Hello Group:

I am glad to see the recent NEBS related discussions. I find them
interesting and relevant. So while I am thinking about NEBS, I thought I'd
ask a couple of questions.

I would like to understand more clearly the relationship between Central
Offices and local building codes.

I understand that the NEC basically exempts CO's.  And that would mean that
any local AHJ adopting the NEC unchanged would have the same exemption.

But I am wondering how the CO's themselves view the local building codes.
Maybe they just ignore them, but perhaps they voluntarily try to meet them ?
Of course there's a lot of the actual requirements that are covered by the
NEBS requirements, but it would seem like some things (mains service
entrance ?) may not be covered.

Also, where exactly is the line that divides the exempt CO area from where
the local codes are applicable ?


As I think about it now, I don't recall the specific wording of the NEC's
exemption, but It would seem that it would include any requirement for using
Listed equipment or components.  Although GR1089 does seem to require
Listing for AC mains connected equipment, do some companies require Listing
for equipment connected to the CO DC supply ?

The benefit of your experience and thoughtful comments will be appreciated.

Thanks

Richard Payne
Tektronix, Inc.
Product Safety Engineering
Tel:  503 627-1820
Fax: 503 627-3838
email:  richard.pa...@tektronix.com 





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Stumped

2002-10-14 Thread Ken Javor

Forum,

I have made some measurements and gotten results which are at odds with my
intuition.  I am wondering if someone out there can shed some light on this
subject.

I was interested in the losses associated with rf traveling on a twisted
shielded pair cable.  The scenario is that a length of this TSP cable is
exposed to an rf environment (as in a test chamber during IEC 1000-4-3
testing) and then the cable penetrates a bulkhead using a grounded connector
that provides excellent shield termination, and the cable continues on the
other side in the pristine rf environment of a shielded control chamber, say
for several meters.  The question is, how much rf signal is at the final
destination point vs. at the bulkhead.  The concern is common mode, not
differential mode.  Meaning that the twisted pair can be looked at like
coax, with an identical signal on both inner conductors relative to the
shield.  I expected losses that would be on the same order or lower than
that associated with off-the-shelf coax types like RG-58.  Instead my losses
were dramatically higher.

Following is my measurement technique.

I measured the transmission line impedance of the TSP in the following way.
I tied the center conductors together.  I shorted the center conductors to
the shield at one end, and measured the inductance, using an LCR meter.  I
opened the connection and measured the open circuit capacitance.  The square
root of the l/c ratio is the characteristic impedance.  I built matching
networks to get from 50 Ohms to the measured impedances which ranged from 15
- 25 Ohms for a variety of different cables.  For each cable, I built two
pairs of identical matching networks:

4 each: 50 to RC adapters

I used an HP 4195A network analyzer, over a range of frequencies 0.1 - 500
MHz.  The set up was as follows.  There was 16 dB of pad coming out of the
source (including the 6 dB splitter).  There was 10 dB of pad at the
reference and test ports.  Results showed little evidence of vswr.

Coming out of the source, there is the 6 dB splitter.  Between one port of
the splitter and the reference port, I inserted one pair of the matching
networks:

Splitter output connects to  50 Ohm to RC adapter connects to RC to 50 Ohm
adapter connects to reference port.

I connected the exact same sequence between the other splitter output and
the test port.  The network analyzer displayed the dB ratio of the test port
signal relative to the reference signal.  This would be the difference in
loss between each pair of matching networks.  If I had built them perfectly,
the analyzer should have shown 0 dB difference.  Actual differences were
under 3 dB.

Then I inserted the cable-under-test between the RC connections on the two
matching networks in the test port side.

The loss associated with cable-under-test (CUT) is the difference between
the losses measured with the CUT in place and with the matching networks
directly connected.

The numbers I got were considerably higher than even a high loss coax such
as RG-174.  Because real coax uses a much thicker dielectric material than
just the insulation around a TSP center conductor, my gut feel is that
losses should be lower than for 50 Ohm coax.  I expect that materials picked
to be dielectrics for coax have low loss tangents relative to wire
insulation, but I don't have a feel for whether the difference in loss
tangents can make up for the extra thickness of the dielectric in real coax.
Can any one tell me if either my test set up or my expectations are wrong,
and why?

Thank you.

