Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-10 Thread Piotr Galka

Hi Glyn,

I understand that there should not be hazard in all expected situations 
(normal / abnormal use and fault condition) and USB cable is too short 
to consider transients.
What I am trying to do is to understand 62368-1 and reading it I came to 
5.4.11 that was hard for me to understand what are exact listed there 
requirements and if they touch my devices.


That laptop I described is an example of device that looks as being not 
excluded from 5.4.11, and USB is looking (for me) as being external 
circuits according to 62368-1 definition of this therm and being 
indicated in table 14.
The only way to solve this laptop problem, I see, is if we have to 
assume that the note in table 14 of not considering transients (as USB 
is wholly in the same building) makes USB being not indicated in table. 
When first time writing my question I was not sure if I can assume this. 
Now I suppose that I have to assume this (if transients are not taken 
into account than cable is not indicated in table 14).


The device I have in mind is 12V powered access controller hawing RS485 
(not isolated) and because of this RS485 I am trying to understand 5.4.11.

Now I suppose that:
1. It is permanently connected equipment so 5.4.11 not apply, and even 
it is not permanently connected (as being isolated from Mains by 12V 
supply) then
2. RS485 as being whole in one building (transients are not taken into 
account) is not indicated in table 14 so 5.4.11 not apply.


The typical 12V supply used (MEAN WELL DRC-40A) specification says:
  SAFETY STANDARDS:   UL60950-1, TUV EN60950-1 approved
  WITHSTAND VOLTAGE:    I/P-O/P:3KVAC I/P-FG:2KVAC O/P-FG:0.5KVAC

I always assumed that it is better to not Earth DC12V (its negative pole).
Reading 62368-2 5.4.11 description I confirm myself in this belief. Not 
Earthing 12V we not provide (by RS485) Earth potential to a remote 
environment making it being still save even if by any other fault the 
Mains potential can be there.

Do you agree with me?

Best Regards
Piotr Galka


W dniu 2024-05-10 o 17:26, Glyn Payne pisze:


Hi Piotr,

Maximum USB cable lengths are quite short, a few meters, and they are 
not designed to be part of the ‘building or structure’, hence 
transients are not considered for these ports. If a USB extender or 
hub is used to extend the USB and this is wired through the building 
or structure then transients would be the problem of the hub 
manufacturer and not your product.



There was/is /IEC 62368-//3/: /Safety aspects for DC power
transfer through communication cables and ports/, which is
referenced by IEC 62368-1 however this being reworked by TC108 and
as far as I can tell few people are using it in it’s present form.


When testing your product under 62368-1 the test house will
determine the maximum voltage and current the USB (or serial) port
can provide, under normal, abnormal and fault conditions, to
ensure that there is no hazard.


Best regards,


Glyn Payne

*From:*Piotr Galka 
*Sent:* Wednesday, May 8, 2024 9:28 PM
*To:* EMC-PSTC@LISTSERV.IEEE.ORG
*Subject:* Re: [PSES] IEC 62368-1: To understand chapter 5.4.11




You don't often get email from piotr.ga...@micromade.pl. Learn why 
this is important <https://aka.ms/LearnAboutSenderIdentification>




Hi Bostjan,

I know that if circuit is not going out of building it is considered 
being without transients. My doubt is mainly because in 5.4.11 says 
about circuits being external and indicated in table 14 and according 
to my understanding 3.3.1.1 USB was external and note about transients 
in table 14 for me didn't make for me USB being not indicated in table.
In my RS485 design even it is in one building I assume during storm up 
to 50V temporary difference between several grounding points and I use 
2 steps protection. I know of two such incidents that after lightning 
struck directly into the building, many systems stopped working, but 
ours did.

I acknowledge that USB is not external circuit.
Thanks a lot.

I have never bought any standard abroad and as I have written 
answering to Johns post I see that 62368-2 is not in current Polish 
Standard Committee offer.


Best regards
Piotr Galka

W dniu 2024-05-08 o 18:45, Boštjan Glavič pisze:

Hi Piotr

If circuit does not go out of building it is not considered as
circuit with transients. I think you should check other standard
like IEC 62151 and IEC 62102 which clasify external circuits.

From my experiences, and I do have quite some, USB is not
considered as external circuit in the sense of clause, where
requirements between external circuit and PE are specified.

Did you also check 62368-2?

Best regards

Bostjan

Poslano iz Outlook za Android <https://aka.ms/AAb9ysg>



*Od:* Piotr Galka 
<mailto:piotr.ga...@micromade.pl>
*Poslano:* sreda, m

Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-10 Thread Glyn Payne
Hi Piotr,

Maximum USB cable lengths are quite short, a few meters, and they are not 
designed to be part of the ‘building or structure’, hence transients are not 
considered for these ports. If a USB extender or hub is used to extend the USB 
and this is wired through the building or structure then transients would be 
the problem of the hub manufacturer and not your product.

There was/is IEC 62368-3: Safety aspects for DC power transfer through 
communication cables and ports, which is referenced by IEC 62368-1 however this 
being reworked by TC108 and as far as I can tell few people are using it in 
it’s present form.
When testing your product under 62368-1 the test house will determine the 
maximum voltage and current the USB (or serial) port can provide, under normal, 
abnormal and fault conditions, to ensure that there is no hazard.

Best regards,
Glyn Payne

From: Piotr Galka 
Sent: Wednesday, May 8, 2024 9:28 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

You don't often get email from 
piotr.ga...@micromade.pl<mailto:piotr.ga...@micromade.pl>. Learn why this is 
important<https://aka.ms/LearnAboutSenderIdentification>
Hi Bostjan,

I know that if circuit is not going out of building it is considered being 
without transients. My doubt is mainly because in 5.4.11 says about circuits 
being external and indicated in table 14 and according to my understanding 
3.3.1.1 USB was external and note about transients in table 14 for me didn't 
make for me USB being not indicated in table.
In my RS485 design even it is in one building I assume during storm up to 50V 
temporary difference between several grounding points and I use 2 steps 
protection. I know of two such incidents that after lightning struck directly 
into the building, many systems stopped working, but ours did.
I acknowledge that USB is not external circuit.
Thanks a lot.

I have never bought any standard abroad and as I have written answering to 
Johns post I see that 62368-2 is not in current Polish Standard Committee offer.

Best regards
Piotr Galka

W dniu 2024-05-08 o 18:45, Boštjan Glavič pisze:
Hi Piotr

If circuit does not go out of building it is not considered as circuit with 
transients. I think you should check other standard like IEC 62151 and IEC 
62102 which clasify external circuits.

