Not going through the NEC, but it doesn't make sense to me to put in an OCPD greater than the rating of the switch.  I am sure you can find in the spec sheet what the maximum OCPD allowed is. Chris

On 8/21/2019 6:12 PM, Greg wrote:
Fellow Wrenches,  I'm having a discussion with a utility engineer regarding the following situation:

Installing a 6kW inverter that has a full rated output of 25 amps.  80% of 30 is 24.  That means to me I need to go up to a 40 amp breaker.  I'm running #8 (continuous load 25 x 1.25 etc.) The engineer believes I should use a 60 amp disco since it's on a 40 amp breaker.  My thinking is I can use a 30 amp disco since it can not produce more than 25 amps ever.

Do any of you have a reference that shows what I'm doing is okay? Not okay?

Thanks again,
Greg Egan
Remote Power Inc.

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to