Re: Wiring under raised floors

2000-09-21 Thread Doug

ted.eck...@apcc.com wrote:
 
 Is it permissible to place electrical receptacles under the raised floor of
 a computer room?  Can power cords pass through openings in the raised floor
 or do all power connections need to be in conduit?  I have received two
 opinions; one stating that receptacles must be accessible above floor level
 and the other stating that receptacles can be placed below the floor.
 
 The United States National Electrical Code is a bit vague on the subject,
 although Article 645-5 (d) (2) seems to imply that conduit is only required
 up to the receptacle.  I can find no references to raised floor
 installations in the Canadian Electrical Code or BS 7671, IEE Wiring
 Regulations.


Ted, 

In order that your company NEVER have any problems with 
this issue ever, you will have to follow NEC 645-5 to 
the letter.  Ultimately, it's up to the interpretation 
of the local inspector. 

Having been called on the rug about this very issue from 
just one customer within the past year, my *suggestion* is: 
Do NOT put ANY power cords under a raised floor no matter 
if it's a plenum issue or not and no matter how long or 
short that power cord may be - none.  

Unless of course you can procure the style power cord 
required by the standard.  And good luck with that. 

- Regards, Doug McKean

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: compactPCI bus

2000-09-21 Thread Doug

Fleury, Bill wrote:
 
 Judging from the number of responses (0) I got to my question about EMI
 problems from compactPCI backplanes I am assumiong that either no one uses
 cPCI backplanes or I'm the only one that has experienced problems when
 testing in this environment. I didn't think that ever happened in this
 group. I'll repost this just in case some of you didn't get the last one.
 
 This is a question regarding systems which use CompactPCI bus architecture.
 On a cPCI backplane the PCI clock is routed to every slot on the backplane
 with up to 7 peripheral slots possible on a normal backplane. My question is
 this: With the cPCI specification calling out specific trace lengths for
 clock traces on both the backplane itself and on peripheral cards, have
 other people experienced any unique EMI problems in trying to meet the
 design constraints associated with this synchronous bus; especially where
 there are unpopulated slots on the backplane?
 
 Please feel free to respond privately if the question is unclear. I wasn't
 sure if it was worded properly.

I didn't catch your former post.  

As the PCI bus is a reflective based bus, in my opinion, 
the PCI bus is one of the worst bus constructions ever 
imagined.  I've had the pleasant experience of trying 
to cope with 132 MHz all over the damn place.  For a 
33 MHz based bus, yes, I'm talking 4th harmonics.  
Harmonics can abound above that was well.  Remember 
that odd harmonics are only produced by a perfect 
square wave.  Any asymmetry to a square wave starts 
including even harmonics.  Add in some fast edge 
rates adding to a bandwidth out to approx (0.35/Tr) 
depending upon who you talk to and you've got a 
potential rats nest. 

Grounding the face plates of interface cards to the 
chassis is especially tricky.  If your box is using 
regular style interface card sheet metal construction 
that you would find on the back of any regular PC, 
then you will have to make special care to inspect 
the vertical rails that are supposed to be in contact 
with the face plates.  I know that's a mouthful, but 
I hope you understand what I'm trying to say. 

I've had to deal with a weird slot effect under some 
circumstances with such a construction.  A voltage 
differential across the slot causes the slot effect 
to radiate onto the cable making the cable *appear* 
to be culprit.  In my case, even though the cable 
was the *radiator*, it's not the source of the 
problem. 

By simply trying to add a ferrite AND discovering 
that the ferrite does little to solve the problem, 
therein lies the hint that this slot effect is, well, 
in effect and doing fine to make your life difficult.  
Anywhere from about 6 to 10 dB of attenuation can be 
had with a gasket.  I can only reiterate and fully 
agree with Mr. Cortland's comment regarding the 
grounding provided by the chassis slot. 

Bottom line, make sure your signal integrity 
guys know what they're doing from an emi 
viewpoint before you even start and make sure 
to gain a close association with some unsung 
heroes in the mechanical department. You just 
may be needing them. 

There.  That's a total of about $10,000 worth of 
advice, experience, theory, pain, and solution. 
I expect my check in the mail by tomorrow ... 
(just joking ...) 

Regards and have fun, Doug McKean

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Component Qualification

2000-09-21 Thread Ralph Cameron

Tony:

I have sold these systems and also used them and they are good for graphing
a profile of a scanned board and giving the field intensity vs postion over
the board area. You can quickly find trouble spots using the computer
interface.

Ralph Cameron

- Original Message -
From: Tony J. O'Hara tonyoh...@compuserve.com
To: Koh Nai Ghee koh...@cyberway.com.sg
Cc: EMC-PSTC emc-p...@majordomo.ieee.org
Sent: Wednesday, September 20, 2000 4:42 PM
Subject: Re: Component Qualification



 You may want to look at using a PCB Electromagnetic Scanning System!  One
 of the advertised uses for these test devices is for quickly comparing EMC
 performance when component changes are made etc.! I believe there are 4
 different manufacturers who make these devices. The one that I'm just
 starting to learn about is made by EMSCAN in Canada. Their web is
 www.emscan.com
 Maybe someone who has  uses one of these scanners can provide an
 experienced viewpoint?
 Regards
 Tony
 Colorado

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Data on Power Lines

2000-09-21 Thread Peter Merguerian

Dear All,

For a unit that transmits and/or recieves data over mains power lines, is
UL1950/IEC950 the correct standard?


Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il 

TO LEARN ABOUT AUSTRALIAN AND NEW ZEALAND REQUIREMENTS, CONTACT ME AT THE
EARLIEST STAGES OF YOUR DESIGN; REQUIREMENTS CAN BE TRICKY!






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Data on Power Lines

2000-09-21 Thread georgea

Peter,

The Scope (1.1) of IEC 60950 is for mains or battery powered ITE.
If the product is mains/battery powered, then IEC 60950 could apply,
regardless of how it performs it's ITE function.  However, there may also
be other applicable standards.

George

-- Forwarded by George Alspaugh/Lex/Lexmark on 09/21/2000
07:34 AM ---

pmerguerian%itl.co...@interlock.lexmark.com on 09/21/2000 06:52:43 AM

Please respond to pmerguerian%itl.co...@interlock.lexmark.com

To:   emc-pstc%majordomo.ieee@interlock.lexmark.com
cc:(bcc: George Alspaugh/Lex/Lexmark)
Subject:  Data on Power Lines




Dear All,

For a unit that transmits and/or recieves data over mains power lines, is
UL1950/IEC950 the correct standard?


Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il









---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: DSSS document on FCC website?

2000-09-21 Thread Wismer, Sam

Hi Paul,
Try FCC 97-114 Appendix C.  It is entitled Guidance on Measurements for
Direct Sequence Spread Spectrum Systems.  I think this is what you're
after.

Good Luck!


~
Sam Wismer
RF Approvals Engineer
LXE, Inc.
(770) 447-4224 Ext. 3654

Visit Our Website at:
http://www.lxe.com



-Original Message-
From: Paul Slavens [mailto:paul_slav...@hotmail.com]
Sent: Wednesday, September 20, 2000 5:22 PM
To: emc-p...@ieee.org
Subject: DSSS document on FCC website?



Dear Group,

I was able find DA 00-705 - Filing and Measurement Guidelines for Frequency

Hopping Spread Spectrum Systems on the FCC web site.  I am pretty sure a 
comparable document exists for Direct Sequence Spread Spectrum Systems, 
however, I was unable to find it.  I sure would appreciate it if any of you 
fine persons could point me in the right direction.

Regards

Paul G. Slavens
Acme Testing

_
Get Your Private, Free E-mail from MSN Hotmail at http://www.hotmail.com.

Share information about yourself, create your own public profile at 
http://profiles.msn.com.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Component Qualification

2000-09-21 Thread Maxwell, Chris

Wait a minute!

Buying a board scanning system to evaluate different vendors for ferrites
and oscillators?  My company doesn't have that kind of money to throw
around.  These systems can cost 10's of thousands of dollars.   Ferrite
beads cost about a dime for a dump truck load.  If it costs $10,000 to
evaluate a second source for ferrites, I 'll stick with the ferrites I have.
I'd like to offer a lower cost alternative.

Koh Nai asked about what specifications were important for qualifying
alternate sources for ferrites and oscillators.

When it comes to ferrites, I look at three things:  I look at the PCB
footprint (it won't work if it won't fit).  I look at the impedance curve
and the current capacity.  If all three of these specifications are equal or
better than what I need, I accept them.  I don't even consider re-testing
for emissions if I have checked these three specifications.  Alternate
sources for ferrites can be qualified for the cost of reading a spec sheet.

Oscillators are a different story.  When one of my digital design colleagues
wants to change oscillators.  They consider its PCB footprint, the output
frequency, its ambient stability, its temperature stability and its load
driving capability.  If it meets their needs; then I take a circuitboard
with the existing oscillator and run a near field probe over it near the
oscillator until if find a location of maximum near field emissions.  (If
you really are strapped for cash, you can make your own near field probe.)
I write down the exact position and orientation of the near field probe and
I either print out or write down the spectrum analyzer readings.  I then put
the new oscillator on the exact same board and repeat the experiment.  If
the measurements are close (within a dB or two) I don't worry.  If the
measurements are more than  4 dB higher, then I look further. Then I
consider:  testing the whole unit with the new oscillator with my antenna
set up 1 meter away  in-house, or re-testing the unit for emissions at an
OATS, or not using the new oscillator.  

ONE WARNING:  if the new oscillator is at a different frequency, then the
method above WILL NOT yield any useful results.

One thing that we have done with new designs is to put a 1206 surface mount
PCB footprint in line with the oscillator output.  We start our testing with
a 0 ohm resistor.  If we run into problems, we can put either a ferrite bead
or higher value resistor in this position to cool off the oscillator.
This has worked well with oscillators under 100MHz. I don't know if it will
work for faster oscillator.  

I know that there are problems with using near field probes to make such
correlations, however using a board scanning device would cost much more
than a near field probe and still only be measuring near fields.  Even so,
if I had the budget, I'd love to try one out.

