RE: Wire spool labeling requirements

2002-03-15 Thread Gary McInturff

Doug,
Not sure how we appear to be on the opposite side of the stick here. 
Believe it or not I support almost all of the NRTL compliance engineers I have 
worked with. They are like any group of people some are very good some should 
quit consuming oxygen at the first opportunity (I'm kidding here!) The 
occasional request that makes my life more difficult is weighed with how many 
times they have really done a superb job - and yes that happens. 
All I was pointing out is that their system is set up so that it helps 
them first, then me and I expect them to use the tools they have first. They do 
that by looking directly at the reports which are different than just the 
on-line cards. I also agree those aren't as up to date as I would have 
anticipated - but they are more current than the UL recognition books. 
I still have to get certificates for TUV etc, but not for UL. The 
biggest problem with that is half the time the vendors don't even know who has 
that documentation.
I don't always have, as my 25 year daughter would say my cranky pants 
on.
Have a good week end Doug
Gary



-Original Message-
From: Doug McKean [mailto:dmck...@corp.auspex.com]
Sent: Friday, March 15, 2002 9:36 AM
To: emc-p...@ieee.org
Subject: Re: Wire spool labeling requirements



Gary, 

I can go along with the documentation hunt as well. 
And I can understand that their approval cycle would 
probably increase by a factor of x10 (I'm not joking) 
if they had to do all the research to the parts themselves.  
I believe that's really what's at the bottom of it all.  

But, it's having to put up with vendors who would burn 
your ear off complaining that the NRTL is one with the 
approval and the records and that's what they're paying 
all this money to do, etc ... I've gotten to point where I'm 
beginning to sympathize greatly with these vendors.  And, 
I am also very aware (from an unfortunate experience) 
that the website is not that reliable as in being updated 
as it should on a regular basis. There's lots of reasons 
for that.  Some most definitely with the vendor. 

Not to detract from their or anyone else's quality of work, 
but I do know that as of only a couple of years ago, it 
was the engineers who wrote up the reports.  Now, all 
that gets handed over to a secretary pool and that 
mistakes have increased as a result.  I'm assuming that 
may also factor in to the rather strict show me state 
of mind over there.  Something I don't think they should 
slack off on.  After some of the things I've seen, I'm 
rather glad everyone gets the same scrutiny and I've 
gotten quite an education being involved with it. 

It may be a pain in the butt sometimes and there are 
certainly times where issues appear from left field, but 
I really do have a lot of respect for the engineers who 
have more than 3 years experience working 15 to 20 
(or so) product approvals per month. All different kinds 
of products.  The reviewers seem to be very well 
qualified. All very approachable and all very procedural. 
Which I guess it really should be. 

I do know that they requiring you to get the paperwork 
instead of them at time of submittal hits several birds with 
one stone - educating the submitter what's needed, verification 
FROM the vendor, verification OF the vendor, etc  

I've had the experience of handing over a copy of a live 
approval from the vendor but something on it was not right.  
For some reason, it didn't effect my product approval, but 
the engineer contacted the field office about it.  And I was 
not privy as to why. they certainly do keep a very professional 
atmosphere as well. At least the people I've worked with 
directly. 

Yes, there are times where we throw a wrench and complain, 
but in the end, I can understand most of what they require. 

- Doug McKean 



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For 

Re: DSL on residential buildings.

2002-03-15 Thread Cortland Richmond

The reason for the Part 15 residential (Class B) limit is to protect
reception, and the levels prescribed are (arguably) low enough to do so. If
we allow higher levels, we are asking for service calls and perhaps
official attention. But (unless I am mistaken) it is now the USER who
responsible for interference generated by his Class A devices, and it's
perfectly legal for us to sell them to him.

I recently spent some years working for a company that makes telecomm
equipment. I there encountered for the first time the telco point of view
(which is probably not uncommon). In the telephone world, the service
provider is responsible for everything up to the network interface.
Everything beyond that is the responsibility of the customer. Therefore,
some people assume that equipment installed prior to the NIC can be, and
should be Class A for Part 15. I have argued, with success, that this is an
error with potentially expensive consequences.

Part 15 contains an exemption for equipment located within a facility -
even just a locked room, cabinet or vault - controlled by the telco. There
is an argument, which I make, that when we do this in a residential
building, if we are NOT Class B compliant, we may wish we had been. (Even
Class B is often not enough, and I have seen equipment meant for customer
use whose specification was well below the FCC limit.) And though our
employers' products may comply with Part 15 we are still liable for harmful
interference.

However, emissions may be suppressed by other means than installing only
Class B equipment and this is often the way to go. The utility exemption
does make this easier.

I personally believe that one may make a case for the mechanical room being
Class A. It often contains furnaces, motors, and many other unregulated
devices which generate high levels of radio and television interference,
and to impose a stricter standard on telecom equipment in the same place
seems a bit of a reach.

But look at the environment! Will emissions reaching a customer location be
above the Class B limit? If so, then I would say due diligence requires
suppressing them further.  A vault in a steel reinforced building's
basement is a different matter than a rooftop utility hut with TV antennas
just 3 meters away. If deployment entails a wide range of installations,
then it is probably best to suppress all of it to Class B, rather than
install Class B retrofit kits on a case-by-case basis. This is a decision I
believe has to be made when the product is proposed.


Regards,

Cortland Richmond
(unemployed, and looking)

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


DSL on residential buildings.

2002-03-15 Thread Gary McInturff

Just making a quick check here. I'm seeing some product brochures out 
indicating some of these home units are class A. Am I missing something here, 
shouldn't that be class B. The fact its phone stuff (also carries the FCC part 
68 stuff) can't override this classification correct? 
How about apartment buildings - is their mechanical room A or B?
Gary

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: creepage v breakdown voltage

2002-03-15 Thread Stephen Phillips

  Time certainly couldn't account for wide ranging humidity
or altitude, but perhaps lessor humidity and air pressure
changes.  The time may have more to do with settling
capacitive effects first.

  Stephen


At 10:38 AM 3/15/2002, MCA Compliance wrote:
These factors are certainly all relevant, but I was under the impression 
(maybe incorrectly so?) that the requirement to apply the test voltage for 
60 seconds during the type test was to account for all these degradating 
factors.



