ETSI standards vs NEBS

2000-09-28 Thread Dave Wilson
Does anyone have a feel for the degree of acceptance of GR-63/1089 in
Europe? I can remember at a previous company we got LONIIS in Russia to
accept NEBS test results with minimal additional assessment against ETS 300
019/119.

Anyone else have any stories to tell, other than the obvious spatial
differences?

Thanks,

Dave Wilson
Alidian Networks


Re: Probing power plane with analyser.

2000-09-28 Thread Robert Macy

We made a probe using rigid coax with its built in SMA connector.  Solder a
pin to the side of the coax and file it diagonally to create a sharp point.
To increase the loading impedance we used an SMA collar that had been
filed out to place a series chip resistor of 470 ohms in series with the
center conductor.

Then we calibrated the probe for insertion loss up to 2 GHz and could
probe around on the board.

If I had it to do again, I would move the resistor out very close to the
probe tip to reduce the effects of the series inductance, but what worked
worked, so we went on.

- Robert -

-Original Message-
From: pwmc...@ra.rockwell.com pwmc...@ra.rockwell.com
To: Cameron O'phee O'p...@ali.com.au
Cc: 'EMC - PSTC Forum' emc-p...@majordomo.ieee.org; Roman Seifert
seif...@ali.com.au
List-Post: emc-pstc@listserv.ieee.org
Date: Thursday, September 28, 2000 5:50 AM
Subject: Re: Probing power plane with analyser.




Cameron,
 If you are looking for a measure of the conducted RF coming off the
board the standard AC LISN works for DC power as well. The voltage probe
per CISPR 16 will also work and gives a standardized impedance that can be
probed from point to point (or if you are looking for a down and dirty
measurement just put a capacitor in series with your probe to block the
DC).

Paul McCoy





Cameron O'phee O'p...@ali.com.au@ieee.org on 09/27/2000 07:59:24 PM

Please respond to Cameron O'phee O'p...@ali.com.au

Sent by:  owner-emc-p...@ieee.org


To:   'EMC - PSTC Forum' emc-p...@majordomo.ieee.org
cc:   Roman Seifert seif...@ali.com.au
Subject:  Probing power plane with analyser.



Hello All,

I have been asked by one of our design engineers if I can measure the RF
signature on the 3v plane on one of our PCB designs.  The purpose of this
is
to compare it to proposed changes for cost reduction, ie removal of bypass
caps.  I would assume I need some sort of CDN but I have no designs for
this
application.  Does anyone have any ideas on how I can safely probe a 3v DC
power rail with an EMC analyser (HP8591E)?


Regards,

Cameron O'Phee.
EMC  Safety Precompliance.
Aristocrat Technologies Australia.

Telephone : +61 2 9697 4420
Facsimile  : +61 2 9663 1412
Mobile  :   0418 464 016

---



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Probing power plane with analyser.

2000-09-28 Thread George Sparacino
Cameron,

Checkout Doug Smith's webpage for some insight on making RF measurements
using various (homemade) probes.
http://emcesd.com/

Good Luck,
George




-Original Message-
From: Cameron O'phee [mailto:O'p...@ali.com.au]
Sent: Wednesday, September 27, 2000 8:59 PM
To: 'EMC - PSTC Forum'
Cc: Roman Seifert
Subject: Probing power plane with analyser.



Hello All,

I have been asked by one of our design engineers if I can measure the RF
signature on the 3v plane on one of our PCB designs.  The purpose of this is
to compare it to proposed changes for cost reduction, ie removal of bypass
caps.  I would assume I need some sort of CDN but I have no designs for this
application.  Does anyone have any ideas on how I can safely probe a 3v DC
power rail with an EMC analyser (HP8591E)?


Regards,

Cameron O'Phee.
EMC  Safety Precompliance.
Aristocrat Technologies Australia.

Telephone : +61 2 9697 4420
Facsimile  : +61 2 9663 1412
Mobile  :   0418 464 016

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Probing power plane with analyser.

