RE: Shield Room Lighting

2002-10-31 Thread Gary McInturff

Well, except for the cold inrush current wear. I always left my lights 
off when I wasn't working in the chamber. A camera still allowed me to monitor 
equipment activity, which was either on a CRT or indicator lights.  
Fluorescents can indeed cause a large problem, but generally changing the tube 
every so often (the analyzer will tell you long before your eye) and eventually 
the ballast the fluorescents, in my experience will do fine.
I have a current problem with some special ballasts and expensive 
spectral output fluorescents that require me to turn them off if I want to see 
anything below 100 Mhz, and pretty much anything up to 200 Mhz. Its all nasty 
broadband. Very expensive to fix, so I just put in some task lighting so that I 
can walk around without killing myself while measuring, and when I need to 
troubleshoot or repair I snap the fluorescents back on. Dirty but cheap and 
accomplishes the purpose for the prescan chamber.
Gary
-Original Message-
From: Ralph McDiarmid [mailto:ralph.mcdiar...@xantrex.com]
Sent: Thursday, October 31, 2002 11:55 AM
To: EMC-PSTC (E-mail)
Subject: RE: Shield Room Lighting



We use four florescent screw-in lights in our 3-metre chamber and detect
some
emission 3dB or so above the noise floor.

Ralph McDiarmid, AScT 
Member Technical Staff
Engineering Services
Xantrex Technology Inc.

-Original Message-
From: POWELL, DOUG [mailto:doug.pow...@aei.com]
Sent: Thursday, October 31, 2002 9:49 AM
To: EMC-PSTC (E-mail)
Subject: Shield Room Lighting



Greetings all,

I wanted to share an experience and I hope benefits someone else.

My past experience with shield room lighting is that incandescent bulbs
frequently burn out, about once every 2-3 months.  I tried ruggedized lamps
of various sorts, still with the same results.  Obviously, I wanted to avoid
florescent lighting because of the huge fields they radiate.  After some
investigation and discussions with co-workers, it became apparent that the
problem is the line filter for service power in the room and the tungsten
filament in the bulb.  These line filters are typically have a really large
line to neutral capacitance which significantly lowers the source impedance
of the line.   Coupled with this, tungsten experiences a fairly high in-rush
current owing to it's very dynamic negative temperature coefficient.  I
toyed with idea of using inrush limiters but I thought there had to be a
reliable low-tech solution.  And at all costs, whatever solution I used, I
wanted to avoid injecting unwanted RF noise into the room.

I discovered traffic light signal bulbs.  Available from a few sources,
these bulbs have at least 5 filament supports,  heat dissipaters and
reflectors and are designed for continuous on/off operation in all sorts of
weather conditions.  They even keep working when the hanging fixtures bang
into each other in wind storms.  I also learned that these bulbs have about
a 1 to 2 year life expectancy in these conditions, so I tried it out in my
room.  So far, I've logged a full year of use on 4 x 150W bulbs with no burn
out.  And no, I don't just leave them turned on.

If you want to try this, do it soon because it appears that these bulbs may
become a thing of the past and prices may be driven up.  Over the last few
years, many cities and counties are replacing their incandescent bulbs with
the new LED bulbs and with great success.  As soon as a white LED light
becomes available I may try it out, although I guess I could use red LED
lamps since I used to be in the navy.



Best regards,

-doug

Douglas E. Powell
Compliance Engineer
Advanced Energy Industries, Inc.
Fort Collins, CO 80535 USA



___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc 

Circuit pack ESD drain

2002-10-31 Thread David Heald

All,
  Does anyone know of a sample waveform or general characteristics for worst
case VI on an ESD drain pin when a circuit pack is inserted into an
equipment shelf?  This is an odd question I know, but my management asked
for the info and I really have no idea (and it shouldn't happen anyway ;o)

I guess even a typical maximum charge that can be expected to be on a
circuit pack would be sufficient information.

Thanks in advance!

Dave Heald

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: CE marking/testing of military equipment

2002-10-31 Thread John Allen

Hi Folks

Sorry - it's me again.!

'Her Majesty's Stationery Office' (HMSO is NOT the goverment standards
group - it is the official government REGULATIONS publiishing site and is
just like the Government Printing Office (at least, I think that is what it
is called) in Washington etc.

Also, I think you will find that many other countries that are not republics
(God Forbid that should happen to the UK! - we already almost have
President Tony Blair, and that is bad enough!) have odd names for some
of their national institutions and organisations. Therefore I think I could
make a few derogatory remarks about some US names and traditions - like
calling a baseball or American football [??? - the ball is hardly ever
kicked by anone's foot!] series, the World Series when the game in
question is only played in the USA and a very few other countries) - so
let's leave that type of  funny remark for another time and place.

Regards

John Allen
Technical Consultant
Electromagnetics, Safety and Reliability Group
ERA Technology Ltd
Cleeve Rd
Leatherhead
Surrey KT22 7SA
Tel: +44 (0) 1372-367025 (Direct)
+44 (0) 1372-367000 (Switchboard)
Fax: +44 (0) 1372-367102 (Fax)
(but sent from my home email address!)

- Original Message -
From: plaw...@west.net
To: EMC-PSTC emc-p...@ieee.org
Sent: Wednesday, October 30, 2002 10:50 PM
Subject: Re: CE marking/testing of military equipment



Hi Gert:

I made the comment about the UK based on the following information:
http://www.emctla.org/Tech%20Notes/technical_guidance_note_33.htm

2) I found the standard referred to at:
http://www.hmso.gov.uk/si/si1992/Uksi_19922372_en_1.htm
See section 20.

PS: I love the Brits - who else would title the government standards group
'Her
Majesty's Stationery Office'!


On Wed, 30 Oct 2002 20:48:18 +0100, Gert Gremmen g.grem...@cetest.nl
wrote:
There is no ground to beieve that military equiment is to be excluded
in any country in Europe. This is definitely not the case in the
Netherlands.

Regards,

Gert Gremmen
ce-test, qualified testing
Rotterdam, The Netherlands

http://www.ce-test.nl


-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of plaw...@west.net
Sent: woensdag 30 oktober 2002 18:49
To: EMC-PSTC
Subject: CE marking/testing of military equipment



I have a customer asking for CISPR 22 test results on a commercial power
supply
intended for use in military equipment in Europe.

I've heard the UK excludes military equipment from CE marking.  Do other
countries also exclude military equipment from the EMC Directive?

If CISPR standards are not used for European military equipment, would
MIL-STD-461 be used?

Patrick Lawler
plaw...@west.net

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Patrick Lawler
plaw...@west.net

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:

Re: CE marking/testing of military equipment

2002-10-31 Thread John Allen

Hi Folks
Sorry the first message today was incomplete - here is the full version:

I fully support Nick's observations.

In respect of the comments made by Gert, I would like to point out that
the UK appears to be not the only Member country that has taken advantage of
Article 223 , and those countries are Full members  - not half-members -
so those comments are unjustiable!

Even more to the point, it should be remembered (as I pointed out in my
earlier message) that many newer directives include specific exclusions for
equipment for military and state security applications - so everyone else
now appears to accept and agree that the UK stance and legislation on the
EMC Directive is entirely justifiable!

Regards

John Allen
Technical Consultant
Electromagnetics, Safety and Reliability Group
ERA Technology Ltd
Cleeve Rd
Leatherhead
Surrey KT22 7SA
Tel: +44 (0) 1372-367025 (Direct)
+44 (0) 1372-367000 (Switchboard)
Fax: +44 (0) 1372-367102 (Fax)
(but sent from my home email address!)


- Original Message -
From: Nick Williams nick.willi...@conformance.co.uk
To: emc-p...@majordomo.ieee.org
Sent: Thursday, October 31, 2002 4:30 PM
Subject: RE: CE marking/testing of military equipment



 The UK's position is consistent with the provisions of, inter alia,
 article 223 of  the Treaty of Rome and is therefore entirely legal.

 I shall not dignify the remaining comments by replying to them. They
 are unworthy of a forum such as this.

 Regards

 Nick.


 At 07:23 +0100 31/10/02, Gert Gremmen wrote:
 Hi Patrick,
 
 This text is British law,en the Uk is only a half member of the EC.
 This law is is not backed up by the EMC directive European Text.
 It is therefore contradictory to the EC membership requirements
 and theoretically illegal.
 But who will complain, as it is not creating trade barriers,
 and is limited to pure military equipment.
 As always, the British stand out in Europe, gaining from the profits,
 and not accepting the obligations.
 As Margaret Thatcher already said: Why else did God create the Channel ?
 
 
 Regards,
 
 Gert Gremmen
 ce-test, qualified testing
 Rotterdam, The Netherlands
 
 http://www.ce-test.nl
 
 -Original Message-
 From: owner-emc-p...@majordomo.ieee.org
 [mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of plaw...@west.net
 Sent: woensdag 30 oktober 2002 23:50
 To: EMC-PSTC
 Subject: Re: CE marking/testing of military equipment
 
 
 
 Hi Gert:
 
 I made the comment about the UK based on the following information:
 http://www.emctla.org/Tech%20Notes/technical_guidance_note_33.htm
 
 2) I found the standard referred to at:
 http://www.hmso.gov.uk/si/si1992/Uksi_19922372_en_1.htm
 See section 20.
 