From my experiences, and I do have quite some, USB is not considered as 
external circuit in the sense of clause, where requirements between external 
circuit and PE are specified.

Did you also check 62368-2?

Best regards
Bostjan





Poslano iz Outlook za Android<https://aka.ms/AAb9ysg>


Od: Piotr Galka <mailto:piotr.ga...@micromade.pl>
Poslano: sreda, maj 8, 2024 5:21:33 PM
Za: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG> 
<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
Zadeva: Re: [PSES] IEC 62368-1: To understand chapter 5.4.11


Hi Bostjan,

Thanks for your feedback, but...

I am slowly and carefully reading 62368-1 for the first time.
It defines 'external circuit' in 3.3.1.1 as "electrical circuit that is
external to the equipment and is not mains".
I assumed one device = one equipment so I thought laptop is an
equipment. After your post I checked how equipment is defined in 62368-1
but in 3.3 there is no equipment definition so I don't know what is
equipment.
May be USB device (pendrive) connected without cable to laptop can be
assumed being its part, or even device powered by USB (mouse, keyboard)
can be assumed being its part, but USB can be used to connect other
equipment, I think. Do laser printer being powered separately from mains
connected to laptop is understood as being internal part of equipment?
Laptop is probably manufactured by someone else than laser printer. They
can't assume they manufacture single equipment, I think.
In past I have read about USB being used to connect active wifi antenna
located on the roof (with few hubs to extend connection length). Having
all that in mind it is hard for me to accept that for 62368-1 USB is
equipment internal circuit.

Now.
If we assume laptop with connected to it mouse, external keyboard and
printer is one equipment then going to my field: do the access control
controller with RFID readers connected to it by RS485 is also one
equipment (all powered from one 12V supply, and located in one building)
making RS485 connection being internal equipment circuit?
I don't think so.

And I repeat my main question regarding 5.4.11: Do the access controller
permanently connected to 12V supply that is permanently connected to
mains is permanently connected equipment? I think yes. Even 12V supply
has isolation in it.
If I change understanding of equipment and assume that controller + 12V
supply are one equipment than thinks get easier - such understood
equipment is permanently connected. But is it one equipment if
controller is manufactured by someone other then

Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-09 Thread Bill Owsley
 I have been watching this subject for a while.
i vaguely recall that in some front matter in some standards is a statement 
that indicates that this is the minimum requirements to go to market.
 So in the interests of the Corp/s that I worked for at the time, and any 
quality targets, that they may have, or not, regardless of their awareness of 
such targets...
I often figured out tests that were needed/useful ... but maybe not required in 
the strict minimum requirements.
And reported the results.  
And fixes to meet those "not strictly required" minimum standards.
And did this early in the development process, thus EMC First,
First off product could ship !!!
And then I/they could spend time and money on cost reducing at our leisure.
Cuz product was shipping and bringing in revenue.
On time, or even early before plans.






 

On Thursday, May 9, 2024, 7:44:05 AM EDT, James Pawson (U3C) 
 wrote:  
 
 
Hi Piotr,

  

Just to add to the debate:

  

“I know that if circuit is not going out of building it is considered being 
without transients”

  

If a cable is longer than 30m then most product EMC standards will call up a 
requirement for line-to-earth surge testing. Some do make it explicit that this 
should be only for cables leaving a building or site, some do not…

  

All the best

James

  

James Pawson

Managing Director & EMC Problem Solver

  

Unit 3 Compliance Ltd

EMC : Environmental & Vibration : Electrical Safety : CE & UKCA : Consultancy

  

www.unit3compliance.co.uk | ja...@unit3compliance.co.uk 

+44(0)1274 911747  |  +44(0)7811 139957

2 Wellington Business Park, New Lane, Bradford, BD4 8AL

Registered in England and Wales # 10574298

  

Office hours:

Every morning my full attention is on consultancy, testing, and troubleshooting 
activities for our customers’ projects. I’m available/contactable between 1300h 
to 1730h Mon/Tue/Thurs/Fri.

For inquiries, bookings, and testing updates please send us an email on 
he...@unit3compliance.co.uk or call 01274 911747. Our lead times for testing 
and consultancy are typically 4-5 weeks.

  

  

  

  

From: Piotr Galka  
Sent: Wednesday, May 8, 2024 9:28 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

  

Hi Bostjan,

I know that if circuit is not going out of building it is considered being 
without transients. My doubt is mainly because in 5.4.11 says about circuits 
being external and indicated in table 14 and according to my understanding 
3.3.1.1 USB was external and note about transients in table 14 for me didn't 
make for me USB being not indicated in table.
In my RS485 design even it is in one building I assume during storm up to 50V 
temporary difference between several grounding points and I use 2 steps 
protection. I know of two such incidents that after lightning struck directly 
into the building, many systems stopped working, but ours did.
I acknowledge that USB is not external circuit.
Thanks a lot.

I have never bought any standard abroad and as I have written answering to 
Johns post I see that 62368-2 is not in current Polish Standard Committee offer.

Best regards
Piotr Galka



W dniu 2024-05-08 o 18:45, Boštjan Glavič pisze:


Hi Piotr

  

If circuit does not go out of building it is not considered as circuit with 
transients. I think you should check other standard like IEC 62151 and IEC 
62102 which clasify external circuits.

  

>From my experiences, and I do have quite some, USB is not considered as 
>external circuit in the sense of clause, where requirements between external 
>circuit and PE are specified.

  

Did you also check 62368-2?

  

Best regards 

Bostjan

  

  

  

  

  

Poslano iz Outlook za Android

  

Od: Piotr Galka 
Poslano: sreda, maj 8, 2024 5:21:33 PM
Za: EMC-PSTC@LISTSERV.IEEE.ORG 
Zadeva: Re: [PSES] IEC 62368-1: To understand chapter 5.4.11





Hi Bostjan,

Thanks for your feedback, but...

I am slowly and carefully reading 62368-1 for the first time.
It defines 'external circuit' in 3.3.1.1 as "electrical circuit that is 
external to the equipment and is not mains".
I assumed one device = one equipment so I thought laptop is an 
equipment. After your post I checked how equipment is defined in 62368-1 
but in 3.3 there is no equipment definition so I don't know what is 
equipment.
May be USB device (pendrive) connected without cable to laptop can be 
assumed being its part, or even device powered by USB (mouse, keyboard) 
can be assumed being its part, but USB can be used to connect other 
equipment, I think. Do laser printer being powered separately from mains 
connected to laptop is understood as being internal part of equipment? 
Laptop is probably manufactured by someone else than laser printer. They 
can't assume they manufacture single equipment, I think.
In past I have read about USB being used to connect active wifi antenna 
located on the roof (with few hubs to extend con

Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-09 Thread Piotr Galka

Hi James,

Thank you for drawing attention to this but my sentence was in context 
of 62368-1 only.