2000-09-28 Thread Pwmccoy


Cameron,
 If you are looking for a measure of the conducted RF coming off the
board the standard AC LISN works for DC power as well. The voltage probe
per CISPR 16 will also work and gives a standardized impedance that can be
probed from point to point (or if you are looking for a down and dirty
measurement just put a capacitor in series with your probe to block the
DC).

Paul McCoy





Cameron O'phee O'p...@ali.com.au@ieee.org on 09/27/2000 07:59:24 PM

Please respond to Cameron O'phee O'p...@ali.com.au

Sent by:  owner-emc-p...@ieee.org


To:   'EMC - PSTC Forum' emc-p...@majordomo.ieee.org
cc:   Roman Seifert seif...@ali.com.au
Subject:  Probing power plane with analyser.



Hello All,

I have been asked by one of our design engineers if I can measure the RF
signature on the 3v plane on one of our PCB designs.  The purpose of this
is
to compare it to proposed changes for cost reduction, ie removal of bypass
caps.  I would assume I need some sort of CDN but I have no designs for
this
application.  Does anyone have any ideas on how I can safely probe a 3v DC
power rail with an EMC analyser (HP8591E)?


Regards,

Cameron O'Phee.
EMC  Safety Precompliance.
Aristocrat Technologies Australia.

Telephone : +61 2 9697 4420
Facsimile  : +61 2 9663 1412
Mobile  :   0418 464 016

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



ITU-T H.248

2000-09-28 Thread Dwight Hunnicutt

Anyone know where to obtain a draft copy of the H.248 spec?  The ITU-T
website says To Be Published and a 06/00 date, but doesn't say when
it will really be available...

Thanks

D
--

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Probing power plane with analyser.

2000-09-28 Thread Cameron O'phee

Hello All,

I have been asked by one of our design engineers if I can measure the RF
signature on the 3v plane on one of our PCB designs.  The purpose of this is
to compare it to proposed changes for cost reduction, ie removal of bypass
caps.  I would assume I need some sort of CDN but I have no designs for this
application.  Does anyone have any ideas on how I can safely probe a 3v DC
power rail with an EMC analyser (HP8591E)?


Regards,

Cameron O'Phee.
EMC  Safety Precompliance.
Aristocrat Technologies Australia.

Telephone : +61 2 9697 4420
Facsimile  : +61 2 9663 1412
Mobile  :   0418 464 016

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Probing power plane with analyser.

2000-09-28 Thread Ralph Cameron

Cameron:

That's fairly easy to do as long as you:

1.  Take all measurments from the same reference points before and after the
changes  and

2. Use a DC block on the input to the analyzer ;other wise you may have an
expensive input to replace. Most analyzers inputs are not protected for DC.
Most companies sell the DC isolator as an accessory.

Ralph Cameron

EMC Consultant and Suppression of  Consumer Electronic Equipment.


- Original Message -
From: Cameron O'phee O'p...@ali.com.au
To: 'EMC - PSTC Forum' emc-p...@majordomo.ieee.org
Cc: Roman Seifert seif...@ali.com.au
Sent: Wednesday, September 27, 2000 8:59 PM
Subject: Probing power plane with analyser.



 Hello All,

 I have been asked by one of our design engineers if I can measure the RF
 signature on the 3v plane on one of our PCB designs.  The purpose of this
is
 to compare it to proposed changes for cost reduction, ie removal of bypass
 caps.  I would assume I need some sort of CDN but I have no designs for
this
 application.  Does anyone have any ideas on how I can safely probe a 3v DC
 power rail with an EMC analyser (HP8591E)?


 Regards,

 Cameron O'Phee.
 EMC  Safety Precompliance.
 Aristocrat Technologies Australia.

 Telephone : +61 2 9697 4420
 Facsimile  : +61 2 9663 1412
 Mobile  :   0418 464 016

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



EN50178 question

2000-09-28 Thread Nick Williams


BSI's on-line and printed catalogues give the following information 
about the above standard:


BS EN 50178:1998 Electronic equipment for use in power installations

That's all it says, except a list of cross references as long as both 
your arms. Before I waste GBP56 of my hard earned cash on buying a 
copy just to see if it has any relevance to one of my client's 
projects, can someone give me a good idea of what this standard is 
really all about?


Thanks for any help.

