Blake:
Thank you for the reference from Schneider.
I think the point being missed here is that the ampacity rating of
each device needs to be evaluated in light of the power flow in either
direction. If a 40 Amp breaker is supplied between the utility and
the disconnect in question, in case of a fault, it could supply more
current from the grid than a 30 Amp disconnect is rated to handle.
This is particularly relevant considering the grid is not nearly as
much a current limited source as an inverter.
Sincerely,
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com <http://www.millersolar.com/>
CA Lic. 773985
Quote of the month: “As they age, batteries transition from energy
storage devices to energy consuming devices.“ W. Miller
*From:*Blake Gleason [mailto:[email protected]
<mailto:[email protected]>]
*Sent:* Thursday, August 22, 2019 12:38 PM
*To:* [email protected] <mailto:[email protected]>;
RE-wrenches
*Subject:* Re: [RE-wrenches] 30 amp disconnect/40 amp breaker
Hi William,
Yes, the bulletin I attached was just an example of a 100% rated
disconnect (which happened to be DC since that's the one I had
handy!). My understanding is that most of the NON-fused Square D
switches are rated for 100%.
See this FAQ from the manufacturer:
https://www.schneider-electric.us/en/faqs/FA237949/, quoted below:
*Resolution:**
*All General Duty, Heavy Duty or Double Throw Safety Switches
maximum current rating, either 80% or 100% of the nameplate
rating, depends on if the switch is Fusible or NON-Fusible.
oFusible switches are rated to carry up to 80% of the amp rating
of the fuses installed in the switch
oNon-fusible (unfused) switches are rated to carry 100% of the
switch nameplate ampere rating
Regarding this point:
If, hypothetically, you could find a 30A disconnect that was
continuous duty rated, if it is fed by a 40 Amp breaker, as I
believe would be required, then the 30 Amp disconnect is still not
suitable. You can not feed a 30 Amp rated device with more than
30 Amps.
I believe the original poster was asking about a 6000W inverter with
25A max output. So in that case you could use a 100% rated
non-fusible disconnect, because the max current is only 25A. (The
required 40A breaker is sized larger because commonly available
breakers are only 80% rated, not 100%. But the max current is still
only 25A.) See 690.8(A) for calculation of maximum circuit current,
specifically section (3) for inverters: "The maximum current shall be
the inverter continuous output current rating." (Not "the inverter
continuous output current multiplied by 1.25.")
Best,
Blake
On Wed, Aug 21, 2019 at 10:59 PM William Miller
<[email protected] <mailto:[email protected]>> wrote:
Blake:
Thanks for sharing the data sheet. The document applies to DC PV
systems, however, and I believe the discussion pertains to the AC
inverter output. Therefore the bulletin you attached does not
apply here.
(Note also that this data sheet indicates you need to use two
poles for any application, ungrounded or grounded. I believe that
requirement was usurped later on for Square D Heavy Duty switches,
but again, that is for a different application.)
I looked again at Square D general and heavy duty safety switches
rated at 30 Amps and I could not find any reference that these
switches are continuous duty rated. I still believe that for the
application described, the 125% rating has to be applied.
If, hypothetically, you could find a 30A disconnect that was
continuous duty rated, if it is fed by a 40 Amp breaker, as I
believe would be required, then the 30 Amp disconnect is still not
suitable. You can not feed a 30 Amp rated device with more than 30
Amps.
Bottom line, a 30 Amp disconnect will not meet code on the
described project.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com <http://www.millersolar.com/>
CA Lic. 773985
Quote of the month: “As they age, batteries transition from energy
storage devices to energy consuming devices.“ W. Miller
*From:*RE-wrenches
[mailto:[email protected]
<mailto:[email protected]>] *On Behalf Of
*Blake Gleason
*Sent:* Wednesday, August 21, 2019 4:20 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] 30 amp disconnect/40 amp breaker
Typically a fused disconnect can only handle 80% of it's nominal
current on a continuous basis. Unfused disconnects are often 100%
rated. For example, see attached Square D bulletin #3110DB0401R0410.
So, a 100% rated (unfused) 30A disconnect (at least, from Square
D) should be fine here, as long as your OCPD is provided elsewhere
(eg, the breaker you mentioned).
NEC 690.8(B)(1)(Exception) explicitly allows a 100%-rated device
to be used without multiplying the inverter output current by 125%.
On Wed, Aug 21, 2019 at 3:22 PM Greg <[email protected]
<mailto:[email protected]>> wrote:
Fellow Wrenches, I'm having a discussion with a utility
engineer regarding the following situation:
Installing a 6kW inverter that has a full rated output of 25
amps. 80% of 30 is 24. That means to me I need to go up to a
40 amp breaker. I'm running #8 (continuous load 25 x 1.25 etc.)
The engineer believes I should use a 60 amp disco since it's
on a 40 amp breaker. My thinking is I can use a 30 amp disco
since it can not produce more than 25 amps ever.
Do any of you have a reference that shows what I'm doing is
okay? Not okay?
Thanks again,
Greg Egan
Remote Power Inc.
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
--
*Blake Gleason, PE***| Employee-Owner |
*Director of Innovation & Technical Excellence*
510.845.2997 x128
Follow us onFacebook
<https://www.facebook.com/pages/Sun-Light-Power/119675658118322?ref=hl>,
LinkedIn <https://www.linkedin.com/company/sun-light-and-power> or
our website <https://sunlightandpower.com/>.
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
--
*Blake Gleason, PE***| Employee-Owner |
*Director of Innovation & Technical Excellence*
510.845.2997 x128
Follow us onFacebook
<https://www.facebook.com/pages/Sun-Light-Power/119675658118322?ref=hl>,
LinkedIn <https://www.linkedin.com/company/sun-light-and-power> or our
website <https://sunlightandpower.com/>.
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org