Ken Javor

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: NEBS Level 3 Plus

2002-10-14 Thread Dave Lorusso
Richard,

Verizon does not recognize “NEBS Level 3” as called out in
Telcordia/Bellcore SR-3580.  They had input into this document, but later
regretted it.  What Verizon does recognize is their own checklist at
www.verizonnebs.com http://www.verizonnebs.com/ .  The confusion comes
from the fact that the SR-3580 requirements are scattered throughout Verizon
’s checklist.

At the NEBS 2002 Conference last week, Verizon introduced their latest
revision of their checklist.  They are trying to incorporate all of the
other RBOC’s and ATT requirements into this document.  I caution everyone to
obtain the specific checklists/requirements from each or your potential
customers and comply with them.

“NEBS Plus” is mentioned in an article I wrote for Evaluation Engineering
“What Every Startup Needs to Know About NEBS”:

http://www.evaluationengineering.com/archive/articles/0502emc.htm

The intent was to highlight that just meeting “NEBS Level 3” was not enough
to get equipment into your customer’s central offices.

In summary, there is no “NEBS Level 3 Plus” requirement, there are only
customer requirements.

Best regards,

Dave Lorusso
Lorusso Technologies, LLC
“Your NEBS, Product Safety and EMC Solution”
www.lorusso.com http://www.lorusso.com/
www.nebs-faq.com http://www.nebs-faq.com/
512.695.5871 (phone)
512.233.2939 (fax)

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Georgerian, Richard
Sent: Monday, October 14, 2002 11:10 AM
To: IEEE emc-pstc
Subject: NEBS Level 3 Plus

Greetings All,
Does anyone know the specifics regarding Verizons NEBS Level 3 Plus
requirement. I have checked the Verizon web pages, the archives of the
emc-pstc, and the word search on the internet, with no luck. Otherwise, I
believe this is just another name for the checklist document that Verizon
uses and can be downloaded from their website.
Thanks in-advance.
Richard Georgerian
Compliance Engineer
Carrier Access Corporation
5395 Pearl Parkway
Boulder, CO 80301
USA
Tele: 303-218-5748  Fax: 303-218-5503
mailto:rgeorger...@carrieraccess.com



*
This e-mail transmission, and any documents, files, or previous
e-mail messages attached to it may contain information that is
confidential or legally privileged. If you are not the intended
recipient, or a person responsible for delivering it to the
intended recipient, you are hereby notified that you must not
read this transmission and that any disclosure, copying, printing,
distribution, or use of any of the information contained in or
attached to this transmission is strictly prohibited. If you have
received this transmission in error, please immediately notify the
sender by telephone or return e-mail and delete the original
transmission and its attachments without reading or saving them
in any manner. Thank you.
*


Re: Ground potential differences

2002-10-14 Thread Don_Borowski



The worst case of ground potential difference that I have heard of is a case
where guy got a shock from the grounded metal reflector of his trouble light
while working outside on his car.



Turns out the pump in his neighbor's well (fed from the same transformer) had a
  short from from line to ground. The potential difference between the
  ground tied to line at the neighbor's and the ground tied to neutral at
  this guy's house caused a voltage gradient along ground between the
  properties high enough to cause a shock when enough distance was covered
  (by the cord of the trouble light).



Don Borowski

Schweitzer Engineering Labs

Pullman, WA
This e-mail may contain SEL confidential information.  The opinions expressed
are not necessarily those of SEL.  Any unauthorized disclosure, distribution or
other use is prohibited.  If you received this e-mail in error, please notify
the sender, permanently delete it, and destroy any printout.  Thank you.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: NEBS Level 3 Plus

2002-10-14 Thread Juhasz, John (IndSys, GE Interlogix)
About 6-7 years ago when I was getting ready to go through NEBS for the first 
time, I found it to be confusing and
in some cases daunting.
At that time, Bellcore (now Telcordia) put on a NEBS seminar with a NEBS rep 
from each of the 
operating companies. That seminar proved to be the key that put it all together 
for me and made the job
easier. Further, the operating companies' representatives made themselves 
available to answer questions
specific to your product. This alone was worth it's wait in gold. And if I had 
any further questions, I could contact 
them at their offices.
 
If you can find a NEBS seminar that has reps from the operating companies, I 
suggest making the investment.
I believe there are several choices other than Telcordia for these seminars. 
Check around.
As the testing is so expensive, you want to do it right the first time. 
 
Just my opinion . . . 
 