Nick.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Jim Bacher:  jim_bac...@mail.monarch.com
Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org



Re: VCCI application

2000-09-28 Thread Jon D. Curtis

There is a pdf version of the form in the guest center on our web site at
www.curtis-straus.com

-Jon Curtis.

Jim Bacher wrote:

 forwarding for :  bgilmar...@cereva.com

 Reply Separator
 Subject:VCCI application
 Author: Gilmartin; Bob bgilmar...@cereva.com
 Date:   9/27/00 1:46 PM

 Hello group,
 Does anybody have an application for VCCI they can forward to me.  I
 went to the VCCI website and it's a Catch-22-I can't download an application
 for membership until I have a membership (i.e. username and password).
 There is also no link to email VCCI.

 Bob Gilmartin
 Sr. Regulatory Engineer
 Cereva Networks, Inc.
 3 Network Drive
 Marlboro, MA 01752-3083
 (508) 486-9660 x3412 phone
 (508) 486-9776 fax

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org

--
Jon D. Curtis, P.E.

Director of Engineering
Curtis-Straus LLC

One Stop Laboratory for NEBS, EMC,
Product Safety, and Telecom Testing.
527 Great Road
Littleton, MA 01460 USA
Voice 978-486-8880  Fax 978-486-8828
email: jcur...@curtis-straus.com
WWW.CURTIS-STRAUS.COM



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: VCCI application Membership required??

2000-09-28 Thread Bandele Adepoju

The way I remember it, test labs are 'associate members'.  Only
manufacturers can be 'members'.

Has this changed?

Regards,

Bandele 
Jetstream Communications, Inc.
badep...@jetstream.com



-Original Message-
From: Gary McInturff [mailto:gary.mcintu...@worldwidepackets.com]
Sent: Wednesday, September 27, 2000 3:46 PM
To: 'chasgra...@aol.com'; Gary McInturff; jim_bac...@mail.monarch.com;
bgilmar...@cereva.com; emc-p...@ieee.org
Subject: RE: VCCI application Membership required??



   Any one can be a member and there are two classes; Member
manufacturers and Member test facilities. VCCI collects fees 
from both of
us. From the manufacturer's side the fee's are based upon the 
anticipated
number of submittals per year. The payment is billed once a 
year, but then
there are no individual filling fees. They review your test report and
accept the data and return a stamped copy to you. At that point you can
apply their logo, they send you camera ready artwork of the 
logo and the
required Japanese text.
   There is one other little gotcha. Even though you are a
manufacturing member, the data you submit has to come from the 
other type of
member, the test facility. They are required to have VCCI 
audits and they
also pay a yearly fee. You will need to get the C and R 
numbers which
identify their conducted and radiated test sites. You'll also 
need to have a
report number from them and provide a drawing of the cable 
routing, along
with the description of the cables. E.G.. 3 meter, round 
shielded, RS232
cable, or whatever.
   So VCCI is in effect double dipping. Some from me and some from
you. That is why I maintain them to be the most expensive voluntary
organization that I have ever seen. 
   Gary

-Original Message-
From: chasgra...@aol.com [mailto:chasgra...@aol.com]
Sent: Wednesday, September 27, 2000 3:15 PM
To: gary.mcintu...@worldwidepackets.com; jim_bac...@mail.monarch.com;
bgilmar...@cereva.com; emc-p...@ieee.org
Subject: Re: VCCI application Membership required??


Can anyone apply for VCCI registration. I thought
membership was required prior to sending in
an application.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re:Customer service issues w/ EN61000-3-2 3-3

2000-09-28 Thread Pwmccoy


Don,
 In the EU guidance document for the EMC directive that they published
in July of 1997 they differentiate between apparatus that is simply
repaired, and apparatus that is repaired / refurbished to as new condition.
The latter falls under the EMC directive and standards in effect at the
time of reintroduction to the market. The former appears to be the case you
are interested in; That equipment can be repaired, and even resold in the
EU as long as it is not represented as being AS-NEW, and meets the EMC
requirements it originally had to meet when originally placed (unit by unit
date determination) on the European Market. As long as your repair parts
are only used for repair of existing product and don't reduce performance
below the previous requirements for the product you should be fine.

