APC UPS Trip Lite - usb device keeps disconnecting
Gentlemen, I have recently purchased a small APC UPS unit for my office server. We have power outages from time to time that can last a couple of hours ( Mexico City ). I would like to setup apcupsd to automatically shutdown the server when there is a power outage. Upon connecting the UPS with a USB cable to the server I get this message : ugen1.2: Tripp Lite at usbus1 uhid1: Tripp Lite Tripp Lite UPS, class 0/0, rev 1.10/0.07, addr 2 on usbus1 And then about 20 seconds later : ugen1.2: Tripp Lite at usbus1 (disconnected) uhid1: at uhub1, port 2, addr 2 (disconnected) 20 seconds after that : ugen1.2: Tripp Lite at usbus1 uhid1: Tripp Lite Tripp Lite UPS, class 0/0, rev 1.10/0.07, addr 2 on usbus1 Another 20 seconds : ugen1.2: Tripp Lite at usbus1 (disconnected) uhid1: at uhub1, port 2, addr 2 (disconnected) So on and so forth forever. I'm using 8.2-STABLE. I cvsupd, builttheworld, installedtheworld and all that in hopes that would solve the problem. But unfortunately it did not. I was unable to find a similar situation in Google. Any help would be very appreciated. Thank you! - Jose from Mexico ___ freebsd-questions@freebsd.org mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org
Re: APC UPS Trip Lite - usb device keeps disconnecting
On Wed, Feb 8, 2012 at 9:29 AM, jbiskofski jbiskof...@gmail.com wrote: And then about 20 seconds later : ugen1.2: Tripp Lite at usbus1 (disconnected) uhid1: at uhub1, port 2, addr 2 (disconnected) 20 seconds after that : ugen1.2: Tripp Lite at usbus1 uhid1: Tripp Lite Tripp Lite UPS, class 0/0, rev 1.10/0.07, addr 2 on usbus1 I have a TrippLite UPS that does this too -- it seems to stop disconnecting once the monitoring software runs and connects to the device. I personally use Network UPS Tools for monitoring, but it was a bit more complicated to set up than when I used apcupsd back when I had an APC-branded UPS. Hope this helps, Matt Mullins ___ freebsd-questions@freebsd.org mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org
Re: using nut-ups with apc UPS on USB
I still have one server running 5.X release. 5.X also should automatically generate the devs. Do you have support for usb in your kernel? If you do have usb compiled in your kernel, check your dmesg that the usb devices are properly being identified. -Derek At 07:27 PM 3/27/2007, Michael P. Soulier wrote: On 27/03/07 Derek Ragona said: Which FreeBSD version are you running? In 6.X the devs are created automatically on bootup. In earlier versions you may need to make it. Look at the Makefile in /dev for the correct make option. I'm running 5-STABLE. I don't see a Makefile in /dev. Mike -- This message has been scanned for viruses and dangerous content by MailScanner, and is believed to be clean. MailScanner thanks transtec Computers for their support. ___ freebsd-questions@freebsd.org mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
Re: using nut-ups with apc UPS on USB
On 28/03/07 Derek Ragona said: I still have one server running 5.X release. 5.X also should automatically generate the devs. Do you have support for usb in your kernel? If you do have usb compiled in your kernel, check your dmesg that the usb devices are properly being identified. It's there. ugen0: APC Back-UPS ES 500 FW:824.B1.D USB FW:B1, rev 1.10/1.06, addr 2 [EMAIL PROTECTED] ~]# usbdevs addr 1: OHCI root hub, SiS addr 2: Back-UPS ES 500 FW:824.B1.D USB FW:B1, APC addr 1: OHCI root hub, SiS Hmm, seems that I have it now. [EMAIL PROTECTED] ~]# ls -l /dev/usb* crw-rw 1 root operator 240, 255 Mar 24 11:07 /dev/usb crw-rw 1 root operator 240, 0 Mar 24 11:07 /dev/usb0 crw-rw 1 root operator 240, 1 Mar 24 11:07 /dev/usb1 Mike pgp9dBRRXH3H3.pgp Description: PGP signature
Re: using nut-ups with apc UPS on USB
On 26/03/07 Derek Ragona said: I use nut-ups on a number of systems both attached to a UPS and some as network slaves. In all my systems I use UPS's that have serial interfaces and USB, but connect them via serial. If you read the docs on nut-ups you will see some drivers do support the USB's. You will need to specify the port in ups.conf typically in /usr/local/etc/nut The line would be: port = /dev/usb0 You can experiment with the port to get the right one. Nut will tell you if is can or cannot talk to the UPS. I don't seem to have a /dev/usb0 device file. Do I need to mknod it? Mike pgpDmhloIoKNX.pgp Description: PGP signature
Re: using nut-ups with apc UPS on USB
Which FreeBSD version are you running? In 6.X the devs are created automatically on bootup. In earlier versions you may need to make it. Look at the Makefile in /dev for the correct make option. -Derek At 05:39 PM 3/27/2007, Michael P. Soulier wrote: On 26/03/07 Derek Ragona said: I use nut-ups on a number of systems both attached to a UPS and some as network slaves. In all my systems I use UPS's that have serial interfaces and USB, but connect them via serial. If you read the docs on nut-ups you will see some drivers do support the USB's. You will need to specify the port in ups.conf typically in /usr/local/etc/nut The line would be: port = /dev/usb0 You can experiment with the port to get the right one. Nut will tell you if is can or cannot talk to the UPS. I don't seem to have a /dev/usb0 device file. Do I need to mknod it? Mike -- This message has been scanned for viruses and dangerous content by MailScanner, and is believed to be clean. MailScanner thanks transtec Computers for their support. ___ freebsd-questions@freebsd.org mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
