Is it at all weather related?  Rain, or high humidity?  High temperatures?  Do you have any indication what time of day it trips off at?

Ray Walters
Remote Solar
303 505-8760

On 6/1/20 10:23 AM, Jason Szumlanski wrote:
Well, that didn't resolve it. The main breaker and a branch circuit breaker tripped again a few days ago. It was the same branch this time.

As my next diagnostic step I swapped two circuits (on which breaker they are landed). If history is a guide, it will work for about two weeks and then trip again.

I'm dumbfounded. I really don't want to have to tear this whole system apart. At this point, if I have to remove all the modules, I feel that I need to replace all of the trunk cable which is an expensive proposition. I really don't know what else to do at this point.

Jason


On Mon, May 25, 2020, 10:43 AM Jason Szumlanski <[email protected] <mailto:[email protected]>> wrote:

    I strongly suspect the CH240 combined breaker was compromised (we
    will see). Since it happened that two different strings tripped, I
    doubt I have two microinverters with internal faults. It has to be
    the combined breaker. I was just surprised that branch circuit
    breakers were tripping simultaneously with the combined output
    breaker.

    Of all the supply side connected systems I have installed, I have
    never seen a combined output fusible disconnect fuse blow, but I
    have seen many combined output breakers tripped. I was worried
    early on that I would be replacing fuses constantly, but that has
    not been an issue whatsoever.



        

    *

    *


    On Thu, May 21, 2020 at 11:15 AM <[email protected]
    <mailto:[email protected]>> wrote:

        Actually, we had a IQ7 string loaded up to its max panel size
        and max string length and in the spring on cool, clear day, it
        tripped the string’s associated breaker in the Enphase combiner.

        We reset but of course that breaker was impaired and it
        tripped again. We replaced and never had an issue going
        forward. We suspect the breaker was less than perfect from the
        start as we’ve add equally nice days since.

        This almost reminds me of loading up Outback FM80. It says
        4,000 watts but in reality, 3,600 is the max when amps spike.
        I will be extra careful going forward on IQ7 string length
        when going to the max published…

        My story.

        Scot

        *From:* RE-wrenches <[email protected]
        <mailto:[email protected]>> *On Behalf
        Of *Jason Szumlanski
        *Sent:* Thursday, May 21, 2020 8:57 AM
        *To:* RE-wrenches <[email protected]
        <mailto:[email protected]>>
        *Subject:* [RE-wrenches] Enphase intermittent breaker trippjng

        I'm trying to resolve an intermittent frustrating problem with
        and Enphase IQ system. There are three AC Branch circuits of 9
        microinverters each coming into an Enphase AC combiner.

        What has been happening is one of the BR220 branch circuit
        breakers and the combine CH240 breaker in the main backfed
        load center have been tripping simultaneously. It has happened
        about four times in the last 6 months. It was always the same
        branch circuit breaker, so we kept investigating that string,
        checking the junction box, trunk cable, and cap, etc. Finally
        we swapped out the BR220 breaker.

        Fast forward 4 weeks, and we got another call. This time a
        different branch circuit breaker and the main breaker tripped
        simultaneously. We checked that branch circuit and could not
        find any fault. It seems unlikely that two branch circuit
        breakers would be faulty, so we have now switched out the
        CH240 main breaker in hopes that it is the culprit.

        I'm not totally confident in this resolution and I have my
        fingers crossed. If that doesn't work, does anyone have any
        suggestions on another diagnostic step? These intermittent
        problems are a major hassle. One thought I had was to switch
        to a supply side interconnection with a fusible disconnect.
        Maybe the intermittent fault would blow one of the two line
        fuses so at least I could narrow it down to which line the
        fault is on if there is in fact a fault.

        I have experienced two other tripping breaker issues with
        Enphase systems in the past. Neither of them were systems I
        installed. One turned out to be branch circuits that were not
        properly paired up and landed on different breakers. Another
        time we had an inverter with an internal fault which
        eventually"blew up" with a loud popping noise and smoke
        billowing out of it. That happened after resetting a trip
        breaker multiple times. This case seems to be unrelated to
        those issues. I'm perplexed.

        Jason Szumlanski

        Florida Solar Design Group

        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
        
<https://mailtrack.io/trace/link/796b1796eb4c075a74298513a530f62e4a496cb2?notrack=1&url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c7dea131fd9cb45a>

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html
        
<https://mailtrack.io/trace/link/c06e48af2da3d129a58c08ef2043bd2d8fcbef6f?notrack=1&url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=06899a19621f54d8>

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        
<https://mailtrack.io/trace/link/215cb4d0fcfb04e4124aae9b2616249f1eef5542?notrack=1&url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=8bc84049c81c183c>

        Check out or update participant bios:
        www.members.re-wrenches.org
        
<https://mailtrack.io/trace/link/27c3e706e7f2b4836b1669b31c9454db7fee1b52?notrack=1&url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=4a75a2d55681f39a>


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to