Paul McCoy





jim_bac...@mail.monarch.com (Jim Bacher)@ieee.org on 09/27/2000 04:37:07 PM

Please respond to jim_bac...@mail.monarch.com (Jim Bacher)

Sent by:  owner-emc-p...@ieee.org


To:   Don Rhodes don.rho...@infocus.com, 'emc-p...@majordomo.ieee.org'
  emc-p...@majordomo.ieee.org
cc:
Subject:  Re:Customer service issues w/ EN61000-3-2  3-3



forwarding for don.rho...@infocus.com

Reply Separator
Subject:Customer service issues w/ EN61000-3-2  3-3
Author: Don Rhodes don.rho...@infocus.com
List-Post: emc-pstc@listserv.ieee.org
Date:   9/27/00 10:56 AM

Does anyone know how the Harmonics  Flicker requirements apply to
non-compliant, yet non-saleable product after 1/1/01? We will need to
provide customer service on products via warrantee exchanges  parts
shipments, etc. to the EU after 1/1/01, for product which does not comply
and will not be offered for sale in the EU after the cut-in date.
Is there any known exemption for such cases? References to  any cited
documentation is appreciated.


Don Rhodes

don.rho...@infocus.com mailto:don.rho...@infocus.com

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: UL1697 ???

2000-09-28 Thread Jody Leber

UL1697 (not in existence yet) will likely be the Standard for the broadband 
communications equipment detailed in NEC Article 830.  If your equipment 
fits the description someone may be trying to get a head start.

Best Regards,

Jody Leber
Laboratory Manager

jle...@ustech-lab.com
http://www.ustech-lab.com

U. S. Technologies
3505 Francis Circle
Alpharetta, GA 30004

770.740.0717
Fax:  770.740.1508


-Original Message-
From:   Robert Legg [SMTP:rl...@tectrol.com]
Sent:   Monday, September 25, 2000 4:14 PM
To: IEEE EMC-PSTC Forum
Subject:UL1697 ???



Forumites,

UL1697.

Anyone ever heard of it? It has shown up in a recent design spec for
quotation and I suspect a typo.

Rob Legg
rl...@tectrol.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Sept. 22, 2000 Conformity-Update Now Available

2000-09-28 Thread Glen Dash

Conformity-Update for the week ending Sept. 22, 2000 is now available
at:

http://www.conformity-update.com

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



EN 300 386 in OJ?

2000-09-28 Thread Scott Lemon

Earlier this year, I believe that ETSI EN 300 386 was formally adopted as an
EU harmonized standard for telecom network equipment.  However, looking on
the DG III web page, it looks like this standard has not yet been published
in the OJ.  I had heard earlier that the anticipated target for publication
in the OJ was June '00, but I guess that did not happen.  Anyone have an
update on 300 386 wrt publication in the OJ?  I guess until it is published,
we continue to use 300 386-2 (or others). 

Thanks and Regards,

Scott Lemon
Sr. Compliance Engineer
Network Reliability and Compliance Engineering
Caspian Networks
Research Triangle Park, NC 
email: sle...@caspiannetworks.com
ph: (919) 466-0315 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Canadian Hipot Requirements

2000-09-28 Thread Rich Nute



Hi Mike:


   I'm posting this for a friend who is having a problem with CSA and hipot
   testing.  He has several products which operate on 115/230 VAC. They are
   industrial control products (don't know the CSA standard number but they
   fall under UL508 is the US). In one CSA report he is required to run a 1500
   VAC hipot for one minute (1800 VAC for one second), in another CSA report he
   is required to run 1000 VAC for one minute (1200 VAC for one second).
   
   I know the CSA hipot requirement is elusive and is required by the Canadian
   Electric companies.  Can anyone help me give this guy some guidance?  My
   feeling is that the 1500 VAC requirement is the type test and he should be
   using the 1000 VAC value for routine production tests.
   
   He has been told by CSA that anything under 50 VAC gets tested at 1000 VAC
   and that anything over that gets tested at
   2 x rated voltage +1000 for production line tests.  Seems strange.

