Re:GFCI equivalent in Japan

2000-03-17 Thread Tony Firth

Jim,

Almost all Japanese equipment that I have come across has been fitted with
Earth Leakage trip Circuit Breakers at the input of sensitivity 30mA.  I
suspect that this may be a Japanese Industrial requirement but have no proof of
this.  I have also seen Japanese CBs of earth leakage trip sensitivity of 3mA,
presumably for personnel as opposed to industrial equipment protection.
Operation is identical to US GFCI or Earth Leakage CBs and would expect
comparable compensation for voltage/temp tolerances. All have been fitted with
test buttons.
Also suspect that the more common usage of Earth Leakage may be the result of
the more common use of 3 phase delta connected loads, and, with no Neutral
brought into the equipment as a reference, it becomes essential to detect any
leakage to ground,(earth).
Anyone have any reference to e.g. a JIS Electrical Spec on this?

Regards,

Tony Firth, Elect.Eng.,
Quester Technology Inc.,
Fremont,CA 

Jim Eichner wrote:

  Hi everyone:  Can anyone tell me what gets used in Japan in the way
ofGFCI's?
  1. Is the trip criteria the same (line current minus neutral
   current  5mA = trip)?
  2.Are their unique Japanese GFCI's?
  3. If so, does this have anything to do with the change from
 120Vac to 100Vac (which won't affect item 1 but may affect
 other parameters, for example the Vcc that the internal
   circuitry gets fed, tolerance of line voltage as low as 80Vac,
   design of the test-button circuitry, etc.).


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: EMC, NEBS NRTL's

2000-03-17 Thread Gary McInturff

Yup, but..
I tired pointing out to one of the RBOC's that there reliance on
OSHA NRTL was horribly inadequate because most of them - maybe all of them
had nothing in the scope of accreditation that indicated the could do any of
the EMC tests. The key to any certification is what the scope of your
accreditation is. If you go out to the OSHA site and look at the NRTL scopes
you will see what I mean. Apparently, getting your name into the OSHA NRTL
site qualifies you to do anything and everything, no experience necessary.
Some of the OSHA NRTL's that I have seen probably can do a reasonable EMC
job, a couple I've seen were woefully adequate. (but doesn't matter because
they are NRTL's) As the ol' axiom goes Garbage in Garbage out The RBOC's
that ignore Nationally Recognized EMC Test labs, are doing themselves and us
a large disservice. They are not only nationally recognized by a US
govermental body but any country with a signed Mutual Recognition Agreement
(MRA), 
With EMC testing in the scope of accreditation they are internationally
recognized.
But again, use the EMC lab you want and have your NRTL include the
data and wham-o - your done. (its Friday, I'm in a good mood, and no this
isn't quite as easy as I just made it sound)
Gary


-Original Message-
From:   Grant, Tania (Tania) [mailto:tgr...@lucent.com]
Sent:   Friday, March 17, 2000 2:08 PM
To: 'Naftali Shani'; 'Collins, Jeffrey'; 'Gary
McInturff'
Cc: 'emc-p...@ieee.org'
Subject:RE: EMC, NEBS  NRTL's

Gary and Company,

You have a valid point, but incomplete historical data.
The reason OSHA
blesses NRTLs is because the whole issue started because
the National
Electrical Code used to state that the appliances
(everything is an
appliance in the NEC!) placed into buildings be safety
approved by
nationally recognized testing laboratories, such as
Underwriters
Laboratories.The NEC, as you well understand, does not
care about
radiated emission limits.   Some time later an independent
east coast safety
testing lab sued, or almost sued, OSHA/NEC that the specific
mention of the
UL name was un-American, etc.   As a result, this offending
language was
removed from the NEC, the National Recognized Testing
Laboratory achieved
new status and, it seems, other (any) safety labs could now
approve
appliances.Well now, that did not sit too well with a
lot of labs or
even OSHA.The upshot was, safety labs were made to
submit their
expertise to be blessed by OSHA as an NRTL.

Now, if that same safety lab also happens to offer EMC
testing, it seems
that this also falls into the NRTL umbrella.   I believe
that this is an
incorrect premise.   Several UL offices also perform EMC
testing.   The east
coast lab also performs safety (which is how they first got
NRTL listing)
and EMC.   Thus, to my knowledge, there are at least two
labs that are NRTL
and do both safety and EMC.However, I am not aware that
any independent,
EMC only test lab has gotten OSHA (which is only concerned
with safety) NRTL
approval.

The RBOCs, not realizing this fact, made a sweeping
statement that all
testing had to be performed by an NRTL lab.   This
immediately cut out
excellent independent EMC only testing labs.   This mess is
continuing
because the RBOCs, very often, don't do their homework, but
assume many
things.Too bad. 

To make a long story short, 
Tania Grant,  tgr...@lucent.com mailto:tgr...@lucent.com 
Lucent Technologies, Communications Applications Group


--
From:  Gary McInturff [SMTP:gmcintu...@telect.com]
Sent:  Friday, March 17, 2000 8:57 AM
To:  'Naftali Shani'; 'Collins, Jeffrey'
Cc:  'emc-p...@ieee.org'
Subject:  RE: EMC, NEBS  NRTL's


Still can be done at an independent site. The Lab I use,
ACME Testing,
here in Washington has accreditation to at least the
radiated emissions
portions of the GR-, I have to check on the susceptibility,
but I think so.
Even if that were not true. I believe that if your NRTL
accepts the EMC
data from the other lab they will include it in the overall
report. 
Now there is the dicey part. Many of the NRTL's have
their own EMC labs
and may not want to loose the cash, and try 

RE: Split or Not to Split?

2000-03-17 Thread Gary McInturff

Just curious here, Obviously, the question was asked, and my people have
responded. Is anyone actually counting or even seriously contemplating the
breakup. Just because a question was asked doesn't mean any action is going
on? 
Gary

-Original Message-
From: Mark Hassebrock [mailto:mhass...@qualcomm.com]
Sent: Friday, March 17, 2000 12:46 PM
To: emc-p...@majordomo.ieee.org
Subject: Split or Not to Split?


Greetings All,

I feel EMC and Safety are joined at the hip so I vote NO Split.  

Although some companies are fortunate to have dedicated people, I suspect
there are many more of us that are required to wear multiple hats.

In my humble opinion, the real issue is the shear volume of mailings each
day!

It's not practical to go through the dozens of postings each day.
Unfortunately when I do, I observe many where can I get this standard? or
endless threads on Y2K, etc.  Let's all commit to doing our homework before
posting.

My thanks to those who graciously answer questions and provide valuable
insights.









+++ 
Mark HassebrockPh. Work: 1-303-247-5005 
Regulatory EngineerFax:1-303-247-5116 
Qualcomm, Inc.E-mail:mhass...@qualcomm.com 
Boulder, CO 
+++ 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Split or Not to Split?

2000-03-17 Thread Mike Hopkins

Thought this was over by now;;; but since it continues, my vote is NO
split. 

Mike Hopkins
mhopk...@keytek.com

 -Original Message-
 From: Mark Hassebrock [SMTP:mhass...@qualcomm.com]
 Sent: Friday, March 17, 2000 3:46 PM
 To:   emc-p...@majordomo.ieee.org
 Subject:  Split or Not to Split?
 
 Greetings All,
 
 I feel EMC and Safety are joined at the hip so I vote NO Split.  
 
 Although some companies are fortunate to have dedicated people, I suspect
 there are many more of us that are required to wear multiple hats.
 
 In my humble opinion, the real issue is the shear volume of mailings each
 day!
 
 It's not practical to go through the dozens of postings each day.
 Unfortunately when I do, I observe many where can I get this standard?
 or endless threads on Y2K, etc.  Let's all commit to doing our homework
 before posting.
 
 My thanks to those who graciously answer questions and provide valuable
 insights.
 
 
 
 
 
 
 
 
 
 +++ 
 Mark HassebrockPh. Work: 1-303-247-5005 
 Regulatory EngineerFax:1-303-247-5116 
 Qualcomm, Inc.E-mail:mhass...@qualcomm.com 
 Boulder, CO 
 +++ 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: EMC, NEBS NRTL's

2000-03-17 Thread Grant, Tania (Tania)

Gary and Company,

You have a valid point, but incomplete historical data.The reason OSHA
blesses NRTLs is because the whole issue started because the National
Electrical Code used to state that the appliances (everything is an
appliance in the NEC!) placed into buildings be safety approved by
nationally recognized testing laboratories, such as Underwriters
Laboratories.The NEC, as you well understand, does not care about
radiated emission limits.   Some time later an independent east coast safety
testing lab sued, or almost sued, OSHA/NEC that the specific mention of the
UL name was un-American, etc.   As a result, this offending language was
removed from the NEC, the National Recognized Testing Laboratory achieved
new status and, it seems, other (any) safety labs could now approve
appliances.Well now, that did not sit too well with a lot of labs or
even OSHA.The upshot was, safety labs were made to submit their
expertise to be blessed by OSHA as an NRTL.

Now, if that same safety lab also happens to offer EMC testing, it seems
that this also falls into the NRTL umbrella.   I believe that this is an
incorrect premise.   Several UL offices also perform EMC testing.   The east
coast lab also performs safety (which is how they first got NRTL listing)
and EMC.   Thus, to my knowledge, there are at least two labs that are NRTL
and do both safety and EMC.However, I am not aware that any independent,
EMC only test lab has gotten OSHA (which is only concerned with safety) NRTL
approval.

The RBOCs, not realizing this fact, made a sweeping statement that all
testing had to be performed by an NRTL lab.   This immediately cut out
excellent independent EMC only testing labs.   This mess is continuing
because the RBOCs, very often, don't do their homework, but assume many
things.Too bad. 

