No you cannot AC couple  an AIO like a transformer based unit. 

At least none that I know of. 

Jay

> On Oct 19, 2026, at 7:43 PM, [email protected] wrote:
> 
> 
> Can you AC couple the old fashion way, by back-feeding a breaker in the 
> protected loads panel, to save the generator input?
>  
> Drake
>  
>  
>  
>> On 2026-10-19 19:31, Jay wrote:
>> I agree why wouldn’t you install the generator at the Gen input?
>> 
>> Ok if you’ve got a ac couple then that eats up the Gen input.
>> 
>> But yeah brings up a lot of questions as to integration.
>> 
>> Here is another. Does the sol ark know to reduce the charge rate if
>> the generator is not as big as the grid which I would expect?
>> 
>> Makes the case for multiple sets of CT’s to measure and allow for
>> control.
>> 
>> I’ll be curious what others think/know
>> Jay
>> 