When in 2004 (few days after we joined EU) I went with my devices for 
the first time to EMC lab (it was an internal company laboratory that 
also offered external services) they didn't had a capacitors needed in 
surge testing transmission lines. So we tested them using only 40 ohm 
resistor. Since then I design my not isolated RS485 to withstand 25A 
50us current pulse (Surge generator loaded with 40ohm gives current 
pulse of a shape rather like its voltage pulse then its current pulse).
As I have encountered EMC problems in 90s (devices with RS485 having 
only ICs ESD protection routed between buildings standing on the top of 
hill were hanging after every storm) I was well prepared in 2004 and 
they were surprised that all my devices passed all the tests for the 
first time.


Regards
Piotr

W dniu 2024-05-09 o 13:43, James Pawson (U3C) pisze:


Hi Piotr,

Just to add to the debate:

“I know that if circuit is not going out of building it is considered 
being without transients”


If a cable is longer than 30m then most product EMC standards will 
call up a requirement for line-to-earth surge testing. Some do make it 
explicit that this should be only for cables leaving a building or 
site, some do not…


All the best

James

James Pawson

Managing Director & EMC Problem Solver

*Unit 3 Compliance Ltd*

*EMC : Environmental & Vibration : Electrical Safety : CE & UKCA : 
Consultancy*


www.unit3compliance.co.uk <http://www.unit3compliance.co.uk/> | 
ja...@unit3compliance.co.uk <mailto:ja...@unit3compliance.co.uk>


+44(0)1274 911747  |  +44(0)7811 139957

2 Wellington Business Park, New Lane, Bradford, BD4 8AL

Registered in England and Wales # 10574298

/Office hours:/

/Every morning my full attention is on consultancy, testing, and 
troubleshooting activities for our customers’ projects. I’m 
available/contactable between 1300h to 1730h Mon/Tue/Thurs/Fri./


/For inquiries, bookings, and testing updates please send us an email 
on he...@unit3compliance.co.uk or call 01274 911747. Our lead times 
for testing and consultancy are typically 4-5 weeks./


*From:*Piotr Galka 
*Sent:* Wednesday, May 8, 2024 9:28 PM
*To:* EMC-PSTC@LISTSERV.IEEE.ORG
*Subject:* Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

Hi Bostjan,

I know that if circuit is not going out of building it is considered 
being without transients. My doubt is mainly because in 5.4.11 says 
about circuits being external and indicated in table 14 and according 
to my understanding 3.3.1.1 USB was external and note about transients 
in table 14 for me didn't make for me USB being not indicated in table.
In my RS485 design even it is in one building I assume during storm up 
to 50V temporary difference between several grounding points and I use 
2 steps protection. I know of two such incidents that after lightning 
struck directly into the building, many systems stopped working, but 
ours did.

I acknowledge that USB is not external circuit.
Thanks a lot.

I have never bought any standard abroad and as I have written 
answering to Johns post I see that 62368-2 is not in current Polish 
Standard Committee offer.


Best regards
Piotr Galka

W dniu 2024-05-08 o 18:45, Boštjan Glavič pisze:

Hi Piotr

If circuit does not go out of building it is not considered as
circuit with transients. I think you should check other standard
like IEC 62151 and IEC 62102 which clasify external circuits.

From my experiences, and I do have quite some, USB is not
considered as external circuit in the sense of clause, where
requirements between external circuit and PE are specified.

Did you also check 62368-2?

Best regards

Bostjan

Poslano iz Outlook za Android <https://aka.ms/AAb9ysg>



*Od:*Piotr Galka 
<mailto:piotr.ga...@micromade.pl>
*Poslano:* sreda, maj 8, 2024 5:21:33 PM
*Za:* EMC-PSTC@LISTSERV.IEEE.ORG 
<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
*Zadeva:* Re: [PSES] IEC 62368-1: To understand chapter 5.4.11



Hi Bostjan,

Thanks for your feedback, but...

I am slowly and carefully reading 62368-1 for the first time.
It defines 'external circuit' in 3.3.1.1 as "electrical circuit
that is
external to the equipment and is not mains".
I assumed one device = one equipment so I thought laptop is an
equipment. After your post I checked how equipment is defined in
62368-1
but in 3.3 there is no equipment definition so I don't know what is
equipment.
May be USB device (pendrive) connected without cable to laptop can be
assumed being its part, or even device powered by USB (mouse,
keyboard)
can be assumed being its part, but USB can be used to connect other
equipment, I think. Do laser printer being power

Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-09 Thread James Pawson (U3C)
Hi Piotr,

 

Just to add to the debate:

 

“I know that if circuit is not going out of building it is considered being 
without transients”

 

If a cable is longer than 30m then most product EMC standards will call up a 
requirement for line-to-earth surge testing. Some do make it explicit that this 
should be only for cables leaving a building or site, some do not…

 

All the best

James

 

James Pawson

Managing Director & EMC Problem Solver

 

Unit 3 Compliance Ltd

EMC : Environmental & Vibration : Electrical Safety : CE & UKCA : Consultancy

 

 <http://www.unit3compliance.co.uk/> www.unit3compliance.co.uk |  
<mailto:ja...@unit3compliance.co.uk> ja...@unit3compliance.co.uk 

+44(0)1274 911747  |  +44(0)7811 139957

2 Wellington Business Park, New Lane, Bradford, BD4 8AL

Registered in England and Wales # 10574298

 

Office hours:

Every morning my full attention is on consultancy, testing, and troubleshooting 
activities for our customers’ projects. I’m available/contactable between 1300h 
to 1730h Mon/Tue/Thurs/Fri.

For inquiries, bookings, and testing updates please send us an email on 
he...@unit3compliance.co.uk <mailto:he...@unit3compliance.co.uk>  or call 01274 
911747. Our lead times for testing and consultancy are typically 4-5 weeks.