To make a long story short, 
Tania Grant,  tgr...@lucent.com mailto:tgr...@lucent.com 
Lucent Technologies, Communications Applications Group


--
From:  Gary McInturff [SMTP:gmcintu...@telect.com]
Sent:  Friday, March 17, 2000 8:57 AM
To:  'Naftali Shani'; 'Collins, Jeffrey'
Cc:  'emc-p...@ieee.org'
Subject:  RE: EMC, NEBS  NRTL's


Still can be done at an independent site. The Lab I use, ACME Testing,
here in Washington has accreditation to at least the radiated emissions
portions of the GR-, I have to check on the susceptibility, but I think so.
Even if that were not true. I believe that if your NRTL accepts the EMC
data from the other lab they will include it in the overall report. 
Now there is the dicey part. Many of the NRTL's have their own EMC labs
and may not want to loose the cash, and try reject the independent lab's
report. I would find that a really hard sell however, because the NRTL labs
undoubtedly carry accreditation through NIST for the EMC portion, making any
argument about competency of the independent lab a tough sell.
At any rate I've never quite understood the justification for not
calling laboratories which are accredited through programs set up by and
through the FCC, as NRTLS'. The basic assumption I would make is that the
FCC knows a heck of a lot more about this aspect of testing and
accreditation than OSHA does. Heavy sigh!
Gary

-Original Message-
From: Naftali Shani [mailto:nsh...@nortelnetworks.com]
Sent: Friday, March 17, 2000 6:05 AM
To: 'Collins, Jeffrey'
Cc: 'emc-p...@ieee.org'
Subject: RE: EMC, NEBS  NRTL's



BM__MailDataJeffrey, the requirement that was for NRTL lab (
Bellcore representative) for each section of GR-63  GR-1089, has been
dropped. See section 3.1.2 in the BA-NEBS-R10.

However, FCC data/frequency range for radiated emissions is
insufficient: You should have data based on GR-1089 requirements 
objectives (10 kHz to 10 GHz).

Regards,
Naftali Shani, Nortel Networks, Dept. 0S45, MS 117/C1/M05 
21 Richardson Side Road, Kanata, Ontario, Canada  K2K 2C1
Voice +1.613.765.2505 (ESN 395) Fax +1.613.763.8091 (ESN 393) 
E-mail:  mailto:nsh...@nortelnetworks.com nsh...@nortelnetworks.com or
mailto:n...@ieee.org n...@ieee.org 

-Original Message- 
From:   Collins, Jeffrey [SMTP:jcoll...@ciena.com] 
Sent:   Friday, March 17, 2000 4:57 AM 
To: 'emc-p...@ieee.org' 
Subject:RE: EMC, NEBS  NRTL's 


Group, 


Can anyone confirm that the RBOC's, particularly Bell Atlantic has
agreed to 
accept EMC FCC data from non NRTL's? 
If this is true please provide any documentation to support this. (You know 
a customer is going to want to see it) 


Thanks in advance, 

Jeffrey Collins 
MTS, Principal Compliance Engineer 
Ciena Core Switching Division 
jcoll...@ciena.com 
www.ciena.com 


--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 

To cancel your subscription, send mail to: 
 majord...@ieee.org 
with the single line: 
 unsubscribe 

European Ergonomic Standard

2000-03-17 Thread rbusche

I am looking for the appropriate European Ergonomic standard that addresses
the issue of manual lifting in the workplace. The US equivalent standards
are the NIOSH Work Practices Guide for Manual Lifting , OSHA 1910, 
MIL-STD-1472 or MIL-HDBK-795. 

Its my understanding that there are standards available such as British
Standard 5827,  Health  Safety at Work Etc Act, Health  Safety at Work
Regulations, and Provision and Use of Work Equipment Regulations, but I
assume that these are UK requirements which may or may not be accepted in
the European community.

I realize that this is not necessarily a Product Safety issue but I am
hoping that someone may be familiar with this. Any suggestions would be
appreciated.

Rick Busche
rbus...@es.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Split or Not to Split?

2000-03-17 Thread Mark Hassebrock
Greetings All,

I feel EMC and Safety are joined at the hip so I vote NO Split.  

Although some companies are fortunate to have dedicated people, I suspect
there
are many more of us that are required to wear multiple hats.

In my humble opinion, the real issue is the shear volume of mailings each day!

It's not practical to go through the dozens of postings each day. 
Unfortunately when I do, I observe many where can I get this standard? or
endless threads on Y2K, etc.  Let's all commit to doing our homework before
posting.

My thanks to those who graciously answer questions and provide valuable
insights.









+++ 
Mark HassebrockPh. Work: 1-303-247-5005 
Regulatory EngineerFax:1-303-247-5116 
Qualcomm, Inc.E-mail:mhass...@qualcomm.com 
Boulder, CO 
+++

GFCI equivalent in Japan

2000-03-17 Thread Jim Eichner

Hi everyone:  Can anyone tell me what gets used in Japan in the way of
GFCI's?  There are a few aspects to this question:

1. Is the trip criteria the same (line current minus neutral current  5mA =
trip)?
2. Are their unique Japanese GFCI's?
3. If so, does this have anything to do with the change from 120Vac to
100Vac (which won't affect item 1 but may affect other parameters, for
example the Vcc that the internal circuitry gets fed, tolerance of line
voltage as low as 80Vac, design of the test-button circuitry, etc.).

Thanks for your input,

Regards,

Jim Eichner
 Group Leader - Engineering Services
 Xantrex Technology Inc.
jim.eich...@xantrex.com
Any opinions expressed are those of my invisible friend, who really exists.
Honest.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Dithered clocks and EMC - BEWARE

2000-03-17 Thread khardin

Scott,

Sorry to hear about your experience but we have had great success using Spread
Spectrum Clock Generation (SSCG) since 1994 and have shipped many millions of
units.
Most PC's built over the last 2 to 3 years also use this technology.
For back ground information, see http://www.lexmark.com/sscg/ and
http://developer.intel.com/ial/scalableplatforms/sdt.htm.  Included in this
information
is what SSCG is and its effects on some other devices.  I suggest one read these
references as a basis for further discussions.

Experimental data has clearly shown is that the QP and Peak readings are
exactly the same for SSCG signals (No Fooling).  An SSCG output properly
designed will create
a clock that is frequency modulated at ~30kHz.  The output spectrum is a series
of
stationary harmonics spaced at 30kHz apart.

Finally, this method will attenuate the clock and system as compared to the same
system
with the modulation turned off.  All other EMI reduction techniques will also
reduce emissions further.
Our design philosophy is to bring all good low cost techniques to bare on
reducing the emissions
and SSCG is just one of them.

Keith Hardin
Lexmark International

For the last time this came up, please see the append on the emc-pstc archives
at http://www.rcic.com/ with subject Clock Oscillator Re: Spread spectrum
clock oscillator (1) 20-Feb-97 .




slacey%foxboro@interlock.lexmark.com on 03/17/2000 11:18:46 AM

Please respond to slacey%foxboro@interlock.lexmark.com

To:   macy%california@interlock.lexmark.com
cc:   emc-pstc%ieee@interlock.lexmark.com (bcc: Keith Hardin/Lex/Lexmark)
Subject:  RE: Dithered clocks and EMC - BEWARE




Robert, and the group,
Although I have only limited experience (1 instance) with dithered clocks, I
thought that I might share that experience with the group. I had a product
that was failing radiated emissions at one particular frequency with a
vertical antenna orientation. I tracked the problem down to a particular
cable and circuit card. Use of a near field probe identified the oscillator
package as the source of the emissions (the second harmonic).

The device was located near the card edge, insufficient decoupling, etc. All
the textbook layout errors. A check of the oscillator specifications showed
that it was a standard TTL device with a fanout of 10 inputs. I had already
found some fixes that would reduce emissions, clamp-on ferrites, additional
shielding, etc., but thought it made more sense to reduce the emissions at
the source. I suggested to the design engineer that a low-power TTL
oscillator, with a fanout of 2 inputs, would reduce currents through the
offending etches. Someone else suggested a dithered clock device instead.
When we tested the dithered clock, emissions were actually worse. We had
simply spread the problem over a wider spectrum.

I have heard some success stories for these devices, but results in this
case were disappointing. I still think a lot depends on the layout. I
strongly suspect that real-world disruption to nearby devices is generally
going to be worse, since the idea behind these devices is to fool
quasi-peak measurements in order to pass.

Caveat Emptor!

Scott Lacey


 -Original Message-
 From: Robert Macy [SMTP:m...@california.com]
 Sent: Friday, March 17, 2000 9:38 AM
 To:  emc-p...@ieee.org
 Subject:  Fw: Dithered clocks and EMC - BEWARE


 Of interest, so I forward this to the group:

- Robert -

Robert A. Macy, PEm...@california.com
408 286 3985  fx 408 297 9121
AJM International Electronics Consultants
619 North First St,   San Jose, CA  95112


 -Original Message-
 From: John Woodgate j...@jmwa.demon.co.uk
 Newsgroups: sci.engr.electrical.compliance,sci.electronics.design
 Date: Tuesday, March 14, 2000 11:55 PM
 Subject: Dithered clocks and EMC - BEWARE


 About a year ago we had a thread on this subject, concluding that
some
 research was needed to see whether dithered clocks were better or
worse
 in terms of conforming to EMC requirements.
 
 I learned very recently that some reliable but as-yet unpublished
 research has found that digital TV receivers are some 40 dB (!!)
more
 sensitive to dithered clock emissions than to unmodulated carriers.
This
 is likely to lead to changes in EMC limits within maybe as little
as
 three years, since the authorities certainly don't want to be
deluged
 with complaints of interference from people who have just opted for
 digital TV.
 
 So, if you are thinking of using a dithered clock, think again!
 --
 Regards, John Woodgate, OOO - Own Opinions Only. Phone +44 (0)1268
747839
 Fax +44 (0)1268 777124. http://www.jmwa.demon.co.uk
 I wanted to make a fully-automated nuclear-powered trawler,
 but it went into spontaneous fishing.



 

RE: NRTL(Bell Atlantic) Pre-Approval

2000-03-17 Thread Naftali Shani
Well put. This has been our experience.

