I've installed 20-30 pole mounts with the PVC conduit running from underground,
through the 3' sonotube into the concrete. It then sweeps up to meet the
pole/pipe, exits the concrete right next to it and continues to the DC disco.
Never had an issue with the AHJ.
It doesn't really get much sun on it being under the array (many times
3-3.8KW of PV on an 8" pole) and the array is good at keeping tractors, riding
mowers, etc away. I usually add one conduit clamp between the top of the
concrete and the disco.
As a side note, we use 3 straps (from pole/pipe to temporary driven
anchor) to secure the pole close to vertical during the pour which helps to
keep the bottom of the pole/pipe from moving off center, allows us to secure
(code word for 'duct tape') the aforementioned conduit to the pole and allows
us to "forget" about pushing the pole vertical after about 1/2 the mud is in
the sonotube, because it already is...we fine tune the vertical prior to the
end of mud.
Happy, merry, ho,ho from the northern Sierra,
Bill
Feather River Solar Electric
With pole mount systems, It looks cleaner and is safer to run the PVC conduit
down the pole into the concrete, and use a 90 degree elbow to come out through
the side of the anchor underground. This way, the pipe is protected from
mechanical damage, and there is nothing to trip over when adjusting the array
for seasonal tilt.
I was told that some building departments will not allow this. Has anyone had
a problem with using this method, either technical or legal? How do you like
to route your conduits?
Thank you,
Drake
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org