 

 

 

 

From: Piotr Galka  
Sent: Wednesday, May 8, 2024 9:28 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

 

Hi Bostjan,

I know that if circuit is not going out of building it is considered being 
without transients. My doubt is mainly because in 5.4.11 says about circuits 
being external and indicated in table 14 and according to my understanding 
3.3.1.1 USB was external and note about transients in table 14 for me didn't 
make for me USB being not indicated in table.
In my RS485 design even it is in one building I assume during storm up to 50V 
temporary difference between several grounding points and I use 2 steps 
protection. I know of two such incidents that after lightning struck directly 
into the building, many systems stopped working, but ours did.
I acknowledge that USB is not external circuit.
Thanks a lot.

I have never bought any standard abroad and as I have written answering to 
Johns post I see that 62368-2 is not in current Polish Standard Committee offer.

Best regards
Piotr Galka



W dniu 2024-05-08 o 18:45, Boštjan Glavič pisze:

Hi Piotr

 

If circuit does not go out of building it is not considered as circuit with 
transients. I think you should check other standard like IEC 62151 and IEC 
62102 which clasify external circuits.

 

>From my experiences, and I do have quite some, USB is not considered as 
>external circuit in the sense of clause, where requirements between external 
>circuit and PE are specified.

 

Did you also check 62368-2?

 

Best regards 

Bostjan

 

 

 

 

 

Poslano iz Outlook za Android <https://aka.ms/AAb9ysg> 

 

  _  

Od: Piotr Galka  <mailto:piotr.ga...@micromade.pl> 
Poslano: sreda, maj 8, 2024 5:21:33 PM
Za: EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG>   
<mailto:EMC-PSTC@LISTSERV.IEEE.ORG> 
Zadeva: Re: [PSES] IEC 62368-1: To understand chapter 5.4.11





Hi Bostjan,

Thanks for your feedback, but...

I am slowly and carefully reading 62368-1 for the first time.
It defines 'external circuit' in 3.3.1.1 as "electrical circuit that is 
external to the equipment and is not mains".
I assumed one device = one equipment so I thought laptop is an 
equipment. After your post I checked how equipment is defined in 62368-1 
but in 3.3 there is no equipment definition so I don't know what is 
equipment.
May be USB device (pendrive) connected without cable to laptop can be 
assumed being its part, or even device powered by USB (mouse, keyboard) 
can be assumed being its part, but USB can be used to connect other 
equipment, I think. Do laser printer being powered separately from mains 
connected to laptop is understood as being internal part of equipment? 
Laptop is probably manufactured by someone else than laser printer. They 
can't assume they manufacture single equipment, I think.
In past I have read about USB being used to connect active wifi antenna 
located on the roof (with few hubs to extend connection length). Having 
all that in mind it is hard for me to accept that for 62368-1 USB is 
equipment internal circuit.

Now.
If we assume laptop with connected to it mouse, external keyboard and 
printer is one equipment then going to my field: do the access control 
controller with RFID readers connected to it by RS485 is also one 
equipment (all powered from one 12V supply, and located in one building) 
making RS485 connection being internal equipment circuit?
I don't think so.

And I repeat my main question regarding 5.4.11: Do the access controller 
permanently connected to 12V supply that is permanently connected to 
mains is permanently con

Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-09 Thread Piotr Galka

Hi Ralph and John,

62368-1 I have bought from PKN is in form "first and last page Polish 
and everything inside English".
I suppose they with pleasure will charge me for 62368-2 if I ask them 
for it. The only question is how much time is needed to prepare these 2 
pages.
As I remember from times when I was writing here from time to time - we 
came to conclusion that PKN prices were clearly lower then in other sources.


What I am surprised the most: Do really I (a guy from a company with 4 
employees) am the first one in Poland being interested in 62368-2 :)


Best Regards
Piotr Galka



W dniu 2024-05-08 o 23:07, Ralph McDiarmid pisze:

Signature

The IEC store has IEC TR 62368-2:2019 RLV for 553 Swiss Francs.   Ouch.

*From:*John Woodgate 
*Sent:* Wednesday, May 8, 2024 1:37 PM
*To:* EMC-PSTC@LISTSERV.IEEE.ORG
*Subject:* Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

You can get 62368-2 from: https://www.evs.ee/en/iec-tr-62368-2-2019, 
but it is rather costly.


On 2024-05-08 21:00, Piotr Galka wrote:

After reading your post my decision was to buy 62368-2 but I've
just checked that in PKN (Polish Standards Committee) I can buy
62368-1 what I have done long ago but they don't have 62368-2 :( .

--
OOO - Own Opinions Only
Best wishes
John Woodgate, Rayleigh, Essex UK
Keep trying

<http://www.avg.com/email-signature?utm_medium=email_source=link_campaign=sig-email_content=emailclient>



Virus-free.www.avg.com 
<http://www.avg.com/email-signature?utm_medium=email_source=link_campaign=sig-email_content=emailclient>




This message is from the IEEE Product Safety Engineering Society 
emc-pstc discussion list. To post a message to the list, send your 
e-mail to EMC-PSTC@LISTSERV.IEEE.ORG


All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/ 
<https://www.mail-archive.com/emc-pstc@listserv.ieee.org/%20>


Website: https://ewh.ieee.org/soc/pses/
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how 
to unsubscribe) <https://ewh.ieee.org/soc/pses/list.html>

List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org



To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC=1 
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC=1>




This message is from the IEEE Product Safety Engineering Society 
emc-pstc discussion list. To post a message to the list, send your 
e-mail to EMC-PSTC@LISTSERV.IEEE.ORG


All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website: https://ewh.ieee.org/soc/pses/
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how 
to unsubscribe) <https://ewh.ieee.org/soc/pses/list.html>

List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org



To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC=1




-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  
_
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC=1


Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-08 Thread Ralph McDiarmid
The IEC store has IEC TR 62368-2:2019 RLV for 553 Swiss Francs.   Ouch.

 

From: John Woodgate  
Sent: Wednesday, May 8, 2024 1:37 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

 

You can get 62368-2 from: https://www.evs.ee/en/iec-tr-62368-2-2019, but it is 
rather costly.

On 2024-05-08 21:00, Piotr Galka wrote:

After reading your post my decision was to buy 62368-2 but I've just checked 
that in PKN (Polish Standards Committee) I can buy 62368-1 what I have done 
long ago but they don't have 62368-2 :( .