To me, the real method of doing this starts with the initial testing of your
product.  I try to get more than a 5dB margin during the initial testing.
With these margins, I don't need to worry so much about component
differences.  I know that this is sometimes not possible.  I have sacrificed
margins in order to get a product's testing done and released (I don't get
paid if we don't ship.)  The problem is, without margins, I need to worry
more about component differences.

Another point to remember is that EN 55022 and other emissions standards go
by the 80 % rule.  A product passes if  we are  confident that 80% of
the units that we ship meet the emissions requirements.  Anybody who wants
to dispute whether your units pass or not is REQUIRED to test up to 7
samples in order to get enough data to use statistical methods to compute
the confidence factor.  One failing unit does not equal a guilty verdict.
(Of course, if one unit is failing by 20dB, that's a problem.)  The people
at CISPR put this slack into the limits to allow for slight component
differences and measurement uncertainty.   They allowed us the slack, but it
is our responsibility to use it with common sense.

These are my two cents worth and definitely don't reflect the opinions of my
employer.  (Why would they need me if I thought the same way they do?) 

Have a great day!

Chris Maxwell, Design Engineer
GN Nettest Optical Division
6 Rhoads Drive, Building 4  
Utica, NY 13502
PH:  315-797-4449
FAX:  315-797-8024
EMAIL:  chr...@gnlp.com





 -Original Message-
 From: Ralph Cameron [SMTP:ral...@igs.net]
 Sent: Wednesday, September 20, 2000 11:16 PM
 To:   Tony J. O'Hara; Koh Nai Ghee
 Cc:   EMC-PSTC
 Subject:  Re: Component Qualification
 
 
 Tony:
 
 I have sold these systems and also used them and they are good for
 graphing
 a profile of a scanned board and giving the field intensity vs postion
 over
 the board area. You can quickly find trouble spots using the computer
 interface.
 
 Ralph Cameron
 
 - Original Message -
 From: Tony J. O'Hara tonyoh...@compuserve.com
 To: Koh Nai Ghee koh...@cyberway.com.sg
 Cc: 

Re:Protection or Control?

2000-09-21 Thread georgea

Luiz,

The applicable standards would depend on the product, e.g. whether it is
a laser printer (ITE) with the necessary fuser, or a hair dryer, or a coffee
maker.  However, it is my understanding that most products involving heating
devices would require two components, i.e. a temperature controlling device
(thermostat) and a fail-safe device (thermal fuse).

ITE standards require safety after any single fault.  If the control device
fails in a shorted mode, what prevents the heating element from melting the
product and potentially starting an external fire?

At least for ITE, a bimetal thermostat would not also serve as the protection
device unless there is no possible way to fail in the shorted mode.

George

 Forwarded by George Alspaugh/Lex/Lexmark on 09/21/2000 08:45 AM
---

jim_bacher%mail.monarch@interlock.lexmark.com on 09/21/2000 10:46:00 AM

Please respond to jim_bacher%mail.monarch@interlock.lexmark.com

To:   luizbonilla%ig.com...@interlock.lexmark.com,
  emc-pstc%majordomo.ieee@interlock.lexmark.com
cc:(bcc: George Alspaugh/Lex/Lexmark)
Subject:  Re:Protection or Control?




forwarding for luizboni...@ig.com.br

Reply Separator
Subject:Protection or Control?
Author: Luiz Claudio luizboni...@ig.com.br
List-Post: emc-pstc@listserv.ieee.org
Date:   9/20/00 9:59 PM

I have a question to those who are familiar with the safety requirements
established electrical appliance standards.

A bimetal thermostat is usuallly used to control the temperature of a certain
ambient within certain limits. Can it also be considered as a protection device?
I'm not going to give my oppinion to avoid any possibility of biased answers.
But, please, give your oppinion.
If you have a reference publication which I could use as a reference for a work
to be presented, please include it in your answer. If not, no problem. Just give
your oppinion.

Please answer this message to my personal email address: luizboni...@ig.com.br

Thanks a lot,

Luiz





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: DSSS document on FCC website?

2000-09-21 Thread Bronaugh, Edwin

Paul, the DSSS version of the document was published as Appendix C to the
original final rule-making in FCC ET Docket 96-8.  EdB

-Original Message-
From: Paul Slavens [mailto:paul_slav...@hotmail.com]
Sent: Wednesday, September 20, 2000 4:22 PM
To: emc-p...@ieee.org
Subject: DSSS document on FCC website?



Dear Group,

I was able find DA 00-705 - Filing and Measurement Guidelines for Frequency

Hopping Spread Spectrum Systems on the FCC web site.  I am pretty sure a 
comparable document exists for Direct Sequence Spread Spectrum Systems, 
however, I was unable to find it.  I sure would appreciate it if any of you 
fine persons could point me in the right direction.

Regards

Paul G. Slavens
Acme Testing

_
Get Your Private, Free E-mail from MSN Hotmail at http://www.hotmail.com.

Share information about yourself, create your own public profile at 
http://profiles.msn.com.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Protection or Control?