 PS: I love the Brits - who else would title the government standards
group
 'Her
 Majesty's Stationery Office'!
 
 
 On Wed, 30 Oct 2002 20:48:18 +0100, Gert Gremmen g.grem...@cetest.nl
 wrote:
 There is no ground to beieve that military equiment is to be excluded
 in any country in Europe. This is definitely not the case in the
 Netherlands.
 
 Regards,
 
 Gert Gremmen
 ce-test, qualified testing
 Rotterdam, The Netherlands
 
 http://www.ce-test.nl
 
 
 -Original Message-
 From: owner-emc-p...@majordomo.ieee.org
 [mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of plaw...@west.net
 Sent: woensdag 30 oktober 2002 18:49
 To: EMC-PSTC
 Subject: CE marking/testing of military equipment
 
 
 
 I have a customer asking for CISPR 22 test results on a commercial power
 supply
 intended for use in military equipment in Europe.
 
 I've heard the UK excludes military equipment from CE marking.  Do other
 countries also exclude military equipment from the EMC Directive?
 
 If CISPR standards are not used for European military equipment, would
 MIL-STD-461 be used?
 
 Patrick Lawler
 plaw...@west.net
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
   majord...@ieee.org
 with the single line:
   unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
   Ron Pickard:  emc-p...@hypercom.com
   Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
   Richard Nute:   ri...@ieee.org
   Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
  http://ieeepstc.mindcruiser.com/
  Click on browse and then emc-pstc mailing list
 
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
   majord...@ieee.org
 with the single line:
   unsubscribe emc-pstc
 
 For help, send mail to the list 

Re: CE marking/testing of military equipment

2002-10-31 Thread John Allen

Hi Folks

I fully support Nick's observations.

In respect of the other comments, the UK is not the only Member country
that has taken advantage of Article 223 , and those countries are Full
members  - not half-members - so the comments are unjustiable. Finally, it
should be remembered (as I pointed out in my earlier message) that many
other new



- Original Message -
From: Nick Williams nick.willi...@conformance.co.uk
To: emc-p...@majordomo.ieee.org
Sent: Thursday, October 31, 2002 4:30 PM
Subject: RE: CE marking/testing of military equipment



 The UK's position is consistent with the provisions of, inter alia,
 article 223 of  the Treaty of Rome and is therefore entirely legal.

 I shall not dignify the remaining comments by replying to them. They
 are unworthy of a forum such as this.

 Regards

 Nick.


 At 07:23 +0100 31/10/02, Gert Gremmen wrote:
 Hi Patrick,
 
 This text is British law,en the Uk is only a half member of the EC.
 This law is is not backed up by the EMC directive European Text.
 It is therefore contradictory to the EC membership requirements
 and theoretically illegal.
 But who will complain, as it is not creating trade barriers,
 and is limited to pure military equipment.
 As always, the British stand out in Europe, gaining from the profits,
 and not accepting the obligations.
 As Margaret Thatcher already said: Why else did God create the Channel ?
 
 
 Regards,
 
 Gert Gremmen
 ce-test, qualified testing
 Rotterdam, The Netherlands
 
 http://www.ce-test.nl
 
 -Original Message-
 From: owner-emc-p...@majordomo.ieee.org
 [mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of plaw...@west.net
 Sent: woensdag 30 oktober 2002 23:50
 To: EMC-PSTC
 Subject: Re: CE marking/testing of military equipment
 
 
 
 Hi Gert:
 
 I made the comment about the UK based on the following information:
 http://www.emctla.org/Tech%20Notes/technical_guidance_note_33.htm
 
 2) I found the standard referred to at:
 http://www.hmso.gov.uk/si/si1992/Uksi_19922372_en_1.htm
 See section 20.
 
 PS: I love the Brits - who else would title the government standards
group
 'Her
 Majesty's Stationery Office'!
 
 
 On Wed, 30 Oct 2002 20:48:18 +0100, Gert Gremmen g.grem...@cetest.nl
 wrote:
 There is no ground to beieve that military equiment is to be excluded
 in any country in Europe. This is definitely not the case in the
 Netherlands.
 
 Regards,
 
 Gert Gremmen
 ce-test, qualified testing
 Rotterdam, The Netherlands
 
 http://www.ce-test.nl
 
 
 -Original Message-
 From: owner-emc-p...@majordomo.ieee.org
 [mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of plaw...@west.net
 Sent: woensdag 30 oktober 2002 18:49
 To: EMC-PSTC
 Subject: CE marking/testing of military equipment
 
 
 
 I have a customer asking for CISPR 22 test results on a commercial power
 supply
 intended for use in military equipment in Europe.
 
 I've heard the UK excludes military equipment from CE marking.  Do other
 countries also exclude military equipment from the EMC Directive?
 
 If CISPR standards are not used for European military equipment, would
 MIL-STD-461 be used?
 
 Patrick Lawler
 plaw...@west.net
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
   majord...@ieee.org
 with the single line:
   unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
   Ron Pickard:  emc-p...@hypercom.com
   Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
   Richard Nute:   ri...@ieee.org
   Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
  http://ieeepstc.mindcruiser.com/
  Click on browse and then emc-pstc mailing list
 
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
   majord...@ieee.org
 with the single line:
   unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
   Ron Pickard:  emc-p...@hypercom.com
   Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
   Richard Nute:   ri...@ieee.org
   Jim Bacher: j.bac...@ieee.org
   
 All emc-pstc postings are archived and searchable on the web at:
  http://ieeepstc.mindcruiser.com/
  Click on browse and then emc-pstc mailing list
 
 
 Patrick Lawler
 plaw...@west.net
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  

RE: Shield Room Lighting

2002-10-31 Thread Price, Ed

I think that another factor in shortening the life of incandescent lights is
the fact that they are usually mounted in a heavy glass protective fixture.
These glass globes offer a bit more safety from physical damage, and also
look nicer than a bare light bulb in a socket. But the light bulb runs a lot
hotter when you use the globe. I think this shortens the bulb life too.

In my chambers, I have gone to bare bulbs in sockets. Of course, since my
chambers are 9 feet tall, the bulbs are fairly safe even when people are
moving large objects around (I have never had anyone accidentally hit a bare
light bulb). I now use ordinary 100 W bulbs in open fixtures, and, over the
past two years, my bulb life has improved to a point where I don't even
think about it any more.

BTW, my facilities guys wanted me to use some exotic industrial grade bulbs.
IIRC, they were rated at 135 V for 100 W (so I suppose they were NOT 100 W
bulbs at 120 V g). These bulbs were slightly longer and larger than an
ordinary bulb, and had an anti-breakage Teflon film on the bulb surface.
This gave then a satin appearance. However, those bulbs burned out just
about as fast as ordinary bulbs (I was using them within globes at the
time), and I since they cost several times more, I stopped using them.

Regards,

Ed


Ed Price
ed.pr...@cubic.com
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA  USA
858-505-2780  (Voice)
858-505-1583  (Fax)
Military  Avionics EMC Is Our Specialty
Shake-Bake-Shock - Metrology - Reliability Analysis


-Original Message-
From: richwo...@tycoint.com [mailto:richwo...@tycoint.com]
Sent: Thursday, October 31, 2002 12:00 PM
To: emc-p...@ieee.org
Subject: RE: Shield Room Lighting



We have the same frequent burn out problem and we also have 
attributed it to
the filters. We just keep replacing them. Has anyone tried the 
rugged bulbs
marketed for use with garage door openers or ceiling fans or 
have tried the
extended life bulbs? Do they last longer in chamber use to 
justify the cost?

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: POWELL, DOUG [mailto:doug.pow...@aei.com]
Sent: Thursday, October 31, 2002 12:49 PM
To: EMC-PSTC (E-mail)
Subject: Shield Room Lighting



Greetings all,

I wanted to share an experience and I hope benefits someone else.

My past experience with shield room lighting is that incandescent bulbs
frequently burn out, about once every 2-3 months.  I tried 
ruggedized lamps
of various sorts, still with the same results.  Obviously, I 
wanted to avoid
florescent lighting because of the huge fields they radiate.  
After some
investigation and discussions with co-workers, it became 
apparent that the
problem is the line filter for service power in the room and 
the tungsten
filament in the bulb.  These line filters are typically have a 
really large
line to neutral capacitance which significantly lowers the 
source impedance
of the line.   Coupled with this, tungsten experiences a 
fairly high in-rush
current owing to it's very dynamic negative temperature coefficient.  I
toyed with idea of using inrush limiters but I thought there 
had to be a
reliable low-tech solution.  And at all costs, whatever 
solution I used, I
wanted to avoid injecting unwanted RF noise into the room.