-- 
OOO - Own Opinions Only
Best wishes
John Woodgate, Rayleigh, Essex UK
Keep trying

 


 
<http://www.avg.com/email-signature?utm_medium=email_source=link_campaign=sig-email_content=emailclient>
 

Virus-free. 
<http://www.avg.com/email-signature?utm_medium=email_source=link_campaign=sig-email_content=emailclient>
 www.avg.com

  _  

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG>  

All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/ 
<https://www.mail-archive.com/emc-pstc@listserv.ieee.org/%20>  

Website: https://ewh.ieee.org/soc/pses/  <https://ewh.ieee.org/soc/pses/> 
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe) <https://ewh.ieee.org/soc/pses/list.html> 
List rules: https://ewh.ieee.org/soc/pses/listrules.html 

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net <mailto:msherma...@comcast.net> 
Rick Linford at: linf...@ieee.org <mailto:linf...@ieee.org>  

For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org <mailto:j.bac...@ieee.org>  

  _  

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC 
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC=1> =1 


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  
_
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC=1


Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-08 Thread John Woodgate
You can get 62368-2 from: https://www.evs.ee/en/iec-tr-62368-2-2019, but 
it is rather costly.


On 2024-05-08 21:00, Piotr Galka wrote:
After reading your post my decision was to buy 62368-2 but I've just 
checked that in PKN (Polish Standards Committee) I can buy 62368-1 
what I have done long ago but they don't have 62368-2 :( .

--
Signature OOO - Own Opinions Only
Best wishes
John Woodgate, Rayleigh, Essex UK
Keep trying

--
This email has been checked for viruses by AVG antivirus software.
www.avg.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  
_
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC=1

Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-08 Thread Piotr Galka

Hi Bostjan,

I know that if circuit is not going out of building it is considered 
being without transients. My doubt is mainly because in 5.4.11 says 
about circuits being external and indicated in table 14 and according to 
my understanding 3.3.1.1 USB was external and note about transients in 
table 14 for me didn't make for me USB being not indicated in table.
In my RS485 design even it is in one building I assume during storm up 
to 50V temporary difference between several grounding points and I use 2 
steps protection. I know of two such incidents that after lightning 
struck directly into the building, many systems stopped working, but 
ours did.

I acknowledge that USB is not external circuit.
Thanks a lot.

I have never bought any standard abroad and as I have written answering 
to Johns post I see that 62368-2 is not in current Polish Standard 
Committee offer.


Best regards
Piotr Galka


W dniu 2024-05-08 o 18:45, Boštjan Glavič pisze:

Hi Piotr

If circuit does not go out of building it is not considered as circuit 
with transients. I think you should check other standard like IEC 
62151 and IEC 62102 which clasify external circuits.


From my experiences, and I do have quite some, USB is not considered 
as external circuit in the sense of clause, where requirements between 
external circuit and PE are specified.


Did you also check 62368-2?

Best regards
Bostjan





Poslano iz Outlook za Android <https://aka.ms/AAb9ysg>


*Od:* Piotr Galka 
*Poslano:* sreda, maj 8, 2024 5:21:33 PM
*Za:* EMC-PSTC@LISTSERV.IEEE.ORG 
*Zadeva:* Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

Hi Bostjan,

Thanks for your feedback, but...

I am slowly and carefully reading 62368-1 for the first time.
It defines 'external circuit' in 3.3.1.1 as "electrical circuit that is
external to the equipment and is not mains".
I assumed one device = one equipment so I thought laptop is an
equipment. After your post I checked how equipment is defined in 62368-1
but in 3.3 there is no equipment definition so I don't know what is
equipment.
May be USB device (pendrive) connected without cable to laptop can be
assumed being its part, or even device powered by USB (mouse, keyboard)
can be assumed being its part, but USB can be used to connect other
equipment, I think. Do laser printer being powered separately from mains
connected to laptop is understood as being internal part of equipment?
Laptop is probably manufactured by someone else than laser printer. They
can't assume they manufacture single equipment, I think.
In past I have read about USB being used to connect active wifi antenna
located on the roof (with few hubs to extend connection length). Having
all that in mind it is hard for me to accept that for 62368-1 USB is
equipment internal circuit.

Now.
If we assume laptop with connected to it mouse, external keyboard and
printer is one equipment then going to my field: do the access control
controller with RFID readers connected to it by RS485 is also one
equipment (all powered from one 12V supply, and located in one building)
making RS485 connection being internal equipment circuit?
I don't think so.

And I repeat my main question regarding 5.4.11: Do the access controller
permanently connected to 12V supply that is permanently connected to
mains is permanently connected equipment? I think yes. Even 12V supply
has isolation in it.
If I change understanding of equipment and assume that controller + 12V
supply are one equipment than thinks get easier - such understood
equipment is permanently connected. But is it one equipment if
controller is manufactured by someone other then 12V supply.

Best regards
Piotr Galka

W dniu 2024-05-07 o 19:49, Boštjan Glavič pisze:
> Hi Piotr
>
> USB circuit is internal circuit. There are no transients expected on 
USB. Clause 5.4.11 is not applicable for power supply with USB output.

>
> Paired conductor is a telecommunication network that we had in old 
times (analogue network, ISDN,...).

>
> I hope this helps. If you need more info, you can contact me.
>
> Best regards,
> Boštjan
>
>
>
> -Original Message-
> From: Piotr Galka 
> Sent: Tuesday, May 7, 2024 5:40 PM
> To: EMC-PSTC@LISTSERV.IEEE.ORG
> Subject: [PSES] IEC 62368-1: To understand chapter 5.4.11
>
> CAUTION: This email originated from outside of our organisation. Do 
not click links or open attachments unless you recognise the sender 
and know the content is safe.

>
>
> Trying to understand 62368-1...
>
> I have got laptop with type A power supply so it looks being not 
excluded from 5.4.11 by rules in 5.4.11.1.

> For me USB are external circuits indicated in Table 14, ID numbers 1 and
> 2 (I think USB is 'Paired conductor', but even not it certainly is 
'Any other conductors').
> The note in Table 14 about not taking into account transi

Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-08 Thread Piotr Galka
Piotr

USB circuit is internal circuit. There are no transients expected on 
USB. Clause 5.4.11 is not applicable for power supply with USB output.


Paired conductor is a telecommunication network that we had in old 
times (analogue network, ISDN,...).


I hope this helps. If you need more info, you can contact me.

Best regards,
Boštjan



-Original Message-
From: Piotr Galka 
Sent: Tuesday, May 7, 2024 5:40 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] IEC 62368-1: To understand chapter 5.4.11

CAUTION: This email originated from outside of our organisation. Do 
not click links or open attachments unless you recognise the sender 
and know the content is safe.



Trying to understand 62368-1...

