Wrenches
Looking g at the bigger breaker tripping at the same time is very likely do
to response time of the breaker nothing more. As l suggested in a previous
message. Use a non bridged breaker to see if it is one or both legs that
trip. Also an eguage will help to see what if anything leads up to the
failure and when.
Jerry
Jerry

On Wed, Jun 3, 2020, 7:58 AM Jason Szumlanski <
[email protected]> wrote:

> I wonder about that. Of course, it could be the "inverter output circuit"
> having a fault in the wiring still (an intermittent issue somewhere within
> the IQ cable or home run wiring). But internal to the microinverter, is it
> possible that a fault could still occur at night? I had a suggestion from
> another wrench that there are film capacitors on the AC output side, but
> are these isolated when there is no DC input? It seems unlikely that this
> would be an issue, but I have seen microinverters reporting a couple of
> watts at night (in Enlighten). I'm not sure how real that is.
>
> The overriding question I have is what kind of fault would cause BOTH a
> branch circuit and the main solar breaker to trip simultaneously? That
> seems odd to me. If any normal load branch circuit has a fault, you don't
> often see premises main breakers tripping, or even feeder circuit breakers.
>
> I got to thinking that maybe there is some kind of issue between the BR220
> and CH240 breakers not playing nicely together. But I would think this
> would be a well-known issue because I'm sure there are tons of CH feeder
> breakers in the wild with BR branch circuits downstream.
>
>
>
> On Tue, Jun 2, 2020 at 9:25 AM <[email protected]>
> wrote:
>
>> If it trips at night, we know it is not the output from the inverters
>> causing the tripping. The current must be coming from the grid.
>> ---
>>
>>
>>
>> On 2020-06-01 12:05, Jason Szumlanski wrote:
>>
>>
>> It's not weather. It's at all times of the day and night, and I confirmed
>> that there is no correlation to rain or high winds. That was my first
>> suspicion.
>>
>>
>> On Mon, Jun 1, 2020 at 10:27 AM Ray <[email protected]> wrote:
>>
>> Is it at all weather related?  Rain, or high humidity?  High
>> temperatures?  Do you have any indication what time of day it trips off at?
>>
>> Ray Walters
>> Remote Solar
>> 303 505-8760
>>
>> On 6/1/20 10:23 AM, Jason Szumlanski wrote:
>>
>> Well, that didn't resolve it. The main breaker and a branch circuit
>> breaker tripped again a few days ago. It was the same branch this time.
>>
>> As my next diagnostic step I swapped two circuits (on which breaker they
>> are landed). If history is a guide, it will work for about two weeks and
>> then trip again.
>>
>> I'm dumbfounded. I really don't want to have to tear this whole system
>> apart. At this point, if I have to remove all the modules, I feel that I
>> need to replace all of the trunk cable which is an expensive proposition. I
>> really don't know what else to do at this point.
>>
>> Jason
>>
>>
>> On Mon, May 25, 2020, 10:43 AM Jason Szumlanski <
>> [email protected]> wrote:
>>
>> I strongly suspect the CH240 combined breaker was compromised (we will
>> see). Since it happened that two different strings tripped, I doubt I have
>> two microinverters with internal faults. It has to be the combined breaker.
>> I was just surprised that branch circuit breakers were tripping
>> simultaneously with the combined output breaker.
>>
>> Of all the supply side connected systems I have installed, I have never
>> seen a combined output fusible disconnect fuse blow, but I have seen many
>> combined output breakers tripped. I was worried early on that I would be
>> replacing fuses constantly, but that has not been an issue whatsoever.
>>
>>
>>
>>
>>
>> On Thu, May 21, 2020 at 11:15 AM <[email protected]> wrote:
>>
>> Actually, we had a IQ7 string loaded up to its max panel size and max
>> string length and in the spring on cool, clear day, it tripped the string's
>> associated breaker in the Enphase combiner.
>>
>>
>>
>> We reset but of course that breaker was impaired and it tripped again. We
>> replaced and never had an issue going forward. We suspect the breaker was
>> less than perfect from the start as we've add equally nice days since.
>>
>>
>>
>> This almost reminds me of loading up Outback FM80. It says 4,000 watts
>> but in reality, 3,600 is the max when amps spike. I will be extra careful
>> going forward on IQ7 string length when going to the max published...
>>
>>
>>
>> My story.
>>
>>
>>
>> Scot
>>
>>
>>
>> *From:* RE-wrenches <[email protected]> *On
>> Behalf Of *Jason Szumlanski
>> *Sent:* Thursday, May 21, 2020 8:57 AM
>> *To:* RE-wrenches <[email protected]>
>> *Subject:* [RE-wrenches] Enphase intermittent breaker trippjng
>>
>>
>>
>> I'm trying to resolve an intermittent frustrating problem with and
>> Enphase IQ system. There are three AC Branch circuits of 9 microinverters
>> each coming into an Enphase AC combiner.
