Fellow Wrenches, I'm having a discussion with a utility engineer
regarding the following situation:
Installing a 6kW inverter that has a full rated output of 25 amps. 80%
of 30 is 24. That means to me I need to go up to a 40 amp breaker. I'm
running #8 (continuous load 25 x 1.25 etc.)
The engineer believes I should use a 60 amp disco since it's on a 40 amp
breaker. My thinking is I can use a 30 amp disco since it can not
produce more than 25 amps ever.
Do any of you have a reference that shows what I'm doing is okay? Not okay?
Thanks again,
Greg Egan
Remote Power Inc.
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org