Brian
-Original Message-
From: Stephen Phillips [mailto:step...@cisco.com]
Sent: 15 March 2002 15:17
To: Roman, Dan
Cc: 'MCA Compliance'; Emc-Pstc Post
Subject: RE: creepage v breakdown voltage

  Try this.

  For flat electrodes, at sea level, and normal temperatures;
eliminating such factors as humidity, dust, illumination, and
the electrode materials; the molecules of the gases that
compose common air, get ionized in the presence of an
electric field of about 30KV/cm.

  So, since - electrode shape, barometric pressure, temperature,
humidity, dust, presence of photons, and composition of the
materials and shape of the electrodes, as well as the
composition of the 'air' (gases), and also any other local
(competing) electromagnetic fields - can all affect the definitive
voltage that will jump a given gap - is it any wonder that the
standard includes what otherwise appears to be a lot of
slop.

  Stephen

















At 09:28 AM 3/15/2002, Roman, Dan wrote:


I was looking into this a few weeks ago also and found similar results
experimentally as other posters have mentioned.  The only voltage per inch
spec I was able to come up with was in the IPC specs but they were way out
of whack!  0.12 mils per volt or more meaning that 2121 Vdc distance that
the safety standards say should be 2.5 mm the IPC spec is saying you need 5
mm

While the safety standards may be conservative to allow for temperature,
grease, dirt, etc. over time the IPC specs are ultra-conservative.  The
dielectric tables for hermetically sealed material group III is probably
closer to the actual breakdown but I never did find a spec I could use to
predict the ACTUAL breakdown voltage of a gap between traces.  If anyone
finds a rule of thumb or equation I'd like to have it also.

Dan

-Original Message-
From: MCA Compliance [mailto:bally...@iolfree.ie]
Sent: Friday, March 15, 2002 4:54 AM
To: Emc-Pstc Post
Subject: creepage v breakdown voltage

































does data exist which correlates creepage distance on a pcb with
hi-potential test voltage it should withstand ?

for example, I know 60950 sugests a test voltage of 1500Vrms for 1 minute
and a creepage of 2.5mm (material group III) for basic insulation.

How did they arrive at 2.5 mm ???

Brian
email: i...@mcac.ie

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net
For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org
All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: creepage v breakdown voltage

2002-03-15 Thread Stephen Phillips

  Regarding Paschen's Law:

  http://home.earthlink.net/~jimlux/hv/hvmain.htm
  http://home.earthlink.net/~jimlux/hv/paschen.htm

  Stephen


At 12:51 PM 3/15/2002, Doug McKean wrote:


I've done my own testing and researched the thing as well.
I think we've had some serious discussions here about this
subject in the past.  If the archives are available, it would
be beneficial to go through them. Also, get a little hipot
tester from any of the hipot mfrs for your own bench
testing.  That's highly educational as well as nipping
problems in the bud.

You'll first have to jump into Paschen's Law and all that
involves with pressure/humidity/geometry of the probe
tips used, etc ...

Basically, I start with  1Mv/meter STP and work down
from there.  Therefore, 1mm means 1Kv.  Now, throw
in a x2 safety factor and you get 2mm  spacing.  Now
increase to 1.5Kv and you end up with 2.5mm? Well, okay.
Surface contamination sets in over time? Well, okay again.
Obviously, I've been doing some extreme fudging, but it
ends up darn close most of the time.

Follow the standards when in any doubt.

I'm not really sure, but I was told many years ago that wire
mfrs use as much as a x7 safety factor for their insulation or
used to.

- Doug McKean



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: creepage v breakdown voltage

2002-03-15 Thread Doug McKean

I've done my own testing and researched the thing as well. 
I think we've had some serious discussions here about this 
subject in the past.  If the archives are available, it would 
be beneficial to go through them. Also, get a little hipot 
tester from any of the hipot mfrs for your own bench 
testing.  That's highly educational as well as nipping 
problems in the bud. 

You'll first have to jump into Paschen's Law and all that 
involves with pressure/humidity/geometry of the probe 
tips used, etc ... 

Basically, I start with  1Mv/meter STP and work down 
from there.  Therefore, 1mm means 1Kv.  Now, throw 
in a x2 safety factor and you get 2mm  spacing.  Now 
increase to 1.5Kv and you end up with 2.5mm? Well, okay.  
Surface contamination sets in over time? Well, okay again. 
Obviously, I've been doing some extreme fudging, but it 
ends up darn close most of the time.  

Follow the standards when in any doubt. 

I'm not really sure, but I was told many years ago that wire 
mfrs use as much as a x7 safety factor for their insulation or 
used to. 

- Doug McKean 



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Wire spool labeling requirements

2002-03-15 Thread Doug McKean

Gary, 

I can go along with the documentation hunt as well. 
And I can understand that their approval cycle would 
probably increase by a factor of x10 (I'm not joking) 
if they had to do all the research to the parts themselves.  
I believe that's really what's at the bottom of it all.  

But, it's having to put up with vendors who would burn 
your ear off complaining that the NRTL is one with the 
approval and the records and that's what they're paying 
all this money to do, etc ... I've gotten to point where I'm 
beginning to sympathize greatly with these vendors.  And, 
I am also very aware (from an unfortunate experience) 
that the website is not that reliable as in being updated 
as it should on a regular basis. There's lots of reasons 
for that.  Some most definitely with the vendor. 

Not to detract from their or anyone else's quality of work, 
but I do know that as of only a couple of years ago, it 
was the engineers who wrote up the reports.  Now, all 
that gets handed over to a secretary pool and that 
mistakes have increased as a result.  I'm assuming that 
may also factor in to the rather strict show me state 
of mind over there.  Something I don't think they should 
slack off on.  After some of the things I've seen, I'm 
rather glad everyone gets the same scrutiny and I've 
gotten quite an education being involved with it. 

It may be a pain in the butt sometimes and there are 
certainly times where issues appear from left field, but 
I really do have a lot of respect for the engineers who 
have more than 3 years experience working 15 to 20 
(or so) product approvals per month. All different kinds 
of products.  The reviewers seem to be very well 
qualified. All very approachable and all very procedural. 
Which I guess it really should be. 