Re: using nut-ups with apc UPS on USB
On 27/03/07 Derek Ragona said: Which FreeBSD version are you running? In 6.X the devs are created automatically on bootup. In earlier versions you may need to make it. Look at the Makefile in /dev for the correct make option. I'm running 5-STABLE. I don't see a Makefile in /dev. Mike pgpZUIIzjtp4l.pgp Description: PGP signature
Re: using nut-ups with apc UPS on USB
I use nut-ups on a number of systems both attached to a UPS and some as network slaves. In all my systems I use UPS's that have serial interfaces and USB, but connect them via serial. If you read the docs on nut-ups you will see some drivers do support the USB's. You will need to specify the port in ups.conf typically in /usr/local/etc/nut The line would be: port = /dev/usb0 You can experiment with the port to get the right one. Nut will tell you if is can or cannot talk to the UPS. -Derek At 09:18 PM 3/25/2007, Michael P. Soulier wrote: Hey, I'm new to using nut-ups, or any UPS monitoring software. Mainly I want some kind of reporting on power failures, and for a clean shutdown in the event of a prolonged outage. The UPS is an APC Back-UPS ES 500, with a USB interface. With usbd running, usbdevs shows it connected. [EMAIL PROTECTED] ~]$ sudo usbdevs Password: addr 1: OHCI root hub, SiS addr 2: Back-UPS ES 500 FW:824.B1.D USB FW:B1, APC addr 1: OHCI root hub, SiS The syntax of upsd.conf requires a pathname for the port to talk do. What device file would this work out to? Any hints on setting this up? If nut-ups isn't the right software, I'm open to suggestions. Cheers, Mike -- Michael P. Soulier [EMAIL PROTECTED] Any intelligent fool can make things bigger and more complex... It takes a touch of genius - and a lot of courage to move in the opposite direction. --Albert Einstein ___ freebsd-questions@freebsd.org mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED] -- This message has been scanned for viruses and dangerous content by MailScanner, and is believed to be clean. MailScanner thanks transtec Computers for their support. -- This message has been scanned for viruses and dangerous content by MailScanner, and is believed to be clean. MailScanner thanks transtec Computers for their support. ___ freebsd-questions@freebsd.org mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
using nut-ups with apc UPS on USB
Hey, I'm new to using nut-ups, or any UPS monitoring software. Mainly I want some kind of reporting on power failures, and for a clean shutdown in the event of a prolonged outage. The UPS is an APC Back-UPS ES 500, with a USB interface. With usbd running, usbdevs shows it connected. [EMAIL PROTECTED] ~]$ sudo usbdevs Password: addr 1: OHCI root hub, SiS addr 2: Back-UPS ES 500 FW:824.B1.D USB FW:B1, APC addr 1: OHCI root hub, SiS The syntax of upsd.conf requires a pathname for the port to talk do. What device file would this work out to? Any hints on setting this up? If nut-ups isn't the right software, I'm open to suggestions. Cheers, Mike -- Michael P. Soulier [EMAIL PROTECTED] Any intelligent fool can make things bigger and more complex... It takes a touch of genius - and a lot of courage to move in the opposite direction. --Albert Einstein ___ freebsd-questions@freebsd.org mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
Re: using nut-ups with apc UPS on USB
On Mar 25, 2007, at 9:18 PM, Michael P. Soulier wrote: Hey, I'm new to using nut-ups, or any UPS monitoring software. Mainly I want some kind of reporting on power failures, and for a clean shutdown in the event of a prolonged outage. The UPS is an APC Back-UPS ES 500, with a USB interface. [...] Any hints on setting this up? If nut-ups isn't the right software, I'm open to suggestions. I'm not familiar with nut-ups, but I've been very happy with apcupsd (in ports/sysutils). I am using an APC Back-UPS XS 1200. -j -- Jeffrey Goldberghttp://www.goldmark.org/jeff/ ___ freebsd-questions@freebsd.org mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
APC UPS question
I'm in the market for a UPS that works with FreeBSD. Does anyone know if the APC Back-UPS Pro 280VA Just Works with FreeBSD 4-STABLE and apcupsd? As far as I can tell apcupsd support for usb on FreeBSD is not reliable, but this one's serial and affordable but I'd like to know if it works before I buy. Thanks. -- We all enter this world in the same way: naked, screaming, and soaked in blood. But if you live your life right, that kind of thing doesn't have to stop there. -- Dana Gould ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
RE: APC UPS question