Regards,
Naftali Shani, Nortel Networks, Dept. 0S45, MS 117/C1/M05
21 Richardson Side Road, Kanata, Ontario, Canada  K2K 2C1
Voice +1.613.765.2505 (ESN 395) Fax +1.613.763.8091 (ESN 393)
E-mail: nsh...@nortelnetworks.com mailto:nsh...@nortelnetworks.com  or
n...@ieee.org mailto:n...@ieee.org 

-Original Message-
From:   Ed Nakauchi [SMTP:e...@garwoodtestlabs.com]
Sent:   Friday, March 17, 2000 12:42 PM
To: emc-pstc
Subject:Fw: NRTL(Bell Atlantic) Pre-Approval

To All:
 
Posted for Jason Armstrong of Garwood Laboratories, Inc. by
 
Ed Nakauchi
e...@garwoodtestlabs.com mailto:e...@garwoodtestlabs.com 
 
-Original Message-
From: Jason  jas...@garwoodtestlabs.com
mailto:jas...@garwoodtestlabs.com 
To: Ed Nakauchi  e...@garwoodtestlabs.com
mailto:e...@garwoodtestlabs.com 
Date: Friday, March 17, 2000 9:21 AM
Subject: NRTL(Bell Atlantic) Pre-Approval


Gentlemen,
 
Allow me to introduce myself. My name is Jason Armstrong. I am the
General Manager at Garwood Laboratories, in Placentia Ca. We are an
independent test lab that has been gearing up for NEBS testing for the past
several months. Between our two facilities we are able to perform the
EMC/Surge, safety  physical protection all under one company. I have had
many conversations with Chuck Graff at Bell Atlantic in regards to the
alternate test facilites statement in their latest checklist revision. The
word alternate refers more to in-house or the mfg's test facilities and not
to an independent test lab. They have that statement in there for equipment
that is either too large or not practical to be tested outside of the mfg's
plant due to it's deployment configuration.  If you read para 3.1.1 of Bells
checklist, you'll see that Bell Atlantic does not certify or approve
testing facilities. What DLS has obtained is a letter of recognition and not
an approval. I know it sounds like a play on words, but Chuck at Bell
Atlantic as well as the other RBOC's are very touchy about the wording. This
recognition is something that we are currently striving towards as well.
I'm not sure how DLS went about obtaining this, but I have been informed by
Bell South, Bell Atlantic  US West that if we provide a sample of a NEBS
test report that meets with their acceptance, and we are accredited by a
recognized orginazation, like NAVLAP or A2LA, then we will also be
recognized by them to perform the NEBS requirements. 
 
I hope this helps.
 
Jason Armstrong
General Manager
Garwood Laboratories, Inc.
jas...@garwoodtestlabs.com mailto:jas...@garwoodtestlabs.com 
 


RE: Dithered clocks and EMC

2000-03-17 Thread Matejic, Mirko

Theoretical explanation of how variable clock frequency reduces radiated
emission levels is given in US Patent 5,430,392
/netacgi/nph-Parser?Sect1=PTO1Sect2=HITOFFd=PALLp=1u=/netahtml/srchnum.
htmr=1f=Gl=50s1='5,430,392'.WKU.OS=PN/5,430,392RS=PN/5,430,392  Clock
system and method for reducing the measured level of unintentional
electromagnetic emissions from an electronic device
/netacgi/nph-Parser?Sect1=PTO1Sect2=HITOFFd=PALLp=1u=/netahtml/srchnum.
htmr=1f=Gl=50s1='5,430,392'.WKU.OS=PN/5,430,392RS=PN/5,430,392 from
1993.

http://164.195.100.11/netahtml/srchnum.htm
http://164.195.100.11/netahtml/srchnum.htm 

Mirko




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: EMC/PSTC/NEBS/TREG

2000-03-17 Thread jacob ben ary

Please split the list, EMC should be stand alone.

-Original Message-
From: owner-emc-p...@ieee.org [mailto:owner-emc-p...@ieee.org]On Behalf Of
Rossi Giuseppe
Sent: Friday, March 17, 2000 5:17 PM
To: emc-p...@majordomo.ieee.org
Subject: R:EMC/PSTC/NEBS/TREG



absolutely not , please split the list
I'm just intersted in EMC.

Ing. Giuseppe Rossi, Narte Certified Engineer
EMC manager
Centro Ricerche Fiat
Strada Torino 50
10043 - Orbassano (TO)
tel 011 90 83 114
fax 011 90 83 083
e-mail g.ro...@crf.it



 --
 Da:   pmerguer...@itl.co.il[SMTP:pmerguer...@itl.co.il]
 Risposta a:   pmerguer...@itl.co.il
 Inviato:  venerdì 17 marzo 2000 10.04
 A:emc-p...@majordomo.ieee.org
 Oggetto:  EMC/PSTC/NEBS/TREG


 Dear All,

 DO NOT SPLIT! I AM ALSO IN FAVOR OF MIGRATING TREG AND NEBS GROUPS INTO TO
 THE EMC/PSTC LIST. ARE YOU ALL IN FAVOR?
 Peter Merguerian
 Managing Director
 Product Testing Division
 I.T.L. (Product Testing) Ltd.
 Hacharoshet 26, POB 211
 Or Yehuda 60251, Israel

 Tel: 972-3-5339022 Fax: 972-3-5339019
 e-mail: pmerguer...@itl.co.il
 website: http://www.itl.co.il






 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Fw: NRTL(Bell Atlantic) Pre-Approval

2000-03-17 Thread Ed Nakauchi
To All:

Posted for Jason Armstrong of Garwood Laboratories, Inc. by

Ed Nakauchi
e...@garwoodtestlabs.com

-Original Message-
From: Jason jas...@garwoodtestlabs.com
To: Ed Nakauchi e...@garwoodtestlabs.com
List-Post: emc-pstc@listserv.ieee.org
Date: Friday, March 17, 2000 9:21 AM
Subject: NRTL(Bell Atlantic) Pre-Approval


Gentlemen,
 
Allow me to introduce myself. My name is Jason Armstrong. I am the General 
Manager at Garwood Laboratories, in Placentia Ca. We are an independent test 
lab that has been gearing up for NEBS testing for the past several months. 
Between our two facilities we are able to perform the EMC/Surge, safety  
physical protection all under one company. I have had many conversations with 
Chuck Graff at Bell Atlantic in regards to the alternate test facilites 
statement in their latest checklist revision. The word alternate refers more to 
in-house or the mfg's test facilities and not to an independent test lab. They 
have that statement in there for equipment that is either too large or not 
practical to be tested outside of the mfg's plant due to it's deployment 
configuration.  If you read para 3.1.1 of Bells checklist, you'll see that Bell 
Atlantic does not certify or approve testing facilities. What DLS has 
obtained is a letter of recognition and not an approval. I know it sounds like 
a play on words, but Chuck at Bell Atlantic as well as the other RBOC's are 
very touchy about the wording. This recognition is something that we are 
currently striving towards as well.  I'm not sure how DLS went about obtaining 
this, but I have been informed by Bell South, Bell Atlantic  US West that if 
we provide a sample of a NEBS test report that meets with their acceptance, and 
we are accredited by a recognized orginazation, like NAVLAP or A2LA, then we 
will also be recognized by them to perform the NEBS requirements. 
 
I hope this helps.
 
Jason Armstrong
General Manager
Garwood Laboratories, Inc.
jas...@garwoodtestlabs.com
 


RE: Re[2]: EMC, NEBS NRTL's

2000-03-17 Thread David Spencer

Hey All,
Keep in mind that although Bell Atlantic is often the pickiest, they are not
the only RBOC that flip-flops on the NRTL data issue on an annual basis.  I
believe US West has taken their place on the NRTL Wagon this year.  Bell
South weighs in on the issue regularly as well.  I would not be surprised if
it is not one of those things that keeps the larger switch players on top of
the short list for new equipment rollouts.
Personally, I cannot justify the risk of having official NEBS tests done by
a lab that is not a NRTL.
Dave Spencer
Oresis Communications

-Original Message-
From: Jay Johansmeier [mailto:jay_johansme...@mw.3com.com]
Sent: Friday, March 17, 2000 6:24 AM
To: emc-p...@ieee.org
Subject: Re: Re[2]: EMC, NEBS  NRTL's





Thanks Eric.
If you read on you see that Bell Atlantic must give 'prior' approval for
'alternate' test facilities.
Jeffrey was asking for documentation from a lab that has this 'prior'
approval
and at the moment
DLS is the only one, I haven't checked for others, that I know that have a
letter of approval.
I'm sure there are others.
My guess is that Jeffrey could ask the lab(s) in question to contact Bell
Atlantic to receive this type of prior approval.

Regards,

Jay Johansmeier
Regulatory Engineer
3Com Corporation
jay_johansme...@3com.com





Eric Petitpierre eric.petitpie...@pulse.com on 03/17/2000 07:55:00 AM

Sent by:  Eric Petitpierre eric.petitpie...@pulse.com


To:   emc-pstc @ieee.org emc-p...@ieee.org, Jay Johansmeier/MW/US/3Com
cc:
Subject:  Re[2]: EMC, NEBS  NRTL's



 Jeffey and Jay,

 Bell Atlantic  Specification RNSA-NEB-95-0003, Rev, 10 Issued January
 26,2000 has removed the NRTL requirement,( see sections 1.6.1 and
 3.1.2)

Regards,

Eric Petitpierre
Pulsecom
Herndon,VA
eric.petitpierre

__ Reply Separator
_
Subject: RE: EMC, NEBS  NRTL's
Author:  jay_johansme...@mw.3com.com (Jay Johansmeier) at smtp
List-Post: emc-pstc@listserv.ieee.org
Date:3/17/00 7:49 AM


Jeffrey,

DLS, here in Illinois, claims to have a letter from Bell Atlantic stating
that
their EMC data will be accepted.
You can email Steve Grimes at DLS and ask him if they will give you a copy.
(
sgri...@dlsemc.com )

Regards,

Jay Johansmeier
Regulatory Engineer
3Com Corporation
jay_johansme...@3com.com





Collins, Jeffrey jcoll...@ciena.com on 03/17/2000 03:56:40 AM

Please respond to Collins, Jeffrey jcoll...@ciena.com

Sent by:  Collins, Jeffrey jcoll...@ciena.com


To:   'emc-pstc @ieee.org' emc-p...@ieee.org
cc:(Jay Johansmeier/MW/US/3Com)
Subject:  RE: EMC, NEBS  NRTL's




Group,


Can anyone confirm that the RBOC's, particularly Bell Atlantic has agreed to
accept EMC FCC data from non NRTL's?
If this is true please provide any documentation to support this. (You know
a customer is going to want to see it)


Thanks in advance,

Jeffrey Collins
MTS, Principal Compliance Engineer
Ciena Core Switching Division
jcoll...@ciena.com
www.ciena.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org







---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send 

Re: Antenna factors to be used for NSA measurement

2000-03-17 Thread Paolo . Roncone



Robert,
there are a couple of points that came up in your posts that I would like to
more fully understand.