I do know that they requiring you to get the paperwork 
instead of them at time of submittal hits several birds with 
one stone - educating the submitter what's needed, verification 
FROM the vendor, verification OF the vendor, etc  

I've had the experience of handing over a copy of a live 
approval from the vendor but something on it was not right.  
For some reason, it didn't effect my product approval, but 
the engineer contacted the field office about it.  And I was 
not privy as to why. they certainly do keep a very professional 
atmosphere as well. At least the people I've worked with 
directly. 

Yes, there are times where we throw a wrench and complain, 
but in the end, I can understand most of what they require. 

- Doug McKean 



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: CE Mark on Product Packaging

2002-03-15 Thread Bill Ellingford

Hi Guys
My wording may have been put together in haste however, I think the
important part of the directive is the word OR.  The manufacturer OR his
authorised representative, established within the community.  I had always
beleived this was interpreted as one or the other must be within the EEC
(now EU).  

This does differ from the RTTE requirement and is the basis for the
differing needs to CE mark packaging.  I am of course interested in other
views on this interpretation. 
Bill Ellingford

-Original Message-
From: Scott Lemon [mailto:sle...@caspiannetworks.com]
Sent: 15 March 2002 14:43
To: emc-pstc
Cc: Bill Ellingford; 'Russell'
Subject: Re: CE Mark on Product Packaging



Correct me if I am wrong, but I do not believe the statement below is
entirely
correct.  It is my understanding (per EMC directive and published
guidelines)
that the Manufacturer or Authorized Representative is responsible for
affixing
the CE marking and drawing up the DoC and that only the Authorized Rep (if
applicable) must be established within the community.  In other words, the
Manufacturer (who draws up the DoC and tech docs) does not have to be
established in the community, but if an Authorized Rep is used, they must
be.
It is clear that when neither the Manufacturer or the Auth Rep are
established
within the community, the obligation to keep the DoC available is the
responsibility of the party placing the product on the market (importer).

Scott Lemon
Caspian Networks

Bill Ellingford wrote:

 Under the EMC directive, the person making a DOC and
 placing the goods on the market would be an EU resident.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


*

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: CE Mark on Product Packaging

2002-03-15 Thread richwoods

The Commission has said the same thing in their explainatory document.
http://europa.eu.int/comm/enterprise/newapproach/legislation/guide/legislati
on.htm

Note: this URL is long and may be cut into two sections when you receive
this e-mail. If so, just join the two sections back togther to create the
full URL.

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: Scott Lemon [mailto:sle...@caspiannetworks.com]
Sent: Friday, March 15, 2002 9:43 AM
To: emc-pstc
Cc: Bill Ellingford; 'Russell'
Subject: Re: CE Mark on Product Packaging



Correct me if I am wrong, but I do not believe the statement below is
entirely
correct.  It is my understanding (per EMC directive and published
guidelines)
that the Manufacturer or Authorized Representative is responsible for
affixing
the CE marking and drawing up the DoC and that only the Authorized Rep (if
applicable) must be established within the community.  In other words, the
Manufacturer (who draws up the DoC and tech docs) does not have to be
established in the community, but if an Authorized Rep is used, they must
be.
It is clear that when neither the Manufacturer or the Auth Rep are
established
within the community, the obligation to keep the DoC available is the
responsibility of the party placing the product on the market (importer).

Scott Lemon
Caspian Networks

Bill Ellingford wrote:

 Under the EMC directive, the person making a DOC and
 placing the goods on the market would be an EU resident.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Alternate Country Approvals

2002-03-15 Thread richwoods

As a member of CENELEC, Switzerland uses ENs. I understand Poland uses EN
55022.

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: cecil.gitt...@kodak.com [mailto:cecil.gitt...@kodak.com]
Sent: Friday, March 15, 2002 8:08 AM
To: emc-p...@majordomo.ieee.org
Subject: Alternate Country Approvals





Hi All,


 I have tested ITE products to the FCC, EN55022 and EN55024 Standards.
Does anyone know what additional EMC approvals and documentation is
required for Poland, Russia
and Switzerland?

Thanks for your help

Cecil


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Voltage Spikes on Power Lines etc

2002-03-15 Thread Ken Javor

Regarding the snippet below paralleling the bulk cap with a ceramic 
addresses differential mode noise such as the vacuum cleaner, but it doesn't
help against common mode noise that the cm choke and snap-on ferrite sleeve
address.  Line to ground or Y-caps will work with the cm choke and snap-on
ferrite to attenuate cm spikes.

--
From: John Barnes jrbar...@iglou.com
To: George Stults george.stu...@watchguard.com, emc-p...@majordomo.ieee.org
Subject: Re: Voltage Spikes on Power Lines etc
Date: Thu, Mar 14, 2002, 5:16 PM


 A very basic precaution is to put ceramic capacitors in parallel with
 the bulk electrolytic capacitors in your power supply, to short out the
 high-frequency components of the spikes.  A common-mode choke on the
 input can also help a lot.  To see if this would help, you can put a
 snap-on ferrite sleeve around the power cord next to the power supply.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: creepage v breakdown voltage

2002-03-15 Thread John Woodgate

I read in !emc-pstc that MCA Compliance bally...@iolfree.ie wrote (in
nbbblhpagldfkfbcdencaemojjac.bally...@iolfree.ie) about 'creepage v
breakdown voltage', on Fri, 15 Mar 2002:
How did they arrive at 2.5 mm ???

IEC TC74, responsible for IEC60950, didn't arrive at it. There is a
special committee, TC28, that deals with clearance and creepage. You may
find, from the public part of the IEC web site, that there is an Irish
person on TC28 who can help you.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Australian compliance to ARE: creepage v breakdown voltage

2002-03-15 Thread Kristiaan . Carpentier
Hello,

According to the latest version of the Telecommunication Labelling Notice 
2001, products in the Category A50 are deemed to comply with ACA 
TS-001-1997 and AS/ACIF S043-2001. No problem for TS-001, but S043 needs 
Compliance level 3 only since January 1rst 2002.
The general approach is that testing for S043 must be done by a Recognised 
Testing Authority.
After verifying the latest list of RTA´s 
http://www.nata.asn.au/downloads/rtalist.pdf of March 7th, only 1 lab seems to 
be listed as RTA and it is not even 
located in Australia, but in the US.
From my reading of the Labelling Notice, Schedule 3 seems to give however 
other possibilities to comply, like a Certification or Competent body.
Any-one can shed some light on this issue? 