I discovered traffic light signal bulbs.  Available from a few sources,
these bulbs have at least 5 filament supports,  heat dissipaters and
reflectors and are designed for continuous on/off operation in 
all sorts of
weather conditions.  They even keep working when the hanging 
fixtures bang
into each other in wind storms.  I also learned that these 
bulbs have about
a 1 to 2 year life expectancy in these conditions, so I tried 
it out in my
room.  So far, I've logged a full year of use on 4 x 150W 
bulbs with no burn
out.  And no, I don't just leave them turned on.

If you want to try this, do it soon because it appears that 
these bulbs may
become a thing of the past and prices may be driven up.  Over 
the last few
years, many cities and counties are replacing their 
incandescent bulbs with
the new LED bulbs and with great success.  As soon as a white LED light
becomes available I may try it out, although I guess I could 
use red LED
lamps since I used to be in the navy.



Best regards,

-doug

Douglas E. Powell
Compliance Engineer
Advanced Energy Industries, Inc.
Fort Collins, CO 80535 USA



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org

SV: Surge - injection point on screened cable

2002-10-31 Thread amund

Hello Kevin,

That's correct, we do not have 20 different fire detectors (only 5-6), but
in addition we have some sounders, manual call point, address units, fire
door controllers, etc. And of course the fire alarm panel (control and
indicating equipment).
The cable screen is connected to earth on the panel, but not to any devices
on the detection loop, it just runs through.

I know this 20m requirements, but I wonder how much more induced surge pulse
will occur when testing on a 20m cable compared to induce the pulse close up
(0.5m) to a device ? Could be possible to increase the voltage to make some
sort of correction?

During the discussion with the lab today, it seems that I have to bring my
wire cutter tomorrow and an extra 20m cable 

Best regards
Amund Westin, Oslo / NORWAY



 -Opprinnelig melding-
 Fra: Kevin Harris [mailto:kevinharr...@dsc.com]
 Sendt: 31. oktober 2002 22:41
 Til: 'am...@westin-emission.no'; emc-p...@majordomo.ieee.org
 Emne: RE: Surge - injection point on screened cable


 Hi Amund,

 You only require the one piece of 20 meter cable and it has to be attached
 to your EUT. Only one thing can be the EUT at a time. I don't know if the
 EUT is your control and indicating equipment ( CIE ) or your other devices
 on the cable or if it is all of them. Assuming (worst case) that it is all
 of them, then you need to select each part in turn as the EUT add the 20
 meter cable to it and isolate all the other devices from the surge.
 Trying to surge all 20 devices at the same time is not proper
 either. In the
 case you state, you have whatever protection scheme you have
 implemented in
 each device in parallel with 19 others and therefore improperly distribute
 the surge energy across all of them. BTW are your devices on the cable
 earthed? If they are not, be sure to check that the test house has a 10nF
 cap from the screen to earth at the EUT end of the cable as per
 Fig 3 in EN
 50130-4
 I may be reading things in to far, but I inferred from your wish to surge
 all devices on the cable at the same time that you have 20
 different things
 that you want tested and not 20 identical devices. I can't
 imagine that you
 actually have 20 completely different fire detectors. If you have devices
 that have various options test only a fully loaded one and apply
 the results
 across the whole line. It's a whole lot cheaper testing that way :)

 Best Regards,


 Kevin Harris
 Manager, Approvals and CAD Services
 Digital Security Controls
 3301 Langstaff Road
 Concord, Ontario
 CANADA
 L4K 4L2

 Tel: +1 905 760 3000 Ext. 2378
 Fax +1 905 760 3020

 Email: kevinharr...@dsc.com


 -Original Message-
 From: am...@westin-emission.no [mailto:am...@westin-emission.no]
 Sent: Thursday, October 31, 2002 10:48 AM
 To: emc-p...@majordomo.ieee.org
 Subject: Surge - injection point on screened cable [fadr]



 According to IEC/EN 61000-4-5, the surge pulse shall be injected onto a
 screened cable 20 meters from the DUT.

 We have a fire alarm system with 20 detectors connected on the
 same screened
 cable, 1.5 meters between each detector. We have been told from the local
 test lab that we have to add a 20m cable between each detector in order to
 surge test each detector.

 I'm sure our local cable distributor like that idea ... , but do we really
 have to do this ? Why is this 20 meters cable needed ? Is it to induce the
 surge pulse from the screen into the cable lines?

 The 20 detectors make a total cable distance of 30 meters and the
 screen is
 continuous. Is it possible to insert a pulse in the beginning of the cable
 and test all detectors simultaneous ?

 Regards
 Amund



 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   

Re: Official Languages of Countries

2002-10-31 Thread Hans Mellberg

the CIA website has great descriptions of each country.
Yes, that CIA!!!
http://www.cia.gov/cia/publications/factbook/index.html

--- Stephen Irving sirv...@lutron.com wrote:
 Hello everyone.
 
 My name is Steve Irving, and I am new to this forum. 
 
 Does anyone know where to find a reliable, up-to-date list of the official
 languages of each country? This list would be useful to people selling 
 products
 internationally, as many standards require instructions in the official 
 language
 of each country of sale.
 
 Thanks for your help,
 Steve
 
 
 Stephen R. Irving
 Project Electrical Engineer
 Lutron Electronics, Co. Inc.
 +1 (610) 282 - 6468
 +1 (610) 282 - 7324 [Fax]
 


=
Best Regards
Hans Mellberg
Regulatory Compliance  EMC Design Services Consultant
By the Pacific Coast next to Silicon Valley,
Santa Cruz, CA, USA
office:831-454-9450, cell:408-507-9694, fax:831-454-0755

__
Do you Yahoo!?
HotJobs - Search new jobs daily now
http://hotjobs.yahoo.com/

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Shield Room Lighting

2002-10-31 Thread POWELL, DOUG
All,

I've had at least three requests for sources on bulbs and possibly more
requests on the way.  So I'll reply to the group instead of individually.
By the way, oven, refrigerator, garage door, and drop light bulbs did not
work for me.  They were rugged use but apparently not rugged enough.  In
fact, I thought about buying some of these traffic signal bulbs for my own
use in the shop at home.  Also forget looking into those special life-time
guarantee deals you sometimes see by mail order.  All they do is rate the
bulb for 130V and count on enough people not cashing in on the guarantee to
make a profit.

A couple of makers are ITE, GE Lighting  Sylvania.  Ask specifically for
incandescent traffic signal bulbs.  The ones I am using are the GE
Watt-Miser 135W, 120V, 7000 Hr Traffic Signal bulb.  I got them through a
local electric supply house, not at the local hardware/lumber stores like
Home Depot.  If you use the following link and replace the string 12345
string with your actual zip code you should get a nice list of local places
who might be able to help.

http://www.google.com/search?sa=Xoi=fwppb=fq=electric+12345

Although I've not done it, you should also be able to order online:

http://hhlightinginc.com/traffic.htm
http://www.electriciansupplies.com/index.cfm/S/21/Traffic_Signal_Light_Bulbs
.htm
http://www.eriklighting.com/product.asp?lc=5sc=96
http://www.mmlights.com/trafficsignal.html
http://www.urbantransport-technology.com/contractors/surfacing/luxram/

I attached a photo of one of my bulbs.  As you can see, it has a standard
envelope size and screw-in base, it fits most light fixtures.  These lamps
feature 5 filament support wires, a heat deflector inside the envelope, the
base has special high temperature glue and 95% krypton gas (inert).

Right now I have a similar request in for the same type of lighting but this
time in a spot or flood light configuration.  We'll see what turns up.


-doug



___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.
attachment: ge_bulb.jpg

Re: CCC mark testlab cetification

2002-10-31 Thread Leslie Bai

Fred,
You raised a good point here by answering Chet's questions. Here is the update 
of CNCA accreditation.
Since CCC was initially anounced to be implemented in May, the whole system was 
actually not ready at that time even the cost of testing and certification were 
not defined until late July. BTW - The first US manufacturer who went through 
CCC factory inspection and certification since CCC was implemented is my 
customer so I know they were not ready when my customer applied for CCC.
In June, CNCA announced TWO (2) CCC certification bodies accredited to issue 
CCC certification mark and 68 Chinese labs accredited to perform CCC testing 
covering 19 categories of products regulated under CCC. 9 labs located in 
different regions of China are accredited for electrical electronics and IT 
products testing.
The complete set (47 volumes) of CCC regulations are available for 
manufacturer's reference for a couple of US dollars each volume. If I were you, 
the manufacturer, I would not spend several hundred dollars to buy them from 
other sources.
For Chinese manufacturers, the closest lab will be assigned for CCC testing. 
For foreign manufacturers, the labs located in Beijing will be assigned for CCC 
testing. (This seems to loose recently and foreign manufacturer now can name a 
prefered lab to perform CCC testing if sufficient reasons being raised. One of 
my customers did this recently as two labs in Beijing have different views on 
the issue of whether the power adapter provided by other manufacturer shall be 
included in the certification of their products and we finally achieved a 
perfect agreement with one of the Certification body for the best interest of 
this customer, this, I thought, is the value of using a qualified agent). 
There is no other agency accredited to issue CCC mark other than 2 accredited 
Chinese agencies both located in Beijing.
There is no so-called registered agent to perform CCC certification either 
issueing CCC mark or perform CCC testing.
There is no foreign labs accredited by CNCA to perform CCC testing other than 
68 accredited labs in China.
All application must be made to 2 accredited CCC certification bodies and 
tested by one of 68 labs in China, either directly by the manufacturers or 
through an agent. 
However, the value of employing an agent, I believe, is to efficiently 
communicate with both certification body and test lab to facilitate the 
process, define the testing scope, and trouble-shooting with Chinese Engineers 
if unpleasant failure occurs. So such agent should have both Estern and Western 
backgrounds, understand  Chinese culture, speak their language, and with sound 
Compliance Engineering knowledge.
Please also note that MII Type approval is different. MII and CNCA are not in 
the same boat. MII has its own regulations and accredited labs. For foreign 
manufacturers, MII test lab can assign Engineers to the customer site to 
perform testing and issue MII accredited report for MII type approval - (BWT: 
We have done this for our customers before and it's is extremely helpful and 
benefitial to foreign manuacturers consdiering the transporation cost of big 
telecom racks shipped to China!, It could be OK if US Western coast ports are 
running smoothly).
Should anyone like to understand more of China approvals, feel free to contact 
me off-line.
Hope this helps.
Leslie
 
