Hi Brad, Not a bad idea with this one to run the loads off the SPS's. Has anyone ever tried wiring these directly into a panel, rather than into an outlet? And do you know if the 120V signal from each one would match up, or do they work independantly? In other words can you wire both SPS into the same panel either on different legs, or on the same leg and use an autoxfr?
And with the Rapid shutdown and SPS. Does it not work with SMA's rapid shutdown box? I thought with those, the grid going down would not affect the rapid shutdown, and that it needs the signal from the controller to initiate RSD. So this way it will continue to work with the grid down. Cheers, Dave *Dave Tedeyan, PE* Senior Engineer | Taitem Engineering, PC 110 South Albany Street | Ithaca, NY 14850 o. *607.277.1118 x121* f. 607.277.2119 www.taitem.com Solar • Sustainability • Energy • Design B-Corporation Best for the World 2018 Honoree On Fri, Sep 20, 2019 at 10:33 AM Bradley Bassett <[email protected]> wrote: > If you're not using the SB -40 inverter's rapid shutdown system, it has > the SPS Secure Power Supply which does just what your customer wants. > > My understanding from talking to inverter mfg, is that trying to do AC > coupling with a smaller battery inverters does not work because the > anti-islanding in the grid tie inverter will be able to push the frequency > off too easily. > > Morningstar makes a 600 VDC charge control that has an array transfer > switch, so that during an outage you can switch it to use one or two > strings to charge a 48 V battery bank and power any 48 V inverter. It is > manual so the operator needs to change it back when the power comes back on. > > Brad > > > > On Fri, Sep 20, 2019 at 6:41 AM Dave Tedeyan <[email protected]> wrote: > >> Hi all, >> >> I get asked this question frequently, as I am sure many others do, and of >> course the first answer is "it cannot be done". But can it? I have a >> customer who is very keen on trying to make this happen. After a few >> lengthy conversations, he still wants to try it, even after understanding >> the limitations (i.e. a cloud passes by and now you cannot power loads...) >> >> I have some thoughts on how to make this work, and thought I would post >> it here to get others comments who I am sure have more experience in >> something like this than I do. >> >> -PV system would have to be backfed, so that they can turn off the main >> breaker to disconnect from the utility entirely (and then have to look at >> the neighbors, or guess when the grid comes back) >> -Have a fairly small 12V off grid inverter/charger than can be powered by >> a single 12v battery. This inverter would have to be manually turned off >> until after the grid is down and the main breaker is disconnected. >> -Would also need an auto transformer to bump up the voltage to 240V. >> Something like the Outback PSX240. >> -Once the main breaker is off and the off grid inverter is on, would it >> be able to wake up the grid tied inverters? On this project, there are two >> SMA SB-40 inverters. >> -There would need to be some kind of dump/diversion load to deal with >> excess power coming from the GT inverters. I have not used these in the >> past, but are the controllers smart enough to just deal with any excess >> power in the system? >> -Have a trickle charger on the battery to keep it topped off most of the >> time. >> >> -Another thought would be to DC couple. This would involve having a DC >> switch in one of the strings going to the GT inverter, such that when the >> house is islanded from the grid, they can flip the switch and have that one >> string go to a high voltage CC. Then they could just run some small loads >> off the power from that one string, or maybe we could allow it to try to >> wake up the GT inverters as well. >> >> This particular homeowner specifically does not want much in the way of >> batteries and has a smaller budget than will allow something sensible like >> a Sunny Island. >> >> At least in upstate NY, there are many people who would like to be able >> to take advantage of their solar when the sun is shining, but who just do >> not have the budget for a legit battery system. I am somewhat surprised >> that there is no simple industry solution for this yet, although maybe it >> is more complicated than I am making it out to be. And of course, you need >> a very hands on homeowner who very well understands the limitations of this >> kind of setup. >> >> I would certainly appreciate any feedback or comments on this, and also >> would like to hear if anyone has tried this kind of setup before. >> >> Thanks much! >> -Dave >> >> *Dave Tedeyan, PE* >> Senior Engineer | Taitem Engineering, PC >> >> 110 South Albany Street | Ithaca, NY 14850 >> o. *607.277.1118 x121* f. 607.277.2119 >> www.taitem.com >> >> Solar • Sustainability • Energy • Design >> B-Corporation Best for the World 2018 Honoree >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> List Address: [email protected] >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: >> http://www.mail-archive.com/[email protected]/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/[email protected]/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > >
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org