Regards,
Kris Carpentier

RE: creepage v breakdown voltage

2002-03-15 Thread Gary McInturff

Remember that some of that distance, I believe, accounts for when the 
boards get dirty, and the pollutants build up and reduce the spacings. When you 
test the boards during the evaluation they are almost always clean with no 
pollution build-up.
Gary

-Original Message-
From: MCA Compliance [mailto:bally...@iolfree.ie]
Sent: Friday, March 15, 2002 4:39 AM
To: Emc-Pstc Post
Subject: RE: creepage v breakdown voltage



Peter
I agreee with your comment, but, I have seen lots of boards (material group
III) pass high pot tests at 1.5kV with only 2 mm creepage on the boards.
yet, 950 specifies 2.5mm for basic insulation.

This is why I am after some independent experimental test data correlating
creepage and dielectric strength, with different board material properties
taken into account.

I suppose to flip it around, if a board passes the hi-pot for 1 minute with
2 mm creepage (and the fact that it passes the hi-pot, means the clearance
must also have been adequate?), why does 60950 look for 2.5mm creepage ???

rgds

Brian

-Original Message-
From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
Sent: 15 March 2002 12:00
To: 'MCA Compliance'; Emc-Pstc Post
Subject: RE: creepage v breakdown voltage


Brian,

Your PCB manufacturer should be able to tell you what spacings to keep in
order to withstand the test voltages. It all depends on the base material
used for the PCB which all have different dielectric strength properties.
Remember, the standards reference a minimum creepage distance AND you must
still pass the electric strength tests.


This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.


PETER S. MERGUERIAN
Technical Director
I.T.L. (Product Testing) Ltd.
26 Hacharoshet St., POB 211
Or Yehuda 60251, Israel
Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019
Mobile: + 972-(0)54-838175
http://www.itl.co.il
http://www.i-spec.com





-Original Message-
From: MCA Compliance [mailto:bally...@iolfree.ie]
Sent: Friday, March 15, 2002 11:54 AM
To: Emc-Pstc Post
Subject: creepage v breakdown voltage



does data exist which correlates creepage distance on a pcb with
hi-potential test voltage it should withstand ?

for example, I know 60950 sugests a test voltage of 1500Vrms for 1 minute
and a creepage of 2.5mm (material group III) for basic insulation.

How did they arrive at 2.5 mm ???

Brian
email: i...@mcac.ie


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Wire spool labeling requirements

2002-03-15 Thread Gary McInturff

Doug, 
I have no problem doing just that with my projects. The online data 
thing gives away the source so we are talking about the same folks - but 
different offices. Although I know that the engineer involved in my projects 
pulls copies of the full reports for the device, as he should, to check for 
miscellaneous items that aren't on the Listing or Yellow recognized cards.
Internally I verify the part has recognition and send the manufacturers 
file number off, - after checking the conditions of acceptability.
As long as I am at it, after calling the UL follow-up-services regional 
office, I quit having trouble with surface marked wiring. It took three things, 
A Card that identified the manufacture as having Listed/Recognized wiring, the 
logos and ratings on  the wiring, and a small discussion about the definition 
of package, and the fact that other components have nothing more than surface 
markings on products. Its not my responsibility to enforce UL's markings policy 
and a tag can be as easily forged as the wiring.
As I've said here in the past, if you don't agree with them challenge 
it. The standards are a two-edged sword, they have to live by them as well. If 
the can't show you where it is they can't enforce it.
One of the problems with the NRTL's, all of them, is inconsistent 
interpretation - or worse yet the fact that it need be interpreted at all. 
Throw in the fact that occasionally they make up stuff, called desk standards 
and you find there are times when the extra time spent makes your, and their, 
lives easier. I haven't notice being put into the bucket of nasty clients and 
enjoy a good working relationship with the guys on the other side of the fence 
so just challenging a thorny issue doesn't have hidden costs in the long run. I 
don't win them all and often learn something along the way. 
(Putting on my bell bottoms and tie dyed shirt for the big finish here)
Power to the people! (Stepping off the soap box for now) 
Gary
 

-Original Message-
From: Doug McKean [mailto:dmck...@corp.auspex.com]
Sent: Thursday, March 14, 2002 5:06 PM
To: emc-p...@ieee.org
Subject: Re: Wire spool labeling requirements



 I find it interesting, the possibility that to some degree UL (and others)
 cast doubt on the validity of their own markings and logos by requiring
that
 we as users validate labeling on the wire spool.  I understand the concern

Just to underscore this, I haven't been able to validate
approvals on parts or products to a well known NRTL
without having an actual copy of the approval that was
sent to the vendor of said device from the approving agency.
And it doesn't make a difference even if I can prove the
company and device approval are listed on the website
of the NRTL. - Doug McKean




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: SDR in the US

2002-03-15 Thread djumbdenstock

Kim,

I believe the Part you desire is 47 CFR 15.231 (Part 15, clause 231)
...the intentional radiator is restricted to the transmission of a control
signal such as those used with alarm systems, door openers, remote openers,
etc.  The fundamental is allowed a level of 3,700 - 12,500 uV/m from
260-470 MHz. Other frequency ranges have other limits; some restrictions
apply (sound like a lawyer?) ;-)

If you would rather do 902-908 MHz, 15.247 applies for spread spectrum, or
15.249 for other applications.  Spread spectrum allows more power but is
complicated by the spread spectrum requirements.  15.249 is more restrictive
in the power allowed.   I have attached a link for your convenience.

http://www.fcc.gov/oet/info/rules/

Best regards,

Don Umbdenstock
Sensormatic Electronics Corp
Tyco International

 --
 From: Kim Boll Jensen[SMTP:kimb...@post7.tele.dk]
 Reply To: Kim Boll Jensen
 Sent: Friday, March 15, 2002 7:35 AM
 To:   treg; EMC-PSTC
 Subject:  SDR in the US
 
 File: kimboll.vcf
 Hi all
 
 I have a Radio remote control for use in private homes
 
 I have understood that 433MHz SRD is not possible in the US in the same
 way as in EU.
 