1. ...the site under test is verified against the performance of the site on
which the antenna factors are calibrated.
I honestly don't get this point. The applicable standards (ANSI C63.4 and
CISPR22) require that you verify the measured Normalized Site Attenuation (NSA)
against a Theoretical Normalized Site Attenuation (ThNSA) of an ideal site
(infinite perfectly conductive ground plane), NOT against the site on which the
antenna factors are calibrated. Ref. sec.ANSI C63.4-1992 sec.5.4.6.1, CISPR 22 -
1997 (3.ed) sec.10.3.2. This is what the standard says, although its validity
has been questioned by a number of EMC experts.

2. ...a dual antenna factor calibration suffices if the same antennas will be
used in the NSA measurement, there is no accuracy advantage when using a
three-antenna method in this case.
In ANSI C63.5-1988 I read (sec.5.2 page12): In practice, two antennas are never
identical, and the antenna factor calculated by Eq.8 is the geometric mean of
the individual factor for each of the two antennas..
That's the reason why I said that the 3 antenna method is more accurate.
Also,your statement: Antenna factors provided by the manufacturer or measured
by a cal lab are typically not of sufficient accuracy (with a few exceptions)
reinforces my opinion.

3. There are substantial difference in the antenna factors (and site
attenuation) values at various range distances.
I agree that it's always better to calibrate antennas at the test distance. On
the other end, within the range of 3-10 m distance my experience with broadband
antennas (biconicals and log-periodic) between 30 and 1000 MHz tells me that the
error is well within 1 dB, as long as you are in the far-field at 3 m (which is
the case most of the times using biconicals). I have not direct experience but
my guess is that you may have non-negligible errors for distances  3m and/or
highly directional antennas (horns  freq. 1GHz), whereby you can be  in the
near field even at 3+ meters distance.

4. I know the article you mentioned (Z. Chen and M.Foegelle: Numerical
Investigations of Ground Plane Effects on Biconical Antenna Factor) exposes one
weakness of the ideal (theoretical) model used for calculating ThNSA (see point
1). The analytically derived model assumes that the antennas used are point
dipoles that behave in a different way than the most used broadband antennas.
They use a numerical analysis to measure the effects of the ground plane on AFs
of biconical antennas (field variations and antenna coupling with the ground
plane). Their conclusions are, in their words, that if an ANSI C63.5 standard
site calibrated AF is used for ANSI C63.4 (NSA measurements), all the
approximations and ground plane effects exactly cancel.
My understanding is that if you use the same geometry for the calibration of
antennas (3 antenna method) over a ground plane and for the validation of your
site (OATS or SAR), the variations of antenna factors associated with the
coupling antenna-ground plane are compensated and do not add errors to the NSA
measurements. Provided the two ground planes (calibration site and test site to
be qualified) have ground planes that behave in the same way !
So under these conditions, for NSA measurements and site validation you can
limit the job to horizontal polarization (as required by the standards).
The antenna calibration in vertical polarization is useful to improve accuracy
of emissions measurements of products (using vertical and horizontal AFs) other
than in cases - as mentioned by Don Umbdenstock - where the error introduced by
AF variation does not get you over your total budgeted measurement uncertainty.

Any further comment would be highly appreciated.

Regards,

Paolo Roncone



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: standard for lead shot dielectric testing

2000-03-17 Thread Kelly Tsudama


Barry

You can also look at the UL Standard for Vacuum cleaning machines (UL1017).  
The dielectric test on powered vacuum hoses also employed lead shot.

Kelly

At 10:03 AM 3/17/00 +0200, Peter Merguerian wrote:

Barry,

In my old days working for UL, we used lead shot to test the dielectric
strength properties of insulated wire connectors. I suggest you take a look
at the wire connector standards UL486 Series.



At 15:26 16/03/2000 -0600, barrym wrote:

I'm looking for reference to any standard which may provide specifics for
using lead shot for dielectric strength testing.  I know this done for
insulation system qualifications, just have not identified a standard for
the test set up.

Thanks,
Barry Marks


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il 






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 

Kelly Tsudama
Cisco Systems
ktsud...@cisco.com
408-527-0216
408-525-9150 fax
408-322-9024 pager

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: EMC, NEBS NRTL's

2000-03-17 Thread Gary McInturff

Still can be done at an independent site. The Lab I use, ACME Testing,
here in Washington has accreditation to at least the radiated emissions
portions of the GR-, I have to check on the susceptibility, but I think so.
Even if that were not true. I believe that if your NRTL accepts the EMC
data from the other lab they will include it in the overall report. 
Now there is the dicey part. Many of the NRTL's have their own EMC labs
and may not want to loose the cash, and try reject the independent lab's
report. I would find that a really hard sell however, because the NRTL labs
undoubtedly carry accreditation through NIST for the EMC portion, making any
argument about competency of the independent lab a tough sell.
At any rate I've never quite understood the justification for not
calling laboratories which are accredited through programs set up by and
through the FCC, as NRTLS'. The basic assumption I would make is that the
FCC knows a heck of a lot more about this aspect of testing and
accreditation than OSHA does. Heavy sigh!
Gary

-Original Message-
From: Naftali Shani [mailto:nsh...@nortelnetworks.com]
Sent: Friday, March 17, 2000 6:05 AM
To: 'Collins, Jeffrey'
Cc: 'emc-p...@ieee.org'
Subject: RE: EMC, NEBS  NRTL's



BM__MailDataJeffrey, the requirement that was for NRTL lab (
Bellcore representative) for each section of GR-63  GR-1089, has been
dropped. See section 3.1.2 in the BA-NEBS-R10.

However, FCC data/frequency range for radiated emissions is
insufficient: You should have data based on GR-1089 requirements 
objectives (10 kHz to 10 GHz).

Regards,
Naftali Shani, Nortel Networks, Dept. 0S45, MS 117/C1/M05 
21 Richardson Side Road, Kanata, Ontario, Canada  K2K 2C1
Voice +1.613.765.2505 (ESN 395) Fax +1.613.763.8091 (ESN 393) 
E-mail:  mailto:nsh...@nortelnetworks.com nsh...@nortelnetworks.com or
mailto:n...@ieee.org n...@ieee.org 

-Original Message- 
From:   Collins, Jeffrey [SMTP:jcoll...@ciena.com] 
Sent:   Friday, March 17, 2000 4:57 AM 
To: 'emc-p...@ieee.org' 
Subject:RE: EMC, NEBS  NRTL's 


Group, 


Can anyone confirm that the RBOC's, particularly Bell Atlantic has
agreed to 
accept EMC FCC data from non NRTL's? 
If this is true please provide any documentation to support this. (You know 
a customer is going to want to see it) 


Thanks in advance, 

Jeffrey Collins 
MTS, Principal Compliance Engineer 
Ciena Core Switching Division 
jcoll...@ciena.com 
www.ciena.com 


--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 

To cancel your subscription, send mail to: 
 majord...@ieee.org 
with the single line: 
 unsubscribe emc-pstc 

For help, send mail to the list administrators: 
 Jim Bacher:  jim_bac...@mail.monarch.com 
 Michael Garretson:pstc_ad...@garretson.org 

For policy questions, send mail to: 
 Richard Nute:   ri...@ieee.org 




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: SAF: Insulation resistance and hipot tests

2000-03-17 Thread Dick Grobner

EN60601-1 (Medical Safety) Appendix C provides a list entitled Sequence of
Testing. This list is used during the course of the safety investigation on
the device. It follows as:
C24: Cont. leakage currents and patient auxiliary currents at operating temp
C25: Dielectric strength at operating temp
C26: Humidity preconditioning treatment
C27: Dielectric strength test (cold condition after humidity conditioning)
C28: Leakage current test after humidity preconditioning treatment

In our production testing we perform a high potential dielectric strength
test first followed by a leakage current test. Our high potential tester has
a ground continuity circuit and will warn the operator if the safety ground
circuit is not in place (open).

-Original Message-
From: mark.dagost...@vsea.com [mailto:mark.dagost...@vsea.com]
Sent: Friday, March 17, 2000 7:37 AM
To: Bruce Touzel; Art Michael
Cc: emc-p...@majordomo.ieee.org; Martin Rowe (TMW)
Subject: Re: SAF: Insulation resistance and hipot tests



Folks:

EN 60204-1 also specifies an insulation resistance test.
Depending on the standard, they tell you the sequence of the various safety
tests.
For example, in EN 60204-1, clause 19.1 (the test clause) states:
When these test are performed, it is recommended that they follow the
sequence listed.

For EN 60204-1, it is Ground continuity, then Insulation resistance, then
Hipot, then cap discharge.

I hope this helps.

At 01:21 PM 3/16/00 -0800, Bruce Touzel wrote:

Insulation resistance tests would apply only to IEC 950 I believe, so this
may
not apply for you ?

Art Michael wrote:

 Hello Martin,

 I don't have the answer to your question, but do caution that the First
 Test to be run (if the DUT is grounded) is the Ground Continuity Test
(for
 test-operator protection).

 Regards, Art Michael

  * * * * * * * * * * * * * * * * * * * * * *
 *   International Product Safety Bookshop   *
 *  Check out our current offerings! *
 * http://www.safetylink.com/bookshop.html *
 *   *
 * Now offering BSI's Books  Reports*
 *  including, World Electricity Supplies  *
 *   *
 * Another service of the Safety Link*
 *  www.safetylink.com *
  * * * * * * * * * * * * * * * * * * * * * *
 --

 On Thu, 16 Mar 2000, Martin Rowe (TMW) wrote:

 
  Group,
 
  A reader asked about the order of performing safety tests.
  Should he perform insulation resistance tests before or after
  hipot tests? The reader didn't say what type of product he's
  testing, but I can ask.
 