I have a backups 280 and there is no serial port on it. Are you sure your looking at the right thing? In any case a 280 is barely enough to keep a PC powered much less a PC and monitor. I use mine for my DSL modem and DSL router. There's lots of SmartUPS 450 UPSs on Ebay. Find one that the seller isn't claiming that he has 'refurbished' with new batteries. Buy it and when it arrives just buy new batteries from any electrical store and give them your old ones. (since it's going to be a given that the batteries will be toasted no matter what the seller claims) APS themselves also sells refurbs off their website. Ted -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of Matt Navarre Sent: Wednesday, October 20, 2004 11:06 PM To: [EMAIL PROTECTED] Subject: APC UPS question I'm in the market for a UPS that works with FreeBSD. Does anyone know if the APC Back-UPS Pro 280VA Just Works with FreeBSD 4-STABLE and apcupsd? As far as I can tell apcupsd support for usb on FreeBSD is not reliable, but this one's serial and affordable but I'd like to know if it works before I buy. Thanks. -- We all enter this world in the same way: naked, screaming, and soaked in blood. But if you live your life right, that kind of thing doesn't have to stop there. -- Dana Gould ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED] ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
Re: APC UPS question
http://buy.apc.com/commerce/storefronts/factoryoutlet/default.asp Ted Mittelstaedt wrote: I have a backups 280 and there is no serial port on it. Are you sure your looking at the right thing? In any case a 280 is barely enough to keep a PC powered much less a PC and monitor. I use mine for my DSL modem and DSL router. There's lots of SmartUPS 450 UPSs on Ebay. Find one that the seller isn't claiming that he has 'refurbished' with new batteries. Buy it and when it arrives just buy new batteries from any electrical store and give them your old ones. (since it's going to be a given that the batteries will be toasted no matter what the seller claims) APS themselves also sells refurbs off their website. Ted -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of Matt Navarre Sent: Wednesday, October 20, 2004 11:06 PM To: [EMAIL PROTECTED] Subject: APC UPS question I'm in the market for a UPS that works with FreeBSD. Does anyone know if the APC Back-UPS Pro 280VA Just Works with FreeBSD 4-STABLE and apcupsd? As far as I can tell apcupsd support for usb on FreeBSD is not reliable, but this one's serial and affordable but I'd like to know if it works before I buy. Thanks. -- We all enter this world in the same way: naked, screaming, and soaked in blood. But if you live your life right, that kind of thing doesn't have to stop there. -- Dana Gould ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED] ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED] ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
re: APC UPS question
I have purchased a few APC Ups's from a vendor on Ebay. Wonderful to work with. a few weeks ago the UPS I purchased about 1 and a half years ago had a electrical problem and the ups failed. He sent me another unit and it arrived in just a few days. I Paid $179 for a APC Smart 1400 RM UPS. I currently have 3 servers attached to it with my various other routers and it will run for about 20 or 30 minutes. With only 1 server it will run for almost 90 minutes or so. He sends out NEW batteries with the unit's... http://search.ebay.com/_W0QQgotopageZ1QQsassZupspowerQQsosortorderZ1QQsosortpropertyZ1 already i see he has a few Net UPS 650's for $79 or a Smart UPS 700 for $100 On Wed, 20 Oct 2004 23:05:32 -0700, Matt Navarre [EMAIL PROTECTED] wrote: I'm in the market for a UPS that works with FreeBSD. Does anyone know if the APC Back-UPS Pro 280VA Just Works with FreeBSD 4-STABLE and apcupsd? As far as I can tell apcupsd support for usb on FreeBSD is not reliable, but this one's serial and affordable but I'd like to know if it works before I buy. Thanks. -- We all enter this world in the same way: naked, screaming, and soaked in blood. But if you live your life right, that kind of thing doesn't have to stop there. -- Dana Gould ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED] ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
RE: APC UPS question
Ted Mittelstaedt writes: I have a backups 280 and there is no serial port on it. Are you sure your looking at the right thing? I believe they have the BackUPS _Pro_ 280, the larger brothers (420 and 650) of which are sitting two feet behind me. Both have serial ports only. (They are 5+ years old.) Robert Huff ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
Re: APC UPS question
On Thursday 21 October 2004 07:35, Robert Huff wrote: Ted Mittelstaedt writes: I have a backups 280 and there is no serial port on it. Are you sure your looking at the right thing? I believe they have the BackUPS _Pro_ 280, the larger brothers (420 and 650) of which are sitting two feet behind me. Both have serial ports only. (They are 5+ years old.) Robert Huff Does the 650 work well with FreeBSD? I can get a refurb 650 from APC for the same price as I can find the 280. -- We all enter this world in the same way: naked, screaming, and soaked in blood. But if you live your life right, that kind of thing doesn't have to stop there. -- Dana Gould ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
RE: APC UPS question
