Hi Mike,
For rapid shutdown, we are on NEC2014 in NY. So module level is not
necessary.

And the SPS is a huge reason for the SB inverters on this one. And in this
case, it is almost exactly what the homeowner is looking for. But with the
two inverters, can those SPS be wired into a panel rather than just into an
outlet? So far, this customers house has not even been built yet. The barn
is up, which is where the solar is going. So I am not 100% sure about
loads, but there will likely be heat pumps.

So if the SPS's can put power the same panel, then that might be just what
I am looking for in this particular case.

Although I am still curious if others have retrofitted other systems with
something like I was initially talking about for an inverter that does not
have a SPS. I think that at least in this market a low end 3rd party
solution could gain a lot of traction.

*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC

110 South Albany Street | Ithaca, NY 14850
o. *607.277.1118 x121*  f. 607.277.2119
www.taitem.com

Solar • Sustainability • Energy • Design
B-Corporation Best for the World 2018 Honoree


On Fri, Sep 20, 2019 at 10:58 AM Harry Mahon <[email protected]>
wrote:

> Dave – how is Rapid Shutdown being complied with?  And what load requires
> 240V – or is that needed to “fool” the PV inverters?
>
>
>
> With two SB-40s, you have the ability to wire for the homeowner two Secure
> Power Supply circuits – and get up to 2000W (at 120VAC) from each when sun
> is up and grid is down, no batteries or extra inverter needed.
>
>
>
> This is exactly the “simple industry solution” you mention, and it has
> been available in US from Sunny Boys only since 2013.
>
>
>
> Best regards -
>
> Mike
>
>
>
> SMA America
> Michael Mahon
> Technical Trainer, Solar Academy
> 6020 West Oaks Boulevard, Suite 300
>
> Rocklin, CA 95765
>
> U.S.A.
> Mobile:   +1 916 918 9412
> * www.SMA-America.com <http://www.sma-america.com/>*
>
>
>
> Solar Academy:
> www.SMA-America.com/partners/sma-solar-academy/overview.html
> <http://www.sma-america.com/partners/sma-solar-academy/overview.html>
>
>
>
> Full training schedule:
> https://www.sma-america.com/partners/sma-solar-academy/seminars/trainings/training/list.html
>
>
>
>
>
> [image:
> http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/facebook.jpg]
> <http://www.facebook.com/pages/SMA-America/140290312717395>[image:
> http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/twitter.jpg]
> <http://twitter.com/SMA_America> [image:
> http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/wordpress.jpg]
> <http://www.smainverted.com/> [image: Linkedin Logo]
> <http://www.linkedin.com/company/364675> [image:
> http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/youtube.jpg]
> <http://www.youtube.com/playlist?list=PL840A5336CAC32332> [image:
> SMAAFORUM_ICON] <http://smaadvance.com/signup/>
>
> [image: cid:[email protected]]
> <https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.sma-america.com%2Fhome-systems%2Fpv-solar-and-storage-solutions.html&data=02%7C01%7CMichael.Mahon%40sma-america.com%7Cc4bcd59d55584c70681208d71b72e485%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637008052588484449&sdata=itzAGcXAYe0xd5Zhzjuljm6dijJW%2FRGtItHrvxRkrTI%3D&reserved=0>
>
>
>
>
>
> This email and any attachments thereto may contain SMA America, LLC
> confidential, privileged and private material for the sole use of the
> intended recipient. Any review, copying, or distribution of this email (or
> any attachments thereto) by others is strictly prohibited. If you are not
> the intended recipient, please contact the sender immediately and
> permanently delete the original and any copies of this email and any
> attachments thereto. Thank you.
>
>
>
> *From:* RE-wrenches <[email protected]> *On
> Behalf Of *Dave Tedeyan
> *Sent:* Friday, September 20, 2019 7:41 AM
> *To:* RE-wrenches <[email protected]>
> *Subject:* [RE-wrenches] Running a grid tied system when the grid is down
>
>
>
> Hi all,
>
>
>
> I get asked this question frequently, as I am sure many others do, and of
> course the first answer is "it cannot be done". But can it? I have a
> customer who is very keen on trying to make this happen. After a few
> lengthy conversations, he still wants to try it, even after understanding
> the limitations (i.e. a cloud passes by and now you cannot power loads...)
>
>
>
> I have some thoughts on how to make this work, and thought I would post it
> here to get others comments who I am sure have more experience in something
> like this than I do.
>
>
>
> -PV system would have to be backfed, so that they can turn off the main
> breaker to disconnect from the utility entirely (and then have to look at
> the neighbors, or guess when the grid comes back)
>
> -Have a fairly small 12V off grid inverter/charger than can be powered by
> a single 12v battery. This inverter would have to be manually turned off
> until after the grid is down and the main breaker is disconnected.
>
> -Would also need an auto transformer to bump up the voltage to 240V.
> Something like the Outback PSX240.
>
> -Once the main breaker is off and the off grid inverter is on, would it be
> able to wake up the grid tied inverters? On this project, there are two SMA
> SB-40 inverters.
>
> -There would need to be some kind of dump/diversion load to deal with
> excess power coming from the GT inverters. I have not used these in the
> past, but are the controllers smart enough to just deal with any excess
> power in the system?
>
> -Have a trickle charger on the battery to keep it topped off most of the
> time.
>
>
>
> -Another thought would be to DC couple. This would involve having a DC
> switch in one of the strings going to the GT inverter, such that when the
> house is islanded from the grid, they can flip the switch and have that one
> string go to a high voltage CC. Then they could just run some small loads
> off the power from that one string, or maybe we could allow it to try to
> wake up the GT inverters as well.
>
>
>
> This particular homeowner specifically does not want much in the way of
> batteries and has a smaller budget than will allow something sensible like
> a Sunny Island.
>
>
>
> At least in upstate NY, there are many people who would like to be able to
> take advantage of their solar when the sun is shining, but who just do not
> have the budget for a legit battery system. I am somewhat surprised that
> there is no simple industry solution for this yet, although maybe it is
> more complicated than I am making it out to be. And of course, you need a
> very hands on homeowner who very well understands the limitations of this
> kind of setup.
>
>
>
> I would certainly appreciate any feedback or comments on this, and also
> would like to hear if anyone has tried this kind of setup before.
>
>
>
> Thanks much!
>
> -Dave
>
>
>
> *Dave Tedeyan, PE*
>
> Senior Engineer | Taitem Engineering, PC
>
> 110 South Albany Street | Ithaca, NY 14850
>
> o. *607.277.1118 x121*  f. 607.277.2119
>
> www.taitem.com
> <https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.taitem.com&data=02%7C01%7Cmichael.mahon%40sma-america.com%7Ca35d09062e3b46cc5c5008d73dd042e7%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637045837003902636&sdata=XGHxkG2i08nFeZqwoYHn1cy7mbFuMcJkl%2FTKuXsowf8%3D&reserved=0>
>
>
>
> Solar • Sustainability • Energy • Design
>
> B-Corporation Best for the World 2018 Honoree
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to