 Fred Borda fbo...@typeapproval.com wrote:
Hi Chet,

The set of documents published by CNCA, the authority that administers the 
CCC mark scheme in China, is available in English at:

http://www.typeapproval.com/cn/emc.html

The document labeled Regulations for CPCS.pdf is the overall regulations 
guiding the regime. It addresses type testing. While I don't believe it 
specifically says that testing performed outside China is not accepted, a 
lot is determined at the implementation level. Testing must be performed at 
CNCA accredited laboratories. I don't know of any such accredited labs 
outside China. I know that several US manufacturers had sought to have 
their own labs accredited at one point, but the last I heard was that these 
applications have all been in limbo for a very long time. As a practical 
matter, the testing must be conducted in China.

As for laboratories becoming accepted agents, if by that you mean 
accreditation to have their test reports accepted by certification bodies 
in China, this is the procedure mentioned above that some labs have tried. 
I'm eager to hear from any list members about progress they may have made 
in this accreditation process. If by accepted agent you mean a foreign lab 
to become a certification body to issue the CCC mark, I think we may not 
see this for some time to come.

Has anyone else seen further movement on this front?

-Fred Borda
Compliance International
www.typeapproval.com


At AM 11:01 10/31/02 -0800, Summers, Chet wrote:

Hello Listmembers. I am researching the procedures needed to obtain the CCC
mark for shipment of 

Re: CCC mark testlab cetification

2002-10-31 Thread Leslie Bai

Hi Chet, 
To get an overview of CCC regulations, download this file: 
http://www.siemic.com/Original%20files/CCC%20mark.pdf 
I just want to remind you that some other regulation may be applicable to your 
products in addition to CCC, particularly, the MPS regulations on security 
products. For a general review of Chinese regulations, pls take a look at the 
attached document (CHINA.pdf). 
For those who are not interested in this topic, please ignore the attachment 
although I thought it could be interesting to you. 
For more detail information and procedures of China approvals, pls contact me 
off-line. 
Thanks, 
Leslie 
 
 
 Summers, Chet csumm...@pelco.com wrote: 
Hello Listmembers. I am researching the procedures needed to obtain the CCC
mark for shipment of CCTV equipment into China and need some guidance from
those experienced in the process. 

First, which Chinese document explicitly mandates type testing within China?
I have read from various sourches that any testing not performed within the
country is completely unacceptable. Where can I review the Chinese
Government's official stand on type testing, for EMC and product safety?

Lastly, I am looking for procedures necessary for a Regulatory Compliance
Lab to become an accepted agent within China. 


Any experiences with this process that you are willing to share will be
appreciated. 




Chet Summers
Compliance Engineer
Pelco
tel 1-559-292-1981 X2822
fax 1-559-294-2697

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard: emc-p...@hypercom.com
Dave Heald: davehe...@attbi.com

For policy questions, send mail to:
Richard Nute: ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


-
Do you Yahoo!?
HotJobs - Search new jobs daily now

CHINA.pdf
Description: CHINA.pdf


Official Languages of Countries

2002-10-31 Thread Stephen Irving
Hello everyone.

My name is Steve Irving, and I am new to this forum. 

Does anyone know where to find a reliable, up-to-date list of the official 
languages of each country? This list would be useful to people selling products 
internationally, as many standards require instructions in the official 
language of each country of sale.

Thanks for your help,
Steve


Stephen R. Irving
Project Electrical Engineer
Lutron Electronics, Co. Inc.
+1 (610) 282 - 6468
+1 (610) 282 - 7324 [Fax]


RE: Shield Room Lighting

2002-10-31 Thread richwoods

We have the same frequent burn out problem and we also have attributed it to
the filters. We just keep replacing them. Has anyone tried the rugged bulbs
marketed for use with garage door openers or ceiling fans or have tried the
extended life bulbs? Do they last longer in chamber use to justify the cost?

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: POWELL, DOUG [mailto:doug.pow...@aei.com]
Sent: Thursday, October 31, 2002 12:49 PM
To: EMC-PSTC (E-mail)
Subject: Shield Room Lighting



Greetings all,

I wanted to share an experience and I hope benefits someone else.

My past experience with shield room lighting is that incandescent bulbs
frequently burn out, about once every 2-3 months.  I tried ruggedized lamps
of various sorts, still with the same results.  Obviously, I wanted to avoid
florescent lighting because of the huge fields they radiate.  After some
investigation and discussions with co-workers, it became apparent that the
problem is the line filter for service power in the room and the tungsten
filament in the bulb.  These line filters are typically have a really large
line to neutral capacitance which significantly lowers the source impedance
of the line.   Coupled with this, tungsten experiences a fairly high in-rush
current owing to it's very dynamic negative temperature coefficient.  I
toyed with idea of using inrush limiters but I thought there had to be a
reliable low-tech solution.  And at all costs, whatever solution I used, I
wanted to avoid injecting unwanted RF noise into the room.

I discovered traffic light signal bulbs.  Available from a few sources,
these bulbs have at least 5 filament supports,  heat dissipaters and
reflectors and are designed for continuous on/off operation in all sorts of
weather conditions.  They even keep working when the hanging fixtures bang
into each other in wind storms.  I also learned that these bulbs have about
a 1 to 2 year life expectancy in these conditions, so I tried it out in my
room.  So far, I've logged a full year of use on 4 x 150W bulbs with no burn
out.  And no, I don't just leave them turned on.

If you want to try this, do it soon because it appears that these bulbs may
become a thing of the past and prices may be driven up.  Over the last few
years, many cities and counties are replacing their incandescent bulbs with
the new LED bulbs and with great success.  As soon as a white LED light
becomes available I may try it out, although I guess I could use red LED
lamps since I used to be in the navy.



Best regards,

-doug

Douglas E. Powell
Compliance Engineer
Advanced Energy Industries, Inc.
Fort Collins, CO 80535 USA



___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Shield Room Lighting

2002-10-31 Thread Ralph McDiarmid

We use four florescent screw-in lights in our 3-metre chamber and detect
some
emission 3dB or so above the noise floor.

Ralph McDiarmid, AScT 
Member Technical Staff
Engineering Services
Xantrex Technology Inc.

-Original Message-
From: POWELL, DOUG [mailto:doug.pow...@aei.com]
Sent: Thursday, October 31, 2002 9:49 AM
To: EMC-PSTC (E-mail)
Subject: Shield Room Lighting



Greetings all,

I wanted to share an experience and I hope benefits someone else.

My past experience with shield room lighting is that incandescent bulbs
frequently burn out, about once every 2-3 months.  I tried ruggedized lamps
of various sorts, still with the same results.  Obviously, I wanted to avoid
florescent lighting because of the huge fields they radiate.  After some
investigation and discussions with co-workers, it became apparent that the
problem is the line filter for service power in the room and the tungsten
filament in the bulb.  These line filters are typically have a really large
line to neutral capacitance which significantly lowers the source impedance
of the line.   Coupled with this, tungsten experiences a fairly high in-rush
current owing to it's very dynamic negative temperature coefficient.  I
toyed with idea of using inrush limiters but I thought there had to be a
reliable low-tech solution.  And at all costs, whatever solution I used, I
wanted to avoid injecting unwanted RF noise into the room.

I discovered traffic light signal bulbs.  Available from a few sources,
these bulbs have at least 5 filament supports,  heat dissipaters and
reflectors and are designed for continuous on/off operation in all sorts of
weather conditions.  They even keep working when the hanging fixtures bang
into each other in wind storms.  I also learned that these bulbs have about
a 1 to 2 year life expectancy in these conditions, so I tried it out in my
room.  So far, I've logged a full year of use on 4 x 150W bulbs with no burn
out.  And no, I don't just leave them turned on.

If you want to try this, do it soon because it appears that these bulbs may
become a thing of the past and prices may be driven up.  Over the last few
years, many cities and counties are replacing their incandescent bulbs with
the new LED bulbs and with great success.  As soon as a white LED light
becomes available I may try it out, although I guess I could use red LED
lamps since I used to be in the navy.



