It depends on which all in one inverter you are thinking of.  Many of the
cheaper ones have quite a bit of difficulty with imbalanced loads.
Especially with surge loads on only one leg. Sometimes an inverter that can
handle 9,000 watts continuous with 15,000 watt surge on 240 volts, may
fault out with a 3,000 watt surge on 120 volts.  This was a common issue
with many of the earlier units, even from the better brands.    The current
units from the better brands can usually handle imbalanced surge  and
imbalanced loads far better... but with this caveat:

You only get half the rated capacity on one leg.  Like an old FX setup
without the X240, or a Radian setup -- not like a XW setup that could give
you 3/4 of full rated power on a single leg, or a X240 FX setup that could
give full rated power on a single leg.  So if you buy a 12,000 watt rated
all in one inverter... you only get 6,000 watts on the one leg you are
using, so you are essentially paying for twice the inverter (and incurring
the tare load of twice the inverter) for what you actually get.  If you can
get one of the few all in ones that is designed for only 120 volt output,
or that can be configured for only 120 volt output, it can solve these
issues.

Another issue with an all in one, is high tare load.  If you are upgrading
to an all in one, you will also need to expand the PV array, and possibly
the batteries, to account for this.  Tare on the SW4024 was around 25
watts, and it had a lower power search mode that may or may not work modern
appliances (in my experience, 80% of modern appliances are no longer
compatible with search mode).  Most all in ones are at least 60 watts tare
for the smaller ones, and 90 to 100 watts for the larger ones.  You'll need
to account for that in the load calcs, which on a older system can be
significant.  If you're doing a 8+kW array and much heavier loads that is
typical of a lot of new off grid setups, then the % of the total load spent
for inverter tare loss is actually no more than it was in most old
systems... but directly retrofitting an all in one to a old system with a
2kW array can lead to big problems in the winter in my experience.

Most all in ones will also need the array to be reconfigured to work with
the all in one MPPT inputs.  While most of them can operate under 100 volts
MPPT, to directly connect an older array configured for a 150 volt charge
controller, it does not work well in reality.  The efficiency of their
MPPT's is a bit less if the array is under 130 to 150 volts, plus the
amperage limit of most AIO MPPT's is only 20 to 35 amps depending on the
model... which means an older array may be too high of amperage for a
single MPPT channel as well.  Usually this can reconfigured in the array
combiner box, connecting strings in series instead of parallel, without
having to actually go out into the array wiring.  Also good to remember
that the all in ones get very unhappy (often blowing out the FET board in
the inverter) if the array negatives are grounded, or if multiple arrays
share a negative.  This was common on older arrays, because on the older
150 volt charge controllers, all negatives were common, and grounded in
some fashion.  So check for that when re-using older arrays.

If they just want an inverter update, without also doing battery and array
upsizing, then the Victron Multiplus II inverters are a great option.  Very
low tare loss (even less than the old SW for some comparable models),
better waveform, and they are all 120 volts -- which is annoying when doing
a 120/240 volt system where you need two inverters minimum, but great when
retrofitting a 120 volt system.  Victron also makes nice MPPT charge
controllers (none of which meet code unfortunately... no arc fault
protection for the array), and monitoring equipment, and it's all
compatible with lithium batteries (in open loop at the very least, and
often even in closed loop).




-- 
Zeke Yewdall
PV Engineer
NABCEP #031508-89
[email protected]
303-523-3592
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to