The breaker in the main panel IS tripping simultaneously with one of the
branch circuit breakers each time.






On Wed, Jun 3, 2020 at 12:43 PM Jay <[email protected]> wrote:

> A question that keeps nagging me is why do these breakers trip and not the
> breaker in the main panel?
> Presuming there is a 40 amp in the main
>
> I would have thought that given all the times the breakers have tripped at
> some point that one would have tripped and I can’t understand why not?
>
> Jay
>
> On Jun 3, 2020, at 8:27 AM, Jerry Shafer <[email protected]> wrote:
>
> 
> Wrenches
> Looking g at the bigger breaker tripping at the same time is very likely
> do to response time of the breaker nothing more. As l suggested in a
> previous message. Use a non bridged breaker to see if it is one or both
> legs that trip. Also an eguage will help to see what if anything leads up
> to the failure and when.
> Jerry
> Jerry
>
> On Wed, Jun 3, 2020, 7:58 AM Jason Szumlanski <
> [email protected]> wrote:
>
>> I wonder about that. Of course, it could be the "inverter output circuit"
>> having a fault in the wiring still (an intermittent issue somewhere within
>> the IQ cable or home run wiring). But internal to the microinverter, is it
>> possible that a fault could still occur at night? I had a suggestion from
>> another wrench that there are film capacitors on the AC output side, but
>> are these isolated when there is no DC input? It seems unlikely that this
>> would be an issue, but I have seen microinverters reporting a couple of
>> watts at night (in Enlighten). I'm not sure how real that is.
>>
>> The overriding question I have is what kind of fault would cause BOTH a
>> branch circuit and the main solar breaker to trip simultaneously? That
>> seems odd to me. If any normal load branch circuit has a fault, you don't
>> often see premises main breakers tripping, or even feeder circuit breakers.
>>
>> I got to thinking that maybe there is some kind of issue between the
>> BR220 and CH240 breakers not playing nicely together. But I would think
>> this would be a well-known issue because I'm sure there are tons of CH
>> feeder breakers in the wild with BR branch circuits downstream.
>>
>>
>>
>> On Tue, Jun 2, 2020 at 9:25 AM <[email protected]>
>> wrote:
>>
>>> If it trips at night, we know it is not the output from the inverters
>>> causing the tripping. The current must be coming from the grid.
>>> ---
>>>
>>>
>>>
>>> On 2020-06-01 12:05, Jason Szumlanski wrote:
>>>
>>>
>>> It's not weather. It's at all times of the day and night, and I
>>> confirmed that there is no correlation to rain or high winds. That was my
>>> first suspicion.
>>>
>>>
>>> On Mon, Jun 1, 2020 at 10:27 AM Ray <[email protected]> wrote:
>>>
>>> Is it at all weather related?  Rain, or high humidity?  High
>>> temperatures?  Do you have any indication what time of day it trips off at?
>>>
>>> Ray Walters
>>> Remote Solar
>>> 303 505-8760
>>>
>>> On 6/1/20 10:23 AM, Jason Szumlanski wrote:
>>>
>>> Well, that didn't resolve it. The main breaker and a branch circuit
>>> breaker tripped again a few days ago. It was the same branch this time.
>>>
>>> As my next diagnostic step I swapped two circuits (on which breaker they
>>> are landed). If history is a guide, it will work for about two weeks and
>>> then trip again.
>>>
>>> I'm dumbfounded. I really don't want to have to tear this whole system
>>> apart. At this point, if I have to remove all the modules, I feel that I
>>> need to replace all of the trunk cable which is an expensive proposition. I
>>> really don't know what else to do at this point.
>>>
>>> Jason
>>>
>>>
>>> On Mon, May 25, 2020, 10:43 AM Jason Szumlanski <
>>> [email protected]> wrote:
>>>
>>> I strongly suspect the CH240 combined breaker was compromised (we will
>>> see). Since it happened that two different strings tripped, I doubt I have
>>> two microinverters with internal faults. It has to be the combined breaker.