2000-09-21 Thread Colgan, Chris

Depends.  If the thermal cut out fails, can the product reach unsafe
temperatures?  If yes then it is a protective device, if no then it isn't.

A standard that covers thermal cut outs is IEC60730.  Thermal links are
covered by IEC60691.

Regards

Chris Colgan
EMC  Safety
TAG McLaren Audio Ltd

mailto:chris.col...@tagmclarenaudio.com


 -Original Message-
 From: jim_bac...@mail.monarch.com [SMTP:jim_bac...@mail.monarch.com]
 Sent: 21 September 2000 15:46
 To:   Luiz Claudio; 'emc-pstc'
 Subject:  Re:Protection or Control?
 
 
 forwarding for luizboni...@ig.com.br
 
 Reply Separator
 Subject:Protection or Control?
 Author: Luiz Claudio luizboni...@ig.com.br
 Date:   9/20/00 9:59 PM
 
 I have a question to those who are familiar with the safety requirements
 established electrical appliance standards.
 
 A bimetal thermostat is usuallly used to control the temperature of a
 certain
 ambient within certain limits. Can it also be considered as a protection
 device?
 I'm not going to give my oppinion to avoid any possibility of biased
 answers.
 But, please, give your oppinion.
 If you have a reference publication which I could use as a reference for a
 work
 to be presented, please include it in your answer. If not, no problem.
 Just give
 your oppinion.
 
 Please answer this message to my personal email address:
 luizboni...@ig.com.br
 
 Thanks a lot,
 
 Luiz
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
 
=
Authorised on 09/21/00 at 14:03:31; code 37f48bf3385FBE9E.


**  
   Please visit us at www.tagmclarenaudio.com
**

The contents of this E-mail are confidential and for the exclusive
use of the intended recipient. If you receive this E-mail in error,
please delete it from your system immediately and notify us either
by E-mail, telephone or fax. You  should not  copy, forward or 
otherwise disclose the content of the E-mail.

TAG McLaren Audio Ltd
The Summit, 11 Latham Road
Huntingdon, Cambs, PE29 6ZU
Telephone : 01480 415600 (+44 1480 415600)
Facsimile : 01480 52159 (+44 1480 52159)

**  
   Please visit us at www.tagmclarenaudio.com
**

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Component Qualification

2000-09-21 Thread Ralph Cameron

Chris,

Don't get me wrong. I didn't read the full text of the application and
merely supported the utility of the EMSCAN system.

If you know of sources where you cn get ferrites, specifically ferrite
toroids for a dime a dump truck, I'd be interested. In the past two years my
costs for them have more than tripled as the mfr now uses dealers who have
minu\imum quantities which are out of sight for the small vendor. With the
heavier weights , shipping costs skyrocket.

I like your methods of determining ferrite application and how to look for
hpt spots.

 My opinions are my own since I work for me.

regards

Ralph Cameron
EMC Consultant and Suppression of Consumer Elecronics
(after sale).
- Original Message -
From: Maxwell, Chris chr...@gnlp.com
To: 'Ralph Cameron' ral...@igs.net; Tony J. O'Hara
tonyoh...@compuserve.com; Koh Nai Ghee koh...@cyberway.com.sg
Cc: EMC-PSTC emc-p...@majordomo.ieee.org
Sent: Thursday, September 21, 2000 7:58 AM
Subject: RE: Component Qualification


 Wait a minute!

 Buying a board scanning system to evaluate different vendors for ferrites
 and oscillators?  My company doesn't have that kind of money to throw
 around.  These systems can cost 10's of thousands of dollars.   Ferrite
 beads cost about a dime for a dump truck load.  If it costs $10,000 to
 evaluate a second source for ferrites, I 'll stick with the ferrites I
have.
 I'd like to offer a lower cost alternative.

 Koh Nai asked about what specifications were important for qualifying
 alternate sources for ferrites and oscillators.

 When it comes to ferrites, I look at three things:  I look at the PCB
 footprint (it won't work if it won't fit).  I look at the impedance curve
 and the current capacity.  If all three of these specifications are equal
or
 better than what I need, I accept them.  I don't even consider re-testing
 for emissions if I have checked these three specifications.  Alternate
 sources for ferrites can be qualified for the cost of reading a spec
sheet.

 Oscillators are a different story.  When one of my digital design
colleagues
 wants to change oscillators.  They consider its PCB footprint, the output
 frequency, its ambient stability, its temperature stability and its load
 driving capability.  If it meets their needs; then I take a circuitboard
 with the existing oscillator and run a near field probe over it near the
 oscillator until if find a location of maximum near field emissions.  (If
 you really are strapped for cash, you can make your own near field probe.)
 I write down the exact position and orientation of the near field probe
and
 I either print out or write down the spectrum analyzer readings.  I then
put
 the new oscillator on the exact same board and repeat the experiment.  If
 the measurements are close (within a dB or two) I don't worry.  If the
 measurements are more than  4 dB higher, then I look further. Then I
 consider:  testing the whole unit with the new oscillator with my antenna
 set up 1 meter away  in-house, or re-testing the unit for emissions at an
 OATS, or not using the new oscillator.