they all use the same protocol, the difference is between the smart ups and the backups. all smartups use one protocol all backups use another. The very newest ones with usb and such might have changed this, I don't know. incidentally with the smartups you can query the ups for the amount of runtime left so you know how much life is left in the battery, the ups self-tests this periodically and you can send a command to it to do this. Very useful. Ted -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of Matt Navarre Sent: Thursday, October 21, 2004 8:52 AM To: [EMAIL PROTECTED] Cc: Robert Huff Subject: Re: APC UPS question On Thursday 21 October 2004 07:35, Robert Huff wrote: Ted Mittelstaedt writes: I have a backups 280 and there is no serial port on it. Are you sure your looking at the right thing? I believe they have the BackUPS _Pro_ 280, the larger brothers (420 and 650) of which are sitting two feet behind me. Both have serial ports only. (They are 5+ years old.) Robert Huff Does the 650 work well with FreeBSD? I can get a refurb 650 from APC for the same price as I can find the 280. -- We all enter this world in the same way: naked, screaming, and soaked in blood. But if you live your life right, that kind of thing doesn't have to stop there. -- Dana Gould ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED] ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
RE: APC UPS question
Ted Mittelstaedt writes: incidentally with the smartups you can query the ups for the amount of runtime left so you know how much life is left in the battery, the ups self-tests this periodically and you can send a command to it to do this. Very useful. That's also true for the BackUPS Pro providing you get the right cable (I used the -0095A) and the right software (PowerChute Personal Edition (Windows) or apcupsd (FreeBSD)). Robert Huff ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
Re: APC UPS question
Matt Navarre writes: I believe they have the BackUPS _Pro_ 280, the larger brothers (420 and 650) of which are sitting two feet behind me. Both have serial ports only. (They are 5+ years old.) Does the 650 work well with FreeBSD? I can get a refurb 650 from APC for the same price as I can find the 280. It worked well for many years, then died within the 3 months. It's sitting on my parts shelf in the hope I have an excuse to make a trip to Rhode Island soon. (I replaced the battery within the last year, and would like to get the electronics refurbed.) Robert Huff ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
Re: USB APC UPS support in FreeBSD
apcupsd was written for Linux and it doesn't work with USB UPS devices on FreeBSD due to the hefty differences in the USB implementation between Linux and FreeBSD. The last time I looked there weren't any USB based UPS monitoring services for FreeBSD. On Wed, 28 Jul 2004 15:02:10 +1100, [EMAIL PROTECTED] [EMAIL PROTECTED] wrote: Hello, sorry if it is wrong place to address this issue to... Could anybody port apcupsd daemon or something else on FreeBSD to support APC UPS USB connection? Or is it already done? Regards, Konstantin Nizhegorodov. ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED] ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
USB APC UPS support in FreeBSD
Hello, sorry if it is wrong place to address this issue to... Could anybody port apcupsd daemon or something else on FreeBSD to support APC UPS USB connection? Or is it already done? Regards, Konstantin Nizhegorodov. ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
APC UPS with USB ? Anybody?
Hi, I need to connect my freebsd server to APC BackUPS 500 RS. The problem is that apcupsd does not support this combination. Ports was not really helpful. So, if anybody have the patches, or any idea of how to make it working I would realy appreciate it. Thanks a lot in advance. -- With best regards, Gregory Edigarov -- profi.kharkov.uaSystems Administrator -- ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
Re: APC UPS with USB ? Anybody?
On Tue, 6 Apr 2004 11:11:03 +0300, in sentex.lists.freebsd.questions you wrote: Hi, I need to connect my freebsd server to APC BackUPS 500 RS. The problem is that apcupsd does not support this combination. Ports was not really helpful. So, if anybody have the patches, or any idea of how to make it working I would realy appreciate it. Thanks a lot in advance. We wrote a simple monitoring program that works against the RS and ES series. It doesnt do much but it will let you know when its on battery and not. You can download it off http://www.tancsa.com/apc-usb.tgz ---Mike ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
Re: APC UPS with USB ? Anybody?
That would be sufficient to create a script to monitor the power state, maybe have the script check the status again in 10 minutes and shutdown the PC if necessary. It can be done right? --- Mike Tancsa [EMAIL PROTECTED] wrote: On Tue, 6 Apr 2004 11:11:03 +0300, in sentex.lists.freebsd.questions you wrote: Hi, I need to connect my freebsd server to APC BackUPS 500 RS. The problem is that apcupsd does not support this combination. Ports was not really helpful. So, if anybody have the patches, or any idea of how to make it working I would realy appreciate it. Thanks a lot in advance. We wrote a simple monitoring program that works against the RS and ES series. It doesnt do much but it will let you know when its on battery and not. You can download it off http://www.tancsa.com/apc-usb.tgz ---Mike ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED] __ Do you Yahoo!? Yahoo! Small Business $15K Web Design Giveaway http://promotions.yahoo.com/design_giveaway/ ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
Re: APC UPS with USB ? Anybody?
