I agree Blake - you have to check the specs and consult the mfg. The same is 
true with combiners, some are rated for continuous duty/full load, and some are 
not. Lots of large systems out there with 200A combiners connected to 250A 
OCPDs (and 250A conductors, but that’s another story...). 

Brian

> On Aug 21, 2019, at 5:20 PM, Blake Gleason <[email protected]> wrote:
> 
> Typically a fused disconnect can only handle 80% of it's nominal current on a 
> continuous basis.  Unfused disconnects are often 100% rated.  For example, 
> see attached Square D bulletin #3110DB0401R0410.
> 
> So, a 100% rated (unfused) 30A disconnect (at least, from Square D) should be 
> fine here, as long as your OCPD is provided elsewhere (eg, the breaker you 
> mentioned).  
> 
> NEC 690.8(B)(1)(Exception) explicitly allows a 100%-rated device to be used 
> without multiplying the inverter output current by 125%.
> 
> 
>> On Wed, Aug 21, 2019 at 3:22 PM Greg <[email protected]> wrote:
>> Fellow Wrenches,  I'm having a discussion with a utility engineer regarding 
>> the following situation:
>> 
>> Installing a 6kW inverter that has a full rated output of 25 amps.  80% of 
>> 30 is 24.  That means to me I need to go up to a 40 amp breaker.  I'm 
>> running #8 (continuous load 25 x 1.25 etc.)  
>> The engineer believes I should use a 60 amp disco since it's on a 40 amp 
>> breaker.  My thinking is I can use a 30 amp disco since it can not produce 
>> more than 25 amps ever.  
>> 
>> Do any of you have a reference that shows what I'm doing is okay? Not okay?  
>> 
>> Thanks again, 
>> Greg Egan
>> Remote Power Inc.  
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> 
> 
> -- 
> 
> 
>       
> Blake Gleason, PE | Employee-Owner |
> Director of Innovation & Technical Excellence
> 
> 510.845.2997 x128
> 
> Follow us on Facebook, LinkedIn or our website.  
> 
> <Square-D-Switch-PV-Bulletin_06-10_100percent_rated.pdf>
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to