John A. Juhasz 

GE Interlogix 
Fiber Options Div. 
Bohemia, NY 


Original Message-
From: Georgerian, Richard [mailto:rgeorger...@carrieraccess.com]
Sent: Monday, October 14, 2002 12:10 PM
To: IEEE emc-pstc
Subject: NEBS Level 3 Plus



Greetings All, 

Does anyone know the specifics regarding Verizons NEBS Level 3 Plus 
requirement. I have checked the Verizon web pages, the archives of the 
emc-pstc, and the word search on the internet, with no luck. Otherwise, I 
believe this is just another name for the checklist document that Verizon uses 
and can be downloaded from their website.

Thanks in-advance. 

Richard Georgerian 
Compliance Engineer 
Carrier Access Corporation 
5395 Pearl Parkway 
Boulder, CO 80301 
USA 

Tele: 303-218-5748  Fax: 303-218-5503   
mailto:rgeorger...@carrieraccess.com 




*
This e-mail transmission, and any documents, files, or previous
e-mail messages attached to it may contain information that is 
confidential or legally privileged. If you are not the intended 
recipient, or a person responsible for delivering it to the 
intended recipient, you are hereby notified that you must not 
read this transmission and that any disclosure, copying, printing,
distribution, or use of any of the information contained in or 
attached to this transmission is strictly prohibited. If you have 
received this transmission in error, please immediately notify the 
sender by telephone or return e-mail and delete the original 
transmission and its attachments without reading or saving them 
in any manner. Thank you.
*




Re: Ground potential differences

2002-10-14 Thread Doug McKean

I've no publications, but I did have personal experience with the
more destructive results with ground potential differences. At another
company, I witnessed  the insulation of a coax cable melting after
being connected between equipment in a lab where I worked.  The
problem being a difference in ground potential of 15vac.  That in and
of itself wasn't the problem. The amperage capacity through ground
of the mains system was the culprit.  Circa 1983 or so.

Turned out that the building was supplied by two electrical substations
at opposite ends of the building.  And for some strange reason, the
substations each shared about half the outlets in the lab. And the potential
difference was caused by the electricians connecting to slightly different
points on the transformers for ground.

The electricians were told and were able to fix the problem.

And as far as anything in the field showing a similar problem, I have
only dealt with one such instance.  And relating the substation
transformer ground tap story fixed it for them.

Regards, Doug McKean



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


NEBS Level 3 Plus

2002-10-14 Thread Georgerian, Richard
Greetings All,

Does anyone know the specifics regarding Verizons NEBS Level 3 Plus
requirement. I have checked the Verizon web pages, the archives of the
emc-pstc, and the word search on the internet, with no luck. Otherwise, I
believe this is just another name for the checklist document that Verizon
uses and can be downloaded from their website.

Thanks in-advance.

Richard Georgerian
Compliance Engineer 
Carrier Access Corporation
5395 Pearl Parkway
Boulder, CO 80301
USA

Tele: 303-218-5748  Fax: 303-218-5503
mailto:rgeorger...@carrieraccess.com




*
This e-mail transmission, and any documents, files, or previous
e-mail messages attached to it may contain information that is 
confidential or legally privileged.  If you are not the intended 
recipient, or a person responsible for delivering it to the 
intended recipient, you are hereby notified that you must not 
read this transmission and that any disclosure, copying, printing,
distribution, or use of any of the information contained in or 
attached to this transmission is strictly prohibited.  If you have 
received this transmission in error, please immediately notify the 
sender by telephone or return e-mail and delete the original 
transmission and its attachments without reading or saving them 
in any manner.  Thank you.
*


RE: Ground potential differences

2002-10-14 Thread Robert Johnson
Most earth potential differences come from load currents. Leakage
currents don't usually add up to very much. Electrical installations
should have one neutral to earth connection at the source of the system
(at the transformer or service entry). However many electrical
installations have branch panels with earth and neutral incorrectly
connected together at the panel. This means the neutral and earth paths
are parallel returns to the source. The IR drop generates potential
differences between different building areas. These stray currents can
amount to tens or hundreds of amps in big installations. Occasionally
these same currents come from miswired plugs or receptacles with neutral
and earth switched.  
To look for stray currents, put a clamp on ammeter around all mains
conductors together (phases and neutral). Often they will show up even
with the meter around the conduit. The resulting voltage differences in
grounds typically amount to 2 to 5 volts. It depends on load currents,
neutral resistance, ground resistance, current paths, etc. Transients
and noise of course include all those present on the load currents.
In residential applications where several services, each with their own
ground, are fed from a single transformer (also with its neutral
grounded). Several amps typically flow in the parallel earth connections
between houses, but this is irrelevant. The important thing to achieve
is an equipotential earth environment around the particular house
involved.