At 10:48 PM 06/04/2004, Me wrote: That would be sufficient to create a script to monitor the power state, maybe have the script check the status again in 10 minutes and shutdown the PC if necessary. It can be done right? The time estimate is very inaccurate on the ES and RS units that I have used. You would have better luck shutting down based on battery strength. You can glean this info from the proc title, or process it as it gets sent to local1 via syslog. But yes, it can be done eg here is a sample power failure as it gets recorded in local1 Feb 16 13:04:33 noborders apc-upsd: Battery strength Level 49% ETTL 1 min Feb 16 13:04:34 noborders apc-upsd: Battery strength Level 48% ETTL 1 min Feb 16 13:04:34 noborders apc-upsd: Battery strength Level 47% ETTL 1 min Feb 16 13:04:35 noborders apc-upsd: Battery strength Level 46% ETTL 1 min Feb 16 13:04:57 noborders last message repeated 6 times Feb 16 13:04:57 noborders apc-upsd: Battery strength Level 45% ETTL 1 min Feb 16 13:05:19 noborders last message repeated 7 times Feb 16 13:05:20 noborders apc-upsd: Battery strength Level 44% ETTL 1 min Feb 16 13:05:24 noborders apc-upsd: Battery strength Level 43% ETTL 1 min Feb 16 13:05:24 noborders apc-upsd: Battery strength Level 43% ETTL 1 min Feb 16 13:05:24 noborders apc-upsd: Battery strength Level 42% ETTL 1 min Feb 16 13:05:25 noborders apc-upsd: Battery strength Level 41% ETTL 1 min Feb 16 13:05:49 noborders last message repeated 6 times Feb 16 13:05:53 noborders apc-upsd: Battery strength Level 40% ETTL 1 min Feb 16 13:06:05 noborders last message repeated 8 times Feb 16 13:06:05 noborders apc-upsd: Battery strength Level 39% ETTL 1 min Feb 16 13:06:06 noborders apc-upsd: Battery strength Level 38% ETTL 1 min Feb 16 13:06:06 noborders apc-upsd: Battery strength Level 37% ETTL 1 min Feb 16 13:06:11 noborders apc-upsd: Battery strength Level 37% ETTL 1 min Feb 16 13:06:14 noborders apc-upsd: Battery strength Level 36% ETTL 1 min Feb 16 13:06:41 noborders last message repeated 10 times Feb 16 13:06:45 noborders last message repeated 2 times Feb 16 13:06:45 noborders apc-upsd: Battery strength Level 35% ETTL 1 min Feb 16 13:06:46 noborders apc-upsd: Battery strength Level 34% ETTL 1 min Feb 16 13:06:46 noborders apc-upsd: Battery strength Level 33% ETTL 1 min Feb 16 13:06:47 noborders apc-upsd: Battery strength Level 32% ETTL 1 min Feb 16 13:07:08 noborders last message repeated 6 times Feb 16 13:07:08 noborders apc-upsd: Battery strength Level 31% ETTL 1 min Feb 16 13:07:19 noborders last message repeated 3 times Feb 16 13:07:20 noborders apc-upsd: Battery strength Level 30% ETTL 1 min Feb 16 13:07:20 noborders apc-upsd: Battery strength Level 30% ETTL 1 min Feb 16 13:07:20 noborders apc-upsd: Battery strength Level 29% ETTL 1 min Feb 16 13:07:21 noborders apc-upsd: Battery strength Level 28% ETTL 1 min Feb 16 13:07:22 noborders last message repeated 2 times ___ [EMAIL PROTECTED] mailing list http://lists.freebsd.org/mailman/listinfo/freebsd-questions To unsubscribe, send any mail to [EMAIL PROTECTED]
Re: APC UPS
Mark [EMAIL PROTECTED] writes: Hi, A while ago I posted that I could not get my APC UPS BK350 to work under FreeBSD 4.7R, using apcupsd. Problem was that, though apcupsd test prog sees the power go off-line, the apcupsd daemon itself does not. :( So, since I do need a solution, maybe I just need a smart UPS. I was thinking of buying the APC Smart-UPS 700VA. But before I shell out good money for that, does anyone have that one working for FreeBSD? And with apcupsd? (or other daemon). If so, I would much appreciate you telling me. :) FWIW, and I realize that's not a lot, the APC 1400RM2 does work with apcupsd. -- Dan Pelleg To Unsubscribe: send mail to [EMAIL PROTECTED] with unsubscribe freebsd-questions in the body of the message
Re: APC UPS
At 09:29 AM 2.25.2003 -0500, Dan Pelleg wrote: Mark [EMAIL PROTECTED] writes: Hi, A while ago I posted that I could not get my APC UPS BK350 to work under FreeBSD 4.7R, using apcupsd. Problem was that, though apcupsd test prog sees the power go off-line, the apcupsd daemon itself does not. :( So, since I do need a solution, maybe I just need a smart UPS. I was thinking of buying the APC Smart-UPS 700VA. But before I shell out good money for that, does anyone have that one working for FreeBSD? And with apcupsd? (or other daemon). If so, I would much appreciate you telling me. :) FWIW, and I realize that's not a lot, the APC 1400RM2 does work with apcupsd. That is a good brand and works well with apcupsd. Mine are APC Smart-UPS 1000 and 1500, but believe they employ the same eproms as the 700 Best regards, Jack L. Stone, Administrator SageOne Net http://www.sage-one.net [EMAIL PROTECTED] To Unsubscribe: send mail to [EMAIL PROTECTED] with unsubscribe freebsd-questions in the body of the message
Re: APC UPS