 ONE WARNING:  if the new oscillator is at a different frequency, then the
 method above WILL NOT yield any useful results.

 One thing that we have done with new designs is to put a 1206 surface
mount
 PCB footprint in line with the oscillator output.  We start our testing
with
 a 0 ohm resistor.  If we run into problems, we can put either a ferrite
bead
 or higher value resistor in this position to cool off the oscillator.
 This has worked well with oscillators under 100MHz. I don't know if it
will
 work for faster oscillator.

 I know that there are problems with using near field probes to make such
 correlations, however using a board scanning device would cost much more
 than a near field probe and still only be measuring near fields.  Even so,
 if I had the budget, I'd love to try one out.

 To me, the real method of doing this starts with the initial testing of
your
 product.  I try to get more than a 5dB margin during the initial testing.
 With these margins, I don't need to worry so much about component
 differences.  I know that this is sometimes not possible.  I have
sacrificed
 margins in order to get a product's testing done and released (I don't get
 paid if we don't ship.)  The problem is, without margins, I need to worry
 more about component differences.

 Another point to remember is that EN 55022 and other emissions standards
go
 by the 80 % rule.  A product passes if  we are  confident that 80% of
 the units that we ship meet the emissions requirements.  Anybody who wants
 to dispute whether your units pass or not is REQUIRED to test up to 7
 samples in order to get enough data to use statistical methods to compute
 the confidence factor.  One failing unit does not equal a guilty verdict.
 (Of course, if one unit is failing by 20dB, that's a problem.)  The people
 at CISPR put this slack into the limits to allow for slight component
 differences and 

Sept. 15, 2000 Conformity-Update Now Available

2000-09-21 Thread Glen Dash

Conformity-Update for the week ending Sept. 15, 2000 is now available
at:

http://www.conformity-update.com

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Protection or Control?

2000-09-21 Thread Peter Tarver
Luiz -

Bimetal switched are used as manual and automatic reset thermal protectors
in electric motors, transformers.  Very common and has been for many years.

Regards,

Peter L. Tarver, PE
ptar...@nortelnetworks.com


-Original Message-
From: jim_bac...@mail.monarch.com [mailto:jim_bac...@mail.monarch.com]
Sent: Thursday, September 21, 2000 3:46 PM
To: Luiz Claudio; 'emc-pstc'
Subject: Re:Protection or Control?



forwarding for luizboni...@ig.com.br

Reply Separator
Subject:Protection or Control?
Author: Luiz Claudio luizboni...@ig.com.br
List-Post: emc-pstc@listserv.ieee.org
Date:   9/20/00 9:59 PM

I have a question to those who are familiar with the safety requirements
established electrical appliance standards.

A bimetal thermostat is usuallly used to control the temperature of a
certain
ambient within certain limits. Can it also be considered as a protection
device?
I'm not going to give my oppinion to avoid any possibility of biased
answers.
But, please, give your oppinion.
If you have a reference publication which I could use as a reference for a
work
to be presented, please include it in your answer. If not, no problem. Just
give
your oppinion.

Please answer this message to my personal email address:
luizboni...@ig.com.br

Thanks a lot,

Luiz


Re:Protection or Control?

2000-09-21 Thread Ted . Eckert


Many of the cheap thermal circuit breakers listed under UL 1077
(Supplementary Protectors For Use In Electronic Equipment) are nothing more
than a bimetallic strip.  Current is carried through the bimetallic strip
itself.  As the current increases, the strip heats up and eventually opens
the contacts.  The circuit breakers do have a spring loaded barrier that
moves between the contacts after they open.  This prevents the circuit
breaker from resetting automatically and prevents arcing.  For limiting
current, a recognized circuit breaker should be used.

In addition, UL 1950 section 1.7.13 refers to thermostats.  The standard
allows the thermostat to limit temperature, but they should not be used for
other purposes.

Ted Eckert
Regulatory Compliance Engineer
American Power Conversion Corporation
ted.eck...@apcc.com

The items contained in this e-mail reflect the personal opinions of the
writer and are only provided for the assistance of the reader.  The writer
is not speaking in an official capacity for APC nor representing APC's
official position on any matter.




Jim_Bacher@mail.m   

onarch.com (Jim  To: Luiz Claudio 
luizboni...@ig.com.br, 'emc-pstc'   
Bacher)  emc-p...@majordomo.ieee.org  

Sent by: cc:

owner-emc-pstc@ieSubject: Re:Protection or 
Control? 
ee.org  





09/21/00 09:46 AM   

Please respond to   

Jim_Bacher  










forwarding for luizboni...@ig.com.br

Reply Separator
Subject:Protection or Control?
Author: Luiz Claudio luizboni...@ig.com.br
List-Post: emc-pstc@listserv.ieee.org
Date:   9/20/00 9:59 PM

I have a question to those who are familiar with the safety requirements
established electrical appliance standards.

A bimetal thermostat is usuallly used to control the temperature of a
certain
ambient within certain limits. Can it also be considered as a protection
device?
I'm not going to give my oppinion to avoid any possibility of biased
answers.
But, please, give your oppinion.
If you have a reference publication which I could use as a reference for a
work
to be presented, please include it in your answer. If not, no problem. Just
give
your oppinion.