Bob Johnson
ITE Safety
 

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of John Woodgate
Sent: Saturday, October 12, 2002 12:53 PM
To: emc-p...@majordomo.ieee.org
Subject: Re: Ground potential differences


I read in !emc-pstc that Bailey, Jeff jbai...@mysst.com wrote (in
B115DFA26896D511BAB600105AA3493275EA3F@SSTMAIL) about 'Ground
potential differences' on Fri, 11 Oct 2002:

 I am interested
to know what the actual magnitude of ground differences may be from one
end
of a plant to another as well as where the numbers come from.  

It depends on what sort of equipment is present. Some things have very
high leakage current, putting a lot of amps in total into ground
conductors. Then, in old plants, there may be bad ground wiring that
doesn't show up as a fault.

Have they
been calculated or actually measured? 

Both. Usually after the problem has been discovered by chance. I've
measured 9 V over a distance of 20 m, but there are reports of much
higher voltages.

If shields are connected directly to
chassis at each node of a network will there be an effect of equalizing
the
ground levels through the network or will enough current flow to melt
the
shield of the cable?

Both are possible.
-- 
Regards, John Woodgate, OOO - Own Opinions Only.
http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go
to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list
attachment: Robert Johnson.vcf

CPE Telecom Equipment in Manitoba, Canada

2002-10-14 Thread Peter Merguerian

Dear All,

Has anyone heard of Canadian Manitoba provincial exemption regarding CPE
Telecom Equipment supplied by a Class 2 transformer or power supply? 

This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.




PETER S. MERGUERIAN
Technical Director
I.T.L. (Product Testing) Ltd.
26 Hacharoshet St., POB 211
Or Yehuda 60251, Israel
Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019
Mobile: + 972-(0)54-838175
http://www.itl.co.il
http://www.i-spec.com





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: LED's and laser safety?

2002-10-14 Thread John Woodgate

I read in !emc-pstc that richwo...@tycoint.com wrote (in 846BF526A205F8
4BA2B6045BBF7E9A6A04675859@flbocexu05) about 'LED's and laser safety?'
on Mon, 14 Oct 2002:

I sure would love to hear that argument.

Just get a time machine and go back to the meeting of the IEC TC85
working group on the subject. (;-)

Maybe someone on the group will let you read the Minutes; they are not
in the public domain.

It's a very sensible decision, IMHO. 
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


creepage et seq/spoof

2002-10-14 Thread Ted Rook

In the interests of my own credibility on the board (if I have any?) I should 
wave the white flag of surrender and own up to having posted a nonsense message 
on Oct 9th in response to the genuine request for information about creepage 
limits.
For some inexplicable reason my 'funny bone' was tickled and I wrote and posted 
the stuff about creepage and car batteries, copied below.

I offer my apologies to board members who have been inconvenienced by this 
piece of tom foolery. In future I'll make it much clearer when sending a spoof 
post.

As it happens the responses have been interesting, a testament to the 
intelligence and good humor of the board.

Thank You

Ted Rook

copy of the spoof post:
This is because when you double the voltage the power is proportional to a 
quarter of the current squared. In America the 120V power is at lower voltage 
but the current is twice as much and so the creepage is twice as well.

Very high voltage circuits hardly creep at all whereas low voltages creep the 
most. That is why you should never join the two negative terminals when you 
jump start a car, the car battery charging circuits have so much creepage they 
can melt the battery.

I though everybody knew that...

end of copy



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RTTE - receive only equipment

2002-10-14 Thread amund

As far as I understand the RTTED, the directive also applies to radio
receive-only equipment. But are we required to notify it for each member
state within EU, if it use non-harmonized frequency bands ?

Best regards
Amund Westin, Oslo / Norway




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: LED's and laser safety?

2002-10-14 Thread richwoods

I sure would love to hear that argument.

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: Warren Birmingham [mailto:war...@comfortjets.com]
Sent: Friday, October 11, 2002 6:06 PM
To: emc-p...@ieee.org
Subject: Re: LED's and laser safety?



Gary, I was recently in conversation with UL about LEDs whereas I am 
now being told that UL has convinced the European counterparts that 
LEDs are no longer considered Class I Lasers and the requirements for 
them to be tested as such has been dropped.  UL no longer treats them 
that way in their CB Reports.