Best regards,

-doug

Douglas E. Powell
Compliance Engineer
Advanced Energy Industries, Inc.
Fort Collins, CO 80535 USA



___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: CCC mark testlab cetification

2002-10-31 Thread Fred Borda


Hi Chet,

The set of documents published by CNCA, the authority that administers the 
CCC mark scheme in China, is available in English at:


http://www.typeapproval.com/cn/emc.html

The document labeled Regulations for CPCS.pdf is the overall regulations 
guiding the regime. It addresses type testing. While I don't believe it 
specifically says that testing performed outside China is not accepted, a 
lot is determined at the implementation level. Testing must be performed at 
CNCA accredited laboratories. I don't know of any such accredited labs 
outside China. I know that several US manufacturers had sought to have 
their own labs accredited at one point, but the last I heard was that these 
applications have all been in limbo for a very long time. As a practical 
matter, the testing must be conducted in China.


As for laboratories becoming accepted agents, if by that you mean 
accreditation to have their test reports accepted by certification bodies 
in China, this is the procedure mentioned above that some labs have tried. 
I'm eager to hear from any list members about progress they may have made 
in this accreditation process. If by accepted agent you mean a foreign lab 
to become a certification body to issue the CCC mark, I think we may not 
see this for some time to come.


Has anyone else seen further movement on this front?

-Fred Borda
Compliance International
www.typeapproval.com


At AM 11:01 10/31/02 -0800, Summers, Chet wrote:


Hello Listmembers.  I am researching the procedures needed to obtain the CCC
mark for shipment of CCTV equipment into China and need some guidance from
those experienced in the process.

First, which Chinese document explicitly mandates type testing within China?
I have read from various sourches that any testing not performed within the
country is completely unacceptable.  Where can I review the Chinese
Government's official stand on type testing, for EMC and product safety?

Lastly, I am looking for procedures necessary for a Regulatory Compliance
Lab to become an accepted agent within China.


Any experiences with this process that you are willing to share will be
appreciated.




Chet Summers
Compliance Engineer
Pelco
tel 1-559-292-1981 X2822
fax 1-559-294-2697

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



Fred Borda
Director
Marketing  Business Development
Compliance International
www.typeapproval.com
--
The experts in telecommunications equipment type approval
across the Asia-Pacific region
--
4713 First Street, Suite 280
Pleasanton, California 94566-7362 USA
Tel  +1.925.417.5571 (direct)
Fax  +1.925.417.5574
Mobile  +1.650.740.5762
fbo...@typeapproval.com



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
   http://ieeepstc.mindcruiser.com/
   Click on browse and then emc-pstc mailing list


RE: Surge - injection point on screened cable

2002-10-31 Thread Juhasz, John (IndSys, GE Interlogix)

With respect to 'alarm systems'  - EN 50130-4 is the applicable technical 
standard.
However, 50130-4 refers to the IEC 1000/EN61000 series specs, 'but with 
modifications'.

Let's take for instance the 1000-4-5 Surge spec that Amund referenced.
In EN 50130-4, the following is stated:

The test apparatus and procedure shall be as described in 
IEC 1000-4-5 with the following modifications and clarifications
taken into account:

Then there are two paragraphs - one for Mains and one for I/O lines.
With regard to the length of cables in the I/O lines:
 
The length of the signal lines between the EUT and to coupling/decoupling
network(s) shall be less than/equal to 2m, 

But the sentence continues with a clarification if there is screened cables:

however, if it is specified that certain signal lines must only be connected
with screened cables, the in these cases the transients shall be applied to
the screen of a 20m length of screened cable as show in figure 3. 

(Figure 3 is titled : Typical arrangement for coupling onto screened signal
lines. It shows the test set-up with a 20m dimension between the EUT and
the coupling/decoupling network).

I guess they made that pretty clear in THAT standard.
While a 'typical' installation of my product does not use screened cables of
such lengths, I do make such a length available for the test.

Hope this helps.

John A. Juhasz

GE Interlogix
Fiber Options Div.
Bohemia, NY 


-Original Message-
From: richwo...@tycoint.com [mailto:richwo...@tycoint.com]
Sent: Thursday, October 31, 2002 1:05 PM
To: emc-p...@majordomo.ieee.org
Subject: RE: Surge - injection point on screened cable



This is a good example of an inarticulate clause in a standard. One sentence
in clause 7.5 reads Normally, the maximum length of the specified shielded
cable shall be used. But the following sentence reads With respect to the
frequency spectrum of the surge 20 m length of the specified shielded cable
shall be used in non-inductively bundled configuration for physical
reasons. Duh! What they heck are they trying to say in that last sentence?
Are we expected to use the maximum length cable specified for the
application but no longer than 20 m? That's seems to be what is being said
in a convoluted way.

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: am...@westin-emission.no [mailto:am...@westin-emission.no]
Sent: Thursday, October 31, 2002 10:48 AM
To: emc-p...@majordomo.ieee.org
Subject: Surge - injection point on screened cable



According to IEC/EN 61000-4-5, the surge pulse shall be injected onto a
screened cable 20 meters from the DUT.

We have a fire alarm system with 20 detectors connected on the same screened
cable, 1.5 meters between each detector. We have been told from the local
test lab that we have to add a 20m cable between each detector in order to
surge test each detector.

I'm sure our local cable distributor like that idea ... , but do we really
have to do this ? Why is this 20 meters cable needed ? Is it to induce the
surge pulse from the screen into the cable lines?

The 20 detectors make a total cable distance of 30 meters and the screen is
continuous. Is it possible to insert a pulse in the beginning of the cable
and test all detectors simultaneous ?

Regards
Amund



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our 

CCC mark testlab cetification

2002-10-31 Thread Summers, Chet

Hello Listmembers.  I am researching the procedures needed to obtain the CCC
mark for shipment of CCTV equipment into China and need some guidance from
those experienced in the process.

First, which Chinese document explicitly mandates type testing within China?
I have read from various sourches that any testing not performed within the
country is completely unacceptable.  Where can I review the Chinese
Government's official stand on type testing, for EMC and product safety?

Lastly, I am looking for procedures necessary for a Regulatory Compliance
Lab to become an accepted agent within China.  


Any experiences with this process that you are willing to share will be
appreciated.  




Chet Summers
Compliance Engineer
Pelco
tel 1-559-292-1981 X2822
fax 1-559-294-2697

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re:RE: EN61000-3-3 -3-11 off topic a bit!

2002-10-31 Thread brian_kunde

I was just looking through my new copy of IEC61000-3-3:1994+A1:2001 standard.
Under section 1 SCOPE, in the forth paragraph, it refers to the 3-11 standard
this way;

Part 3-11 is applicable to equipment with rated input current less than or
equal to 75 A per phase and subject to conditional connection.  

Brian Kunde
LECO Corp.

Reply Separator
Subject:RE: EN61000-3-3  -3-11 off topic a bit!
Author: dhe...@tellium.com
List-Post: emc-pstc@listserv.ieee.org
Date:   10/31/02 11:43 AM


But when was the last time you saw a plug rated (just a random example) 250V
3(phase)Y 75A when it means 25A per phase?  the 75A rating is definately
'per phase'.

-Original Message-
From: Spencer, David H [mailto:david.spen...@usa.xerox.com]
Sent: Thursday, October 31, 2002 8:16 AM
To: emc-p...@majordomo.ieee.org
Subject: RE: EN61000-3-3  -3-11 off topic a bit!



I've just looked at all the draft copies of this standard(that I have), and
the older version TR IEC 1000-3-5.  Still only says 75amps.  Again no per
phase.

I would have to say if TC77A wanted it to say 75A per phase, it would be
in there.


Regards
Dave Spencer



-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Wednesday, October 30, 2002 3:07 PM
To: emc-p...@majordomo.ieee.org
Subject: EN61000-3-3  -3-11 off topic a bit!



I read in !emc-pstc that Spencer, David H david.spen...@usa.xerox.com
wrote (in 052106A55179D611B34300096BB02E3F8B93@USAMCMS4) about
'EN61000-3-3  -3-11  off topic a bit!' on Wed, 30 Oct 2002:
Having looked into EN61000-3-11, there is a big difference from
EN61000-3-3.
The scope of 3-3 refers to products rated 16 amps or less  per phase.
There is no per phase specification in EN61000-3-11.  Only this in the
title:  equipment with rated current 75 A.  Further, the scope does not
specify that as a per phase rating.

I would say that the standard does not apply to any product with a total
rating 75A.  That would allow 3 phase products rated greater than 25A per
phase to fall outside the scope of EN61000-3-11!

That certainly needs to be clarified. I'll set the wheels in motion
immediately. It SHOULD say 'per phase'.
-- Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron 

RE: Surge - injection point on screened cable

2002-10-31 Thread richwoods

This is a good example of an inarticulate clause in a standard. One sentence
in clause 7.5 reads Normally, the maximum length of the specified shielded
cable shall be used. But the following sentence reads With respect to the
frequency spectrum of the surge 20 m length of the specified shielded cable
shall be used in non-inductively bundled configuration for physical
reasons. Duh! What they heck are they trying to say in that last sentence?
Are we expected to use the maximum length cable specified for the
application but no longer than 20 m? That's seems to be what is being said
in a convoluted way.