Please answer this message to my personal email address:
luizboni...@ig.com.br

Thanks a lot,

Luiz

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



ESD Opportunities

2000-09-21 Thread Kimberly Leddy


I am doing a graduate research project on the ESD opportunities that exist 
in the telecom market, specifically cell phones and laptops that have LCD's 
which are affected by ESD. Is this a market to look into, and what are the 
requirements and trends that you see going on? What materials or solutions 
are currently being used to address ESD problems in these systems, and are 
they they working?  Lastly, is ESD a factor that is considered when 
designing EMI shielding solutions?


I would appreciate any insight you may have. Thanks!
kl
_
Get Your Private, Free E-mail from MSN Hotmail at http://www.hotmail.com.

Share information about yourself, create your own public profile at 
http://profiles.msn.com.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Jim Bacher:  jim_bac...@mail.monarch.com
Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org



Re:Protection or Control?

2000-09-21 Thread Jim Bacher

forwarding for luizboni...@ig.com.br

Reply Separator
Subject:Protection or Control?
Author: Luiz Claudio luizboni...@ig.com.br
List-Post: emc-pstc@listserv.ieee.org
Date:   9/20/00 9:59 PM

I have a question to those who are familiar with the safety requirements
established electrical appliance standards.

A bimetal thermostat is usuallly used to control the temperature of a certain
ambient within certain limits. Can it also be considered as a protection device?
I'm not going to give my oppinion to avoid any possibility of biased answers.
But, please, give your oppinion.
If you have a reference publication which I could use as a reference for a work
to be presented, please include it in your answer. If not, no problem. Just give
your oppinion.

Please answer this message to my personal email address: luizboni...@ig.com.br

Thanks a lot,

Luiz

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re[2]:Protection or Control?

2000-09-21 Thread duncan . hobbs

I know that most safety standards require the equipment to remain safe under
single fault conditions. In this case the single fault I would consider would be
that of failure of the thermostat (i.e short circuited)

The first thing to consider would be, can the failure of this device allow the
temperature to reach a hazardous level taking into account, touch temperatures,
thermal limits on other components in the vicinity (electrical and mechanical)
and possibility of ignition. If the answer is yes then this component is safety
critical as its failure can lead to an unsafe condition.

If this is so then a protection measure would have to be taken to ensure that
the equipment remained 'safe' under single fault conditions. Now you have one
component for control and one component for protection, the protective device
only operating when the equipment is out of control.

In a previous job I had to run a test on some equipment that included a heating
element. as a result of fault testing the control circuit the element became so
hot its metal fins melted and dripped into the bottom of the enclosure! The
problem was resolved with a series thermal cutout mounted on the element body.

Hope this is helpful...
Regards. 

Reply Separator
Subject:Re:Protection or Control?
Author: jim_bac...@mail.monarch.com
List-Post: emc-pstc@listserv.ieee.org
Date:   21/09/00 15:46


forwarding for luizboni...@ig.com.br

Reply Separator
Subject:Protection or Control?
Author: Luiz Claudio luizboni...@ig.com.br
List-Post: emc-pstc@listserv.ieee.org
Date:   9/20/00 9:59 PM

I have a question to those who are familiar with the safety requirements
established electrical appliance standards.

A bimetal thermostat is usuallly used to control the temperature of a certain
ambient within certain limits. Can it also be considered as a protection device?
I'm not going to give my oppinion to avoid any possibility of biased answers.
But, please, give your oppinion.
If you have a reference publication which I could use as a reference for a work
to be presented, please include it in your answer. If not, no problem. Just give
your oppinion.

Please answer this message to my personal email address: luizboni...@ig.com.br

Thanks a lot,

Luiz

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Brazilian requirements

2000-09-21 Thread James Linehan

I recently completed a Brazilian compliance effort on a telecom device.

It was handled via a consultant with expertise in South American regulatory 
requirements.

I was required to supply copies of existing test reports ( Part 68, Part 15, 
applicable CTRs, and CB Scheme), electronic photos, and a description of the 
device and it's normal functionality.

No test samples or testing was required.  The information was reviewed and 
processed, and the end result was an ANATEL approval certificate.

If you'd like contact information for the Consultant I used, feel free to 
e-mail me.

At 05:04 PM 9/20/00 -0400, Clement Dave-LDC009 wrote:

For Terminal Equipment the generic requirments are;

Federal Official Gazette - Ordance No. 322 - Net No. 001/92

There is also a test procedure - No.225-540-514 Test Procedures for Data
Communications Equipment for Transmission Nominal Speed Up yo 28800
Bits/sec

These are published in Portuguese and you will need to have them translated.
Make sure you get a technical translator. We had a requirement that got
translated incorrectly that placed an out of band requirement on voice band
signals.