Warren Birmingham
Epsilon-Mu Consultants
(510) 793-4806
email: war...@epsilon-mu.com
website: http://www.epsilon-mu.com


On Thursday, Oct 10, 2002, at 08:53 US/Pacific, Gary McInturff wrote:


   IEC-825 has incorporated LED's into the safety standard but, from 
 what I can tell, left a great deal of confusion.
   I typically deal with the 5 - 10 mcd devices and haven't been 
 required to provide any IEC-825 conformity proof for the Western 
 European test house. We may be jumping up to about 60 mcd and 
 non-focused devices and I don't know where the standard starts to 
 become concerned. I hate to buy the standard if it doesn't provide any 
 clarity for these types of parts.
   Could you folks clue me in?
   Gary



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Testing for dry joints - :)

2002-10-14 Thread Chris Chileshe

Scott asks ..

 So I give up - just what exactly is a dry joint?

Dry joint:

Electrical context: - A solder joint in which the electrical connection
between two conductors has been poorly formed by the solder material;
a consequence of incomplete formation or surfaces not properly wetted 
by the soldering material. Testing for these - as this group has shown - 
can be quite difficult. For more information on this type of dry joint, 
visit http://www.circuitsassembly.com

Glastonbury Context: - Crushed weed or herbs of various descriptions usually 
rolled up in light paper ( tabloid newspapers make excellent wrappers) and used 
exactly like cigarettes. Testing for a dry joint should be done in secrecy
as there are legal connotations associated with their use. In the interest
of keeping this forum blameless, the quest for more information on this type
of joint will be left to the reader.

Rastafarian context: - Sensemelia dat bringz I an' I guud vibes man! Jah be 
prezd! Tess-teeng nat necessary. U av' some',  u gretful, U pass it round, 
U a good frend, but wen U pass it around, keep it an de left 'and side.

Night club context: - A night club that has run out of liquor. Testing for 
these is visual. They will usually have no revelers.

Butcher's context: - Leg of lamb of the Halal variety, dried or well done . 
Testing for these is essential as 'succulent' might be the preferred 
end result of the culinary process.

Surgeon's context: - Quality and effectiveness of lubrication following hip
replacement. Testing inevitable.

Homeless context: - Welcome refuge on rainy nights.

Best regards

- Chris

-Original Message-
From:   Scott Douglas [SMTP:dougl...@naradnetworks.com]
Sent:   Friday, October 11, 2002 8:34 PM
To: Chris Chileshe; emc-p...@majordomo.ieee.org
Subject:Re: Testing for dry joints

Chris,

So I give up - just what exactly is a dry joint?

Scott

At 09:55 AM 10/9/2002 +0100, Chris Chileshe wrote:

Hi Group,

Probably not the appropriate forum but here goes anyway.

A colleague is finding numerous problems with subtle dry
joints (partial) between connectors and PCBs and is wondering
if there is a way - short of new procedures in process control - that
dry joints can be tested for?

The specific problem is that the joints appear to be electrically
sound to start with, meaning the units are getting through function
test, but once exposed to endurance (lengthy)  tests or worse
still, actual practical use, the gremlins begin to show. The fault
analysis almost invariably leads to a connector dry joint.

The connectors are rated for 6A DC continuous.

Any ideas how these can be picked up early or what measures you
have in production to eradicate these problems?

Regards

- Chris Chileshe
- Ultronics Ltd




This e-mail has been scanned for all viruses by Star Internet. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
  majord...@ieee.org
with the single line:
  unsubscribe emc-pstc

For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list



This e-mail has been scanned for all viruses by Star Internet. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk



This e-mail has been scanned for all viruses by Star Internet. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 

RE: Filtered D Types.

2002-10-14 Thread David Sproul
Many thanks for all your help.

Best regards,
David Sproul.


RE: Record Retention

2002-10-14 Thread Kevin Richardson

Randall,

As Fred Borda pointed out, for Australia (both C-Tick and A-Tick) is 5 years
for all documentation held in the product Compliance Folder starting from
the time the device is no longer supplied in Australia.  NOTE This may be
different to being considered obsolete.

In addition, if there is any modification introduced, even after the device
is no longer available for purchase such as a repair involving an ECO
(Engineering Change Order) which may impact compliance, the 5 years would
commence from the time of the repair which introduced the ECO'd
modification.