I have got laptop with type A power supply so it looks being not 
excluded from 5.4.11 by rules in 5.4.11.1.
For me USB are external circuits indicated in Table 14, ID numbers 1 
and
2 (I think USB is 'Paired conductor', but even not it certainly is 
'Any other conductors').
The note in Table 14 about not taking into account transients for 
external circuits installed wholly within the same building is only 
about transients so I think it doesn't make USB being not indicated 
in table.
USB cable can be used to connect laptop to printer and in printer 
USB can be earthed, I think.
Dos this means that according to first sentence of 5.4.11.2 each USB 
port in this laptop should be separated from its other USB ports?

I don't believe there is such requirement.

My real problem to understand is as follows:
Typical access controller have several not separated from each other 
inputs (several RFID reader inputs, door state control input, tamper 
inputs and others).

I need to understand if the access controller powered from (external to
it) 12V DC buffered (= having accu in it) supply is permanently 
connected equipment or not?
To disconnect it from 12V supply you need tools, to disconnect 12V 
supply from mains you need tools, but 12V supply has isolation in it 
so access controller is not electrically connected to mains and 
3.3.3.4 says about needing tools to disconnect from mains (if 
something is not connected than tools are not needed to make it 
being disconnected, I think).
Being permanently connected equipment is the easiest way for 
controller to be excluded from 5.4.11.
But if it is not permanently connected than its inputs are in the 
same situation as laptop USB ports I described first as more common 
to everyone.


What I miss or wrongly understand?

Regards
Piotr Galka

P.S.
Last month free time I spend browsing about 2800 EMC-PSTC posts 
collected by my mail program for few years.


-

This message is from the IEEE Product Safety Engineering Society 
emc-pstc discussion list. To post a message to the list, send your 
e-mail to EMC-PSTC@LISTSERV.IEEE.ORG


All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website: https://ewh.ieee.org/soc/pses/
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how 
to unsubscribe) List rules: 
https://ewh.ieee.org/soc/pses/listrules.html


For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher: 
_
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC=1


-

This message is from the IEEE Product Safety Engineering Society 
emc-pstc discussion list. To post a message to the list, send your 
e-mail to EMC-PSTC@LISTSERV.IEEE.ORG


All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website: https://ewh.ieee.org/soc/pses/
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how 
to unsubscribe)

List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher: 
_
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC=1


-

This message is from the IEEE Product Safety Engineering Society 
emc-pstc discussion list. To post a message to the list, send your 
e-mail to EMC-PSTC@LISTSERV.IEEE.ORG


All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website: https://ewh.ieee.org/soc/pses/
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how 
to unsubscribe)

List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail t

Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-08 Thread Boštjan Glavič
Hi Piotr

If circuit does not go out of building it is not considered as circuit with 
transients. I think you should check other standard like IEC 62151 and IEC 
62102 which clasify external circuits.

>From my experiences, and I do have quite some, USB is not considered as 
>external circuit in the sense of clause, where requirements between external 
>circuit and PE are specified.

Did you also check 62368-2?

Best regards
Bostjan





Poslano iz Outlook za Android<https://aka.ms/AAb9ysg>


Od: Piotr Galka 
Poslano: sreda, maj 8, 2024 5:21:33 PM
Za: EMC-PSTC@LISTSERV.IEEE.ORG 
Zadeva: Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

Hi Bostjan,

Thanks for your feedback, but...

I am slowly and carefully reading 62368-1 for the first time.
It defines 'external circuit' in 3.3.1.1 as "electrical circuit that is
external to the equipment and is not mains".
I assumed one device = one equipment so I thought laptop is an
equipment. After your post I checked how equipment is defined in 62368-1
but in 3.3 there is no equipment definition so I don't know what is
equipment.
May be USB device (pendrive) connected without cable to laptop can be
assumed being its part, or even device powered by USB (mouse, keyboard)
can be assumed being its part, but USB can be used to connect other
equipment, I think. Do laser printer being powered separately from mains
connected to laptop is understood as being internal part of equipment?
Laptop is probably manufactured by someone else than laser printer. They
can't assume they manufacture single equipment, I think.
In past I have read about USB being used to connect active wifi antenna
located on the roof (with few hubs to extend connection length). Having
all that in mind it is hard for me to accept that for 62368-1 USB is
equipment internal circuit.

Now.
If we assume laptop with connected to it mouse, external keyboard and
printer is one equipment then going to my field: do the access control
controller with RFID readers connected to it by RS485 is also one
equipment (all powered from one 12V supply, and located in one building)
making RS485 connection being internal equipment circuit?
I don't think so.

And I repeat my main question regarding 5.4.11: Do the access controller
permanently connected to 12V supply that is permanently connected to
mains is permanently connected equipment? I think yes. Even 12V supply
has isolation in it.
If I change understanding of equipment and assume that controller + 12V
supply are one equipment than thinks get easier - such understood
equipment is permanently connected. But is it one equipment if
controller is manufactured by someone other then 12V supply.

Best regards
Piotr Galka

W dniu 2024-05-07 o 19:49, Boštjan Glavič pisze:
> Hi Piotr
>
> USB circuit is internal circuit. There are no transients expected on USB. 
> Clause 5.4.11 is not applicable for power supply with USB output.
>
> Paired conductor is a telecommunication network that we had in old times 
> (analogue network, ISDN,...).
>
> I hope this helps. If you need more info, you can contact me.
>
> Best regards,
> Boštjan
>
>
>
> -Original Message-
> From: Piotr Galka 
> Sent: Tuesday, May 7, 2024 5:40 PM
> To: EMC-PSTC@LISTSERV.IEEE.ORG
> Subject: [PSES] IEC 62368-1: To understand chapter 5.4.11
>
> CAUTION: This email originated from outside of our organisation. Do not click 
> links or open attachments unless you recognise the sender and know the 
> content is safe.
>
>
> Trying to understand 62368-1...
>
> I have got laptop with type A power supply so it looks being not excluded 
> from 5.4.11 by rules in 5.4.11.1.
> For me USB are external circuits indicated in Table 14, ID numbers 1 and
> 2 (I think USB is 'Paired conductor', but even not it certainly is 'Any other 
> conductors').
> The note in Table 14 about not taking into account transients for external 
> circuits installed wholly within the same building is only about transients 
> so I think it doesn't make USB being not indicated in table.
> USB cable can be used to connect laptop to printer and in printer USB can be 
> earthed, I think.
> Dos this means that according to first sentence of 5.4.11.2 each USB port in 
> this laptop should be separated from its other USB ports?
> I don't believe there is such requirement.
>
> My real problem to understand is as follows:
> Typical access controller have several not separated from each other inputs 
> (several RFID reader inputs, door state control input, tamper inputs and 
> others).
> I need to understand if the access controller powered from (external to
> it) 12V DC buffered (= having accu in it) supply is permanently connected 
> equipment or not?
> To disconnect it from 12V supply you need tools, to disconnect 12V supply 
> from mains 

Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-08 Thread John Woodgate
To fully understand IEC 62368-1, you also need to read IEC 62368-2. It 
includes a long explanatory text about 5.4.11. The committee realised 
that it was not practicable to put all the explanations into the same 
document as the requirements. The circuits feeding the USB connectors of 
a device are internal circuits. But are you actually using USB or are 
you mentioning it as an example? For your access controller connected to 
a 12V supply that is permanently connected to mains, the isolated 
low-voltage circuits in the 12 V supply equipment are internal circuits 
and are not subject to transients. Anything connected to the 12 V DC 
supply is ES1.


On 2024-05-08 16:21, Piotr Galka wrote:

Hi Bostjan,

Thanks for your feedback, but...

I am slowly and carefully reading 62368-1 for the first time.
It defines 'external circuit' in 3.3.1.1 as "electrical circuit that 
is external to the equipment and is not mains".
I assumed one device = one equipment so I thought laptop is an 
equipment. After your post I checked how equipment is defined in 
62368-1 but in 3.3 there is no equipment definition so I don't know 
what is equipment.
May be USB device (pendrive) connected without cable to laptop can be 
assumed being its part, or even device powered by USB (mouse, 
keyboard) can be assumed being its part, but USB can be used to 
connect other equipment, I think. Do laser printer being powered 
separately from mains connected to laptop is understood as being 
internal part of equipment? Laptop is probably manufactured by someone 
else than laser printer. They can't assume they manufacture single 
equipment, I think.
In past I have read about USB being used to connect active wifi 
antenna located on the roof (with few hubs to extend connection 
length). Having all that in mind it is hard for me to accept that for 
62368-1 USB is equipment internal circuit.


Now.
If we assume laptop with connected to it mouse, external keyboard and 
printer is one equipment then going to my field: do the access control 
controller with RFID readers connected to it by RS485 is also one 
equipment (all powered from one 12V supply, and located in one 
building) making RS485 connection being internal equipment circuit?

I don't think so.

And I repeat my main question regarding 5.4.11: Do the access 
controller permanently connected to 12V supply that is permanently 
connected to mains is permanently connected equipment? I think yes. 
Even 12V supply has isolation in it.
If I change understanding of equipment and assume that controller + 
12V supply are one equipment than thinks get easier - such understood 
equipment is permanently connected. But is it one equipment if 
controller is manufactured by someone other then 12V supply.


Best regards
Piotr Galka

W dniu 2024-05-07 o 19:49, Boštjan Glavič pisze:

Hi Piotr

USB circuit is internal circuit. There are no transients expected on 
USB. Clause 5.4.11 is not applicable for power supply with USB output.


Paired conductor is a telecommunication network that we had in old 
times (analogue network, ISDN,...).


I hope this helps. If you need more info, you can contact me.

Best regards,
Boštjan



-Original Message-
From: Piotr Galka 
Sent: Tuesday, May 7, 2024 5:40 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] IEC 62368-1: To understand chapter 5.4.11

CAUTION: This email originated from outside of our organisation. Do 
not click links or open attachments unless you recognise the sender 
and know the content is safe.



Trying to understand 62368-1...

I have got laptop with type A power supply so it looks being not 
excluded from 5.4.11 by rules in 5.4.11.1.

For me USB are external circuits indicated in Table 14, ID numbers 1 and
2 (I think USB is 'Paired conductor', but even not it certainly is 
'Any other conductors').
The note in Table 14 about not taking into account transients for 
external circuits installed wholly within the same building is only 
about transients so I think it doesn't make USB being not indicated 
in table.
USB cable can be used to connect laptop to printer and in printer USB 
can be earthed, I think.
Dos this means that according to first sentence of 5.4.11.2 each USB 
port in this laptop should be separated from its other USB ports?

I don't believe there is such requirement.

My real problem to understand is as follows:
Typical access controller have several not separated from each other 
inputs (several RFID reader inputs, door state control input, tamper 
inputs and others).

I need to understand if the access controller powered from (external to
it) 12V DC buffered (= having accu in it) supply is permanently 
connected equipment or not?
To disconnect it from 12V supply you need tools, to disconnect 12V 
supply from mains you need tools, but 12V supply has isolation in it 
so access controller is not electrically connected to mains and 
3.3.3.4 says about needing tools to disconnect from mains (if 
something is not connected 

Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-08 Thread Piotr Galka

Hi Bostjan,

Thanks for your feedback, but...

I am slowly and carefully reading 62368-1 for the first time.
It defines 'external circuit' in 3.3.1.1 as "electrical circuit that is 
external to the equipment and is not mains".
I assumed one device = one equipment so I thought laptop is an 
equipment. After your post I checked how equipment is defined in 62368-1 
but in 3.3 there is no equipment definition so I don't know what is 
equipment.
May be USB device (pendrive) connected without cable to laptop can be 
assumed being its part, or even device powered by USB (mouse, keyboard) 
can be assumed being its part, but USB can be used to connect other 
equipment, I think. Do laser printer being powered separately from mains 
connected to laptop is understood as being internal part of equipment? 
Laptop is probably manufactured by someone else than laser printer. They 
can't assume they manufacture single equipment, I think.
In past I have read about USB being used to connect active wifi antenna 
located on the roof (with few hubs to extend connection length). Having 
all that in mind it is hard for me to accept that for 62368-1 USB is 
equipment internal circuit.


Now.
If we assume laptop with connected to it mouse, external keyboard and 
printer is one equipment then going to my field: do the access control 
controller with RFID readers connected to it by RS485 is also one 
equipment (all powered from one 12V supply, and located in one building) 
making RS485 connection being internal equipment circuit?

I don't think so.

And I repeat my main question regarding 5.4.11: Do the access controller 
permanently connected to 12V supply that is permanently connected to 
mains is permanently connected equipment? I think yes. Even 12V supply 
has isolation in it.
If I change understanding of equipment and assume that controller + 12V 
supply are one equipment than thinks get easier - such understood 
equipment is permanently connected. But is it one equipment if 
controller is manufactured by someone other then 12V supply.