Mark, I have an APC 750XL smart UPS powering my server and home automation setup. I have taken to using the PowerChute software provided by APC under linux emulation, which works quite well so long as you modify the shell scripts for use on a BSD system. I haven't tried running the apcupsd daemon, though, so YMMV. Good luck, Seth Henry To Unsubscribe: send mail to [EMAIL PROTECTED] with unsubscribe freebsd-questions in the body of the message
Re: APC UPS
Hi, A while ago I posted that I could not get my APC UPS BK350 to work under FreeBSD 4.7R, using apcupsd. Problem was that, though apcupsd test prog sees the power go off-line, the apcupsd daemon itself does not. :( So, since I do need a solution, maybe I just need a smart UPS. I was thinking of buying the APC Smart-UPS 700VA. But before I shell out good money for that, does anyone have that one working for FreeBSD? And with apcupsd? (or other daemon). If so, I would much appreciate you telling me. :) Thanks, - Mark To Unsubscribe: send mail to [EMAIL PROTECTED] with unsubscribe freebsd-questions in the body of the message
Re: APC UPS
In [EMAIL PROTECTED], Mark [EMAIL PROTECTED] typed: A while ago I posted that I could not get my APC UPS BK350 to work under FreeBSD 4.7R, using apcupsd. Problem was that, though apcupsd test prog sees the power go off-line, the apcupsd daemon itself does not. :( Try nut with the 350. I've got that working with an APC 650. mike -- Mike Meyer [EMAIL PROTECTED] http://www.mired.org/consulting.html Independent WWW/Perforce/FreeBSD/Unix consultant, email for more information. To Unsubscribe: send mail to [EMAIL PROTECTED] with unsubscribe freebsd-questions in the body of the message
RE: Need help with software to run my APC UPS
I have the same UPS and I will check tonight if I have the same cable (sounds right from memory). I have one question. Actually 2.. Did you buy the cable or build it? I tried for weeks to build a cable from the plans I found on the net. In the end I bought one from APC and guess what? Worked out of the box.. Also... Do you have 2 UPS's or are you testing with one on two machines? -D :-Original Message- :From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED]] :Sent: Monday, July 15, 2002 11:23 PM :To: [EMAIL PROTECTED]; jon :Subject: Re: Need help with software to run my APC UPS : : : :did you comment out : :#ttyd0 /usr/libexec/getty std.9600 dialup off secure :or :#ttyd0 /usr/libexec/getty std.9600 dialup off secure : in /etc/ttys? this was my problem. : :Tried this and it didn't work. : :This is where I stand now: : :1. Two computers each with a APC Back-UPS Pro 650 and cable :attached (one has a 940-0095A and the other has a 940-0095B). : :2. One computer runs FreeBSD4.6 and the other runs FreeBSD4.4 : :3. *Neither* computer will work with bkpupsd or apcupsd :from the ports collection. : :A) type: bkpupsd /dev/cuaa0 :result: on one computer it starts the daemon, but won't perform : when power plug is pulled, : on the other computer it starts the daemon, but :immediately : annouces the power has failed and shuts down : :B) type: apcupsd start :result: one computer hangs, the other complains it can't :communicate : with UPS. : :Note: A guy on the apcupsd mail-list has the same exact UPS+cable :and runs FreeBSD4.6 and sent me his apcupsd.conf file. I had :the same result with it. : :4. Tried installing upsd from the ports collection on one computer :and the computer hung on booting -- isn't this one needed for :NUT to work? :(Also installed NUT, BTW.) : :5. Totally baffled at this point. : :According to apcupsd.com, one possible source of error in a :situation like this one is: : :Chosen serial port has logins enabled. You must disable logins on that :port, otherwise, the system prevents apcupsd from using it. :Normally, the :file /etc/inittab specifies the ports for which a getty :process is started. :You must disable getty for the port which you wish to use. : :I'm not sure I disabled logins for the device correctly. :Not sure what to do now. : :Important note: Several years ago one of these UPSs worked with :bkpupsd with the exact same hardware -- but after I upgraded :that very :old version of FreeBSD it won't work. : :Any ideas? : ::) : : : : : :--- : : Dr. Joseph A. Bentley : Professor of Chemistry : Dept. of Physical SciencesPhone: (662) 846-4482 : P.O. Box 3255-DSU FAX: (662) 846-4486 : Delta State UniversityE-mail: [EMAIL PROTECTED] : Cleveland, MS 38733 E-mail: [EMAIL PROTECTED] : : :It is not enough to succeed. Others must fail. : :-- Gore Vidal : :--- : : :To Unsubscribe: send mail to [EMAIL PROTECTED] :with unsubscribe freebsd-questions in the body of the message : - ATTENTION: The information in this electronic mail message is private and confidential, and only intended for the addressee. Should you receive this message by mistake, you are hereby notified that any disclosure, reproduction, distribution or use of this message is strictly prohibited. Please inform the sender by reply transmission and delete the message without copying or opening it. Messages and attachments are scanned for all viruses known. If this message contains password-protected attachments, the files have NOT been scanned for viruses by the ING mail domain. Always scan attachments before opening them. - To Unsubscribe: send mail to [EMAIL PROTECTED] with unsubscribe freebsd-questions in the body of the message