>>
>>
>>
>> What has been happening is one of the BR220 branch circuit breakers and
>> the combine CH240 breaker in the main backfed load center have been
>> tripping simultaneously. It has happened about four times in the last 6
>> months. It was always the same branch circuit breaker, so we kept
>> investigating that string, checking the junction box, trunk cable, and cap,
>> etc. Finally we swapped out the BR220 breaker.
>>
>>
>>
>> Fast forward 4 weeks, and we got another call. This time a different
>> branch circuit breaker and the main breaker tripped simultaneously. We
>> checked that branch circuit and could not find any fault. It seems unlikely
>> that two branch circuit breakers would be faulty, so we have now switched
>> out the CH240 main breaker in hopes that it is the culprit.
>>
>>
>>
>> I'm not totally confident in this resolution and I have my fingers
>> crossed. If that doesn't work, does anyone have any suggestions on another
>> diagnostic step? These intermittent problems are a major hassle. One
>> thought I had was to switch to a supply side interconnection with a fusible
>> disconnect. Maybe the intermittent fault would blow one of the two line
>> fuses so at least I could narrow it down to which line the fault is on if
>> there is in fact a fault.
>>
>>
>>
>> I have experienced two other tripping breaker issues with Enphase systems
>> in the past. Neither of them were systems I installed. One turned out to be
>> branch circuits that were not properly paired up and landed on different
>> breakers. Another time we had an inverter with an internal fault which
>> eventually"blew up" with a loud popping noise and smoke billowing out of
>> it. That happened after resetting a trip breaker multiple times. This case
>> seems to be unrelated to those issues. I'm perplexed.
>>
>>
>>
>> Jason Szumlanski
>>
>> Florida Solar Design Group
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/dc1408aca00c41244fe77ed625ca77cc2aed6b69?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=e15aae24dc0cc81e>
>>
>> List-Archive:
>> http://www.mail-archive.com/[email protected]/maillist.html
>> <https://mailtrack.io/trace/link/11f7f73569aff2a927352131f02dc3716710c091?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=aa74c137b4873d28>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/257fb893e7a3e6257343d1a4fd4e401137120b0a?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=0f34567a810ba70e>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/62a2e7d730bf511d0499a58a2924e07cf6146d2f?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=40833a6aa6048128>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & 
>> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>  
>> <https://mailtrack.io/trace/link/1c6c69baf46e62f014059da592cebe35236423ad?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=752a376a3ff2d7eb>
>>
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html 
>> <https://mailtrack.io/trace/link/be3608df481d1760ec9a3415fed3b6f41ebb7fda?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=5e99800ddc53b9e7>
>>
>> List rules & etiquette:www.re-wrenches.org/etiquette.htm 
>> <https://mailtrack.io/trace/link/a07b043e4f6c7e96a0f69d66333dfcb390c0d308?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=a8f5d09af8d25e60>
>>
>> Check out or update participant bios:www.members.re-wrenches.org 
>> <https://mailtrack.io/trace/link/736304ac2bc871839538763b02052b5d6134cad8?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=acfa7695256209f1>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/47b726f2e9c105204b2b73ffc17a37ba6f8652cf?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=51f3453a4ec92523>
>>
>> List-Archive:
>> http://www.mail-archive.com/[email protected]/maillist.html
>> <https://mailtrack.io/trace/link/2a11b06b9c049f4468d4c7b1bc5929f51476795e?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=dec1127f1b3e5f5d>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/152589ca78104b276b3176ba0bae5a8e5be72b9a?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=4b131793846a0766>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/e70ce3a7260866c916b829dd4dd86499f2cc9ada?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=ffdf688eaa6fcf1f>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/4e5a3e83a155fddc0272fa337153476a518337a4?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=6e32d9d9fcff8d53>
>>
>> List-Archive:
>> http://www.mail-archive.com/[email protected]/maillist.html
>> <https://mailtrack.io/trace/link/866446bf135c952c5c93b2c75822149179ea4f16?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f0a8679e6f3cc021>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/eed535be471dfbdf1d2846f870df31ca60fd5f38?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=4da10b82e50c7dab>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/df65609821695e59d9b79e8e94ba484ba571a6f9?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=99bb3850626d507b>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/5950b777916f4996f34591c5cc14b5406617cb45?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=12ad81516723c311>
>>
>> List-Archive:
>> http://www.mail-archive.com/[email protected]/maillist.html
>> <https://mailtrack.io/trace/link/7afcfafa7c02e8563bb37bd82ded1f627795e8f6?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=a30c085d2e484f09>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/6bc6a18353fae4659799abc13dc7f260e0eac92c?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=39aad799777cafec>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/7628a6e0dc090d4d673a2d827538784fff07f682?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=a4ca2d39942b2112>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to