I have run into this many times and have never found a definitive answer.
The disconnect spec typically says that it must be protected with an ocpd
at or less than the disco rating, but we are dealing with a current limited
device (inverter) in this case so it would seem legal to me.

On Wed, Aug 21, 2019, 5:22 PM Greg <[email protected]> wrote:

> Fellow Wrenches,  I'm having a discussion with a utility engineer
> regarding the following situation:
>
> Installing a 6kW inverter that has a full rated output of 25 amps.  80% of
> 30 is 24.  That means to me I need to go up to a 40 amp breaker.  I'm
> running #8 (continuous load 25 x 1.25 etc.)
> The engineer believes I should use a 60 amp disco since it's on a 40 amp
> breaker.  My thinking is I can use a 30 amp disco since it can not produce
> more than 25 amps ever.
>
> Do any of you have a reference that shows what I'm doing is okay? Not
> okay?
>
> Thanks again,
> Greg Egan
> Remote Power Inc.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to