You can use all 4 Smart Load inputs on the Gridboss simultaneously for AC
Coupled PV and there is a separate dedicated Generator input.

Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208




On Tue, Oct 20, 2026 at 12:16 AM Zeke Yewdall <[email protected]>
wrote:

> I don't know of any AIO's that allow AC coupling on the backed up loads
> panel rather than the dedicated AC coupled input.  It's an issue of
> monitoring and controls, not physics.  The physics would work the same
> either way, but the inverter wants to know what is going on, and control
> that AC coupled input so it can turn it off if needed.  Same with the ones
> using an external gateway like the Gridboss, or the Powerwall type ones
> that use a gateway for the AC coupled PV input, at least the ones I've
> designed for (Franklin and Sigenergy).  Those won't allow the AC coupled PV
> on the backed up loads panel either.
>
> I think Victron still allows AC coupled PV on the loads output and can
> handle that fine, perhaps with a bunch of external CT's and a cerbo to tell
> it what's going on instead of trying to handle it all internally.
>
> Technically I think code required a secondary method of dropping the AC
> coupled array on older systems, but we usually just hoped that the
> frequency shifting would work the way it was supposed to (sometimes it did,
> sometimes it was way to slow and the lithium BMS would cut out before the
> inverter shifted and knocked the AC coupled array off, and at least once I
> saw an AGM battery bank very pressurized and unhappy when the AC coupled
> array did not cut out).  In theory, the frequency shifting on an AIO would
> also drop the AC coupled array, even if it was not on the AC coupled input
> where the relay can drop it.  But even if so, the monitoring is still going
> to be messed up for what the inverter shows as solar production.
>
> The Sol-max AIO has separate AC coupled PV and Generator inputs, so you
> can have both wired in at the same time, and still have a smartload output
> available too.  The Franklin gateway and I believe the Signeergy gateway
> also have separate inputs for AC coupled PV and Generator and smartload
> outputs so you can do all three at once.  Not sure about the Gridboss
> gateway.  But a lot of the AIO's by themselves you have to pick just one.
>
> Zeke
>
> ----------------------
>
> Can you AC couple the old fashion way, by back-feeding a breaker in the
> protected loads panel, to save the generator input?
>
> Drake
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
>
> https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to