>>> I was just surprised that branch circuit breakers were tripping
>>> simultaneously with the combined output breaker.
>>>
>>> Of all the supply side connected systems I have installed, I have never
>>> seen a combined output fusible disconnect fuse blow, but I have seen many
>>> combined output breakers tripped. I was worried early on that I would be
>>> replacing fuses constantly, but that has not been an issue whatsoever.
>>>
>>>
>>>
>>>
>>>
>>> On Thu, May 21, 2020 at 11:15 AM <[email protected]> wrote:
>>>
>>> Actually, we had a IQ7 string loaded up to its max panel size and max
>>> string length and in the spring on cool, clear day, it tripped the string's
>>> associated breaker in the Enphase combiner.
>>>
>>>
>>>
>>> We reset but of course that breaker was impaired and it tripped again.
>>> We replaced and never had an issue going forward. We suspect the breaker
>>> was less than perfect from the start as we've add equally nice days since.
>>>
>>>
>>>
>>> This almost reminds me of loading up Outback FM80. It says 4,000 watts
>>> but in reality, 3,600 is the max when amps spike. I will be extra careful
>>> going forward on IQ7 string length when going to the max published...
>>>
>>>
>>>
>>> My story.
>>>
>>>
>>>
>>> Scot
>>>
>>>
>>>
>>> *From:* RE-wrenches <[email protected]> *On
>>> Behalf Of *Jason Szumlanski
>>> *Sent:* Thursday, May 21, 2020 8:57 AM
>>> *To:* RE-wrenches <[email protected]>
>>> *Subject:* [RE-wrenches] Enphase intermittent breaker trippjng
>>>
>>>
>>>
>>> I'm trying to resolve an intermittent frustrating problem with and
>>> Enphase IQ system. There are three AC Branch circuits of 9 microinverters
>>> each coming into an Enphase AC combiner.
>>>
>>>
>>>
>>> What has been happening is one of the BR220 branch circuit breakers and
>>> the combine CH240 breaker in the main backfed load center have been
>>> tripping simultaneously. It has happened about four times in the last 6
>>> months. It was always the same branch circuit breaker, so we kept
>>> investigating that string, checking the junction box, trunk cable, and cap,
>>> etc. Finally we swapped out the BR220 breaker.
>>>
>>>
>>>
>>> Fast forward 4 weeks, and we got another call. This time a different
>>> branch circuit breaker and the main breaker tripped simultaneously. We
>>> checked that branch circuit and could not find any fault. It seems unlikely
>>> that two branch circuit breakers would be faulty, so we have now switched
>>> out the CH240 main breaker in hopes that it is the culprit.
>>>
>>>
>>>
>>> I'm not totally confident in this resolution and I have my fingers
>>> crossed. If that doesn't work, does anyone have any suggestions on another
>>> diagnostic step? These intermittent problems are a major hassle. One
>>> thought I had was to switch to a supply side interconnection with a fusible
>>> disconnect. Maybe the intermittent fault would blow one of the two line
>>> fuses so at least I could narrow it down to which line the fault is on if
>>> there is in fact a fault.
>>>
>>>
>>>
>>> I have experienced two other tripping breaker issues with Enphase
>>> systems in the past. Neither of them were systems I installed. One turned
>>> out to be branch circuits that were not properly paired up and landed on
>>> different breakers. Another time we had an inverter with an internal fault
>>> which eventually"blew up" with a loud popping noise and smoke billowing out
>>> of it. That happened after resetting a trip breaker multiple times. This
>>> case seems to be unrelated to those issues. I'm perplexed.