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: am...@westin-emission.no [mailto:am...@westin-emission.no]
Sent: Thursday, October 31, 2002 10:48 AM
To: emc-p...@majordomo.ieee.org
Subject: Surge - injection point on screened cable



According to IEC/EN 61000-4-5, the surge pulse shall be injected onto a
screened cable 20 meters from the DUT.

We have a fire alarm system with 20 detectors connected on the same screened
cable, 1.5 meters between each detector. We have been told from the local
test lab that we have to add a 20m cable between each detector in order to
surge test each detector.

I'm sure our local cable distributor like that idea ... , but do we really
have to do this ? Why is this 20 meters cable needed ? Is it to induce the
surge pulse from the screen into the cable lines?

The 20 detectors make a total cable distance of 30 meters and the screen is
continuous. Is it possible to insert a pulse in the beginning of the cable
and test all detectors simultaneous ?

Regards
Amund



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: CE marking/testing of military equipment/off topic

2002-10-31 Thread Grasso, Charles

Hmm conferred by the Pope? I thought be generated the CofE in direct
conflict to the Catholic Church...

Best Regards
Charles Grasso
Senior Compliance Engineer
Echostar Communications Corp.
Tel:  303-706-5467
Fax: 303-799-6222
Cell: 303-204-2974
Email: charles.gra...@echostar.com;  
Email Alternate: chasgra...@ieee.org
 

-Original Message-
From: Cortland Richmond [mailto:72146@compuserve.com] 
Sent: Thursday, October 31, 2002 10:33 AM
To: Ted Rook; ieee pstc list
Subject: Re: CE marking/testing of military equipment/off topic


 Her Majesty Queen Elizabeth Second of The United Kingdom of Great
Britain and Northern Ireland (G*d help us); Defender Of The Faith 

Funny you should mention that; it relates to certain matters under
discussion here.

Did you know that the first British monarch to bear the title Defender Of
The Faith was Henry VIII? And that it was conferred on him by the Pope?

See what happens when there's no DOW specified?

(grin)

Cortland

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Shield Room Lighting

2002-10-31 Thread POWELL, DOUG

Greetings all,

I wanted to share an experience and I hope benefits someone else.

My past experience with shield room lighting is that incandescent bulbs
frequently burn out, about once every 2-3 months.  I tried ruggedized lamps
of various sorts, still with the same results.  Obviously, I wanted to avoid
florescent lighting because of the huge fields they radiate.  After some
investigation and discussions with co-workers, it became apparent that the
problem is the line filter for service power in the room and the tungsten
filament in the bulb.  These line filters are typically have a really large
line to neutral capacitance which significantly lowers the source impedance
of the line.   Coupled with this, tungsten experiences a fairly high in-rush
current owing to it's very dynamic negative temperature coefficient.  I
toyed with idea of using inrush limiters but I thought there had to be a
reliable low-tech solution.  And at all costs, whatever solution I used, I
wanted to avoid injecting unwanted RF noise into the room.

I discovered traffic light signal bulbs.  Available from a few sources,
these bulbs have at least 5 filament supports,  heat dissipaters and
reflectors and are designed for continuous on/off operation in all sorts of
weather conditions.  They even keep working when the hanging fixtures bang
into each other in wind storms.  I also learned that these bulbs have about
a 1 to 2 year life expectancy in these conditions, so I tried it out in my
room.  So far, I've logged a full year of use on 4 x 150W bulbs with no burn
out.  And no, I don't just leave them turned on.

If you want to try this, do it soon because it appears that these bulbs may
become a thing of the past and prices may be driven up.  Over the last few
years, many cities and counties are replacing their incandescent bulbs with
the new LED bulbs and with great success.  As soon as a white LED light
becomes available I may try it out, although I guess I could use red LED
lamps since I used to be in the navy.



Best regards,

-doug

Douglas E. Powell
Compliance Engineer
Advanced Energy Industries, Inc.
Fort Collins, CO 80535 USA



___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: CE marking/testing of military equipment/off topic

2002-10-31 Thread Cortland Richmond

 Her Majesty Queen Elizabeth Second of The United Kingdom of Great
Britain and Northern Ireland (G*d help us); Defender Of The Faith 

Funny you should mention that; it relates to certain matters under
discussion here.

Did you know that the first British monarch to bear the title Defender Of
The Faith was Henry VIII? And that it was conferred on him by the Pope?

See what happens when there's no DOW specified?

(grin)

Cortland

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Another interesting UK vacancy

2002-10-31 Thread james collum

I was reading the news.bbc.uk web page today (again). I followed the link
from the Apache helicopters parked in shed due to the lack of pilots story,
this led me to Westland Helicopters. They have a vacancy posted for an EMC
engineer at the HNC+ some experience level.

I wish I could spot jobs in the San Jose bay area as easily.

Jim


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: CE marking/testing of military equipment

2002-10-31 Thread Nick Williams


The UK's position is consistent with the provisions of, inter alia, 
article 223 of  the Treaty of Rome and is therefore entirely legal.


I shall not dignify the remaining comments by replying to them. They 
are unworthy of a forum such as this.


Regards

Nick.


At 07:23 +0100 31/10/02, Gert Gremmen wrote:

Hi Patrick,

This text is British law,en the Uk is only a half member of the EC.
This law is is not backed up by the EMC directive European Text.
It is therefore contradictory to the EC membership requirements
and theoretically illegal.
But who will complain, as it is not creating trade barriers,
and is limited to pure military equipment.
As always, the British stand out in Europe, gaining from the profits,
and not accepting the obligations.
As Margaret Thatcher already said: Why else did God create the Channel ?


Regards,

Gert Gremmen
ce-test, qualified testing
Rotterdam, The Netherlands

http://www.ce-test.nl

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of plaw...@west.net
Sent: woensdag 30 oktober 2002 23:50
To: EMC-PSTC
Subject: Re: CE marking/testing of military equipment



Hi Gert:

I made the comment about the UK based on the following information:
http://www.emctla.org/Tech%20Notes/technical_guidance_note_33.htm

2) I found the standard referred to at:
http://www.hmso.gov.uk/si/si1992/Uksi_19922372_en_1.htm
See section 20.

PS: I love the Brits - who else would title the government standards group
'Her
Majesty's Stationery Office'!


On Wed, 30 Oct 2002 20:48:18 +0100, Gert Gremmen g.grem...@cetest.nl
wrote:

There is no ground to beieve that military equiment is to be excluded
in any country in Europe. This is definitely not the case in the
Netherlands.

Regards,

Gert Gremmen
ce-test, qualified testing
Rotterdam, The Netherlands

http://www.ce-test.nl


-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of plaw...@west.net
Sent: woensdag 30 oktober 2002 18:49
To: EMC-PSTC
Subject: CE marking/testing of military equipment



I have a customer asking for CISPR 22 test results on a commercial power
supply
intended for use in military equipment in Europe.

I've heard the UK excludes military equipment from CE marking.  Do other
countries also exclude military equipment from the EMC Directive?

If CISPR standards are not used for European military equipment, would
MIL-STD-461 be used?

Patrick Lawler
plaw...@west.net

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

 

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



Patrick Lawler
plaw...@west.net

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc 

RE: EN61000-3-3 -3-11 off topic a bit!

2002-10-31 Thread David Heald

But when was the last time you saw a plug rated (just a random example) 250V
3(phase)Y 75A when it means 25A per phase?  the 75A rating is definately
'per phase'.

-Original Message-
From: Spencer, David H [mailto:david.spen...@usa.xerox.com]
Sent: Thursday, October 31, 2002 8:16 AM
To: emc-p...@majordomo.ieee.org
Subject: RE: EN61000-3-3  -3-11 off topic a bit!



I've just looked at all the draft copies of this standard(that I have), and
the older version TR IEC 1000-3-5.  Still only says 75amps.  Again no per
phase.

I would have to say if TC77A wanted it to say 75A per phase, it would be
in there.


Regards
Dave Spencer



-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Wednesday, October 30, 2002 3:07 PM
To: emc-p...@majordomo.ieee.org
Subject: EN61000-3-3  -3-11 off topic a bit!



I read in !emc-pstc that Spencer, David H david.spen...@usa.xerox.com
wrote (in 052106A55179D611B34300096BB02E3F8B93@USAMCMS4) about
'EN61000-3-3  -3-11  off topic a bit!' on Wed, 30 Oct 2002:
Having looked into EN61000-3-11, there is a big difference from
EN61000-3-3.
The scope of 3-3 refers to products rated 16 amps or less  per phase.
There is no per phase specification in EN61000-3-11.  Only this in the
title:  equipment with rated current 75 A.  Further, the scope does not
specify that as a per phase rating.

I would say that the standard does not apply to any product with a total
rating 75A.  That would allow 3 phase products rated greater than 25A per
phase to fall outside the scope of EN61000-3-11!  