  Thanks,
 
  /\
  | Martin Rowe  |   /  \
  | Senior Technical Editor  |  /\  /\
  | Test  Measurement World | /  \/  \/\  
  | voice 617-558-4426   |/\  /\  /  \/
  | fax 617-928-4426 |  \/  \/
  | e-mail m.r...@ieee.org   |   \  /
  | http://www.tmworld.com   |\/
  
 
 
  ---
  This message is from the IEEE EMC Society Product Safety
  Technical Committee emc-pstc discussion list.
 
  To cancel your subscription, send mail to:
   majord...@ieee.org
  with the single line:
   unsubscribe emc-pstc
 
  For help, send mail to the list administrators:
   Jim Bacher:  jim_bac...@mail.monarch.com
   Michael Garretson:pstc_ad...@garretson.org
 
  For policy questions, send mail to:
   Richard Nute:   ri...@ieee.org
 
 
 

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 
Mark A. D'Agostino
Sr. Product Safety Engineer
978 282 7520
978 281 3162 (fax)

---
This 

RE: Dithered clocks and EMC - BEWARE

2000-03-17 Thread Lacey,Scott

Robert, and the group,
Although I have only limited experience (1 instance) with dithered clocks, I
thought that I might share that experience with the group. I had a product
that was failing radiated emissions at one particular frequency with a
vertical antenna orientation. I tracked the problem down to a particular
cable and circuit card. Use of a near field probe identified the oscillator
package as the source of the emissions (the second harmonic).

The device was located near the card edge, insufficient decoupling, etc. All
the textbook layout errors. A check of the oscillator specifications showed
that it was a standard TTL device with a fanout of 10 inputs. I had already
found some fixes that would reduce emissions, clamp-on ferrites, additional
shielding, etc., but thought it made more sense to reduce the emissions at
the source. I suggested to the design engineer that a low-power TTL
oscillator, with a fanout of 2 inputs, would reduce currents through the
offending etches. Someone else suggested a dithered clock device instead.
When we tested the dithered clock, emissions were actually worse. We had
simply spread the problem over a wider spectrum.

I have heard some success stories for these devices, but results in this
case were disappointing. I still think a lot depends on the layout. I
strongly suspect that real-world disruption to nearby devices is generally
going to be worse, since the idea behind these devices is to fool
quasi-peak measurements in order to pass.

Caveat Emptor!

Scott Lacey


-Original Message-
From:   Robert Macy [SMTP:m...@california.com]
Sent:   Friday, March 17, 2000 9:38 AM
To: emc-p...@ieee.org
Subject:Fw: Dithered clocks and EMC - BEWARE


Of interest, so I forward this to the group:

   - Robert -

   Robert A. Macy, PEm...@california.com
   408 286 3985  fx 408 297 9121
   AJM International Electronics Consultants
   619 North First St,   San Jose, CA  95112


-Original Message-
From: John Woodgate j...@jmwa.demon.co.uk
Newsgroups: sci.engr.electrical.compliance,sci.electronics.design
Date: Tuesday, March 14, 2000 11:55 PM
Subject: Dithered clocks and EMC - BEWARE


About a year ago we had a thread on this subject, concluding that
some
research was needed to see whether dithered clocks were better or
worse
in terms of conforming to EMC requirements.

I learned very recently that some reliable but as-yet unpublished
research has found that digital TV receivers are some 40 dB (!!)
more
sensitive to dithered clock emissions than to unmodulated carriers.
This
is likely to lead to changes in EMC limits within maybe as little
as
three years, since the authorities certainly don't want to be
deluged
with complaints of interference from people who have just opted for
digital TV.

So, if you are thinking of using a dithered clock, think again!
-- 
Regards, John Woodgate, OOO - Own Opinions Only. Phone +44 (0)1268
747839
Fax +44 (0)1268 777124. http://www.jmwa.demon.co.uk
I wanted to make a fully-automated nuclear-powered trawler,
but it went into spontaneous fishing.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



European EPA

2000-03-17 Thread Peter Merguerian

Hello All,

Does anyone know the equivalent of the US Environmental Protection Agency
(EPA) in Europe?

Thanks
Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il 






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: EMC/PSTC/NEBS/TREG

2000-03-17 Thread Doug

Peter Merguerian wrote:
 
 Dear All,
 
 DO NOT SPLIT! I AM ALSO IN FAVOR OF MIGRATING TREG AND NEBS GROUPS INTO TO
 THE EMC/PSTC LIST. ARE YOU ALL IN FAVOR?

Absolutely not.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: EMC, NEBS NRTL's

2000-03-17 Thread Penny D. Robbins


John-
Actually, GR-1089 starts at 60 Hz (magnetic field) and 10 kHz (electric field
and conducted tests).
Penny Robbins
Telcordia Technologies




John Juhasz jjuh...@fiberoptions.com on 03/17/2000 08:23:25 AM

Please respond to John Juhasz jjuh...@fiberoptions.com

To:   'Collins, Jeffrey' jcoll...@ciena.com, 'emc-p...@ieee.org'
  emc-p...@ieee.org
cc:(bcc: Penny D. Robbins/Telcordia)
Subject:  RE: EMC, NEBS  NRTL's




You have to be careful here Jeff. The frequency range for evaluation to
GR-1089 starts at 150kHz and goes up to 10 GHz. The FCC Part 15 testing
range is from 30MHz-1.0GHz.
The GR-1089 spec also contains Immunity requirements.
Further, the objective is to meet the spec with all covers, panels, doors
off/open which is
not typically done during FCC testing.
Additionally, look at it from this perspective: If an RBOC is going to be
reviewing
proposals, if there are two similar products competing, they will choose the
one that
meets the details of the NEBS spec, than the one that took steps to 'look
like' they meet NEBS,
even if the product costs more.
The RBOCs are a different breed than the usual commercial customer.

John Juhasz
Fiber Options
Bohemia, NY

-Original Message-
From: Collins, Jeffrey [mailto:jcoll...@ciena.com]
Sent: Friday, March 17, 2000 4:57 AM
To: 'emc-p...@ieee.org'
Subject: RE: EMC, NEBS  NRTL's



Group,


Can anyone confirm that the RBOC's, particularly Bell Atlantic has agreed to
accept EMC FCC data from non NRTL's?
If this is true please provide any documentation to support this. (You know
a customer is going to want to see it)


Thanks in advance,

Jeffrey Collins
MTS, Principal Compliance Engineer
Ciena Core Switching Division
jcoll...@ciena.com
www.ciena.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


Title: RE: EMC, NEBS  NRTL's





You have to be careful here Jeff. The frequency range for evaluation to GR-1089 starts at 150kHz and goes up to 10 GHz. The FCC Part 15 testing range is from 30MHz-1.0GHz. 

The GR-1089 spec also contains Immunity requirements. 
Further, the objective is to meet the spec with all covers, panels, doors off/open which is
not typically done during FCC testing. 
Additionally, look at it from this perspective: If an RBOC is going to be reviewing
proposals, if there are two similar products competing, they will choose the one that
meets the details of the NEBS spec, than the one that took steps to 'look like' they meet NEBS,
even if the product costs more. 
The RBOCs are a different breed than the usual commercial customer. 


John Juhasz
Fiber Options
Bohemia, NY


-Original Message-
From: Collins, Jeffrey [mailto:jcoll...@ciena.com]
Sent: Friday, March 17, 2000 4:57 AM
To: 'emc-p...@ieee.org'
Subject: RE: EMC, NEBS  NRTL's




Group,



Can anyone confirm that the RBOC's, particularly Bell Atlantic has agreed to
accept EMC FCC data from non NRTL's?
If this is true please provide any documentation to support this. (You know
a customer is going to want to see it)



Thanks in advance,


Jeffrey Collins 
MTS, Principal Compliance Engineer
Ciena Core Switching Division
jcoll...@ciena.com
www.ciena.com



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.


To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc


For help, send mail to the list administrators:
 Jim Bacher: jim_bac...@mail.monarch.com
 Michael Garretson: pstc_ad...@garretson.org


For policy questions, send mail to:
 Richard Nute: ri...@ieee.org





Re: Fwd:Isolations on inner layers

2000-03-17 Thread volker . gasse



Hello Jim and Mihai,

According to IEC 60950 3rd. edition, Clause 2.10.5.3, the distance between
two adjacent tracks on the same inner layer of a printed circuit board is
treated as distance through insulation, and therefore 0,4 mm apply for
supplementary or reinforced insulation.
Your question regarding air bubbles or other defects is should be covered
by the applied electric strength test.

mit freundlichen Gruessen/ best regards
Volker Gasse

IBM Germany, Technical Relations/Product Safety,
Tel: +49-7031-642-6796, Fax: -6916, e-mail: volker.ga...@de.ibm.com
Mail:  D3114/7103-91, D-70548 Stuttgart, Germany


jim_bac...@mail.monarch.com (Jim Bacher) on 17.03.2000 13:50:53

Please respond to jim_bac...@mail.monarch.com (Jim Bacher)

To:   emc-p...@ieee.org
cc:   mih...@trenew.pcnet.ro (bcc: Volker Gasse/Germany/IBM)
Subject:  Fwd:Isolations on inner layers





forwarding for mih...@trenew.pcnet.ro  ...  Jim

Forward Header_
Subject:Isolations on inner layers
Author: Mihai Vintila mih...@trenew.pcnet.ro
List-Post: emc-pstc@listserv.ieee.org
Date:   3/16/00 7:34 PM

Hello,

I have a question concerning isolations for hazardous voltages on
inner
layers of a multilayer PCB.
The material is standard FR4.
I have read the EN60950 spec and it seems like for copper on
different
inner layers an isolation of 0.4mm would be good enough. Now what I could
not
figure is about traces on the same inner layer. In this case an isolation
of 0.4
mm is as good as it is between different layers, or should I take into
consideration the manufacturing errors (impurities, air bubbles, a.s.o.)
and
make a bigger isolation, but how much bigger?
The voltages I am working with are some of them TNV1 and others
220VAC
(mains).

Many thanks,

Mihai


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



R:EMC/PSTC/NEBS/TREG

2000-03-17 Thread Rossi Giuseppe

absolutely not , please split the list
I'm just intersted in EMC.

