Has anyone else experienced this?  Any insight to be offered?

Thanks in advance.

William Miller
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to