Best regards,
Kevin Richardson

Stanimore Pty Limited
Compliance Advice  Solutions for Technology (including Australian Agent
Services)
(Legislation/Regulations/Standards)
Ph:   02-4329-4070   (Int'l: +61-2-4329-4070)
Fax:  02-4328-5639   (Int'l: +61-2-4328-5639)
Mobile:  04-1224-1620   (Int'l: +61-4-1224-1620)
Email:kevin.richard...@ieee.org

This material (this message and the information contained in all attachments
to this message) is confidential and/or privileged information and is
intended only for the addressee/s named above. Any unauthorised
dissemination, copying, use of or reliance upon this material by persons or
entities other than the addressee/s named above is prohibited. If you
receive this material in error, please notify Stanimore Pty Limited and
destroy all copies (electronic and hardcopy) of this message and all
attachments immediately.



-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Flinders, Randall
Sent: Friday, 11 October 2002 2:04 AM
To: Emc-Pstc (E-mail)
Subject: Record Retention



Can anyone give me the record retention requirements for FCC Part 15,
CE-Mark, and C-Tick certifications?  How long must we keep the test reports
once the product has gone obsolete?  I believe this to be 2 years from the
last date of manufacture for FCC but can't seem to find the section in the
regs.  Not sure where to even look for this information within the EMC
directive or C-Tick framework.  Any suggestions on where this information is
located would be helpful.

Thanks!

Randy Flinders
Electromagnetic Compatibility Engineer

Emulex Corporation - We Network Storage
3535 Harbor Blvd.
Costa Mesa, Ca. 92626

Direct:  (714) 513-8012
Fax: (714) 513-5408
Email:   randall.flind...@emulex.com mailto:randall.flind...@emulex.com
Web:  http://www.emulex.com




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Filtered D types and ground potential

2002-10-14 Thread Neil Helsby

1.Filtered D can be obtained from Cinch who also have filter blocks that 
can be added as a retro-fit. ITT Cannon also supply connectors under 
their D*JK series.

Many years ago as an apprentice, I needed to use more test equipment than 
sockets on the bench permitted. Placing a piece of test equipment on the bench 
behind me, it drew a spark as the bnc connection was made. The 
engineer I worked with just laughed and found an extension block. I 
suspect that the benches in that lab were fed from different phases from 
the mains input to the building.

Regards,

Neil Helsby


**
This email and any files transmitted with it are confidential and
intended solely for the use of the individual or entity to whom they
are addressed. If you have received this email in error please notify
the system manager.

This footnote also confirms that this email message has been swept by
MIMEsweeper for the presence of computer viruses.

www.mimesweeper.com
**


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: coax grounding of E3/DS3 in the EU

2002-10-14 Thread Gemma Paolo

Look on the last version of ITU-T G.703. 
IN this the clause to isolate the RX side was deleted.
Bye
Paolo

 
_
Paolo Gemma
Siemens Mobile Communications  S.p.A.
PG MW ST EMC  Safety
SS Padana sup. KM 158 20060 Cassina de' Pecchi (MI) Italy
phone +39 02 9526 6587fax +39 02 9526 6203
mobile +39 348 3690185
e-mail paolo.ge...@icn.siemens.it
_
 

 -Original Message-
 From: pfitzgib...@attbi.com [mailto:pfitzgib...@attbi.com]
 Sent: Monday, September 23, 2002 8:00 PM
 To: emc-p...@majordomo.ieee.org
 Subject: coax grounding of E3/DS3 in the EU
 
 
 Greetings all,
 
   I have a general question about E3/DS-3 in the EU.  I
 have heard that it is no longer necessary to isolate one
 of the two Tx/Rx coax ports but can't find a definite
 answer.  I'd like to know if I can directly tie both the
 TX and RX ports to chassis for intrabuilding only CO
 lines.  This would make EMI/EMC much easier to pass and
 would get rid of the special AC coupling that would
 otherwise be necessary.
 
 The only reason that I could ever understand for the DC
 isolation requirements that used to be in place was to
 prevent ground connections in IBN CO's or to eliminate
 current on the shields due to differences in earth
 potential between buildings.  As neither of these really
 apply, I really don't see why it should still be
 necessary to provide the DC isolation (I have only
 intrabuilding lines and most CO's are now CBN
 installations).
 
 Does anyone know what the current status on this is?
 
 Thanks,
 Patrick
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list