Gary,
  I keep 24v and 48 v IOTA chargers with jumper cables attached for those times 
when systems are dead.  Just a minute or so plugged into my Honda 2000I or 
generator on bypass gets everything lit up and running. 
Just did one yesterday.  Got Kohler running but Mate 3 and inverter would not 
turn on. 

John B

Sent from my iPhone

> On Feb 10, 2018, at 3:37 AM, Sindelar Solar <[email protected]> wrote:
> 
> Gary, you might try an old-fashioned approach: bypass the controller to send 
> the array straight to the batteries until threshold voltage is reached. More 
> specifically, bypass one of the controllers; assuming 48, 60 or 72 Vnom 
> depending on array. Let the other controller remain in normal operation. Send 
> the unregulated array to bring initial battery voltage up; then the other 
> controller takes over and the one that was bypassed now is reconnected. 
> Better if the unregulated array is the smaller of the two, I would suspect.
> What I'm suggesting will work with flooded lead-acid, and likely VRLA 
> lead-acid as well, as long as the unregulated array is taken out of the 
> system before voltage exceeds bulk. It may not work at all with these Li-I, 
> as I have no experience with restoring them.       Daryl may well be right 
> about being unrestorable below a threshold voltage; also the batteries may 
> need an operational BMS to take a charge. So this is perhaps just food for 
> thought.
> 
> Allan
> -- 
> Allan Sindelar
> [email protected]
> NABCEP Certified PV Installation Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> 505 780-2738 cell
> 
>> On 2/9/2018 6:16 PM, Gary Rochlin wrote:
>> Does anyone have any information or specifications for an older circa 
>> 2010-2012 iCel System Lithium Ion Battery.  We are doing a repair on an 
>> older 48V Lithium Ion system consisting of 3-6 ICel batteries wired in 
>> parallel and 1 Xantrex 6848 and 2 Xantrex Conext MPPT 60 150 Solar Charge 
>> controllers.  Via a surge from SCE system shut down and sat before we were 
>> called in.  Batteries are sitting at 6.67V and the charge controller will 
>> not turn on unless the batteries are at 40V since at the time they were made 
>> for lead acid batteries.  I’m looking at finding the way to charge the iCel  
>> batteries or goose the charge controller into thinking 40V are coming from 
>> the batteries.  I think I’m making sense here. 
>> 
>> Blue Sky Energy
>> 
>> [email protected]
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to