Re: Need help with software to run my APC UPS
I'm keeping the freebsd-questions on these emails in case someone needs to know this stuff, too. :) At 04:03 PM 7/15/02 -0700, you wrote: --- [EMAIL PROTECTED] wrote: did you comment out #ttyd0 /usr/libexec/getty std.9600 dialup off secure or #ttyd0 /usr/libexec/getty std.9600 dialup off secure in /etc/ttys? this was my problem. Tried this and it didn't work. This is where I stand now: 1. Two computers each with a APC Back-UPS Pro 650 and cable attached (one has a 940-0095A and the other has a 940-0095B). 2. One computer runs FreeBSD4.6 and the other runs FreeBSD4.4 3. *Neither* computer will work with bkpupsd or apcupsd from the ports collection. A) type: bkpupsd /dev/cuaa0 result: on one computer it starts the daemon, but won't perform when power plug is pulled, on the other computer it starts the daemon, but immediately annouces the power has failed and shuts down B) type: apcupsd start result: one computer hangs, the other complains it can't communicate with UPS. Note: A guy on the apcupsd mail-list has the same exact UPS+cable and runs FreeBSD4.6 and sent me his apcupsd.conf file. I had the same result with it. 4. Tried installing upsd from the ports collection on one computer and the computer hung on booting -- isn't this one needed for NUT to work? (Also installed NUT, BTW.) 5. Totally baffled at this point. According to apcupsd.com, one possible source of error in a situation like this one is: Chosen serial port has logins enabled. You must disable logins on that port, otherwise, the system prevents apcupsd from using it. Normally, the file /etc/inittab specifies the ports for which a getty process is started. You must disable getty for the port which you wish to use. I'm not sure I disabled logins for the device correctly. Not sure what to do now. Important note: Several years ago one of these UPSs worked with bkpupsd with the exact same hardware -- but after I upgraded that very old version of FreeBSD it won't work. Any ideas? :) the first suggestion i sent was to to make the changes to /etc/tty that should disable logins via serial ;) Yeah, this didn't seem to change anything. are the ports enabled in the bios? cuaa0 (serial 1 ) should be port 0x3f8-0x3ff irq 4. I checked and one computer had serial 1 disabled. So, obviously this is a problem. I tried to change it to enabled but then I had some kind of conflict. I don't really know about this stuff. The other computer has: serial port 1 3F8/IRQ4 serial port 2 2F8/IRQ3 Thanks, Joe B. --- Dr. Joseph A. Bentley Professor of Chemistry Dept. of Physical SciencesPhone: (662) 846-4482 P.O. Box 3255-DSU FAX: (662) 846-4486 Delta State UniversityE-mail: [EMAIL PROTECTED] Cleveland, MS 38733 E-mail: [EMAIL PROTECTED] It is not enough to succeed. Others must fail. -- Gore Vidal --- To Unsubscribe: send mail to [EMAIL PROTECTED] with unsubscribe freebsd-questions in the body of the message
RE: Need help with software to run my APC UPS
At 02:20 PM 7/16/02 +0200, you wrote: I have the same UPS and I will check tonight if I have the same cable (sounds right from memory). I have one question. Actually 2.. Did you buy the cable or build it? I tried for weeks to build a cable from the plans I found on the net. In the end I bought one from APC and guess what? Worked out of the box.. No, I didn't make it. The cable came with the UPS. Also... Do you have 2 UPS's or are you testing with one on two machines? Yes, I have two UPS's. One on each computer. I'm using the cables that came with each UPS. I just posted a response to a guy who figured out one problem which was that a serial port on one of the machines wasn't enabled. Thanks, Joe B. -D :-Original Message- :From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED]] :Sent: Monday, July 15, 2002 11:23 PM :To: [EMAIL PROTECTED]; jon :Subject: Re: Need help with software to run my APC UPS : : : :did you comment out : :#ttyd0 /usr/libexec/getty std.9600 dialup off secure :or :#ttyd0 /usr/libexec/getty std.9600 dialup off secure : in /etc/ttys? this was my problem. : :Tried this and it didn't work. : :This is where I stand now: : :1. Two computers each with a APC Back-UPS Pro 650 and cable :attached (one has a 940-0095A and the other has a 940-0095B). : :2. One computer runs FreeBSD4.6 and the other runs FreeBSD4.4 : :3. *Neither* computer will work with bkpupsd or apcupsd :from the ports collection. : :A) type: bkpupsd /dev/cuaa0 :result: on one computer it starts the daemon, but won't perform : when power plug is pulled, : on the other