Sol-Ark calls for larger generators to be installed at the grid lugs. I always 
assumed that was a sizing/ampacity issue and it likely still is but I wonder 
now if there was some desire to use in this "whole house generator" 
configuration, too?

Lots of questions. Sol-Ark: you on here?

Howard "Scot" Arey
Owner, Solar CenTex
254-300-1228

________________________________
From: RE-Wrenches <[email protected]> on behalf of Jay 
<[email protected]>
Sent: Monday, October 19, 2026 6:31 PM
To: [email protected] <[email protected]>
Subject: Re: [Re-wrenches] Sol-Ark for 400-amp service; help me understand this 
whole-house generation diagram

I agree why wouldn’t you install the generator at the Gen input?

Ok if you’ve got a ac couple then that eats up the Gen input.

But yeah brings up a lot of questions as to integration.

Here is another. Does the sol ark know to reduce the charge rate if the 
generator is not as big as the grid which I would expect?

Makes the case for multiple sets of CT’s to measure and allow for control.

I’ll be curious what others think/know
Jay


On Oct 19, 2026, at 4:10 PM, [email protected] wrote:


So I've always been of mindset that solar integrated downstream (customer-side) 
of a whole-house generator was a backfeeding debacle to avoid as a solar 
inverter had no means to backfeed into a generator as there is no grid to 
export excess solar production too.

So while researching a possible method I come across the SolArk schematic for 
integration to whole house generator integration and even though my eyes have 
gone across it dozens of times, this was first time I really LOOKED at it. Was 
shocked to see the whole house generator upstream of the inverter.

Seems to me that one only wants an inverter with a whole-house generator if you 
want the solar and the battery's energy management features. The always 
excellent SolArk tech said in this config the inverter knows the gen is on via 
the 2-wire start wires; this was eye opening to me as I had a paradigm this was 
only a relay to trigger the gen on and I never considered the two-way 
communication part. The CT's at the transfer switch would measure gen output 
and I suppose the inverter will "know" that output via the associate CT wires.

So my questions are:


  *
Why would we ever want the inverter to produce during a grid outage when the 
gen is running?
  *
If the gen power was "clean enough" that the inverter kept on making power, is 
the SolArk truly "know" via the 2-wire start that the gen is on and to not make 
(any?) power?
  *
Would the SolArk try to make power to offset the power of the Gen and reduce 
that to zero or does that functionality go away because the SolArk knows the 
gen is on?

And the final question: If the SolArk is in this configuration only to provide 
energy management (since the whole-house gen is providing whole house backup) 
can I put this schematic in place on a house where there is a 400A service and 
two 200A panels but since I'm wanting to retain the whole house gen backup but 
also want the ESS energy management, one SolArk 18 provides that in this config 
on just one of the panels: I have the whole house backup but using battery 
power from one inverter to meet energy management needs.

Been doing this for almost 14 years and for some reason, this schematic nearly 
fried my brain to mush...

Any thoughts or inside or knowledge you can share?

PPS - one more question - this helps me AC couple a Fronius 12.5 onto the GEN 
inputs, too and 'solves' the quandary I was having.

<image.png>

Howard "Scot" Arey
Owner, Solar CenTex

NABCEP PV Installation Professional
TECL 29755
254-300-1228
<image.png>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to