No you cannot AC couple an AIO like a transformer based unit. At least none that I know of.
Jay > On Oct 19, 2026, at 7:43 PM, [email protected] wrote: > > > Can you AC couple the old fashion way, by back-feeding a breaker in the > protected loads panel, to save the generator input? > > Drake > > > >> On 2026-10-19 19:31, Jay wrote: >> I agree why wouldn’t you install the generator at the Gen input? >> >> Ok if you’ve got a ac couple then that eats up the Gen input. >> >> But yeah brings up a lot of questions as to integration. >> >> Here is another. Does the sol ark know to reduce the charge rate if >> the generator is not as big as the grid which I would expect? >> >> Makes the case for multiple sets of CT’s to measure and allow for >> control. >> >> I’ll be curious what others think/know >> Jay >> _______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/ There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/ List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org