computer it starts the daemon, but :immediately : annouces the power has failed and shuts down : :B) type: apcupsd start :result: one computer hangs, the other complains it can't :communicate : with UPS. : :Note: A guy on the apcupsd mail-list has the same exact UPS+cable :and runs FreeBSD4.6 and sent me his apcupsd.conf file. I had :the same result with it. : :4. Tried installing upsd from the ports collection on one computer :and the computer hung on booting -- isn't this one needed for :NUT to work? :(Also installed NUT, BTW.) : :5. Totally baffled at this point. : :According to apcupsd.com, one possible source of error in a :situation like this one is: : :Chosen serial port has logins enabled. You must disable logins on that :port, otherwise, the system prevents apcupsd from using it. :Normally, the :file /etc/inittab specifies the ports for which a getty :process is started. :You must disable getty for the port which you wish to use. : :I'm not sure I disabled logins for the device correctly. :Not sure what to do now. : :Important note: Several years ago one of these UPSs worked with :bkpupsd with the exact same hardware -- but after I upgraded :that very :old version of FreeBSD it won't work. : :Any ideas? : ::) : : : : : :--- : : Dr. Joseph A. Bentley : Professor of Chemistry : Dept. of Physical SciencesPhone: (662) 846-4482 : P.O. Box 3255-DSU FAX: (662) 846-4486 : Delta State UniversityE-mail: [EMAIL PROTECTED] : Cleveland, MS 38733 E-mail: [EMAIL PROTECTED] : : :It is not enough to succeed. Others must fail. : :-- Gore Vidal : :--- : : :To Unsubscribe: send mail to [EMAIL PROTECTED] :with unsubscribe freebsd-questions in the body of the message : - ATTENTION: The information in this electronic mail message is private and confidential, and only intended for the addressee. Should you receive this message by mistake, you are hereby notified that any disclosure, reproduction, distribution or use of this message is strictly prohibited. Please inform the sender by reply transmission and delete the message without copying or opening it. Messages and attachments are scanned for all viruses known. If this message contains password-protected attachments, the files have NOT been scanned for viruses by the ING mail domain. Always scan attachments before opening them. - --- Dr. Joseph A. Bentley Professor of Chemistry Dept. of Physical SciencesPhone: (662) 846-4482 P.O. Box 3255-DSU FAX: (662) 846-4486 Delta State UniversityE-mail: [EMAIL PROTECTED] Cleveland, MS 38733 E-mail: [EMAIL PROTECTED] It is not enough to succeed. Others must fail. -- Gore Vidal --- To Unsubscribe: send mail to [EMAIL PROTECTED] with unsubscribe freebsd
Re: Need help with software to run my APC UPS
did you comment out #ttyd0 /usr/libexec/getty std.9600 dialup off secure or #ttyd0 /usr/libexec/getty std.9600 dialup off secure in /etc/ttys? this was my problem. Tried this and it didn't work. This is where I stand now: 1. Two computers each with a APC Back-UPS Pro 650 and cable attached (one has a 940-0095A and the other has a 940-0095B). 2. One computer runs FreeBSD4.6 and the other runs FreeBSD4.4 3. *Neither* computer will work with bkpupsd or apcupsd from the ports collection. A) type: bkpupsd /dev/cuaa0 result: on one computer it starts the daemon, but won't perform when power plug is pulled, on the other computer it starts the daemon, but immediately annouces the power has failed and shuts down B) type: apcupsd start result: one computer hangs, the other complains it can't communicate with UPS. Note: A guy on the apcupsd mail-list has the same exact UPS+cable and runs FreeBSD4.6 and sent me his apcupsd.conf file. I had the same result with it. 4. Tried installing upsd from the ports collection on one computer and the computer hung on booting -- isn't this one needed for NUT to work? (Also installed NUT, BTW.) 5. Totally baffled at this point. According to apcupsd.com, one possible source of error in a situation like this one is: Chosen serial port has logins enabled. You must disable logins on that port, otherwise, the system prevents apcupsd from using it. Normally, the file /etc/inittab specifies the ports for which a getty process is started. You must disable getty for the port which you wish to use. I'm not sure I disabled logins for the device correctly. Not sure what to do now. Important note: Several years ago one of these UPSs worked with bkpupsd with the exact same hardware -- but after I upgraded that very old version of FreeBSD it won't work. Any ideas? :) --- Dr. Joseph A. Bentley Professor of Chemistry Dept. of Physical SciencesPhone: (662) 846-4482 P.O. Box 3255-DSU FAX: (662) 846-4486 Delta State UniversityE-mail: [EMAIL PROTECTED] Cleveland, MS 38733 E-mail: [EMAIL PROTECTED] It is not enough to succeed. Others must fail. -- Gore Vidal --- To Unsubscribe: send mail to [EMAIL PROTECTED] with unsubscribe freebsd-questions in the body of the message