Hi-pot test voltages are not standardized, although
IEC SC28A has attempted to do so in IEC Publication
664.

Standards such as UL 508 are not subject to 
international standardization, so there is little or 
no influence of IEC 664 on the test requirements in 
UL 508 and the CSA equivalent.

So, to understand the CSA requirements, we must look
at the history of hi-pot test voltages.

In North America, in the 1960s and 1970s, virtually 
all products were 120 V.  We simply were not in the
international marketplace.  (Those that were, their
products had to be internally re-wired -- by the
customer -- with a soldering iron -- to operate at 
220 V or 240 V.)  There were no switch-selectable or 
wide-range products.

At the time, the standard hi-pot test voltage in
both the USA and Canada was either 900 or 1000 V rms,
depending on the standard.  For any other voltage,
the standard was 2V + 1000, where V is the rated
voltage.  Thus, for a product rated 220 V, the test
voltage was 1440 V rms.  Later, the formula, 
2V + 1000, was applied to all voltages, so for 
products rated 120 V, the test voltage became 1240 V
rms.  These were often rounded to 1250 V and 1500 V.

So, now we have four test voltages, 900, 1000, 1250,
and 1500.  And, nobody understood why we needed to 
do such testing.  Often, we felt that this testing 
represented some kind of abnormal condition, but,at
the same time, it seemed quite unreasonable to expect 
the mains to go such a high voltage.  But, we went 
ahead and did the testing, usually without any 
difficulty.

Because of the lack of understanding of the purpose
of the hi-pot test, back in those days hi-pot testing 
was applied to any terminal that was connected to an 
external voltage source.  So, even low-voltage 
circuits were subjected to the minimum hi-pot voltage, 
1000 V.

So, in answer to your colleague's question, all of 
the CSA-required hi-pot voltages are correct.  They
simply are not standardized, either within the 
standard or among standards.  I believe the same
situation exists in UL.

If your colleague wants standardization, he can 
simply choose to test his products at the worst-case 
CSA-required voltage.

However, his particular CSA engineer may not allow
this.  The problem is that the standard specifies 
the hi-pot voltage.  Any test voltage that is not
that specified in the standard means that the test
is not conducted per the standard and is therefore
not acceptable (even though the actual test is a
worst-case test).  Many certification engineers are
unwilling to accept data that is not in accordance
with the standard.  Indeed, there is a good reason
for a certification house to not accept a worst-
case test voltage.  That voltage may be damaging 
the insulation; the test house does not want to be
seen as requiring a test that could be damaging the 
insulation and thereby causing a safety problem.
So, the certification engineer may require testing
at the voltage specified in the standard.  He will
say that if you want to test at worst-case, that is 
your perogative, but that is over and above and in 
addition to the certification house test.


Best regards,
Rich


ps:  Perhaps Egon will offer his explanations and
 put a different spin on this question.






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Canadian Hipot Requirements

2000-09-28 Thread Andrews, Kurt

Mike,

Doesn't sound that strange to me. To help answer your question I looked at
several UL Follow-Up Service Procedures that we have here in the plant for
various types of Information Technology Equipment. This equipment has input
voltages of 100-240VAC. UL has a table in the FUS that specifies the
voltages and times for Hipot tests. The table for Class 1 equipment
(Non-Double Insulated) has the following specifications:

Rated 60 VDC or less: 500 VAC or 700 VDC for 1 second.
Rated less than or equal to 130 VAC (184 VDC): 1000 VAC or 1400 VDC for 1
second.
Rated more than 130 VAC (184 VDC) and less than or equal to 600 VAC (849
VDC): 1500 VAC or 2100 VDC for 1 second.

It does seem strange that they would want him to run the tests for 1 minute
as opposed to 1 second. I would go with the slightly higher voltages for 1
second to save time.

I believe that the 2 times the (maximum) rated input voltage plus 1000 VAC
is what is typically used for type testing, although I believe I have also
heard this used for production line testing. This is also found in the
booklet by Associated Research titled A Basic Guide to Electrical Product
Safety Testing in the section on Hipot testing. Quoted directly from the
booklet: Test voltages are seldom less than 1000V, and for some products
intended to operate at voltages between 100V and 240V, the test voltage can
exceed 4000 volts (usually double insulated products). A rule of thumb that
most safety agencies use to determine the appropriate test voltage is to
multiply the DUT's normal operating voltage by two and add 1000V. By the
way I strongly recommend this free booklet from Associated Research. It has
a lot of good information in it.