 Some FCC notes points to 902 - 928 MHz for this kind of equipment.
 
 I'm trying to understand the FCC but I'm hindered by no possible
 download of relevant 47CFR code
 
 (http://www.access.gpo.gov/nara/cfr/waisidx_00/47cfr90_00.html doesn't
 seem to function at the moment)
 
 Is it correct that 902 -928 is allowed in part 15 without license if
 output is below 50mV/m at 3m, and if I need more power I will have to
 apply for a general license under part 90 ?
 
 Please help me !
 
 
 Best regards,
 
 Kim Boll Jensen
 Bolls Raadgivning
 Denmark
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: creepage v breakdown voltage

2002-03-15 Thread Stephen Phillips

  Try this.

  For flat electrodes, at sea level, and normal temperatures;
eliminating such factors as humidity, dust, illumination, and
the electrode materials; the molecules of the gases that
compose common air, get ionized in the presence of an
electric field of about 30KV/cm.

  So, since - electrode shape, barometric pressure, temperature,
humidity, dust, presence of photons, and composition of the
materials and shape of the electrodes, as well as the
composition of the 'air' (gases), and also any other local
(competing) electromagnetic fields - can all affect the definitive
voltage that will jump a given gap - is it any wonder that the
standard includes what otherwise appears to be a lot of
slop.

  Stephen


At 09:28 AM 3/15/2002, Roman, Dan wrote:


I was looking into this a few weeks ago also and found similar results
experimentally as other posters have mentioned.  The only voltage per inch
spec I was able to come up with was in the IPC specs but they were way out
of whack!  0.12 mils per volt or more meaning that 2121 Vdc distance that
the safety standards say should be 2.5 mm the IPC spec is saying you need 5
mm

While the safety standards may be conservative to allow for temperature,
grease, dirt, etc. over time the IPC specs are ultra-conservative.  The
dielectric tables for hermetically sealed material group III is probably
closer to the actual breakdown but I never did find a spec I could use to
predict the ACTUAL breakdown voltage of a gap between traces.  If anyone
finds a rule of thumb or equation I'd like to have it also.

Dan

-Original Message-
From: MCA Compliance [mailto:bally...@iolfree.ie]
Sent: Friday, March 15, 2002 4:54 AM
To: Emc-Pstc Post
Subject: creepage v breakdown voltage



does data exist which correlates creepage distance on a pcb with
hi-potential test voltage it should withstand ?

for example, I know 60950 sugests a test voltage of 1500Vrms for 1 minute
and a creepage of 2.5mm (material group III) for basic insulation.

How did they arrive at 2.5 mm ???

Brian
email: i...@mcac.ie

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: creepage v breakdown voltage

2002-03-15 Thread Robert Macy

Doing high voltage power supplies we found we always got in trouble using
20,000 V/in and things worked well when we kept below 10,000 V/in.

Metric that's 790 V/mm and 390 V/mm

This was free air and not some kind of pointy structure.

  - Robert -

   Robert A. Macy, PEm...@california.com
   408 286 3985  fx 408 297 9121
   AJM International Electronics Consultants
   619 North First St,   San Jose, CA  95112


-Original Message-
From: Roman, Dan dan.ro...@intel.com
To: 'MCA Compliance' bally...@iolfree.ie; Emc-Pstc Post
emc-p...@majordomo.ieee.org
List-Post: emc-pstc@listserv.ieee.org
Date: Friday, March 15, 2002 6:49 AM
Subject: RE: creepage v breakdown voltage



I was looking into this a few weeks ago also and found similar results
experimentally as other posters have mentioned.  The only voltage per inch
spec I was able to come up with was in the IPC specs but they were way out
of whack!  0.12 mils per volt or more meaning that 2121 Vdc distance that
the safety standards say should be 2.5 mm the IPC spec is saying you need 5
mm

While the safety standards may be conservative to allow for temperature,
grease, dirt, etc. over time the IPC specs are ultra-conservative.  The
dielectric tables for hermetically sealed material group III is probably
closer to the actual breakdown but I never did find a spec I could use to
predict the ACTUAL breakdown voltage of a gap between traces.  If anyone
finds a rule of thumb or equation I'd like to have it also.

Dan

-Original Message-
From: MCA Compliance [mailto:bally...@iolfree.ie]
Sent: Friday, March 15, 2002 4:54 AM
To: Emc-Pstc Post
Subject: creepage v breakdown voltage



does data exist which correlates creepage distance on a pcb with
hi-potential test voltage it should withstand ?

for example, I know 60950 sugests a test voltage of 1500Vrms for 1 minute
and a creepage of 2.5mm (material group III) for basic insulation.

How did they arrive at 2.5 mm ???

Brian
email: i...@mcac.ie




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: creepage v breakdown voltage

2002-03-15 Thread Chris Maxwell


*snippped from Stephen Phillips email**
  The geometry of the surface across which the potential 
is laid matters too (curves, points, parallel planes), 
doesn't it.  Again, maybe the committee just added 
guaranteed slop.  


*

Yes, definitely.  The Electric field gradients increase dramatically
around sharp metal points.  (if you were graphing the electric field,
the equipotentials get closer).  The breakdown distance between two
pointy electrodes is much less than the breakdown distance between two
round balls. 

A great reference for intuitively sketching field lines around
conductors can be found on pages 53-55 of Fields and Waves in
Communication Electronics, second edition by Ramo, Whinnery and Van
Duzer.

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797
8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 


  

 -Original Message-
 From: Stephen Phillips [SMTP:step...@cisco.com]
 Sent: Friday, March 15, 2002 7:50 AM
 To:   MCA Compliance
 Cc:   Emc-Pstc Post
 Subject:  RE: creepage v breakdown voltage
 
   Humidity matters.  
 
Some years back, when doing some experiments 
 around this subject - I too was surprised at just how 
 much voltage different gaps could bear, such that the 
 standard seemed gross overkill.  But in a less than 
 purely scientific way, I decided to breath (just breath, 
 not blow) in the vicinity of the withstand, and got different 
 results.  It was winter (dry air), and my merely breathing 
 normally - within about a foot of the gap under test - 
 caused a 400V(DC) lower breakdown.  I know the 
 standard doesn't hold us to tight humidity spec's, 
 only pollution degree, but maybe the committee that 
 came up with this added enough margin to be sure 
 to always cover such issues.  
 