>>>
>>>
>>>
>>> Jason Szumlanski
>>>
>>> Florida Solar Design Group
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/59a7e9d723e158998873ca5baa7a638767134d27?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=007df91bacd1323a>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> <https://mailtrack.io/trace/link/003d3bab0f8d81b9e77f0e336fe0653fa6b72db7?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=60a2f4ad62308706>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/3284432edf0e54def1f98550159b81006d7955c5?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=c088400cda1aedeb>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/2fc898c4231f5b5aee26e16d3b288a64fe7c17f3?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=05bd9402b755e279>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & 
>>> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>  
>>> <https://mailtrack.io/trace/link/d46f3f44f64e6372efd2794d4d6c17baf68fbb43?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=b65fd411eb242ea7>
>>>
>>> List-Archive: 
>>> http://www.mail-archive.com/[email protected]/maillist.html 
>>> <https://mailtrack.io/trace/link/2c5aa8cf7a2077366b70724f854e09c89da47ac7?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=3a7266131380e65f>
>>>
>>> List rules & etiquette:www.re-wrenches.org/etiquette.htm 
>>> <https://mailtrack.io/trace/link/a3a4bb1c1a5d466c25dce75c84f438618ef73f8d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=95894279ccfabb34>
>>>
>>> Check out or update participant bios:www.members.re-wrenches.org 
>>> <https://mailtrack.io/trace/link/413c44feecb8180ef2abedf5ae94b6fd6d9a1110?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=b139dcc7b94a10d8>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/62fd4148b0bc6a855a3e5d33e745dd67dea74199?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=991be995cf70aaf6>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> <https://mailtrack.io/trace/link/e35567d9a108f5e52af80b7bfdb9165c3c8bdbdc?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=eeb6342a28178352>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/92fa6a8bde050b49d8ec1a64205892e188742a03?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=4208b53e4a315da0>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/b626a119f96ab5c7696c3f4cfc73d0c1c8b0dafa?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=2c74837929d3e812>
>>>
>>> <blocked.gif>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/b908d8767f4935c3886ebe9001d538f330d12b20?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=8e39eec1c56421db>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> <https://mailtrack.io/trace/link/16965d2373a318af82cf069bea32162ad75cbe47?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=870b4655b78e79f8>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/a31c352c8b2966ebd43abc34865e2c4c5ce70aae?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=d26a4a64d4957cbd>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/767a09d3a743da10080dc5f780aa2794a92720f1?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=dc6a874b300dc656>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/51db132bfd3691cc73ae37e2ef941c888ef13948?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=afafa8adda749a93>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> <https://mailtrack.io/trace/link/bfce5e940bbedaab1e75048018b6994a5b9197e2?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=1d0aa1a85a003066>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/5f14ca54215f680e9a22c36b7bfefbef8063a364?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=53df7ac8789e98df>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/bbb56d9c03c7083bf87619b1b08c8559fb0b21e3?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=86fc9c809809d01d>
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/51db132bfd3691cc73ae37e2ef941c888ef13948?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=afafa8adda749a93>
>>
>> List-Archive:
>> http://www.mail-archive.com/[email protected]/maillist.html
>> <https://mailtrack.io/trace/link/bfce5e940bbedaab1e75048018b6994a5b9197e2?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=1d0aa1a85a003066>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/5f14ca54215f680e9a22c36b7bfefbef8063a364?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=53df7ac8789e98df>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/bbb56d9c03c7083bf87619b1b08c8559fb0b21e3?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=86fc9c809809d01d>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/8bb541ba99717ada1867f5a429b07edcab4c3104?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=532c834dc90f032d>
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
> <https://mailtrack.io/trace/link/d54b14d5cd46011596ef52ce4f5f0f8b0b7216c4?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=228d92cf759e33e9>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/f45c754a1f3ecd228a8d48e2d814af57ad021e32?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=5c28fda394300e50>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/27bf5f4ddebcf4a11740381410f90a036b292358?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=bc003d6f9c33ffa1>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/8bb541ba99717ada1867f5a429b07edcab4c3104?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=532c834dc90f032d>
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
> <https://mailtrack.io/trace/link/d54b14d5cd46011596ef52ce4f5f0f8b0b7216c4?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=228d92cf759e33e9>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/f45c754a1f3ecd228a8d48e2d814af57ad021e32?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=5c28fda394300e50>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/27bf5f4ddebcf4a11740381410f90a036b292358?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=bc003d6f9c33ffa1>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to