David Clement
Motorola Inc.
Global Homologation Engineering
20 Cabot Blvd.
Mansfield, MA 02048

P: 508-261-4389
F: 508-261-4777
E: mailto:dave.clem...@motorola.com

Pager:
Numeric: 978-545-5452
Alpha: mailto:6178020099.0705...@pagenet.net



-Original Message-
From: jradom...@clare.com [mailto:jradom...@clare.com]
Sent: Wednesday, September 20, 2000 1:43 PM
To: emc-p...@ieee.org
Subject: Brazilian requirements



Group,

Could you advise me on the Brazilian telecom requirements for interfaces to
be connected to the analog PSTN?
I was not able to find any information on this subject in English.

Thank you in advance.

John Radomski
Product Compliance Engineer
Clare Corp.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
  majord...@ieee.org
with the single line:
  unsubscribe emc-pstc

For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
  majord...@ieee.org
with the single line:
  unsubscribe emc-pstc

For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org


Jim Linehan
Hardware Engineer
VGSBU
Cisco Systems Inc.
300 Apollo Drive
Chelmsford, MA. 01824
Phone: (978) 244-5716
Fax:(978) 244-5908

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Protection or Control?

2000-09-21 Thread georgea

Ted's note said:

In addition, UL 1950 section 1.7.13 refers to thermostats.  The standard
allows the thermostat to limit temperature, but they should not be used for
other purposes.

Actually, section 1.7.13 pertains only to marking and instructions related
to adjustable thermostats.  It does not address the use or testing of such
devices.  Annex K does address the test requirements for thermal controls.

George



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Susceptibility of USP ports to Industrial Environment test levels.

2000-09-21 Thread Terry Meck

Hello:

RE:Susceptibility of USB ports to Industrial Environment test levels.

Does anyone have experience to the susceptibility of commercially available 
PC's and mother boards at the industrial test levels?  
For example RS232 and USB ports with the 1000 V EFT, 10V/M RF radiated, and 10V 
RF conducted immunity tests.  (EN 61000-4-4, -4-6 etc.)
Do they fold under those levels?

I always protect them when using them as support equipment.  Am I over cautious?

Regards,
Terry Meck



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re:FW: RE: Brazilian requirements

2000-09-21 Thread Jim Bacher

forwarding for ncc1...@nccrc.com

Reply Separator
Subject:FW: RE: Brazilian requirements
Author: Net Connection Corp ncc1...@nccrc.com
List-Post: emc-pstc@listserv.ieee.org
Date:   9/21/00 9:19 AM

TO: John Radomski
Product Compliance Engineer
Clare Corp.

David Clement
Motorola Inc.
Global Homologation Engineering

FROM: Richard L. Swarz
  Net Connection Corp

Hi John and David,

Jim was kind enough to forward these e-mails.

We look forward to address any questions on Brazil
and all other countries South of the US Border.

David, the regulation that you site may be of interest, if you
plan to test in Brazil.   We have been successful in avoiding
IN Country Testing by utilizing our Licensed engineers and
Test Reports based primarily on European Standards.  Brazil's
Standards are currently from the former Telebras
Until 1998 the only phone provider in Brazil.

There are alternative Brazilian Standards that may work equally well in
determining if the Product meets Brazil's regulations.



Awaiting your  e-mail / call.

Best regards,

Richard
310 821-0700
310 574-9540 FAX
ncc1...@nccrc.com


-Original Message-
From: Net Connection Corp [mailto:ncc1...@nccrc.com]
Sent: Thursday, September 21, 2000 9:07 AM
To: 'James Linehan'
Subject: RE: RE: Brazilian requirements


Hi Jim,

Many thanks, your kindness is greatly appreciated.

Best regards,

Richard
310 821-0700
310 574-9540 FAX
ncc1...@nccrc.com


-Original Message-
From: James Linehan [mailto:jline...@cisco.com]
Sent: Thursday, September 21, 2000 11:37 AM
To: ncc1...@nccrc.com
Subject: Fwd: RE: Brazilian requirements


Richard,  FYI

There may be some business coming your way, I've forwarded your contact
information to each of the gentlemen noted below.

From: Dave Clark david.cl...@spikebroadband.net
To: 'James Linehan' jline...@cisco.com
Subject: RE: Brazilian requirements
Date: Thu, 21 Sep 2000 11:18:30 -0400
X-Mailer: Internet Mail Service (5.5.2650.21)

James,

I am very interested in the consultant you used.  Please forward me their
contact info.

Dave

-Original Message-
From: James Linehan [mailto:jline...@cisco.com]
Sent: Thursday, September 21, 2000 12:36 PM
To: Clement Dave-LDC009; 'jradom...@clare.com'; emc-p...@ieee.org
Subject: RE: Brazilian requirements



I recently completed a Brazilian compliance effort on a telecom device.

It was handled via a consultant with expertise in South American regulatory
requirements.

I was required to supply copies of existing test reports ( Part 68, Part
15,
applicable CTRs, and CB Scheme), electronic photos, and a description of
the
device and it's normal functionality.

No test samples or testing was required.  The information was reviewed and
processed, and the end result was an ANATEL approval certificate.

If you'd like contact information for the Consultant I used, feel free to
e-mail me.