Ing. Giuseppe Rossi, Narte Certified Engineer
EMC manager
Centro Ricerche Fiat
Strada Torino 50
10043 - Orbassano (TO)
tel 011 90 83 114
fax 011 90 83 083
e-mail g.ro...@crf.it



 --
 Da:   pmerguer...@itl.co.il[SMTP:pmerguer...@itl.co.il]
 Risposta a:   pmerguer...@itl.co.il
 Inviato:  venerdì 17 marzo 2000 10.04
 A:emc-p...@majordomo.ieee.org
 Oggetto:  EMC/PSTC/NEBS/TREG
 
 
 Dear All,
 
 DO NOT SPLIT! I AM ALSO IN FAVOR OF MIGRATING TREG AND NEBS GROUPS INTO TO
 THE EMC/PSTC LIST. ARE YOU ALL IN FAVOR?
 Peter Merguerian
 Managing Director
 Product Testing Division
 I.T.L. (Product Testing) Ltd.
 Hacharoshet 26, POB 211
 Or Yehuda 60251, Israel
 
 Tel: 972-3-5339022 Fax: 972-3-5339019
 e-mail: pmerguer...@itl.co.il
 website: http://www.itl.co.il 
 
 
 
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
 
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



FW: EMC, NEBS NRTL's

2000-03-17 Thread John Juhasz
I stand corrected regarding my response to Jeff Collins. The frequency range
starts at 10kHz.
Sorry if I misled anyone.

John Juhasz
Fiber Options
Bohemia, NY

-Original Message-
From: e...@itsqs.com [mailto:e...@itsqs.com] 
Sent: Friday, March 17, 2000 9:23 AM
To: jjuh...@fiberoptions.com
Subject: RE: EMC, NEBS  NRTL's


Hi John, Actually the frequency range starts at 10kHz for both Emissions and
Immunity.
Eddie O'Toole
ITS, Boxboro, MA

-Original Message-
From: John Juhasz [mailto:jjuh...@fiberoptions.com]
Sent: Friday, March 17, 2000 8:23 AM
To: 'Collins, Jeffrey'; 'emc-p...@ieee.org'
Subject: RE: EMC, NEBS  NRTL's



You have to be careful here Jeff. The frequency range for evaluation to
GR-1089 starts at 150kHz and goes up to 10 GHz. The FCC Part 15 testing
range is from 30MHz-1.0GHz. 

The GR-1089 spec also contains Immunity requirements. 
Further, the objective is to meet the spec with all covers, panels, doors
off/open which is 
not typically done during FCC testing. 
Additionally, look at it from this perspective: If an RBOC is going to be
reviewing 
proposals, if there are two similar products competing, they will choose the
one that 
meets the details of the NEBS spec, than the one that took steps to 'look
like' they meet NEBS, 
even if the product costs more. 
The RBOCs are a different breed than the usual commercial customer. 

John Juhasz 
Fiber Options 
Bohemia, NY 

-Original Message- 
From: Collins, Jeffrey [ mailto:jcoll...@ciena.com
mailto:jcoll...@ciena.com ] 
Sent: Friday, March 17, 2000 4:57 AM 
To: 'emc-p...@ieee.org' 
Subject: RE: EMC, NEBS  NRTL's 



Group, 


Can anyone confirm that the RBOC's, particularly Bell Atlantic has agreed to

accept EMC FCC data from non NRTL's? 
If this is true please provide any documentation to support this. (You know 
a customer is going to want to see it) 


Thanks in advance, 

Jeffrey Collins 
MTS, Principal Compliance Engineer 
Ciena Core Switching Division 
jcoll...@ciena.com 
www.ciena.com 


--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 

To cancel your subscription, send mail to: 
 majord...@ieee.org 
with the single line: 
 unsubscribe emc-pstc 

For help, send mail to the list administrators: 
 Jim Bacher:  jim_bac...@mail.monarch.com 
 Michael Garretson:pstc_ad...@garretson.org 

For policy questions, send mail to: 
 Richard Nute:   ri...@ieee.org 


Fw: Dithered clocks and EMC - BEWARE

2000-03-17 Thread Robert Macy

Of interest, so I forward this to the group:

   - Robert -

   Robert A. Macy, PEm...@california.com
   408 286 3985  fx 408 297 9121
   AJM International Electronics Consultants
   619 North First St,   San Jose, CA  95112


-Original Message-
From: John Woodgate j...@jmwa.demon.co.uk
Newsgroups: sci.engr.electrical.compliance,sci.electronics.design
List-Post: emc-pstc@listserv.ieee.org
Date: Tuesday, March 14, 2000 11:55 PM
Subject: Dithered clocks and EMC - BEWARE


About a year ago we had a thread on this subject, concluding that some
research was needed to see whether dithered clocks were better or worse
in terms of conforming to EMC requirements.

I learned very recently that some reliable but as-yet unpublished
research has found that digital TV receivers are some 40 dB (!!) more
sensitive to dithered clock emissions than to unmodulated carriers. This
is likely to lead to changes in EMC limits within maybe as little as
three years, since the authorities certainly don't want to be deluged
with complaints of interference from people who have just opted for
digital TV.

So, if you are thinking of using a dithered clock, think again!
-- 
Regards, John Woodgate, OOO - Own Opinions Only. Phone +44 (0)1268 747839
Fax +44 (0)1268 777124. http://www.jmwa.demon.co.uk
I wanted to make a fully-automated nuclear-powered trawler,
but it went into spontaneous fishing.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Safety Std. for CCTV

2000-03-17 Thread WOODS

I have some additional information to add to the recent thread concerning if
EN60065 or EN60950 apply to CCTV equipment for security use. As I reported,
EN 50132-2-1, the performance standard for black and white CCTV cameras for
security use, has been published in the OJ under the LVD. I should have read
the standard in detail because the answer is there. Clause 4.14 says, The
camera shall comply with the EN60065 or EN60950 safety requirements. 

Richard Woods

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Re[2]: EMC, NEBS NRTL's

2000-03-17 Thread Jay Johansmeier



Thanks Eric.
If you read on you see that Bell Atlantic must give 'prior' approval for
'alternate' test facilities.
Jeffrey was asking for documentation from a lab that has this 'prior' approval
and at the moment
DLS is the only one, I haven't checked for others, that I know that have a
letter of approval.
I'm sure there are others.
My guess is that Jeffrey could ask the lab(s) in question to contact Bell
Atlantic to receive this type of prior approval.

Regards,

Jay Johansmeier
Regulatory Engineer
3Com Corporation
jay_johansme...@3com.com





Eric Petitpierre eric.petitpie...@pulse.com on 03/17/2000 07:55:00 AM

Sent by:  Eric Petitpierre eric.petitpie...@pulse.com


To:   emc-pstc @ieee.org emc-p...@ieee.org, Jay Johansmeier/MW/US/3Com
cc:
Subject:  Re[2]: EMC, NEBS  NRTL's



 Jeffey and Jay,

 Bell Atlantic  Specification RNSA-NEB-95-0003, Rev, 10 Issued January
 26,2000 has removed the NRTL requirement,( see sections 1.6.1 and
 3.1.2)

Regards,

Eric Petitpierre
Pulsecom
Herndon,VA
eric.petitpierre

__ Reply Separator _
Subject: RE: EMC, NEBS  NRTL's
Author:  jay_johansme...@mw.3com.com (Jay Johansmeier) at smtp
List-Post: emc-pstc@listserv.ieee.org
Date:3/17/00 7:49 AM


Jeffrey,

DLS, here in Illinois, claims to have a letter from Bell Atlantic stating that
their EMC data will be accepted.
You can email Steve Grimes at DLS and ask him if they will give you a copy. (
sgri...@dlsemc.com )

Regards,

Jay Johansmeier
Regulatory Engineer
3Com Corporation
jay_johansme...@3com.com





Collins, Jeffrey jcoll...@ciena.com on 03/17/2000 03:56:40 AM

Please respond to Collins, Jeffrey jcoll...@ciena.com

Sent by:  Collins, Jeffrey jcoll...@ciena.com


To:   'emc-pstc @ieee.org' emc-p...@ieee.org
cc:(Jay Johansmeier/MW/US/3Com)
Subject:  RE: EMC, NEBS  NRTL's




Group,


Can anyone confirm that the RBOC's, particularly Bell Atlantic has agreed to
accept EMC FCC data from non NRTL's?
If this is true please provide any documentation to support this. (You know
a customer is going to want to see it)


Thanks in advance,

Jeffrey Collins
MTS, Principal Compliance Engineer
Ciena Core Switching Division
jcoll...@ciena.com
www.ciena.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org







---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Component Supplier's Exhibition

2000-03-17 Thread Alan Weeks

Try the europe wide exhibition, Electronica 2000 in Munich. 21-24 Nov.

http://www.electronica.de/englisch/index.html

Alan
-Original Message-
From: Peter Merguerian pmerguer...@itl.co.il
To: emc-p...@majordomo.ieee.org emc-p...@majordomo.ieee.org
List-Post: emc-pstc@listserv.ieee.org
Date: 17 March 2000 10:59
Subject: Component Supplier's Exhibition



Hello Group,

Could someone lead me into the largest worldwide exhibitions for Component
Suppliers Exhibitions for Electrical and Electronic Equipment.

Thanks in Advance
Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il 






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Fwd:Isolations on inner layers

2000-03-17 Thread E Eszlari


Mihai,

In the past I have worked with many multilayer boards and have applied the 
following criteria:


1) Most PC boards are made up of multiple layers (prepreg). This has to be 
taken into consideration for traces on opposite layers of the board. In this 
case you cannot use the 0.4mm thickness requirement because it is not 1 
solid layer. I would suggest you contact the board vendor and request 
information on the build. You will usually receive a cut-away drawing of the 
board stating each material used and the thickness of the layers. You can 
use this information when referring to clause 2.9.4.3 in EN60950 in order to 
determine if it meets the requirements.


2) As for traces on inner layers of the board, I would consider it pollution 
degree 1 (sealed against moisture and dust) which will reduce the normal 
required spacing. Also, you may be able to reduce the spacing further if the 
board meets the requirements of clause 2.9.5.