I hope this has been of some help to you.

Kurt Andrews
Compliance Engineer

Tracewell Systems, Inc.
567 Enterprise Drive
Westerville, Ohio 43081
voice:  614.846.6175
toll free:  800.848.4525
fax: 614.846.7791

http://www.tracewellsystems.com/ http://www.tracewellsystems.com/ 


-Original Message-
From:   Mike Morrow [SMTP:mi...@ucentric.com]
Sent:   Thursday, September 28, 2000 2:52 PM
To: EMC Society
Subject:Canadian Hipot Requirements


I'm posting this for a friend who is having a problem with CSA and
hipot
testing.  He has several products which operate on 115/230 VAC. They
are
industrial control products (don't know the CSA standard number but
they
fall under UL508 is the US). In one CSA report he is required to run
a 1500
VAC hipot for one minute (1800 VAC for one second), in another CSA
report he
is required to run 1000 VAC for one minute (1200 VAC for one
second).

I know the CSA hipot requirement is elusive and is required by the
Canadian
Electric companies.  Can anyone help me give this guy some guidance?
My
feeling is that the 1500 VAC requirement is the type test and he
should be
using the 1000 VAC value for routine production tests.

He has been told by CSA that anything under 50 VAC gets tested at
1000 VAC
and that anything over that gets tested at
2 x rated voltage +1000 for production line tests.  Seems strange.

Mike Morrow
Senior Compliance Engineer
Ucentric Systems
978-897-6482
mi...@ucentric.com
www.ucentric.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Canadian Hipot Requirements

2000-09-28 Thread Mike Morrow

I'm posting this for a friend who is having a problem with CSA and hipot
testing.  He has several products which operate on 115/230 VAC. They are
industrial control products (don't know the CSA standard number but they
fall under UL508 is the US). In one CSA report he is required to run a 1500
VAC hipot for one minute (1800 VAC for one second), in another CSA report he
is required to run 1000 VAC for one minute (1200 VAC for one second).

I know the CSA hipot requirement is elusive and is required by the Canadian
Electric companies.  Can anyone help me give this guy some guidance?  My
feeling is that the 1500 VAC requirement is the type test and he should be
using the 1000 VAC value for routine production tests.

He has been told by CSA that anything under 50 VAC gets tested at 1000 VAC
and that anything over that gets tested at
2 x rated voltage +1000 for production line tests.  Seems strange.

Mike Morrow
Senior Compliance Engineer
Ucentric Systems
978-897-6482
mi...@ucentric.com
www.ucentric.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Safety test your EMC test sample?

2000-09-28 Thread eric . lifsey



Equipment shall not become dangerous or unsafe as a result of the application
of the tests defined in this section of IEC  1000-4.

That statement appears in (with only slight variations) -2, -3, -4, -5 and -6.
Dangerous or unsafe is not defined.  There are no links to any safety standards
or other criteria to apply.  So, which one of the following would apply?

  1. No smoke, no fire, the cover didn't fly off, dogs still hate cats, so it's
safe!
  2. The usual standards-driven safety qualification is done on another sample,
the EMC sample is not safety tested unless something very obvious has happened.
  3. Take the EMC sample(s) to the safety lab for validating key parameters like
dielectric withstand and leakage current.
  4. Take the EMC sample(s) to the safety lab for a full safety evaluation.

Regards,
Eric Lifsey
Compliance Manager
National Instruments



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Purpose of Electric Strength Testing (Hi-Pot)

2000-09-28 Thread Rich Nute




Hello from San Diego:


One of our colleagues has asked me to discuss further
the reason behind the hi-pot test.

The insulation between the mains and accessible 
conductive parts (including low-voltage-energized
accessible conductive parts) is critical to the 
scheme of protection from electric shock.