   The geometry of the surface across which the potential 
 is laid matters too (curves, points, parallel planes), 
 doesn't it.  Again, maybe the committee just added 
 guaranteed slop.  
 
   There is no such thing as too safe.  
   Stephen  
 
 
 At 07:39 AM 3/15/2002, MCA Compliance wrote:
 
 
 
   Peter
   I agreee with your comment, but, I have seen lots of boards
 (material group
   III) pass high pot tests at 1.5kV with only 2 mm creepage on the
 boards.
   yet, 950 specifies 2.5mm for basic insulation.
   
   This is why I am after some independent experimental test data
 correlating
   creepage and dielectric strength, with different board material
 properties
   taken into account.
   
   I suppose to flip it around, if a board passes the hi-pot for 1
 minute with
   2 mm creepage (and the fact that it passes the hi-pot, means the
 clearance
   must also have been adequate?), why does 60950 look for 2.5mm
 creepage ???
   
   rgds
   
   Brian
   
   -Original Message-
   From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
   Sent: 15 March 2002 12:00
   To: 'MCA Compliance'; Emc-Pstc Post
   Subject: RE: creepage v breakdown voltage
   
   
   Brian,
   
   Your PCB manufacturer should be able to tell you what spacings
 to keep in
   order to withstand the test voltages. It all depends on the base
 material
   used for the PCB which all have different dielectric strength
 properties.
   Remember, the standards reference a minimum creepage distance
 AND you must
   still pass the electric strength tests.
   
   
   This e-mail message may contain privileged or confidential
 information. If
   you are not the intended recipient, you may not disclose, use,
 disseminate,
   distribute, copy or rely upon this message or attachment in any
 way. If you
   received this e-mail message in error, please return by
 forwarding the
   message and its attachments to the sender.
   
   
   PETER S. MERGUERIAN
   Technical Director
   I.T.L. (Product Testing) Ltd.
   26 Hacharoshet St., POB 211
   Or Yehuda 60251, Israel
   Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019
   Mobile: + 972-(0)54-838175
   http://www.itl.co.il/
   http://www.i-spec.com/
   
   
   
   
   
   -Original Message-
   From: MCA Compliance [mailto:bally...@iolfree.ie]
   Sent: Friday, March 15, 2002 11:54 AM
   To: Emc-Pstc Post
   Subject: creepage v breakdown voltage
   
   
   
   does data exist which correlates creepage distance on a pcb with
   hi-potential test voltage it should withstand ?
   
   for example, I know 60950 sugests a test voltage of 1500Vrms for
 1 minute
   and a creepage of 2.5mm (material group III) for basic
 insulation.
   
 

Re: CE Mark on Product Packaging

2002-03-15 Thread Scott Lemon

Correct me if I am wrong, but I do not believe the statement below is entirely
correct.  It is my understanding (per EMC directive and published guidelines)
that the Manufacturer or Authorized Representative is responsible for affixing
the CE marking and drawing up the DoC and that only the Authorized Rep (if
applicable) must be established within the community.  In other words, the
Manufacturer (who draws up the DoC and tech docs) does not have to be
established in the community, but if an Authorized Rep is used, they must be.
It is clear that when neither the Manufacturer or the Auth Rep are established
within the community, the obligation to keep the DoC available is the
responsibility of the party placing the product on the market (importer).

Scott Lemon
Caspian Networks

Bill Ellingford wrote:

 Under the EMC directive, the person making a DOC and
 placing the goods on the market would be an EU resident.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: creepage v breakdown voltage

2002-03-15 Thread Scott Barrows

Hi All,
The Creepage and clearance specifications take into account the long term
degradation of spacings due to environmental conditions. Just because it will
pass the test today when it is clean and pure does not mean that this condition
will last forever.

Scott

MCA Compliance wrote:

 Peter
 I agreee with your comment, but, I have seen lots of boards (material group
 III) pass high pot tests at 1.5kV with only 2 mm creepage on the boards.
 yet, 950 specifies 2.5mm for basic insulation.

 This is why I am after some independent experimental test data correlating
 creepage and dielectric strength, with different board material properties
 taken into account.

 I suppose to flip it around, if a board passes the hi-pot for 1 minute with
 2 mm creepage (and the fact that it passes the hi-pot, means the clearance
 must also have been adequate?), why does 60950 look for 2.5mm creepage ???

 rgds

 Brian

 -Original Message-
 From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
 Sent: 15 March 2002 12:00
 To: 'MCA Compliance'; Emc-Pstc Post
 Subject: RE: creepage v breakdown voltage

 Brian,

 Your PCB manufacturer should be able to tell you what spacings to keep in
 order to withstand the test voltages. It all depends on the base material
 used for the PCB which all have different dielectric strength properties.
 Remember, the standards reference a minimum creepage distance AND you must
 still pass the electric strength tests.

 This e-mail message may contain privileged or confidential information. If
 you are not the intended recipient, you may not disclose, use, disseminate,
 distribute, copy or rely upon this message or attachment in any way. If you
 received this e-mail message in error, please return by forwarding the
 message and its attachments to the sender.

 PETER S. MERGUERIAN
 Technical Director
 I.T.L. (Product Testing) Ltd.
 26 Hacharoshet St., POB 211
 Or Yehuda 60251, Israel
 Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019
 Mobile: + 972-(0)54-838175
 http://www.itl.co.il
 http://www.i-spec.com

 -Original Message-
 From: MCA Compliance [mailto:bally...@iolfree.ie]
 Sent: Friday, March 15, 2002 11:54 AM
 To: Emc-Pstc Post
 Subject: creepage v breakdown voltage

 does data exist which correlates creepage distance on a pcb with
 hi-potential test voltage it should withstand ?

 for example, I know 60950 sugests a test voltage of 1500Vrms for 1 minute
 and a creepage of 2.5mm (material group III) for basic insulation.

 How did they arrive at 2.5 mm ???