That certainly needs to be clarified. I'll set the wheels in motion
immediately. It SHOULD say 'per phase'.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: CE marking/testing of military equipment/off topic

2002-10-31 Thread Ted Rook

Not only that but when a King succeeds to the throne it will become His 
Majesty's Stationery Office. Yep it is a bit quaint but the organization was up 
to date the last time I contacted them.

Your Humble Servant
Ted Rook
A Subject of Her Majesty Queen Elizabeth Second of The United Kingdom of Great 
Britain and Northern Ireland (G*d help us); Defender Of The Faith, and until 
daddy died, Emperor of India.




Best Regards

Ted Rook, Console Engineering, ext 4659

Please note our new location and phone numbers:

Crest Audio Inc, 16-00 Pollitt Drive
Fair Lawn, NJ 07410 USA

201 475 4600 telephone receptionist, 8.30 - 5 pm EST.
201 475 4659 direct line w/voice mail, 24 hrs.
201 475 4677 fax, 24 hrs.

 plaw...@west.net 30-Oct-02 5:50:10 PM 

Hi Gert:

I made the comment about the UK based on the following information:
http://www.emctla.org/Tech%20Notes/technical_guidance_note_33.htm 

2) I found the standard referred to at:
http://www.hmso.gov.uk/si/si1992/Uksi_19922372_en_1.htm 
See section 20.

PS: I love the Brits - who else would title the government standards group 'Her
Majesty's Stationery Office'!


On Wed, 30 Oct 2002 20:48:18 +0100, Gert Gremmen g.grem...@cetest.nl wrote:
There is no ground to beieve that military equiment is to be excluded
in any country in Europe. This is definitely not the case in the
Netherlands.

Regards,

Gert Gremmen
ce-test, qualified testing
Rotterdam, The Netherlands

http://www.ce-test.nl 


-Original Message-
From: owner-emc-p...@majordomo.ieee.org 
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of plaw...@west.net
Sent: woensdag 30 oktober 2002 18:49
To: EMC-PSTC
Subject: CE marking/testing of military equipment



I have a customer asking for CISPR 22 test results on a commercial power
supply
intended for use in military equipment in Europe.

I've heard the UK excludes military equipment from CE marking.  Do other
countries also exclude military equipment from the EMC Directive?

If CISPR standards are not used for European military equipment, would
MIL-STD-461 be used?

Patrick Lawler
plaw...@west.net 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com 
 Dave Heald:   davehe...@attbi.com 

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/ 
Click on browse and then emc-pstc mailing list




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com 
 Dave Heald:   davehe...@attbi.com 

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/ 
Click on browse and then emc-pstc mailing list


Patrick Lawler
plaw...@west.net 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com 
 Dave Heald:   davehe...@attbi.com 

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/ 
Click on browse and then emc-pstc mailing list



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   

Surge - injection point on screened cable

2002-10-31 Thread amund

According to IEC/EN 61000-4-5, the surge pulse shall be injected onto a
screened cable 20 meters from the DUT.

We have a fire alarm system with 20 detectors connected on the same screened
cable, 1.5 meters between each detector. We have been told from the local
test lab that we have to add a 20m cable between each detector in order to
surge test each detector.

I'm sure our local cable distributor like that idea ... , but do we really
have to do this ? Why is this 20 meters cable needed ? Is it to induce the
surge pulse from the screen into the cable lines?

The 20 detectors make a total cable distance of 30 meters and the screen is
continuous. Is it possible to insert a pulse in the beginning of the cable
and test all detectors simultaneous ?

Regards
Amund



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Temp/Humidity Meter

2002-10-31 Thread Price, Ed


-Original Message-
From: HALL,KEN (HP-Roseville,ex1) [mailto:ken_h...@hp.com]
Sent: Wednesday, October 30, 2002 4:32 PM
To: 'POWELL, DOUG'
Cc: 'g...@microprecision.com'; Emc-Pstc (E-mail)
Subject: RE: Temp/Humidity Meter



Hello,

We buy Radio Shack and others and have them calibrated by 
MicroPrecision

Regards,

Ken Hall
Hewlett-Packard

http://www.microprecision.com/index.html


There's just something about the above statement that makes me feel so
ancient  obsolete. g


Ed


Ed Price
ed.pr...@cubic.com
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA  USA
858-505-2780  (Voice)
858-505-1583  (Fax)
Military  Avionics EMC Is Our Specialty
Shake-Bake-Shock - Metrology - Reliability Analysis

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: EN61000-3-3 -3-11 off topic a bit!

2002-10-31 Thread Spencer, David H

I've just looked at all the draft copies of this standard(that I have), and
the older version TR IEC 1000-3-5.  Still only says 75amps.  Again no per
phase.

I would have to say if TC77A wanted it to say 75A per phase, it would be
in there.


Regards
Dave Spencer



-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Wednesday, October 30, 2002 3:07 PM
To: emc-p...@majordomo.ieee.org
Subject: EN61000-3-3  -3-11 off topic a bit!



I read in !emc-pstc that Spencer, David H david.spen...@usa.xerox.com
wrote (in 052106A55179D611B34300096BB02E3F8B93@USAMCMS4) about
'EN61000-3-3  -3-11  off topic a bit!' on Wed, 30 Oct 2002:
Having looked into EN61000-3-11, there is a big difference from
EN61000-3-3.
The scope of 3-3 refers to products rated 16 amps or less  per phase.
There is no per phase specification in EN61000-3-11.  Only this in the
title:  equipment with rated current 75 A.  Further, the scope does not
specify that as a per phase rating.

I would say that the standard does not apply to any product with a total
rating 75A.  That would allow 3 phase products rated greater than 25A per
phase to fall outside the scope of EN61000-3-11!  

That certainly needs to be clarified. I'll set the wheels in motion
immediately. It SHOULD say 'per phase'.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: CE marking/testing of military equipment

2002-10-31 Thread Luke Turnbull

I believe that the Germans insist on military equipment being CE marked.

UK military equipment needs to comply with Def Stan 59-41 for EMC requirements. 
 Find it at www.dstan.mod.uk

Luke Turnbull


 plaw...@west.net 10/30/02 05:48pm 

I have a customer asking for CISPR 22 test results on a commercial power supply
intended for use in military equipment in Europe.

I've heard the UK excludes military equipment from CE marking.  Do other
countries also exclude military equipment from the EMC Directive?

If CISPR standards are not used for European military equipment, would
MIL-STD-461 be used?

Patrick Lawler
plaw...@west.net 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com 
 Dave Heald:   davehe...@attbi.com 

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/ 
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: CE marking/testing of military equipment

2002-10-31 Thread John Woodgate

I read in !emc-pstc that plaw...@west.net wrote (in aun0su4ie5qe20vnk5b
p66i32clboe7...@4ax.com) about 'CE marking/testing of military
equipment' on Wed, 30 Oct 2002:
PS: I love the Brits - who else would title the government standards group 'Her
Majesty's Stationery Office'!

It isn't the standards group, it's the government publisher, now part
privatised.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: CE marking/testing of military equipment

2002-10-31 Thread Gert Gremmen

Hi Patrick,

This text is British law,en the Uk is only a half member of the EC.
This law is is not backed up by the EMC directive European Text.
It is therefore contradictory to the EC membership requirements
and theoretically illegal.
But who will complain, as it is not creating trade barriers,
and is limited to pure military equipment.
As always, the British stand out in Europe, gaining from the profits,
and not accepting the obligations.
As Margaret Thatcher already said: Why else did God create the Channel ?


Regards,

Gert Gremmen
ce-test, qualified testing
Rotterdam, The Netherlands

http://www.ce-test.nl

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of plaw...@west.net
Sent: woensdag 30 oktober 2002 23:50
To: EMC-PSTC
Subject: Re: CE marking/testing of military equipment



Hi Gert:

I made the comment about the UK based on the following information:
http://www.emctla.org/Tech%20Notes/technical_guidance_note_33.htm

2) I found the standard referred to at:
http://www.hmso.gov.uk/si/si1992/Uksi_19922372_en_1.htm
See section 20.

PS: I love the Brits - who else would title the government standards group
'Her
Majesty's Stationery Office'!


On Wed, 30 Oct 2002 20:48:18 +0100, Gert Gremmen g.grem...@cetest.nl
wrote:
There is no ground to beieve that military equiment is to be excluded
in any country in Europe. This is definitely not the case in the
Netherlands.

Regards,

Gert Gremmen
ce-test, qualified testing
Rotterdam, The Netherlands

http://www.ce-test.nl


-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of plaw...@west.net
Sent: woensdag 30 oktober 2002 18:49
To: EMC-PSTC
Subject: CE marking/testing of military equipment



I have a customer asking for CISPR 22 test results on a commercial power
supply
intended for use in military equipment in Europe.

I've heard the UK excludes military equipment from CE marking.  Do other
countries also exclude military equipment from the EMC Directive?

If CISPR standards are not used for European military equipment, would
MIL-STD-461 be used?

