: Sprinklerforum On
Behalf Of Cesar Lira
Sent: Thursday, August 9, 2018 1:53 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Building Heights Requiring Standpipes
Hi.
I have a doubt. NFPA13 request that all sprinklers system shall have a
Retarding device. But in our sprinkler systems
]
On Behalf Of Cesar Lira
Sent: Thursday, August 09, 2018 11:53 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Building Heights Requiring Standpipes
Hi.
I have a doubt. NFPA13 request that all sprinklers system shall have a
Retarding device. But in our sprinkler systems installed we
Hi.
I have a doubt. NFPA13 request that all sprinklers system shall have a
Retarding device. But in our sprinkler systems installed we are not using
it. Because we have a water flow sensor above check alarm instead of an
alarm pressure switch or water motor alarm.
Is it correct as I have it?. Wha
-904-6823
From: Sprinklerforum [sprinklerforum-boun...@lists.firesprinkler.org] on behalf
of Taylor Schumacher [tay...@sfsprinkler.com]
Sent: Thursday, August 09, 2018 8:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Building Heights Requiring Standpipes
We had already walked
t: RE: Building Heights Requiring Standpipes
Good example diagrams are in the ICC Fire /Bldg Code Commentary books.
On Aug 8, 2018 18:01, Jim Davidson
mailto:jdavid...@davidsonassociates.net>>
wrote:
Go to the Building Code for the definition of height above lowest level of FD
Access, if ICC
forum@lists.firesprinkler.org
Subject: Building Heights Requiring Standpipes
I have an AHJ that is adamant that a 3-story 13R project I have requires Class
I standpipes because the underground parking level will exceed the 30' height
requirement. I have always viewed these heights as from the parking lot c
I think the code says if the highest floor elevation exceeds 30' above the
lowest level of fire department access, stand pipes are required. Not
quoting just remembering off the top of my head.
On Wed, Aug 8, 2018, 5:55 PM Taylor Schumacher
wrote:
> I have an AHJ that is adamant that a 3-story 1
ailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Taylor Schumacher
Sent: Wednesday, August 08, 2018 2:55 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Building Heights Requiring Standpipes
I have an AHJ that is adamant that a 3-story 13R project I have requires Class
I standpipe
owest level of FD access.
Have a fire safe day!
Jim Davidson
From: Sprinklerforum On Behalf
Of Taylor Schumacher
Sent: Wednesday, August 8, 2018 5:55 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Building Heights Requiring Standpipes
I have an AHJ that is adamant that a 3-story 13R proj
I have an AHJ that is adamant that a 3-story 13R project I have requires Class
I standpipes because the underground parking level will exceed the 30' height
requirement. I have always viewed these heights as from the parking lot closest
to main entry or where the FDC is located rather than the f