 Brian
 email: i...@mcac.ie

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: creepage v breakdown voltage

2002-03-15 Thread Roman, Dan

I was looking into this a few weeks ago also and found similar results
experimentally as other posters have mentioned.  The only voltage per inch
spec I was able to come up with was in the IPC specs but they were way out
of whack!  0.12 mils per volt or more meaning that 2121 Vdc distance that
the safety standards say should be 2.5 mm the IPC spec is saying you need 5
mm

While the safety standards may be conservative to allow for temperature,
grease, dirt, etc. over time the IPC specs are ultra-conservative.  The
dielectric tables for hermetically sealed material group III is probably
closer to the actual breakdown but I never did find a spec I could use to
predict the ACTUAL breakdown voltage of a gap between traces.  If anyone
finds a rule of thumb or equation I'd like to have it also.

Dan

-Original Message-
From: MCA Compliance [mailto:bally...@iolfree.ie]
Sent: Friday, March 15, 2002 4:54 AM
To: Emc-Pstc Post
Subject: creepage v breakdown voltage



does data exist which correlates creepage distance on a pcb with
hi-potential test voltage it should withstand ?

for example, I know 60950 sugests a test voltage of 1500Vrms for 1 minute
and a creepage of 2.5mm (material group III) for basic insulation.

How did they arrive at 2.5 mm ???

Brian
email: i...@mcac.ie

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Alternate Country Approvals

2002-03-15 Thread cecil . gittens



Hi All,


 I have tested ITE products to the FCC, EN55022 and EN55024 Standards.
Does anyone know what additional EMC approvals and documentation is
required for Poland, Russia
and Switzerland?

Thanks for your help

Cecil


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: SDR in the US

2002-03-15 Thread richwoods

Try downloading from this location: 
http://www.fcc.gov/oet/info/rules/

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: Kim Boll Jensen [mailto:kimb...@post7.tele.dk]
Sent: Friday, March 15, 2002 7:36 AM
To: treg; EMC-PSTC
Subject: SDR in the US


Hi all

I have a Radio remote control for use in private homes

I have understood that 433MHz SRD is not possible in the US in the same
way as in EU.

Some FCC notes points to 902 - 928 MHz for this kind of equipment.

I'm trying to understand the FCC but I'm hindered by no possible
download of relevant 47CFR code

(http://www.access.gpo.gov/nara/cfr/waisidx_00/47cfr90_00.html doesn't
seem to function at the moment)

Is it correct that 902 -928 is allowed in part 15 without license if
output is below 50mV/m at 3m, and if I need more power I will have to
apply for a general license under part 90 ?

Please help me !


Best regards,

Kim Boll Jensen
Bolls Raadgivning
Denmark

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: creepage v breakdown voltage

2002-03-15 Thread Stephen Phillips

  Humidity matters.

   Some years back, when doing some experiments
around this subject - I too was surprised at just how
much voltage different gaps could bear, such that the
standard seemed gross overkill.  But in a less than
purely scientific way, I decided to breath (just breath,
not blow) in the vicinity of the withstand, and got different
results.  It was winter (dry air), and my merely breathing
normally - within about a foot of the gap under test -
caused a 400V(DC) lower breakdown.  I know the
standard doesn't hold us to tight humidity spec's,
only pollution degree, but maybe the committee that
came up with this added enough margin to be sure
to always cover such issues.

  The geometry of the surface across which the potential
is laid matters too (curves, points, parallel planes),
doesn't it.  Again, maybe the committee just added
guaranteed slop.

  There is no such thing as too safe.
  Stephen


At 07:39 AM 3/15/2002, MCA Compliance wrote:


Peter
I agreee with your comment, but, I have seen lots of boards (material group
III) pass high pot tests at 1.5kV with only 2 mm creepage on the boards.
yet, 950 specifies 2.5mm for basic insulation.

This is why I am after some independent experimental test data correlating
creepage and dielectric strength, with different board material properties
taken into account.

I suppose to flip it around, if a board passes the hi-pot for 1 minute with
2 mm creepage (and the fact that it passes the hi-pot, means the clearance
must also have been adequate?), why does 60950 look for 2.5mm creepage ???

rgds

Brian

-Original Message-
From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
Sent: 15 March 2002 12:00
To: 'MCA Compliance'; Emc-Pstc Post
Subject: RE: creepage v breakdown voltage


Brian,

Your PCB manufacturer should be able to tell you what spacings to keep in
order to withstand the test voltages. It all depends on the base material
used for the PCB which all have different dielectric strength properties.
Remember, the standards reference a minimum creepage distance AND you must
still pass the electric strength tests.


This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.


PETER S. MERGUERIAN
Technical Director
I.T.L. (Product Testing) Ltd.
26 Hacharoshet St., POB 211
Or Yehuda 60251, Israel
Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019
Mobile: + 972-(0)54-838175
http://www.itl.co.il
http://www.i-spec.com





-Original Message-
From: MCA Compliance [mailto:bally...@iolfree.ie]
Sent: Friday, March 15, 2002 11:54 AM
To: Emc-Pstc Post
Subject: creepage v breakdown voltage



does data exist which correlates creepage distance on a pcb with
hi-potential test voltage it should withstand ?

for example, I know 60950 sugests a test voltage of 1500Vrms for 1 minute
and a creepage of 2.5mm (material group III) for basic insulation.

How did they arrive at 2.5 mm ???

Brian
email: i...@mcac.ie


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: creepage v breakdown voltage

2002-03-15 Thread MCA Compliance

Peter
I agreee with your comment, but, I have seen lots of boards (material group
III) pass high pot tests at 1.5kV with only 2 mm creepage on the boards.
yet, 950 specifies 2.5mm for basic insulation.

This is why I am after some independent experimental test data correlating
creepage and dielectric strength, with different board material properties
taken into account.

I suppose to flip it around, if a board passes the hi-pot for 1 minute with
2 mm creepage (and the fact that it passes the hi-pot, means the clearance
must also have been adequate?), why does 60950 look for 2.5mm creepage ???

rgds

Brian

-Original Message-
From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
Sent: 15 March 2002 12:00
To: 'MCA Compliance'; Emc-Pstc Post
Subject: RE: creepage v breakdown voltage


Brian,

Your PCB manufacturer should be able to tell you what spacings to keep in
order to withstand the test voltages. It all depends on the base material
used for the PCB which all have different dielectric strength properties.
Remember, the standards reference a minimum creepage distance AND you must
still pass the electric strength tests.


