Folks,

Thread points up the ever present weakness of the Code to deal with PV. In terms of specifying OCP, the Code completely fails to parse out overload protection from short circuit protection and always looks at it from the point of view of the grid. To Blake's credit he did bring in the issue of current interrupt capacity.

Point is that a 40A breaker between the gird and (grid-tied) inverter will never see a condition where the the inverter is drawing any current of any significant magnitude for any significant period of time. The only time it will draw current from the grid is if some element within it is in short-circuit mode. In this case it really doesn't matter what the rating of the breaker is, 30 A, 40 A, of 100 A, it is going to trip very quickly when it sees a short circuit condition. All the over-sizing stuff in the code really only addresses high load/over load conditions which are not relevant to the situation we are talking about.

Another way of saying this, which would be more sensible is: yes, evaluate the circuit in both directions, but only consider the load to be continuous in the direction from the inverter to the grid.

Mark

On 8/22/2019 2:29 PM, William Miller wrote:

Blake:

Thank you for the reference from Schneider.

I think the point being missed here is that the ampacity rating of each device needs to be evaluated in light of the power flow in either direction.  If a 40 Amp breaker is supplied between the utility and the disconnect in question, in case of a fault, it could supply more current from the grid than a 30 Amp disconnect is rated to handle.   This is particularly relevant considering the grid is not nearly as much a current limited source as an inverter.

Sincerely,

William Miller

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com <http://www.millersolar.com/>

CA Lic. 773985

Quote of the month:  “As they age, batteries transition from energy

storage devices to energy consuming devices.“ W. Miller

*From:*Blake Gleason [mailto:[email protected] <mailto:[email protected]>]
*Sent:* Thursday, August 22, 2019 12:38 PM
*To:* [email protected] <mailto:[email protected]>; RE-wrenches
*Subject:* Re: [RE-wrenches] 30 amp disconnect/40 amp breaker

Hi William,

Yes, the bulletin I attached was just an example of a 100% rated disconnect (which happened to be DC since that's the one I had handy!).  My understanding is that most of the NON-fused Square D switches are rated for 100%.

See this FAQ from the manufacturer: https://www.schneider-electric.us/en/faqs/FA237949/, quoted below:

    *Resolution:**
    *All General Duty, Heavy Duty or Double Throw Safety Switches
    maximum current rating, either 80% or 100% of the nameplate
    rating, depends on if the switch is Fusible or NON-Fusible.

    oFusible switches are rated to carry up to 80% of the amp rating
    of the fuses installed in the switch

    oNon-fusible (unfused) switches are rated to carry 100% of the
    switch nameplate ampere rating

 Regarding this point:

    If, hypothetically, you could find a 30A disconnect that was
    continuous duty rated, if it is fed by a 40 Amp breaker, as I
    believe would be required, then the 30 Amp disconnect is still not
    suitable.  You can not feed a 30 Amp rated device with more than
    30 Amps.

I believe the original poster was asking about a 6000W inverter with 25A max output.  So in that case you could use a 100% rated non-fusible disconnect, because the max current is only 25A.  (The required 40A breaker is sized larger because commonly available breakers are only 80% rated, not 100%.  But the max current is still only 25A.)  See 690.8(A) for calculation of maximum circuit current, specifically section (3) for inverters: "The maximum current shall be the inverter continuous output current rating."  (Not "the inverter continuous output current multiplied by 1.25.")

Best,

Blake

On Wed, Aug 21, 2019 at 10:59 PM William Miller <[email protected] <mailto:[email protected]>> wrote:

    Blake:

    Thanks for sharing the data sheet.  The document applies to DC PV
    systems, however, and I believe the discussion pertains to the AC
    inverter output. Therefore the bulletin you attached does not
    apply here.

    (Note also that this data sheet indicates you need to use two
    poles for any application, ungrounded or grounded.  I believe that
    requirement was usurped later on for Square D Heavy Duty switches,
    but again, that is for a different application.)

    I looked again at Square D general and heavy duty safety switches
    rated at 30 Amps and I could not find any reference that these
    switches are continuous duty rated.  I still believe that for the
    application described, the 125% rating has to be applied.

    If, hypothetically, you could find a 30A disconnect that was
    continuous duty rated, if it is fed by a 40 Amp breaker, as I
    believe would be required, then the 30 Amp disconnect is still not
    suitable. You can not feed a 30 Amp rated device with more than 30
    Amps.

    Bottom line, a 30 Amp disconnect will not meet code on the
    described project.

    William Miller

    Miller Solar

    17395 Oak Road, Atascadero, CA 93422

    805-438-5600

    www.millersolar.com <http://www.millersolar.com/>

    CA Lic. 773985

    Quote of the month:  “As they age, batteries transition from energy

    storage devices to energy consuming devices.“ W. Miller

    *From:*RE-wrenches
    [mailto:[email protected]
    <mailto:[email protected]>] *On Behalf Of
    *Blake Gleason
    *Sent:* Wednesday, August 21, 2019 4:20 PM
    *To:* RE-wrenches
    *Subject:* Re: [RE-wrenches] 30 amp disconnect/40 amp breaker

    Typically a fused disconnect can only handle 80% of it's nominal
    current on a continuous basis.  Unfused disconnects are often 100%
    rated.  For example, see attached Square D bulletin #3110DB0401R0410.

    So, a 100% rated (unfused) 30A disconnect (at least, from Square
    D) should be fine here, as long as your OCPD is provided elsewhere
    (eg, the breaker you mentioned).

    NEC 690.8(B)(1)(Exception) explicitly allows a 100%-rated device
    to be used without multiplying the inverter output current by 125%.

    On Wed, Aug 21, 2019 at 3:22 PM Greg <[email protected]
    <mailto:[email protected]>> wrote:

        Fellow Wrenches,  I'm having a discussion with a utility
        engineer regarding the following situation:

        Installing a 6kW inverter that has a full rated output of 25
        amps.  80% of 30 is 24. That means to me I need to go up to a
        40 amp breaker.  I'm running #8 (continuous load 25 x 1.25 etc.)
        The engineer believes I should use a 60 amp disco since it's
        on a 40 amp breaker.  My thinking is I can use a 30 amp disco
        since it can not produce more than 25 amps ever.

        Do any of you have a reference that shows what I'm doing is
        okay? Not okay?

        Thanks again,
        Greg Egan
        Remote Power Inc.

        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>


--
        

    *Blake Gleason, PE***| Employee-Owner |

    *Director of Innovation & Technical Excellence*


    510.845.2997 x128

    Follow us onFacebook
    <https://www.facebook.com/pages/Sun-Light-Power/119675658118322?ref=hl>,
    LinkedIn <https://www.linkedin.com/company/sun-light-and-power> or
    our website <https://sunlightandpower.com/>.

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


--

        

*Blake Gleason, PE***| Employee-Owner |

*Director of Innovation & Technical Excellence*


510.845.2997 x128

Follow us onFacebook <https://www.facebook.com/pages/Sun-Light-Power/119675658118322?ref=hl>, LinkedIn <https://www.linkedin.com/company/sun-light-and-power> or our website <https://sunlightandpower.com/>.


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to