Because the insulation is critical to protection
from electric shock, the design of the mains 
insulation must be such as to maximize the 
preservation (reliablity) of the insulation.  Or, 
to put it another way, the product design must 
minimize the deteriorating influences on the mains 
insulation.

One of the deteriorating influences on insulation 
is voltage.  

Mains insulation is subject to two different voltages.
The first is the normal mains voltage itself.  The
second is the normal overvoltages.

Note that I said that overvoltages are normal.

Mains overvoltages are generated by the normal 
operation of inductive devices connected to the mains
such as motors and transformers and ignitors and
similar devices.  These inductances in their normal
operation create back-EMFs that are imposed on the
mains circuits and propagated throughout the system.
Under standard conditions, these overvoltages can 
be predicted at the point where they are generated.  
But, their amplitude at any point in the system is 
a variable depending on the local distribution 
system and its parameters.   

These overvoltages have been studied and measured,
and the results have been published in numerous 
technical articles.  The conclusions, time and 
again, show that the maximum overvoltages are in 
the 900 to 1200 volts peak.  From these studies,
a standard test waveform, representing these 
overvoltages, has been established, the 1.2 x 50 
impulse.

So, the mains insulation is subject to both the
normal mains operating voltage and the normal mains
overvoltage.  

Over the years, we have found that designing the
mains insulation for 1500 V rms provides adequate 
preservation (reliability).  Simply by selecting
certified mains components insures adequate 
insulation to withstand the normal mains 
overvoltages.  Certified mains components such
as appliance couplers, fuseholders, and wire rated
at 120 V or 250 V are subjected to 1500-volt 
dielectric withstand tests.  

We test the design with the hi-pot test.  This test
confirms that we have selected and controlled the
two forms of insulation, solid and air, to have an 
electric strength of at least 1500 V rms.

We also test the production process with the hi-pot 
test.  This test confirms that our production 
process has assembled the unit properly, and that no 
manufacturing defects are in the product that would 
cause the insulation to fail in the event of a 
normal overvoltage.


Best regards,
Rich


ps:  Note that a creepage is not an insulation; it
 is the interface between solid and air 
 insulations.  A creepage is critical to safety
 because the solid insulation at the interface
 is subject to the long-term deteriorating 
 influences of the normal mains voltage, not the 
 normal overvoltage.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Canadian Hipot Requirements

2000-09-28 Thread Mike Morrow

The problem is that when two separate products have the same input voltage
and have been tested to the same standard, why are there two different hipot
levels?  Its rather difficult to have procedures etc. that don't line up.
Also try and explain this to a worker trying to understand hipot testing.

Mike

-Original Message-
From: Robert Legg [mailto:rl...@tectrol.com]
Sent: Thursday, September 28, 2000 11:53 AM
To: Mike Morrow
Subject: RE: Canadian Hipot Requirements


Mike,

You've told about CSA requirements for your friend's products, but you
haven't indicated what the problem was.

Rob Legg
Tectrol Inc
rl...@tectrol.com

-Original Message-
From: owner-emc-p...@ieee.org [mailto:owner-emc-p...@ieee.org]On Behalf
Of Mike Morrow
Sent: Thursday, September 28, 2000 2:52 PM
To: EMC Society
Subject: Canadian Hipot Requirements



I'm posting this for a friend who is having a problem with CSA and hipot
testing.  He has several products which operate on 115/230 VAC. They are
industrial control products (don't know the CSA standard number but they
fall under UL508 is the US). In one CSA report he is required to run a 1500
VAC hipot for one minute (1800 VAC for one second), in another CSA report
he
is required to run 1000 VAC for one minute (1200 VAC for one second).

I know the CSA hipot requirement is elusive and is required by the Canadian
Electric companies.  Can anyone help me give this guy some guidance?  My
feeling is that the 1500 VAC requirement is the type test and he should
be
using the 1000 VAC value for routine production tests.

He has been told by CSA that anything under 50 VAC gets tested at 1000 VAC
and that anything over that gets tested at
2 x rated voltage +1000 for production line tests.  Seems strange.

Mike Morrow
Senior Compliance Engineer
Ucentric Systems
978-897-6482
mi...@ucentric.com
www.ucentric.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org