Patrick Lawler
plaw...@west.net

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Patrick Lawler
plaw...@west.net

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:

Re: EN61326:1997 Planning

2002-10-31 Thread Lfresearch

And you seem to have forgotten that Schaffner also have products that compete 
for these test too Frank. lol

Derek.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: EN61326:1997 Planning

2002-10-31 Thread Michael Hopkins

Didn't forget at all. there are 7 or 8 manufacturers that can supply
this equipment.


Mike Hopkins


- Original Message -
From: Frank Krozel fr...@electronicinstrument.com
To: Mike Hopkins michael.hopk...@thermo.com; 'Bill Flanigan'
bflani...@ameritherm.com; emc-p...@majordomo.ieee.org
Sent: Wednesday, October 30, 2002 7:05 PM
Subject: Re: EN61326:1997 Planning



 Mike / all.
 You seem to have forgotten Amplifier Research has competing equipment to
the
 one that you work for.
 Frank
 - Original Message -
 From: Mike Hopkins michael.hopk...@thermo.com
 To: 'Bill Flanigan' bflani...@ameritherm.com;
 emc-p...@majordomo.ieee.org
 Sent: Wednesday, October 30, 2002 12:34 PM
 Subject: RE: EN61326:1997 Planning


 
  These days, there are a number of combination testers on the market
that
  will perform tests to both IEC 61000-4-5 and 61000-4-11. Thermo KeyTek
has
  one for just under $10k that also does EFT and Mag fields for the same
  price Other manufacturers have similar units - prices depend on
things
  like voltage (testing to as high as 6kV for surge), how the dip 
 interrupt
  tests are done (external variac's and switches vs. internal tap switched
  transformers), software control, etc...
 
  I'll leave the CISPR 11 questions to someone more qualified than I
am.
 
  Mike Hopkins
 
  -Original Message-
  From: Bill Flanigan [mailto:bflani...@ameritherm.com]
  Sent: Wednesday, October 30, 2002 10:27 AM
  To: emc-p...@majordomo.ieee.org
  Subject: EN61326:1997 Planning
 
 
 
  A few questions about compliance to EN 61326. Guidance requested from my
  emc-pstc colleagues
 
  What happened in Amendment 2; I have the standard to +A1
 
  Immunity:
  EN 61000-4-5 [Imm'y Surge] what kind of equipment is needed to
  conduct this test?
  EN 61000-4-11[Imm'y Voltage dips] what kind of equipment is needed
  to conduct this test?
 
  Emissions:
  We manufacture equipment classified under EN55011 as ClassA Group2;
  we generate RF energy for industrial purposes, excluding communications.
  Section 7.2 says 'For equipment using ISM frequencies, see CISPR11.'
  *Does this mean _use_ EN55011:91 for emissions limits as I have been
  doing? EN 61326-1 doesn't mention anything about Group2 limits.
  *Is there now a distinction between ISM equipment and equipment
  using ISM frequencies? Not trying to split hairs here, but if it doesn't
  actually use ISM frequencies my equipment is calssified as ISM
equipment,
  right?
 
  Wm Flanigan
  Standards Engineer
  Ameritherm Inc
  1.800.456.4328
  bflani...@ameritherm.com
 
 
 
 
  ---
  This message is from the IEEE EMC Society Product Safety
  Technical Committee emc-pstc discussion list.
 
  Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
  To cancel your subscription, send mail to:
   majord...@ieee.org
  with the single line:
   unsubscribe emc-pstc
 
  For help, send mail to the list administrators:
   Ron Pickard:  emc-p...@hypercom.com
   Dave Heald:   davehe...@attbi.com
 
  For policy questions, send mail to:
   Richard Nute:   ri...@ieee.org
   Jim Bacher: j.bac...@ieee.org
 
  All emc-pstc postings are archived and searchable on the web at:
  http://ieeepstc.mindcruiser.com/
  Click on browse and then emc-pstc mailing list
 
  ---
  This message is from the IEEE EMC Society Product Safety
  Technical Committee emc-pstc discussion list.
 
  Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
  To cancel your subscription, send mail to:
   majord...@ieee.org
  with the single line:
   unsubscribe emc-pstc
 
  For help, send mail to the list administrators:
   Ron Pickard:  emc-p...@hypercom.com
   Dave Heald:   davehe...@attbi.com
 
  For policy questions, send mail to:
   Richard Nute:   ri...@ieee.org
   Jim Bacher: j.bac...@ieee.org
 
  All emc-pstc postings are archived and searchable on the web at:
  http://ieeepstc.mindcruiser.com/
  Click on browse and then emc-pstc mailing list
 



 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list





RE: Measuring AC Line Impedance

2002-10-31 Thread Ralph McDiarmid

I would have expected that the inductance would dominate the branch
impedance at line frequency and its harmonics.

Ralph McDiarmid, AScT 
Member Technical Staff
Engineering Services
Xantrex Technology Inc.
www.xantrex.com


-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Wednesday, October 30, 2002 11:30 AM
To: emc-p...@majordomo.ieee.org
Subject: Re: Measuring AC Line Impedance



I read in !emc-pstc that Spencer, David H david.spen...@usa.xerox.com
wrote (in 052106A55179D611B34300096BB02E3F8B94@USAMCMS4) about
'Measuring AC Line Impedance' on Wed, 30 Oct 2002:

Any comments or input would be welcome.

It's how I do it. It comes as a surprise to some people that the voltage
goes up when you put a big capacitor across the supply. Don't go over
the top with BIG caps and resonate the supply inductance. You would NOT
like the result, and neither would the electricity supplier.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Temp/Humidity Meter

2002-10-31 Thread Electrical-Safety - Bill Addiss


Here are some EXTECH brand meters, somewhat mingled under Moisture Meters 
and Thermometers:


http://www.electrical-contractor.net/the_store/EX/HMoisture_Main.htm

http://www.electrical-contractor.net/the_store/EX/Therm_Main.htm

Bill Addiss

At 10:44 AM 10/30/02 -0800, Flinders, Randall wrote:


Greetings fellow EMC'ers..

We are looking for a quality outdoor Temperature/Humidity meter for our open
area test site.  Any recommendations?

Thanks!

Randy Flinders
Electromagnetic Compatibility Engineer

Emulex Corporation - We Network Storage
3535 Harbor Blvd.
Costa Mesa, Ca. 92626

Direct:  (714) 513-8012
Fax: (714) 513-5408
Email:   randall.flind...@emulex.com mailto:randall.flind...@emulex.com
Web:  http://www.emulex.com




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list
This E-mail scanned for viruses by RAVES(ReadyConnect.Net Anti-Virus EMail 
System)


Bill Addiss
Electrical Safety Forum
http://www.Electrical-Safety.com

This E-mail scanned for viruses by RAVES(ReadyConnect.Net Anti-Virus EMail 
System)


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
   http://ieeepstc.mindcruiser.com/
   Click on browse and then emc-pstc mailing list


Re: measuring AC line impedance (:-)

2002-10-31 Thread Ken Javor

I did that once. I had been measuring resistance and then needed to measure
ac outlet potential, but forgot to change the meter knob position.  Now I
have a new meter.

--
From: Ted Rook t...@crestaudio.com
To: emc-p...@ieee.org
Subject: measuring AC line impedance (:-)
Date: Wed, Oct 30, 2002, 5:42 PM



 don't you stick the probes in the outlet with the knob set to 'OHMS'?  (;o)

 sorry couldn't resist it.
 don't try this at home folks.



 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Temp/Humidity Meter

2002-10-31 Thread HALL,KEN (HP-Roseville,ex1)

Hello,

We buy Radio Shack and others and have them calibrated by MicroPrecision

Regards,

Ken Hall
Hewlett-Packard

http://www.microprecision.com/index.html

-Original Message-
From: POWELL, DOUG [mailto:doug.pow...@aei.com]
Sent: Wednesday, October 30, 2002 2:42 PM
To: 'Flinders, Randall'; Emc-Pstc (E-mail)
Subject: RE: Temp/Humidity Meter



You could buy a Radio Shack hand held unit, but I don't know if you can
trace calbration.

Check out Vaisala Products at
http://www.vaisala.com/thumbnail.asp?Section=5444

Best regards,

-doug

Douglas E. Powell
Compliance Engineer
Advanced Energy Industries, Inc.
Fort Collins, CO 80535 USA



-Original Message-
From: Flinders, Randall [mailto:randall.flind...@emulex.com]
Sent: Wednesday, October 30, 2002 11:44 AM
To: Emc-Pstc (E-mail)
Subject: Temp/Humidity Meter



Greetings fellow EMC'ers..

We are looking for a quality outdoor Temperature/Humidity meter for our open
area test site.  Any recommendations?

Thanks!

Randy Flinders
Electromagnetic Compatibility Engineer
 
Emulex Corporation - We Network Storage   
3535 Harbor Blvd.
Costa Mesa, Ca. 92626
 
Direct:  (714) 513-8012 
Fax: (714) 513-5408 
Email:   randall.flind...@emulex.com mailto:randall.flind...@emulex.com
Web:  http://www.emulex.com
 
 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list