Good luck

Edward Eszlari
Bose Corporation


From: jim_bac...@mail.monarch.com (Jim Bacher)
Reply-To: jim_bac...@mail.monarch.com (Jim Bacher)
To: emc-p...@ieee.org
CC: mih...@trenew.pcnet.ro
Subject: Fwd:Isolations on inner layers
Date: Fri, 17 Mar 2000 07:50:53 -0500


forwarding for mih...@trenew.pcnet.ro  ...  Jim

Forward Header_
Subject:Isolations on inner layers
Author: Mihai Vintila mih...@trenew.pcnet.ro
Date:   3/16/00 7:34 PM

Hello,

I have a question concerning isolations for hazardous voltages on 
inner

layers of a multilayer PCB.
The material is standard FR4.
I have read the EN60950 spec and it seems like for copper on 
different
inner layers an isolation of 0.4mm would be good enough. Now what I could 
not
figure is about traces on the same inner layer. In this case an isolation 
of 0.4

mm is as good as it is between different layers, or should I take into
consideration the manufacturing errors (impurities, air bubbles, a.s.o.) 
and

make a bigger isolation, but how much bigger?
The voltages I am working with are some of them TNV1 and others 
220VAC

(mains).

Many thanks,

Mihai


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org




__
Get Your Private, Free Email at http://www.hotmail.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Jim Bacher:  jim_bac...@mail.monarch.com
Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org



RE: EMC, NEBS NRTL's

2000-03-17 Thread Naftali Shani
Jeffrey, the requirement that was for NRTL lab ( Bellcore
representative) for each section of GR-63  GR-1089, has been dropped. See
section 3.1.2 in the BA-NEBS-R10.

However, FCC data/frequency range for radiated emissions is
insufficient: You should have data based on GR-1089 requirements 
objectives (10 kHz to 10 GHz).

Regards,
Naftali Shani, Nortel Networks, Dept. 0S45, MS 117/C1/M05
21 Richardson Side Road, Kanata, Ontario, Canada  K2K 2C1
Voice +1.613.765.2505 (ESN 395) Fax +1.613.763.8091 (ESN 393)
E-mail: nsh...@nortelnetworks.com mailto:nsh...@nortelnetworks.com
or n...@ieee.org mailto:n...@ieee.org 

-Original Message-
From:   Collins, Jeffrey [SMTP:jcoll...@ciena.com]
Sent:   Friday, March 17, 2000 4:57 AM
To: 'emc-p...@ieee.org'
Subject:RE: EMC, NEBS  NRTL's


Group,


Can anyone confirm that the RBOC's, particularly Bell
Atlantic has agreed to
accept EMC FCC data from non NRTL's?
If this is true please provide any documentation to support
this. (You know
a customer is going to want to see it)


Thanks in advance,

Jeffrey Collins 
MTS, Principal Compliance Engineer
Ciena Core Switching Division
jcoll...@ciena.com
www.ciena.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org




Re[2]: EMC, NEBS NRTL's

2000-03-17 Thread Eric Petitpierre

 Jeffey and Jay,
 
 Bell Atlantic  Specification RNSA-NEB-95-0003, Rev, 10 Issued January 
 26,2000 has removed the NRTL requirement,( see sections 1.6.1 and 
 3.1.2)

Regards,

Eric Petitpierre
Pulsecom
Herndon,VA
eric.petitpierre

__ Reply Separator _
Subject: RE: EMC, NEBS  NRTL's
Author:  jay_johansme...@mw.3com.com (Jay Johansmeier) at smtp
List-Post: emc-pstc@listserv.ieee.org
Date:3/17/00 7:49 AM


Jeffrey,
 
DLS, here in Illinois, claims to have a letter from Bell Atlantic stating that 
their EMC data will be accepted.
You can email Steve Grimes at DLS and ask him if they will give you a copy. ( 
sgri...@dlsemc.com )
 
Regards,
 
Jay Johansmeier
Regulatory Engineer
3Com Corporation
jay_johansme...@3com.com
 
 
 
 
 
Collins, Jeffrey jcoll...@ciena.com on 03/17/2000 03:56:40 AM
 
Please respond to Collins, Jeffrey jcoll...@ciena.com
 
Sent by:  Collins, Jeffrey jcoll...@ciena.com
 
 
To:   'emc-pstc @ieee.org' emc-p...@ieee.org 
cc:(Jay Johansmeier/MW/US/3Com)
Subject:  RE: EMC, NEBS  NRTL's
 
 
 
 
Group,
 
 
Can anyone confirm that the RBOC's, particularly Bell Atlantic has agreed to 
accept EMC FCC data from non NRTL's?
If this is true please provide any documentation to support this. (You know 
a customer is going to want to see it)
 
 
Thanks in advance,
 
Jeffrey Collins
MTS, Principal Compliance Engineer
Ciena Core Switching Division
jcoll...@ciena.com
www.ciena.com
 
 
---
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list.
 
To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc
 
For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com 
 Michael Garretson:pstc_ad...@garretson.org
 
For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 
 
 
 
 
 
 
---
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list.
 
To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc
 
For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com 
 Michael Garretson:pstc_ad...@garretson.org
 
For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re[2]: Spanish analog interface

2000-03-17 Thread Tony Reynolds

 All,
 
 ..and is this where all the problems are going to start!
 
 Regards
 
 Tony Reynolds
 Pitney Bowes Ltd
 
 NB This is not intended as a criticism of David Gelfand and/or his 
 company but just a comment on the implications of the RTTE Directive.


__ Reply Separator _
Subject: Re: Spanish analog interface 
Author:  David Gelfand gelf...@memotec.com at smtpgwy
List-Post: emc-pstc@listserv.ieee.org
Date:16/03/00 14:13


 
This is VERY interesting.  Am I naive, but does the RTTE directive mean that 
after April 8, 2000 we can export analog ITE equipment to Europe just based on 
safety, emc emissions and immunity testing alone?
 
Does this apply to CTR 2 and CTR12 as well?
 
Thank you,
 
David.
 
- Original Message -
From: Corinne SALINGRE corinne.salin...@cstelecom.com 
Subject: Re: Spanish analog interface
 
 
After april, 8th 2000 : analog telephone can access to EU market 
under RTTE Directive, which prescribes, for that equipment 
compliance against LVD and EMC directives only. Interworking with 
network is no longer essential requirement.
 
 
 
---
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list.
 
To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc
 
For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com 
 Michael Garretson:pstc_ad...@garretson.org
 
For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 
 
 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: SAF: Insulation resistance and hipot tests

2000-03-17 Thread D'Agostino Mark

Folks:

EN 60204-1 also specifies an insulation resistance test.
Depending on the standard, they tell you the sequence of the various safety
tests.
For example, in EN 60204-1, clause 19.1 (the test clause) states:
When these test are performed, it is recommended that they follow the
sequence listed.

For EN 60204-1, it is Ground continuity, then Insulation resistance, then
Hipot, then cap discharge.

I hope this helps.

At 01:21 PM 3/16/00 -0800, Bruce Touzel wrote:

Insulation resistance tests would apply only to IEC 950 I believe, so this
may
not apply for you ?

Art Michael wrote:

 Hello Martin,

 I don't have the answer to your question, but do caution that the First
 Test to be run (if the DUT is grounded) is the Ground Continuity Test (for
 test-operator protection).

 Regards, Art Michael

  * * * * * * * * * * * * * * * * * * * * * *
 *   International Product Safety Bookshop   *
 *  Check out our current offerings! *
 * http://www.safetylink.com/bookshop.html *
 *   *
 * Now offering BSI's Books  Reports*
 *  including, World Electricity Supplies  *
 *   *
 * Another service of the Safety Link*
 *  www.safetylink.com *
  * * * * * * * * * * * * * * * * * * * * * *
 --

 On Thu, 16 Mar 2000, Martin Rowe (TMW) wrote:

 
  Group,
 
  A reader asked about the order of performing safety tests.
  Should he perform insulation resistance tests before or after
  hipot tests? The reader didn't say what type of product he's
  testing, but I can ask.
 
  Thanks,
 
  /\
  | Martin Rowe  |   /  \
  | Senior Technical Editor  |  /\  /\
  | Test  Measurement World | /  \/  \/\  
  | voice 617-558-4426   |/\  /\  /  \/
  | fax 617-928-4426 |  \/  \/
  | e-mail m.r...@ieee.org   |   \  /
  | http://www.tmworld.com   |\/
  
 
 
  ---
  This message is from the IEEE EMC Society Product Safety
  Technical Committee emc-pstc discussion list.
 
  To cancel your subscription, send mail to:
   majord...@ieee.org
  with the single line:
   unsubscribe emc-pstc
 
  For help, send mail to the list administrators:
   Jim Bacher:  jim_bac...@mail.monarch.com
   Michael Garretson:pstc_ad...@garretson.org
 
  For policy questions, send mail to:
   Richard Nute:   ri...@ieee.org
 
 
 

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 
Mark A. D'Agostino
Sr. Product Safety Engineer
978 282 7520
978 281 3162 (fax)

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



What is Margin Testing

2000-03-17 Thread Scott Douglas

Hi All,

This may not be the right forum so if not, please point me in another
direction.

Question:  can anyone tell me what is Margin Testing as it is applied to
ATM, Frame Relay, Internet backbone type of equipment?

I do not have any more than that to go on right now. I do know some tiny bit
about the equipment but not about the question. Not sure if this is testing
of equipment at high and low line voltages/frequencies/environments or if
this has to do with % of capacity a given piece of equipment can handle
without errors or something entirely different.

Replies to me directly will avoid channel clutter and are much appreciated.

Scott
s_doug...@ecrm.com
ECRM Incorporated
Tewksbury, MA  USA



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: EMC, NEBS NRTL's

2000-03-17 Thread John Juhasz
You have to be careful here Jeff. The frequency range for evaluation to
GR-1089 starts at 150kHz and goes up to 10 GHz. The FCC Part 15 testing
range is from 30MHz-1.0GHz. 
The GR-1089 spec also contains Immunity requirements. 
Further, the objective is to meet the spec with all covers, panels, doors
off/open which is
not typically done during FCC testing. 
Additionally, look at it from this perspective: If an RBOC is going to be
reviewing
proposals, if there are two similar products competing, they will choose the
one that
meets the details of the NEBS spec, than the one that took steps to 'look
like' they meet NEBS,
even if the product costs more. 
The RBOCs are a different breed than the usual commercial customer. 