This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.


PETER S. MERGUERIAN
Technical Director
I.T.L. (Product Testing) Ltd.
26 Hacharoshet St., POB 211
Or Yehuda 60251, Israel
Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019
Mobile: + 972-(0)54-838175
http://www.itl.co.il
http://www.i-spec.com





-Original Message-
From: MCA Compliance [mailto:bally...@iolfree.ie]
Sent: Friday, March 15, 2002 11:54 AM
To: Emc-Pstc Post
Subject: creepage v breakdown voltage



does data exist which correlates creepage distance on a pcb with
hi-potential test voltage it should withstand ?

for example, I know 60950 sugests a test voltage of 1500Vrms for 1 minute
and a creepage of 2.5mm (material group III) for basic insulation.

How did they arrive at 2.5 mm ???

Brian
email: i...@mcac.ie


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: creepage v breakdown voltage

2002-03-15 Thread Peter Merguerian

Brian,

Your PCB manufacturer should be able to tell you what spacings to keep in
order to withstand the test voltages. It all depends on the base material
used for the PCB which all have different dielectric strength properties.
Remember, the standards reference a minimum creepage distance AND you must
still pass the electric strength tests.


This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.


PETER S. MERGUERIAN
Technical Director
I.T.L. (Product Testing) Ltd.
26 Hacharoshet St., POB 211
Or Yehuda 60251, Israel
Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019
Mobile: + 972-(0)54-838175
http://www.itl.co.il
http://www.i-spec.com





-Original Message-
From: MCA Compliance [mailto:bally...@iolfree.ie]
Sent: Friday, March 15, 2002 11:54 AM
To: Emc-Pstc Post
Subject: creepage v breakdown voltage



does data exist which correlates creepage distance on a pcb with
hi-potential test voltage it should withstand ?

for example, I know 60950 sugests a test voltage of 1500Vrms for 1 minute
and a creepage of 2.5mm (material group III) for basic insulation.

How did they arrive at 2.5 mm ???

Brian
email: i...@mcac.ie


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Voltage Spikes on Power Lines etc

2002-03-15 Thread Bill Ellingford

One clear piece of evidence is that safety standards committees always
specify much larger creepage and clearance distances for externaly supplied
hazardous voltages than for those generated within a product.  A good
example are the two sets of tables in IEC or EN 60 950.  This is to
accomodate high voltage spikes and lightning induced voltages etc.
Bill Ellingford

-Original Message-
From: George Stults [mailto:george.stu...@watchguard.com]
Sent: 14 March 2002 17:17
To: emc-p...@majordomo.ieee.org
Subject: Voltage Spikes on Power Lines etc




Hi Folks,

I am trying right now to convince some folks that power line voltage spike
problems can be and usually are severe enough to degrade or kill ITE
products that don't have adequate over-voltage protection.   I found a link
using Google that describes the problems [
http://www.kalglo.com/powrline.htm ] but I'm looking for additional links to
specifics or summaries if any one knows of such.

Thanks in advance.

George S. 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


*

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: CE Mark on Product Packaging

2002-03-15 Thread Bill Ellingford

I beleive the change in stance is due to the change in requirement regarding
a European presence.  Under the EMC directive, the person making a DOC and
placing the goods on the market would be an EU resident.  The RTTE allows
parties outside of the EU to make the DOC and hold the Technical file, it is
the person placing product on the market who carries legal liability.  This
means that goods can be imported into the EU with the CE declaration so
marking the packaging resolves customs issues in these circumstances.

Bill Ellingford

-Original Message-
From: Russell [mailto:r@totalise.co.uk]
Sent: 14 March 2002 15:39
To: emc-pstc
Subject: CE Mark on Product Packaging



Does anybody know why the placing of the CE mark on product packaging is 
compulsory under the RTTE Directive, yet optional under the EMC and LVD 
Directives?

Or am I wrong?

Only curious,

Russell.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


*

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


creepage v breakdown voltage

2002-03-15 Thread MCA Compliance

does data exist which correlates creepage distance on a pcb with
hi-potential test voltage it should withstand ?

for example, I know 60950 sugests a test voltage of 1500Vrms for 1 minute
and a creepage of 2.5mm (material group III) for basic insulation.

How did they arrive at 2.5 mm ???

Brian
email: i...@mcac.ie


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: IP67 Water Ingress Testing

2002-03-15 Thread Peter Merguerian

Alex,

I am currently testing some lithium ion battery pack for a major
international renowned manufacturer.  None of their lithium ion battery
packs are vented and many are already Accessory Listed to UL60950. This
leads me to believe that venting is not a problem with such 
battery packs. However, you must protect the cells from overcharge and
discharge under normal and abnormal conditions.

Regards


This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.


PETER S. MERGUERIAN
Technical Director
I.T.L. (Product Testing) Ltd.
26 Hacharoshet St., POB 211
Or Yehuda 60251, Israel
Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019
Mobile: + 972-(0)54-838175
http://www.itl.co.il
http://www.i-spec.com





-Original Message-
From: McKinney, Alex [mailto:mckinne...@ems-t.com]
Sent: Thursday, March 14, 2002 9:51 PM
To: IEEE EMC-PSTC Forum (E-mail)
Subject: IP67 Water Ingress Testing



All,

We are currently working on a new handheld product that will be tested for
IP67 Water Ingress (1 meter submersion for 30 minutes) and we are trying to
determine the safety impact of not including the lithium ion battery pack as
part of this rating.  This product will be UL60950 Listed.  One question
that has also been asked of me is whether this battery pack needs to be
vented.  A few lithium ion cell manufactures whom I have researched on this
say that the pack should definitely be vented.  If vented then the IP67
rating on the battery pack is definitely out of the question without
designing some costly pressure release mechanism.

I guess my ultimate question is, how safe is a lithium ion battery pack if
water is introduced in to the circuit?

Any help is greatly appreciated.

Regards,

Alex McKinney
Safety Engineer
LXE, Inc.
Tel: 770-447-4224 x3606
Fax: 770-447-6928



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list