Best regards
Piotr Galka

W dniu 2024-05-07 o 19:49, Boštjan Glavič pisze:

Hi Piotr

USB circuit is internal circuit. There are no transients expected on USB. 
Clause 5.4.11 is not applicable for power supply with USB output.

Paired conductor is a telecommunication network that we had in old times 
(analogue network, ISDN,...).

I hope this helps. If you need more info, you can contact me.

Best regards,
Boštjan



-Original Message-
From: Piotr Galka 
Sent: Tuesday, May 7, 2024 5:40 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] IEC 62368-1: To understand chapter 5.4.11

CAUTION: This email originated from outside of our organisation. Do not click 
links or open attachments unless you recognise the sender and know the content 
is safe.


Trying to understand 62368-1...

I have got laptop with type A power supply so it looks being not excluded from 
5.4.11 by rules in 5.4.11.1.
For me USB are external circuits indicated in Table 14, ID numbers 1 and
2 (I think USB is 'Paired conductor', but even not it certainly is 'Any other 
conductors').
The note in Table 14 about not taking into account transients for external 
circuits installed wholly within the same building is only about transients so 
I think it doesn't make USB being not indicated in table.
USB cable can be used to connect laptop to printer and in printer USB can be 
earthed, I think.
Dos this means that according to first sentence of 5.4.11.2 each USB port in 
this laptop should be separated from its other USB ports?
I don't believe there is such requirement.

My real problem to understand is as follows:
Typical access controller have several not separated from each other inputs 
(several RFID reader inputs, door state control input, tamper inputs and 
others).
I need to understand if the access controller powered from (external to
it) 12V DC buffered (= having accu in it) supply is permanently connected 
equipment or not?
To disconnect it from 12V supply you need tools, to disconnect 12V supply from 
mains you need tools, but 12V supply has isolation in it so access controller 
is not electrically connected to mains and 3.3.3.4 says about needing tools to 
disconnect from mains (if something is not connected than tools are not needed 
to make it being disconnected, I think).
Being permanently connected equipment is the easiest way for controller to be 
excluded from 5.4.11.
But if it is not permanently connected than its inputs are in the same 
situation as laptop USB ports I described first as more common to everyone.

What I miss or wrongly understand?

Regards
Piotr Galka

P.S.
Last month free time I spend browsing about 2800 EMC-PSTC posts collected by my 
mail program for few years.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to

Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-07 Thread Boštjan Glavič
Hi Piotr

USB circuit is internal circuit. There are no transients expected on USB. 
Clause 5.4.11 is not applicable for power supply with USB output.

Paired conductor is a telecommunication network that we had in old times 
(analogue network, ISDN,...).

I hope this helps. If you need more info, you can contact me.

Best regards,
Boštjan



-Original Message-
From: Piotr Galka  
Sent: Tuesday, May 7, 2024 5:40 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] IEC 62368-1: To understand chapter 5.4.11

CAUTION: This email originated from outside of our organisation. Do not click 
links or open attachments unless you recognise the sender and know the content 
is safe.


Trying to understand 62368-1...

I have got laptop with type A power supply so it looks being not excluded from 
5.4.11 by rules in 5.4.11.1.
For me USB are external circuits indicated in Table 14, ID numbers 1 and
2 (I think USB is 'Paired conductor', but even not it certainly is 'Any other 
conductors').
The note in Table 14 about not taking into account transients for external 
circuits installed wholly within the same building is only about transients so 
I think it doesn't make USB being not indicated in table.
USB cable can be used to connect laptop to printer and in printer USB can be 
earthed, I think.
Dos this means that according to first sentence of 5.4.11.2 each USB port in 
this laptop should be separated from its other USB ports?
I don't believe there is such requirement.

My real problem to understand is as follows:
Typical access controller have several not separated from each other inputs 
(several RFID reader inputs, door state control input, tamper inputs and 
others).
I need to understand if the access controller powered from (external to
it) 12V DC buffered (= having accu in it) supply is permanently connected 
equipment or not?
To disconnect it from 12V supply you need tools, to disconnect 12V supply from 
mains you need tools, but 12V supply has isolation in it so access controller 
is not electrically connected to mains and 3.3.3.4 says about needing tools to 
disconnect from mains (if something is not connected than tools are not needed 
to make it being disconnected, I think).
Being permanently connected equipment is the easiest way for controller to be 
excluded from 5.4.11.
But if it is not permanently connected than its inputs are in the same 
situation as laptop USB ports I described first as more common to everyone.

What I miss or wrongly understand?

Regards
Piotr Galka

P.S.
Last month free time I spend browsing about 2800 EMC-PSTC posts collected by my 
mail program for few years.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe) List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  
_
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC=1

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  
_
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC=1


[PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-07 Thread Piotr Galka

Trying to understand 62368-1...

I have got laptop with type A power supply so it looks being not 
excluded from 5.4.11 by rules in 5.4.11.1.
For me USB are external circuits indicated in Table 14, ID numbers 1 and 
2 (I think USB is 'Paired conductor', but even not it certainly is 'Any 
other conductors').
The note in Table 14 about not taking into account transients for 
external circuits installed wholly within the same building is only 
about transients so I think it doesn't make USB being not indicated in 
table.
USB cable can be used to connect laptop to printer and in printer USB 
can be earthed, I think.
Dos this means that according to first sentence of 5.4.11.2 each USB 
port in this laptop should be separated from its other USB ports?

I don't believe there is such requirement.

My real problem to understand is as follows:
Typical access controller have several not separated from each other 
inputs (several RFID reader inputs, door state control input, tamper 
inputs and others).
I need to understand if the access controller powered from (external to 
it) 12V DC buffered (= having accu in it) supply is permanently 
connected equipment or not?
To disconnect it from 12V supply you need tools, to disconnect 12V 
supply from mains you need tools, but 12V supply has isolation in it so 
access controller is not electrically connected to mains and 3.3.3.4 
says about needing tools to disconnect from mains (if something is not 
connected than tools are not needed to make it being disconnected, I think).
Being permanently connected equipment is the easiest way for controller 
to be excluded from 5.4.11.
But if it is not permanently connected than its inputs are in the same 
situation as laptop USB ports I described first as more common to everyone.


What I miss or wrongly understand?

Regards
Piotr Galka

P.S.
Last month free time I spend browsing about 2800 EMC-PSTC posts 
collected by my mail program for few years.


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  
_
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC=1