John Juhasz
Fiber Options
Bohemia, NY

-Original Message-
From: Collins, Jeffrey [mailto:jcoll...@ciena.com]
Sent: Friday, March 17, 2000 4:57 AM
To: 'emc-p...@ieee.org'
Subject: RE: EMC, NEBS  NRTL's



Group,


Can anyone confirm that the RBOC's, particularly Bell Atlantic has agreed to
accept EMC FCC data from non NRTL's?
If this is true please provide any documentation to support this. (You know
a customer is going to want to see it)


Thanks in advance,

Jeffrey Collins 
MTS, Principal Compliance Engineer
Ciena Core Switching Division
jcoll...@ciena.com
www.ciena.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Fwd:Isolations on inner layers

2000-03-17 Thread Jim Bacher

forwarding for mih...@trenew.pcnet.ro  ...  Jim

Forward Header_
Subject:Isolations on inner layers
Author: Mihai Vintila mih...@trenew.pcnet.ro
List-Post: emc-pstc@listserv.ieee.org
Date:   3/16/00 7:34 PM

Hello,

I have a question concerning isolations for hazardous voltages on inner
layers of a multilayer PCB.
The material is standard FR4.
I have read the EN60950 spec and it seems like for copper on different
inner layers an isolation of 0.4mm would be good enough. Now what I could not
figure is about traces on the same inner layer. In this case an isolation of 0.4
mm is as good as it is between different layers, or should I take into
consideration the manufacturing errors (impurities, air bubbles, a.s.o.) and
make a bigger isolation, but how much bigger?
The voltages I am working with are some of them TNV1 and others 220VAC
(mains).

Many thanks,

Mihai


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: EMC, NEBS NRTL's

2000-03-17 Thread Jay Johansmeier



Jeffrey,

DLS, here in Illinois, claims to have a letter from Bell Atlantic stating that
their EMC data will be accepted.
You can email Steve Grimes at DLS and ask him if they will give you a copy. (
sgri...@dlsemc.com )

Regards,

Jay Johansmeier
Regulatory Engineer
3Com Corporation
jay_johansme...@3com.com





Collins, Jeffrey jcoll...@ciena.com on 03/17/2000 03:56:40 AM

Please respond to Collins, Jeffrey jcoll...@ciena.com

Sent by:  Collins, Jeffrey jcoll...@ciena.com


To:   'emc-pstc @ieee.org' emc-p...@ieee.org
cc:(Jay Johansmeier/MW/US/3Com)
Subject:  RE: EMC, NEBS  NRTL's




Group,


Can anyone confirm that the RBOC's, particularly Bell Atlantic has agreed to
accept EMC FCC data from non NRTL's?
If this is true please provide any documentation to support this. (You know
a customer is going to want to see it)


Thanks in advance,

Jeffrey Collins
MTS, Principal Compliance Engineer
Ciena Core Switching Division
jcoll...@ciena.com
www.ciena.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org







---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Fwd:Re: Mexico Regulatory Requirements

2000-03-17 Thread Jim Bacher

forwarded for Doug  ...  Jim

Forward Header_
Subject:Re: Mexico Regulatory Requirements
Author: Doug McKean dmck...@corp.auspex.com
List-Post: emc-pstc@listserv.ieee.org
Date:   3/16/00 5:27 PM

Last I heard: 

1. You must get the testing completed in Mexico.  

2. And you must get someone with a Mexican tax ID 
   to sign for your product. I.e. distributor, sales rep. 

3. Translate everything into Mexican Spanish. 
   Not Castilian Spanish. 

4. Only one place that I knew of at the time for the 
   testing and approval was in Mexico City. 

Little dated on this info. 
Verify with 2nd source. 

Regards, Doug McKean 

Lubeski, Paul wrote:
 
 Dear List members:
 
 Can anyone provide the Product Safety and Industry/Regulatory Network
 requirements and approval authority contact(s) for Mexico?
 
 Thank you.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Component Supplier's Exhibition

2000-03-17 Thread James, Chris

Nepcon UK 4-6 April, NEC Birmingham, UK

www.nepcon.co.uk

-Original Message-
From: pmerguer...@itl.co.il [mailto:pmerguer...@itl.co.il]
Sent: Friday, March 17, 2000 9:20 AM
To: emc-p...@majordomo.ieee.org
Subject: Component Supplier's Exhibition



Hello Group,

Could someone lead me into the largest worldwide exhibitions for Component
Suppliers Exhibitions for Electrical and Electronic Equipment.

Thanks in Advance
Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il 






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: EMC/PSTC/NEBS/TREG

2000-03-17 Thread Jerry Roberton

If you put TREG into it I'm off.

Jerry Roberton
NET Europe Ltd



Peter Merguerian wrote:

 Dear All,

 DO NOT SPLIT! I AM ALSO IN FAVOR OF MIGRATING TREG AND NEBS GROUPS INTO TO
 THE EMC/PSTC LIST. ARE YOU ALL IN FAVOR?
 Peter Merguerian
 Managing Director
 Product Testing Division
 I.T.L. (Product Testing) Ltd.
 Hacharoshet 26, POB 211
 Or Yehuda 60251, Israel

 Tel: 972-3-5339022 Fax: 972-3-5339019
 e-mail: pmerguer...@itl.co.il
 website: http://www.itl.co.il

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: EMC, NEBS NRTL's

2000-03-17 Thread Collins, Jeffrey

Group,


Can anyone confirm that the RBOC's, particularly Bell Atlantic has agreed to
accept EMC FCC data from non NRTL's?
If this is true please provide any documentation to support this. (You know
a customer is going to want to see it)


Thanks in advance,

Jeffrey Collins 
MTS, Principal Compliance Engineer
Ciena Core Switching Division
jcoll...@ciena.com
www.ciena.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Component Supplier's Exhibition

2000-03-17 Thread Peter Merguerian

Hello Group,

Could someone lead me into the largest worldwide exhibitions for Component
Suppliers Exhibitions for Electrical and Electronic Equipment.

Thanks in Advance
Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il 






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



EMC/PSTC/NEBS/TREG

2000-03-17 Thread Peter Merguerian

Dear All,

DO NOT SPLIT! I AM ALSO IN FAVOR OF MIGRATING TREG AND NEBS GROUPS INTO TO
THE EMC/PSTC LIST. ARE YOU ALL IN FAVOR?
Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il 






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: standard for lead shot dielectric testing

2000-03-17 Thread volker . gasse



Hello Barry,

you might check IEC 60851-5 (Test methods for winding wires) where Clause
4, (Test 13) uses the metal shot when determining breakdown voltages of a
twisted winding wire.
This test is also referenced in IEC 60950 Annex U.2.1.

mit freundlichen Gruessen/ best regards
Volker Gasse

IBM Germany, Technical Relations/Product Safety,
Tel: +49-7031-642-6796, Fax: -6916, e-mail: volker.ga...@de.ibm.com
Mail:  D3114/7103-91, D-70548 Stuttgart, Germany


barrym bar...@spaceship.com on 16.03.2000 22:26:37

Please respond to barrym bar...@spaceship.com





I'm looking for reference to any standard which may provide specifics for
using lead shot for dielectric strength testing.  I know this done for
insulation system qualifications, just have not identified a standard for
the test set up.

Thanks,
Barry Marks






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: standard for lead shot dielectric testing

2000-03-17 Thread Peter Merguerian

Barry,

In my old days working for UL, we used lead shot to test the dielectric
strength properties of insulated wire connectors. I suggest you take a look
at the wire connector standards UL486 Series.



At 15:26 16/03/2000 -0600, barrym wrote:

I'm looking for reference to any standard which may provide specifics for
using lead shot for dielectric strength testing.  I know this done for
insulation system qualifications, just have not identified a standard for
the test set up.

Thanks,
Barry Marks


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il 






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Agilent Technologies Safety position (medical)

2000-03-17 Thread OSBORN,DAVE (A-Andover,ex1)

Agilent Technologies Health Care Solutions Group has an opening for a
Regulatory Engineer to work in our safety test lab.  


For a keen position as a Senior Quality Engineer, Regulatory Engineering,
Medical Product Safety

Access the URL: http://www.agilent.com/
Select Jobs
Select Search
Select Job Search
In the Keywords or Job Number field, enter: 666593
Select Submit Search, and the job posting should appear

---
Additionally, here is a summary of the position:

Job Description 
The Regulatory Engineer works in the Andover Safety Test Lab. Based on
knowledge of device safety standards and experience with related testing,
the Regulatory Engineer works independently, but within the general
oversight of the Safety Test Lab Team Leader. The Engineer meets with
product development teams, advises on product requirements and designs,
plans and schedules tests, performs tests, documents results, and works with
external agencies to obtain timely compliance reports and certifications.
From time to time, the Regulatory Engineer works with Manufacturing
Engineering to ensure products continue to be manufactured in compliance
with the standards. The primary safety standards are the IEC 60601 medical
device family and the IEC 950 information technology safety standard.
The Regulatory Engineer also works as the Medical Device Safety Topic
Expert. This individual represents Agilent Technologies as a member of one
or more international safety committees. 
 

If you have additional questions, let me know.

Best regards,
Dave Osborn 
Chairman, Boston Section, IEEE
+1 781 862 7116
dosb...@agilent.com
Agilent Technologies

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Mexico Regulatory Requirements

2000-03-17 Thread Doug McKean
Last I heard: 

1. You must get the testing completed in Mexico.  

2. And you must get someone with a Mexican tax ID 
   to sign for your product. I.e. distributor, sales rep. 

3. Translate everything into Mexican Spanish. 
   Not Castilian Spanish. 

4. Only one place that I knew of at the time for the 
   testing and approval was in Mexico City. 

Little dated on this info. 
Verify with 2nd source. 

Regards, Doug McKean 

Lubeski, Paul wrote:
 
 Dear List members:
 
 Can anyone provide the Product Safety and Industry/Regulatory Network
 requirements and approval authority contact(s) for Mexico?
 
 Thank you.