I agree why wouldn’t you install the generator at the Gen input?

Ok if you’ve got a ac couple then that eats up the Gen input. 

But yeah brings up a lot of questions as to integration. 

Here is another. Does the sol ark know to reduce the charge rate if the 
generator is not as big as the grid which I would expect? 

Makes the case for multiple sets of CT’s to measure and allow for control. 

I’ll be curious what others think/know 
Jay


> On Oct 19, 2026, at 4:10 PM, [email protected] wrote:
> 
> 
> So I've always been of mindset that solar integrated downstream 
> (customer-side) of a whole-house generator was a backfeeding debacle to avoid 
> as a solar inverter had no means to backfeed into a generator as there is no 
> grid to export excess solar production too.
> 
> So while researching a possible method I come across the SolArk schematic for 
> integration to whole house generator integration and even though my eyes have 
> gone across it dozens of times, this was first time I really LOOKED at it. 
> Was shocked to see the whole house generator upstream of the inverter.
> 
> Seems to me that one only wants an inverter with a whole-house generator if 
> you want the solar and the battery's energy management features. The always 
> excellent SolArk tech said in this config the inverter knows the gen is on 
> via the 2-wire start wires; this was eye opening to me as I had a paradigm 
> this was only a relay to trigger the gen on and I never considered the 
> two-way communication part. The CT's at the transfer switch would measure gen 
> output and I suppose the inverter will "know" that output via the associate 
> CT wires.
> 
> So my questions are:
> 
> Why would we ever want the inverter to produce during a grid outage when the 
> gen is running?
> If the gen power was "clean enough" that the inverter kept on making power, 
> is the SolArk truly "know" via the 2-wire start that the gen is on and to not 
> make (any?) power?
> Would the SolArk try to make power to offset the power of the Gen and reduce 
> that to zero or does that functionality go away because the SolArk knows the 
> gen is on?
> 
> And the final question: If the SolArk is in this configuration only to 
> provide energy management (since the whole-house gen is providing whole house 
> backup) can I put this schematic in place on a house where there is a 400A 
> service and two 200A panels but since I'm wanting to retain the whole house 
> gen backup but also want the ESS energy management, one SolArk 18 provides 
> that in this config on just one of the panels: I have the whole house backup 
> but using battery power from one inverter to meet energy management needs.
> 
> Been doing this for almost 14 years and for some reason, this schematic 
> nearly fried my brain to mush...
> 
> Any thoughts or inside or knowledge you can share?
> 
> PPS - one more question - this helps me AC couple a Fronius 12.5 onto the GEN 
> inputs, too and 'solves' the quandary I was having.
> 
> <image.png>
> 
> Howard "Scot" Arey
> Owner, Solar CenTex
> 
> NABCEP PV Installation Professional
> TECL 29755
> 254-300-1228 
> <image.png>
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to