At 05:04 PM 9/20/00 -0400, Clement Dave-LDC009 wrote:

 For Terminal Equipment the generic requirments are;
 
 Federal Official Gazette - Ordance No. 322 - Net No. 001/92
 
 There is also a test procedure - No.225-540-514 Test Procedures for Data
 Communications Equipment for Transmission Nominal Speed Up yo 28800
 Bits/sec
 
 These are published in Portuguese and you will need to have them
translated.
 Make sure you get a technical translator. We had a requirement that got
 translated incorrectly that placed an out of band requirement on voice
band
 signals.
 
 David Clement
 Motorola Inc.
 Global Homologation Engineering
 20 Cabot Blvd.
 Mansfield, MA 02048
 
 P: 508-261-4389
 F: 508-261-4777
 E: mailto:dave.clem...@motorola.com
 
 Pager:
 Numeric: 978-545-5452
 Alpha: mailto:6178020099.0705...@pagenet.net
 
 
 
 -Original Message-
 From: jradom...@clare.com [mailto:jradom...@clare.com]
 Sent: Wednesday, September 20, 2000 1:43 PM
 To: emc-p...@ieee.org
 Subject: Brazilian requirements
 
 
 
 Group,
 
 Could you advise me on the Brazilian telecom requirements for interfaces
to
 be connected to the analog PSTN?
 I was not able to find any information on this subject in English.
 
 Thank you in advance.
 
 John Radomski
 Product Compliance Engineer
 Clare Corp.
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 To cancel your subscription, send mail to:
   majord...@ieee.org
 with the single line:
   unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
   Jim Bacher:  jim_bac...@mail.monarch.com
   Michael Garretson:pstc_ad...@garretson.org
 
 For policy questions, send mail to:
   Richard Nute:   ri...@ieee.org
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 To cancel your subscription, send mail to:
   majord...@ieee.org
 

Argentina IRAM

2000-09-21 Thread George Sparacino
Hello All..

Does anyone have a URL for the IRAM homepage .. in English ??

Thanks,
George


Re: Argentina IRAM

2000-09-21 Thread Art Michael

Hi George,

There is a link on the Safety Link (to IRAM).  However, I expect there is
no English language link.  When you are in Argentina - speak Argentine ;-)

An alternative:
Try AltaVista's translator at: babelfish.altavista.com and point it at
IRAM's URLs. The translation, although not perfect, will give you a good
idea of what's up, down there.

Regards, Art Michael

Int'l Product Safety News
A.E. Michael, Editor
166 Congdon St. East
P.O. Box 1561 
Middletown CT 06457 U.S.A.

Phone  :  (860) 344-1651
Fax:  (860) 346-9066
Email  :  i...@connix.com
Website:  http://www.safetylink.com
ISSN   :  1040-7529
--

On Thu, 21 Sep 2000, George Sparacino wrote:

 Hello All..
 
 Does anyone have a URL for the IRAM homepage .. in English ??
 
 Thanks,
 George
 



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: A14 to EN61000-3-2 Did it pass?

2000-09-21 Thread John Cronin


Yes prA14 did pass I have been reliably informed.

It will be interesting to see when it is going to be published in the OJEC.

John Cronin



From: wo...@sensormatic.com
Reply-To: wo...@sensormatic.com
To: emc-p...@majordomo.ieee.org
Subject: RE: A14 to EN61000-3-2  Did it pass?
Date: Mon, 18 Sep 2000 14:57:11 -0400


A14 moves all equipment out of Class D except for personal computers and
televisions, and the 75 lower limit remains. However, the dop is scheduled
to be after 2001-01-01. Until then, our Notified Body (SEE) is accepting
prA14 for use in a TCF.

Richard Woods

--
From:  Jim Eichner [SMTP:jim.eich...@xantrex.com]
Sent:  Monday, September 18, 2000 2:30 PM
To:  'EMC-PSTC - forum'
Subject:  RE: A14 to EN61000-3-2  Did it pass?


Follow-on question:

Just to be really sure I haven't missed anything, A14 is a
clarification of
requirements and test methods and does nothing to postpone the drop
dead
date for this standard, right?

Thanks,

Jim

-Original Message-
From: Tolbert, J. Joe x1105 [mailto:jtolb...@genicom.com]
Sent: Monday, September 18, 2000 10:34 AM
To: 'emc-p...@ieee.org'
Subject: A14 to EN61000-3-2 Did it pass?



Was Amendment 14 accepted?
I understood that it was suppose to be voted on last Friday.

Joe

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org




_
Get Your Private, Free E-mail from MSN Hotmail at http://www.hotmail.com.

Share information about yourself, create your own public profile at 
http://profiles.msn.com.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Jim Bacher:  jim_bac...@mail.monarch.com
Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org



Re: Argentina IRAM

2000-09-21 Thread Kevin Newland

George,

Their web site is :

www.iram.com.ar

Thanks
Kevin
--- George Sparacino
george.sparac...@bostonacoustics.com wrote:
 Hello All..
 
 Does anyone have a URL for the IRAM homepage .. in
 English ??
 
 Thanks,
 George
 


__
Do You Yahoo!?
Send instant messages  get email alerts with Yahoo! Messenger.
http://im.yahoo.com/

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org